Smart Meter P1 actual usage Fase1, Fase2, Fase3 to Daily total KW
Knibor
- Domoticz version: Stable
I have a Smart Meter P1 that measures the actual usage of Fase1, Fase2 and Fase3 in watts
How can I convert it to Daily total KW used of each Fase?
Thanks.
Thanks.
krizzz
Re: Smart Meter P1 actual usage Fase1, Fase2, Fase3 to Daily total KW
Do you have the Smart Meter connected with the P1-Cable? If so I have the same, one device per Phase/Fase and they display the usage in watts.Knibor wrote:Hi,
Thanks.
But check your (unused) devices, you should also have three devices displaying the volts and one device showing the combiner usage in kWh. Trust me, its there.
If not, I would suggest to remove all P1 devices, remove the P1 hardware and re-add again.
gordonb3
- Domoticz version: Custom
You can't. The data is simply not there.
krizzz
What do you mean? I presume the the usage per Fase/Phase shows up as a device per Fase/Phase within your domoticz currently?gordonb3 wrote:You can't. The data is simply not there.
gordonb3
No. The only per phase data that the P1 telegram will show you is current/instantaneous use, voltage and ampere, all as integer values and thus the ampere value happens to be pretty useless. If you assume that the meter displays Ws as the Watt value, you might be able to calculate the overall usage per phase by keeping track of every meter update if it at least conforms to ESMR 5.0 and you did not limit the update rate. If you have an older meter: no chance.krizzz wrote: Wednesday 08 January 2020 22:42What do you mean? I presume the the usage per Fase/Phase shows up as a device per Fase/Phase within your domoticz currently?gordonb3 wrote:You can't. The data is simply not there.
krizzz
I don’t agree fully. At least I have the one device with the total kWh consumption. You should have it to after adding P1 hardware.
And you are right about the three devices per Fase. These only show the usage at that moment and not for that day/week.
- FireWizard
Knibor wrote:
It is possible, but I wonder what to goal is, that you want to know these values.
If the goal is, that you want to charge other persons for the power consumption on a specific phase, I recommend to use a separate kWh meter, as these are more accurate and are calibrated.
If it is just for fun or curiosity you can create a virtual "Electricity" sensor for each phase. (Electric (Instant + Counter)).
Keep in mind the following:
krizzz wrote:
ESMR 5.0 (See: https://www.netbeheernederland.nl/_uplo ... fce1f1.pdf) do provide the following sensors in Domoticz:
- Total Electricity Usage (Current usage (W), Daily usage (kWh) and Total usage (kWh), idem Return values)
- Gas usage (Daily usage and Total usage (m3)).
- Line Voltages for L1, L2 and L3, if you have a 3-phase kWh meter; in case you have a 1-phase kWh meter, you have only L1)
- Power Consumption for L1, L2 and L3, if you have a 3-phase kWh meter. (In case you have a 1-phase kWh meter, you have only L1)
- If you have solar panels, then also Power Delivery for L1, L2 and L3, if you have a 3-phase kWh meter.
If you have a Smart meter, with the protocol DSMR 4.0 or earlier (See: http://files.domoticaforum.eu/uploads/S ... l%20P1.pdf), you do not have any information about each phase (L1,L2 and L3).
As gordonb3 said:
- All values are integer values, and as the current consumption is relative low ( < 25A ) per phase the inaccuracy is too big, and that is the reason that Domoticz does not use the Current as a sensor. It is a useless value. If you need that, you have to calculate it yourself, by dividing the power by the voltage. This assumes, that you have a resistive load. (cos phi = 1)
If you have limit the meter update and therefore have reduced the sampling frequency it will reduce in theory the accuracy further. However over the long term it will not make that much difference.
As said, you can create a virtual "Electricity" sensor for each phase. (Electric (Instant + Counter)).
Create the device and in the "Utility" tab you can edit this device as below:
Click the "Radio" button for Energy read as "Computed".
It will give you a sensor as:
The next step is to create a script (e.g. dzVents) that pushes the Current Watts per phase to the newly created sensor.
The daily usage is calculated (See after: Today:) and you can replace the "old" Usage sensor with this one.
Knibor wrote:
I assume that you mean daily kWh instead of kW of each phase.I have a Smart Meter P1 that measures the actual usage of Fase1, Fase2 and Fase3 in watts
krizzz wrote:
Smart meters with the protocol DSMR 4. 2 (See: https://www.netbeheernederland.nl/_uplo ... e3cc38.pdf) andDo you have the Smart Meter connected with the P1-Cable? If so I have the same, one device per Phase/Fase and they display the usage in watts.
As gordonb3 said:The only per phase data that the P1 telegram will show you is current/instantaneous use, voltage and ampere, all as integer values and thus the ampere value happens to be pretty useless. If you assume that the meter displays Ws as the Watt value, you might be able to calculate the overall usage per phase by keeping track of every meter update if it at least conforms to ESMR 5.0 and you did not limit the update rate. If you have an older meter: no chance.
- waaren
Hi, can you test this one. Please read the comments in the script before you start and report your findings here. ThxKnibor wrote: Wednesday 08 January 2020 16:33 I have a Smart Meter P1 that measures the actual usage of Fase1, Fase2 and Fase3 in watts
have Fun !
--[[ script to estimate energy usage per phase for a 3 phase P1 meter
Before activating the script do:
Create receiving devices as virtual device Type counter and on the utilities tab change them to
Type: Counter
Counter Divider: 1000
Value Quantity: Count
Value Units: kWh
The offset must NOT be set in this screen but if required must be entered in the settings below. Again only possible
before the first execution of the script
tested with my 1 phase P1 meter for some hours and there the delta compared to real measurement is less then 1%
but still: This is not a real measurement but an estimate !! and as always YMMV.
In my situation the script fires every 10 seconds. You can change this by changing the scriptTrigger to be time
based but it might have consequences for the delta between real values and estimated calculated values.
The script writes to the kwH devices max. ones per minute and this frequency can be changed by changing the.
local writeDelay variable ( higher is less frequent and v.v.
return
on =
devices =
1168, -- change to id or 'name' of your L1 device. Only one device or the script will explode !
logging =
level = domoticz.LOG_ERROR, -- set to LOG_ERROR when tested and OK
marker = 'kWh estimated values',
data =
usage =
initial =
execute = function(dz, item)
local L1 = dz.devices('Usage L1') -- change to name / ID of your L1 usage device
local L2 = dz.devices('Usage L2') -- L2 watt
local L3 = dz.devices('Usage L3') -- L3 watt
local L1C = dz.devices('L1C') -- Change to name of your virtual device for L1 kWh used. (type counter, subtype counter, X-as kWh)
local L2C = dz.devices('L2C') -- L2
local L3C = dz.devices('L3C') -- L3
local writeDelay = 60
local L1Offset = 15609 -- change to
local L2Offset = 0
local L3Offset = 0
-- No changes required below this line
local function setPersistent(deltaSeconds)
dz.log('setPersistent',dz.LOG_DEBUG)
dz.data.usage.L1Wh = dz.data.usage.L1Wh + ( L1.actualWatt * deltaSeconds / 3600 )
dz.data.usage.L2Wh = dz.data.usage.L2Wh + ( L2.actualWatt * deltaSeconds / 3600 )
dz.data.usage.L3Wh = dz.data.usage.L3Wh + ( L3.actualWatt * deltaSeconds / 3600 )
dz.data.usage.dDate = dz.time.dDate
local function resetPersistent()
dz.log('resetPersistent',dz.LOG_DEBUG)
dz.data.usage.L1Wh = 0
dz.data.usage.L2Wh = 0
dz.data.usage.L3Wh = 0
dz.data.usage.reset = dz.time.dDate
local function update_kWhDevices()
dz.log('updateCounter ' .. L1C.counter .. ' with ' .. dz.utils.round(dz.data.usage.L1Wh,3) ,dz.LOG_FORCE)
L1C.updateCounter(L1C.counter + dz.data.usage.L1Wh / 1000 )
L2C.updateCounter(L2C.counter + dz.data.usage.L2Wh / 1000 )
L3C.updateCounter(L3C.counter + dz.data.usage.L3Wh / 1000 )
local function setOffset()
if L1C.counter == 0 and L1Offset and L1Offset > 0 then L1C.setValues(0,L1Offset) end
if L2C.counter == 0 and L2Offset and L2Offset > 0 then L2C.setValues(0,L2Offset) end
if L3C.counter == 0 and L3Offset and L3Offset > 0 then L3C.setValues(0,L3Offset) end
-- initialize dz.data.usage data
if dz.data.usage.dDate == nil then
setOffset() -- Only once
resetPersistent() -- Once initially and every time the datafile ihas been removed manually
setPersistent(dz.time.dDate - dz.data.usage.dDate) -- every cycle
if dz.data.usage.reset < ( dz.time.dDate - writeDelay ) then
update_kWhDevices()
resetPersistent()
}Debian buster, bullseye on RPI-4, Intel NUC.
Knibor
Hi, thanks all for the info.
Thanks for the dzVents script.
What should I fill in at devices
devices =
Is this the P1 Smartmeter Device with IDX 3 ? or IDX 4 (P1) Power
devices =
- Schermafbeelding 2020-01-10 om 19.12.25.png (38.73 KiB) Viewed 7300 times
- Schermafbeelding 2020-01-10 om 19.11.47.png (116.08 KiB) Viewed 7300 times
Knibor
Hi, tried to run this script, no succes. What do you mean with "id or 'name of your L1 device" . I suppose that this is P1. But P1 has 3 readings L1,L2 and L3. When i use the idx = usage L1. in Watts" than I get an error log.
2020-01-12 10:27:27.507 Status: dzVents: Error (2.4.19): kWh estimated values: An error occured when calling event handler Daily use Fase1
2020-01-12 10:27:27.507 Status: dzVents: Error (2.4.19): kWh estimated values: ...cz/scripts/dzVents/generated_scripts/Daily use Fase1.lua:74: attempt to perform arithmetic on field 'actualWatt' (a nil value)
- waaren
Replace actualWatt with WhActual. They show the same but the method actualWatt was introduced in a later version of dzVents then the one you use.Knibor wrote: Sunday 12 January 2020 10:28 Hi, tried to run this script, no succes. What do you mean with "id or 'name of your L1 device" . I suppose that this is P1. But P1 has 3 readings L1,L2 and L3. When i use the idx = usage L1. in Watts" than I get an error log.
Knibor
Hi Waaren,
I've been testing this script for a few days.
Device L1C, L2C and L3C works excellent.
I can't set the devices to zero in between.
I only use the script L1Offset which I change because I want to monitor the usage per day.
Is it also possible to create a "daily use in Kwh" of L1,L2 and L3 script?
- waaren
Stop the script for a moment, delete the device and recreate it. Adjust the offset value in the script and start the script again. After a day or so you will also see a calculated day usage.Knibor wrote: Tuesday 14 January 2020 8:21 Device L1C, L2C and L3C works excellent. I can't set the devices to zero in between.
I don't understand this remark. Can you please explain?I only use the script L1 Offset which I change because I want to monitor the usage per day.
I think so using what @FireWizard described. When combined with the original script it could look likeIs it also possible to create a "daily use in Kwh" of L1,L2 and L3 script?
Create receiving L1C devices as virtual device Type counter and on the utilities tab change them to
Type: Counter
Value Units: kWh
An offset must not be set in this screen but if required must be entered in the settings below. Again only possible
as explained by @FireWizard in post https://www.domoticz.com/forum/viewtopic.php?f=59&t=30823#p233241
Create receiving L1U devices as virtual device Type (Electric (Instant + Counter)) and on the utilities tab change them to
use the 'Counted' method for Energy read
The script writes to the daily usage devices every cycle and to the kwH devices max. ones per minute and this frequency can be changed by
changing the.
return
on =
devices =
logging =
data =
usage =
initial =
local L1U = dz.devices('L1 daily use') -- change to name / ID of your L1 daily usage device
local L2U = dz.devices('L2 daily use') -- L2
local L3U = dz.devices('L3 daily use') -- L3
local L2Offset = 0
local L3Offset = 5609
dz.data.usage.L1Wh = dz.data.usage.L1Wh + ( L1.WhActual * deltaSeconds / 3600 )
dz.data.usage.L2Wh = dz.data.usage.L2Wh + ( L2.WhActual * deltaSeconds / 3600 )
dz.data.usage.L3Wh = dz.data.usage.L3Wh + ( L3.WhActual * deltaSeconds / 3600 )
local function update_UsageDevices()
if L1U then
dz.log('updateUsage' ,dz.LOG_DEBUG)
L1U.updateElectricity(L1.WhActual)
if L2U then L2U.updateElectricity(L2.WhActual) end
if L3U then L3U.updateElectricity(L3.WhActual) end
if L1C then
if L2C then L2C.updateCounter(L2C.counter + dz.data.usage.L2Wh / 1000 ) end
if L3C then L3C.updateCounter(L3C.counter + dz.data.usage.L3Wh / 1000 ) end
setOffset()
resetPersistent()
update_kWhDevices()
resetPersistent()
Knibor
Thanks for the modified script.
Yesterday I implemented the new script with the daily use.
Actual use in Watts works perfect, but I have no value in used "kWh Today"
- Schermafbeelding 2020-01-15 om 09.01.43.png (126.55 KiB) Viewed 7202 times
- waaren
Did you change the Energy read: method as described by @FireWizard ?Knibor wrote: Wednesday 15 January 2020 9:17 Actual use in Watts works perfect, but I have no value in used "kWh Today"
Knibor
Yes, the radio button is marked as Computed.
I run on stable version Domoticz V4.10717
- waaren
Not much dzVents can do about that.Knibor wrote: Wednesday 15 January 2020 15:54 Yes, the radio button is marked as Computed.
I am on a recent Beta
Knibor
O.k thanks, I'm running on Stable V4.10717, could this be the problem?
fortissimo
I'm trying this script, but after a day the values are 0.
I've just changed WhActual to actualWatt and will check the results (still 0).
The L1C (and L2C and L3C) are of the type: 'RFXMeter, RFXMeter counter' is that correct?
fortissimo
The Raspi wasn't operating anymore.
I rebooted it and Domoticz didn't start.
Tried it manually and got these errors:
I tried
and
and
All gave the same error
Those ID's are corect.2021-09-03 16:59:27.854 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 5
2021-09-03 16:59:27.854 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 6
2021-09-03 16:59:27.854 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 7
2021-09-03 16:59:27.854 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 113
2021-09-03 16:59:27.854 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 114
2021-09-03 16:59:27.855 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 115
2021-09-03 16:59:27.855 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 116
2021-09-03 16:59:27.855 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 117
2021-09-03 16:59:27.855 Error: dzVents: Error: (3.1.7) kWh estimated values: There is no device with that name or id: 118
2021-09-03 16:59:27.855 Error: dzVents: Error: (3.1.7) kWh estimated values: An error occurred when calling event handler Stroomverbruik per fase
2021-09-03 16:59:27.856 Error: dzVents: Error: (3.1.7) kWh estimated values: ...ts/dzVents/generated_scripts/Stroomverbruik per fase.lua:122: attempt to index a nil value (upvalue 'L1C')
I tried
local L1 = dz.devices('5') -- change to name / ID of your L1 usage device
local L2 = dz.devices('6') -- L2 watt
local L3 = dz.devices('7') -- L3 watt
local L1C = dz.devices('113') -- Change to name of your virtual device for L1 kWh used. (type counter, subtype counter, X-as kWh)
local L2C = dz.devices('114') -- L2
local L3C = dz.devices('115') -- L3
local L1U = dz.devices('116') -- change to name / ID of your L1 daily usage device
local L2U = dz.devices('117') -- L2
local L3U = dz.devices('118') -- L3 Code: Select all
local L1 = dz.devices(5) -- change to name / ID of your L1 usage device
local L2 = dz.devices(6) -- L2 watt
local L3 = dz.devices(7) -- L3 watt
local L1C = dz.devices(113) -- Change to name of your virtual device for L1 kWh used. (type counter, subtype counter, X-as kWh)
local L2C = dz.devices(114) -- L2
local L3C = dz.devices(115) -- L3
local L1U = dz.devices(116) -- change to name / ID of your L1 daily usage device
local L2U = dz.devices(117) -- L2
local L3U = dz.devices(118) -- L3 Code: Select all
local L1 = dz.devices('Verbruik L1 : kookplaat / oven / bg') -- change to name / ID of your L1 usage device
local L2 = dz.devices('Verbruik L2 : keuken, 1e, 2e') -- L2 watt
local L3 = dz.devices('Verbruik L3 : qkr / mk / trap / schr' ) -- L3 watt
local L1U = dz.devices('L1U') -- change to name / ID of your L1 daily usage device
local L2U = dz.devices('L2U') -- L2
local L3U = dz.devices('L3U') -- L3