So far from inclusion? I imagine it's not possible to block new sub-devices adds a few minutes after inclusion as a lot only expose them at the first measurement sent... so unchecking accept new hardware will not fix this?
Temp sensors suddenly recognized as Temp+Hum
Moderator: leecollings
-
- Posts: 616
- Joined: Thursday 10 November 2016 9:30
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
- Egregius
- Posts: 2582
- Joined: Thursday 09 April 2015 12:19
- Target OS: Linux
- Domoticz version: v2024.7
- Location: Beitem, BE
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
Same story here...
I updated Domoticz on September 23th to version 4.10007.
Several weeks later, on November 17th, one of my Fibaro smoke detectors (badkamer_temp) stopped reporting temperature. When I looked in the device table a new device was added:
In my case not a huge problem, I strip of the humidity in pass2php so only the temp stays, but a very strange thing.
I think this is the relative part of my zwave xml:
I updated Domoticz on September 23th to version 4.10007.
Several weeks later, on November 17th, one of my Fibaro smoke detectors (badkamer_temp) stopped reporting temperature. When I looked in the device table a new device was added:
In my case not a huge problem, I strip of the humidity in pass2php so only the temp stays, but a very strange thing.
I think this is the relative part of my zwave xml:
Code: Select all
<CommandClass id="49" name="COMMAND_CLASS_SENSOR_MULTILEVEL" version="8" innif="true">
<Instance index="1" />
<Value type="decimal" genre="user" instance="1" index="1" label="Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="22.6" />
<Value type="decimal" genre="user" instance="1" index="5" label="Relative Humidity" units="%" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="18.8" />
<Value type="decimal" genre="user" instance="1" index="9" label="Barometric Pressure" units="kPa" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="20.4" />
</CommandClass>
- gizmocuz
- Posts: 2352
- Joined: Thursday 11 July 2013 18:59
- Target OS: Raspberry Pi / ODroid
- Domoticz version: beta
- Location: Top of the world
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
@gerardvs, well i have specifically designed it like this, so it is definitely not a flow
But, you could make an 'advanced' setting to not combine multiple sensor types in one type
Also, you are not the average user, please keep that in mind ! Most users buy (for example) a zwave temp+hum sensor, so... a temp+hum sensor
Anyways, please make a PR with a setting that , when enabled, will not combine sensors.
But, you could make an 'advanced' setting to not combine multiple sensor types in one type
Also, you are not the average user, please keep that in mind ! Most users buy (for example) a zwave temp+hum sensor, so... a temp+hum sensor
Anyways, please make a PR with a setting that , when enabled, will not combine sensors.
Quality outlives Quantity!
-
- Posts: 81
- Joined: Sunday 04 January 2015 0:01
- Target OS: Raspberry Pi / ODroid
- Domoticz version: latest-1
- Location: /dev/null
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
ok, fair enough. Thanks for the suggestion.
-
- Posts: 85
- Joined: Tuesday 06 September 2016 9:08
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Location: Sorø, DK
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
I have just deleted stuff in my zwave xml file: /home/pi/domoticz/Config/zwcfg_0x014cdf33.xml
before anything, make a backup
I searched for COMMAND_CLASS_SENSOR_MULTILEVEL and the below sensors appears that I don't have (have only Temperature) Relative humidity and CO2 level. I did this for deletion for each "faulty" sensor in my Qubino relay with DS18B20
and after deleting:
And then OpenZawe looks better, those annoying humidity and CO2 sensors are gone
before anything, make a backup
Code: Select all
cp zwcfg_0x014cdf33.xml backup_zwcfg_0x014cdf33.xml
Code: Select all
<CommandClass id="49" name="COMMAND_CLASS_SENSOR_MULTILEVEL" version="7" request_flags="1" innif="true">
<Instance index="1" endpoint="2" />
<Value type="decimal" genre="user" instance="1" index="1" label="Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="21.5" />
<Value type="decimal" genre="user" instance="1" index="5" label="Relative Humidity" units="%" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="21.5" />
<Value type="decimal" genre="user" instance="1" index="17" label="CO2 Level" units="ppm" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="24.0" />
</CommandClass>
Code: Select all
<CommandClass id="49" name="COMMAND_CLASS_SENSOR_MULTILEVEL" version="7" request_flags="1" innif="true">
<Instance index="1" endpoint="2" />
<Value type="decimal" genre="user" instance="1" index="1" label="Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="21.5" />
</CommandClass>
And then OpenZawe looks better, those annoying humidity and CO2 sensors are gone
- gizmocuz
- Posts: 2352
- Joined: Thursday 11 July 2013 18:59
- Target OS: Raspberry Pi / ODroid
- Domoticz version: beta
- Location: Top of the world
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
@bjacobse, good to see this !!... i hope in a few days it will stay the same...
Also try to power off/on the node... just in case
Also try to power off/on the node... just in case
Quality outlives Quantity!
-
- Posts: 85
- Joined: Tuesday 06 September 2016 9:08
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Location: Sorø, DK
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
Yes I will monitor and try power cycle as you propose, Thank you @gizmocuz for pointing me to this direction
BTW I have created a bug in OpenZwave, as I am unsure if this is similar for other manufactures, I have only created this as Qubino ZMNHADx Flush 1 specific bug
https://github.com/OpenZWave/open-zwave/issues/1658
-
- Posts: 46
- Joined: Wednesday 07 October 2015 0:43
- Target OS: Linux
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
I have suddenly had this problem also, with a Fibaro FGBS-222.
It was installed 11th November, and has been working flawlessly, until a month ago, in the beginning of march.
In my domoticz config folder I didn´t have a zwcfg file, so I took a backup of the ozwcache file, and I think that I also took that file and renamed to a zwcfg file, maybe that doesn´t work?
Well, now a month later, the problems started again with the same temp sensors.
So, I did as "lost" pointed out in this thread, to delete those lines in the zwcfg that are sensors that I don´t have.
Before deleting:
Efter deleting:
My ozwcache file reports this
Is this really correct? The config file seems to me that it contains veeeery much information for that node, is it that advanced?
Why does this keep happening for me?
Or have I solved it by now?
It seems to show correct values for now, but it have changed instance numbers for the sensors, so I don´t know which is which.
But I can live with that, it´s easy to check.
I tried to paste the whole "node 55" config from zwcfg, but that was too many characters for the forum.
It was installed 11th November, and has been working flawlessly, until a month ago, in the beginning of march.
In my domoticz config folder I didn´t have a zwcfg file, so I took a backup of the ozwcache file, and I think that I also took that file and renamed to a zwcfg file, maybe that doesn´t work?
Well, now a month later, the problems started again with the same temp sensors.
So, I did as "lost" pointed out in this thread, to delete those lines in the zwcfg that are sensors that I don´t have.
Before deleting:
Code: Select all
<CommandClass id="49" name="COMMAND_CLASS_SENSOR_MULTILEVEL">
<Compatibility />
<State>
<CCVersion>11</CCVersion>
<InNif>true</InNif>
<StaticRequests>1</StaticRequests>
</State>
<Instance index="1" endpoint="3" />
<Instance index="2" endpoint="4" />
<Instance index="3" endpoint="7" />
<Instance index="4" endpoint="8" />
<Instance index="5" endpoint="9" />
<Instance index="6" endpoint="10" />
<Value type="decimal" genre="user" instance="3" index="0" label="Unknown" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="12.6">
<Help></Help>
</Value>
<Value type="decimal" genre="user" instance="6" index="0" label="Unknown" units="" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="4.5">
<Help></Help>
</Value>
<Value type="decimal" genre="user" instance="1" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="11.5">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="3" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="12.0">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="4" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="2.1">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="5" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="3.4">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="6" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="2.9">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="5" index="5" label="Humidity" units="%" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="1.5">
<Help>Humidity Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="1" index="15" label="Voltage" units="V" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="10.73">
<Help>Voltage Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="2" index="15" label="Voltage" units="V" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="10.07">
<Help>Voltage Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="6" index="17" label="Carbon Dioxide" units="Ppm" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="3.2">
<Help>Carbon Dioxide Sensor Value</Help>
</Value>
<Value type="list" genre="system" instance="3" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="4" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="5" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="6" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="1" index="270" label="Voltage Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Voltage Sensor Available Units</Help>
<Item label="Volts" value="0" />
</Value>
<Value type="list" genre="system" instance="2" index="270" label="Voltage Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Voltage Sensor Available Units</Help>
<Item label="Volts" value="0" />
</Value>
</CommandClass>
Code: Select all
<CommandClass id="49" name="COMMAND_CLASS_SENSOR_MULTILEVEL">
<Compatibility />
<State>
<CCVersion>11</CCVersion>
<InNif>true</InNif>
<StaticRequests>1</StaticRequests>
</State>
<Instance index="1" endpoint="3" />
<Instance index="2" endpoint="4" />
<Instance index="3" endpoint="7" />
<Instance index="4" endpoint="8" />
<Instance index="5" endpoint="9" />
<Instance index="6" endpoint="10" />
<Value type="decimal" genre="user" instance="1" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="11.5">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="3" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="12.0">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="4" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="2.1">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="5" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="3.4">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="6" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="2" min="0" max="0" value="2.9">
<Help>Air Temperature Sensor Value</Help>
<Value type="list" genre="system" instance="3" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="4" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="5" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="6" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="1" index="270" label="Voltage Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Voltage Sensor Available Units</Help>
<Item label="Volts" value="0" />
</Value>
<Value type="list" genre="system" instance="2" index="270" label="Voltage Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Voltage Sensor Available Units</Help>
<Item label="Volts" value="0" />
</Value>
Code: Select all
<CommandClass id="49" name="COMMAND_CLASS_SENSOR_MULTILEVEL">
<Compatibility />
<State>
<CCVersion>11</CCVersion>
<InNif>true</InNif>
<StaticRequests>1</StaticRequests>
</State>
<Instance index="1" endpoint="3" />
<Instance index="2" endpoint="4" />
<Instance index="3" endpoint="8" />
<Instance index="4" endpoint="10" />
<Value type="decimal" genre="user" instance="1" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="3.0">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="3" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="6.1">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="4" index="1" label="Air Temperature" units="C" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="4.8">
<Help>Air Temperature Sensor Value</Help>
</Value>
<Value type="decimal" genre="user" instance="1" index="15" label="Voltage" units="V" read_only="true" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" value="10.71">
<Help>Voltage Sensor Value</Help>
</Value>
<Value type="list" genre="system" instance="3" index="256" label="Air Temperature Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Air Temperature Sensor Available Units</Help>
<Item label="Celsius" value="0" />
</Value>
<Value type="list" genre="system" instance="1" index="270" label="Voltage Units" units="" read_only="false" write_only="false" verify_changes="false" poll_intensity="0" min="0" max="0" vindex="0" size="1">
<Help>Voltage Sensor Available Units</Help>
<Item label="Volts" value="0" />
</Value>
</CommandClass>
Why does this keep happening for me?
Or have I solved it by now?
It seems to show correct values for now, but it have changed instance numbers for the sensors, so I don´t know which is which.
But I can live with that, it´s easy to check.
I tried to paste the whole "node 55" config from zwcfg, but that was too many characters for the forum.
-
- Posts: 1
- Joined: Wednesday 08 May 2019 16:24
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
Same problem as descibed. Worked perfect for few months. After that same problem. Missing 1 or 2 sensors. And having a temp/rv sensor. Regarding the fibaro first version of binaire switch.
-
- Posts: 14
- Joined: Tuesday 17 October 2017 9:02
- Target OS: Windows
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
Same issue here. New devices created with subtype "WTGR800" (used to be "LaCrosse TX3") on a Fibaro UBS FGBS-001 hooked up to 4 DS18B20 sensors.
My Domoticz version is 2020.1 running on Win7 and using Aeotec Z-Stick for Z-Wave connectivity.
Any tip on how to revert or should I just use the new added devices instead? From my experience, it will happen from time to time (every x months) resulting in loss of temperature readings history + messing up JSON requests with the old devices id.
My Domoticz version is 2020.1 running on Win7 and using Aeotec Z-Stick for Z-Wave connectivity.
Any tip on how to revert or should I just use the new added devices instead? From my experience, it will happen from time to time (every x months) resulting in loss of temperature readings history + messing up JSON requests with the old devices id.
-
- Posts: 46
- Joined: Wednesday 07 October 2015 0:43
- Target OS: Linux
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
This has just happened to me again.lamama1234 wrote: ↑Tuesday 01 June 2021 9:33 Same issue here. New devices created with subtype "WTGR800" (used to be "LaCrosse TX3") on a Fibaro UBS FGBS-001 hooked up to 4 DS18B20 sensors.
My Domoticz version is 2020.1 running on Win7 and using Aeotec Z-Stick for Z-Wave connectivity.
Any tip on how to revert or should I just use the new added devices instead? From my experience, it will happen from time to time (every x months) resulting in loss of temperature readings history + messing up JSON requests with the old devices id.
Did you found a solution?
-
- Posts: 14
- Joined: Tuesday 17 October 2017 9:02
- Target OS: Windows
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
There seems to be a workaround, as described here: viewtopic.php?p=264337#p264337TheeDude wrote: ↑Monday 07 June 2021 21:40This has just happened to me again.lamama1234 wrote: ↑Tuesday 01 June 2021 9:33 Same issue here. New devices created with subtype "WTGR800" (used to be "LaCrosse TX3") on a Fibaro UBS FGBS-001 hooked up to 4 DS18B20 sensors.
My Domoticz version is 2020.1 running on Win7 and using Aeotec Z-Stick for Z-Wave connectivity.
Any tip on how to revert or should I just use the new added devices instead? From my experience, it will happen from time to time (every x months) resulting in loss of temperature readings history + messing up JSON requests with the old devices id.
Did you found a solution?
I haven't tried it yet..
-
- Posts: 616
- Joined: Thursday 10 November 2016 9:30
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
Hello,
I did not dig into this for now, but one fibaro "eye" PIR did it again in July... Last time I was on OZW 1.4 and zwcfg file change did the trick. Looking at files dates in Config directory, looks this file was not updated since I first upgraded to a domoticz version that's OZW 1.6 based. Only ozwcache file looks in use now.
If someone can confirm that this last file must now have temp+hum related lines purged (while domoticz/OZW is stopped, of course) to restore temp readings?
Also, if some progress was made on the root cause of this issue & ways to avoid this in the future, please let me know!
I did not dig into this for now, but one fibaro "eye" PIR did it again in July... Last time I was on OZW 1.4 and zwcfg file change did the trick. Looking at files dates in Config directory, looks this file was not updated since I first upgraded to a domoticz version that's OZW 1.6 based. Only ozwcache file looks in use now.
If someone can confirm that this last file must now have temp+hum related lines purged (while domoticz/OZW is stopped, of course) to restore temp readings?
Also, if some progress was made on the root cause of this issue & ways to avoid this in the future, please let me know!
-
- Posts: 616
- Joined: Thursday 10 November 2016 9:30
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Temp sensors suddenly recognized as Temp+Hum
Looks changing ozwcache file (removing bad temp+hum lines + restoring original temp ; I have another same device, this helps) while domoticz service is stopped did the trick to restore temp readings. But looks a device wake-up close to controller was needed and this wake-up than hanged zwave driver, as this occurs sometimes. Before wake-up/hang, after waiting for all nodes queried message, every triggered devices (Like PIRs) reported on then off several times in a few hundred ms.
So I would not recommend it as this triggered a weird z-wave behavior, even if this looks OK now after a second domoticz restart and no more device manual wake-up.
So I would not recommend it as this triggered a weird z-wave behavior, even if this looks OK now after a second domoticz restart and no more device manual wake-up.