Here comes my script which I thought is quite close to dannyblue's example.


Code: Select all

-- assumptions:

local BOILER_DEVICE = 'FB 41 Heizkreis Gaestebad' -- switch device
local SETPOINT_DEVICE = 'Setpoint Gaestebad' -- selector dummy device
local TEMPERATURE_SENSOR = 'Gaestebad'
local HYSTERESIS = 0.5 -- temp has to drop this value below setpoint before boiler is on again
local SMOOTH_FACTOR = 3
local LOGGING = true

return {
	on = {
		['timer'] = {
			'every minute',
		},
		devices = {
			TEMPERATURE_SENSOR,
			SETPOINT_DEVICE
		}
	},
	data = {
		temperatureReadings = { history = true, maxItems = SMOOTH_FACTOR }
	},
	active = true,
	execute = function(domoticz, device, triggerInfo)

		local avgTemp
		local temperatureReadings = domoticz.data.temperatureReadings

		-- first check if the sensor got a new reading or the setpoint was changed:
		if (triggerInfo.type == domoticz.EVENT_TYPE_DEVICE) then

			local sensor = domoticz.devices(TEMPERATURE_SENSOR)
			local setpoint =  domoticz.devices(SETPOINT_DEVICE)
			if (sensor.changed) then
				-- sensor just reported a new reading
				-- add it to the readings table

				local tcurrent = sensor.temperature
                if LOGGING then domoticz.log('tcurrent = ' .. tcurrent) end
				if (tcurrent ~= 0 and tcurrent ~= nil) then
					temperatureReadings.add(tcurrent)
					
				else
					-- no need to be here, weird state detected
					domoticz.log('Strange sensor reading.. skiping', domoticz.LOG_ERROR)
					return
				end

			elseif (setpoint.changed) then
				-- a new setpoint was set
				local scurrent = setpoint.setPoint
				if LOGGING then domoticz.log('Setpoint was set to ' .. scurrent) end
			else
				-- no business here, bail out...
				return
			end
		end

		-- now determine what to do

		local boiler = domoticz.devices(BOILER_DEVICE)
		
		if (scurrent == nil or scurrent == 0) then
			boiler.switchOff()
			return -- we're done here
		end

		
		-- determine at which temperature the boiler should be
		-- switched on
		local switchOnTemp = scurrent - HYSTERESIS

		-- don't use the current reading but average it out over
		-- the past <SMOOTH_FACTOR> readings (data smoothing) to get rid of noise, wrong readings etc
		local avgTemp = temperatureReadings.avg(1, SMOOTH_FACTOR)

		if LOGGING then
			domoticz.log('Average: ' .. avgTemp, domoticz.LOG_INFO)
			domoticz.log('Setpoint: ' .. scurrent, domoticz.LOG_INFO)
			domoticz.log('Current boiler state: ' .. boiler.state, domoticz.LOG_INFO)
			domoticz.log('Switch-on temperature: ' .. switchOnTemp, domoticz.LOG_INFO)
		end

		if (avgTemp >= scurrent and boiler.state == 'On') then
			if LOGGING then domoticz.log('Target temperature reached, boiler off') end
			boiler.switchOff()
		end

		if (avgTemp < scurrent and boiler.state == 'Off') then
			if (avgTemp < switchOnTemp) then
				if LOGGING then domoticz.log('Heating is required, boiler switched on') end
				boiler.switchOn()
			else
				if LOGGING then domoticz.log('Average temperature below setpoint but within hysteresis range, waiting for temperature to drop to ' .. switchOnTemp) end
			end
		end
	end
}
Last edited by jkimmel on Sunday 16 July 2017 9:54, edited 2 times in total.
Rfxcom
Raspi 4
dannybloe
Posts: 1355
Joined: Friday 29 August 2014 11:26
Target OS: Raspberry Pi / ODroid
Domoticz version:
Location: Ermelo
Contact:

Re: Heating control Script not switching

Post by dannybloe »

Yes, that's also fixed in the next pull request :)
Sorry again for that. This is the updated code:

Code: Select all

-- assumptions:
-- the setpoint is set by a selector dummy device where the values are numeric temperatures
-- but you can easily change it to a setpoint device

local BOILER_DEVICE = 'Boiler' -- switch device
local SETPOINT_DEVICE = 'Setpoint' -- selector dummy device
local TEMPERATURE_SENSOR = 'Temperature'
local HYSTERESIS = 0.5 -- temp has to drop this value below setpoint before boiler is on again
local SMOOTH_FACTOR = 3
local LOGGING = true

return {
	on = {
		['timer'] = {
			'every minute',
		},
		devices = {
			TEMPERATURE_SENSOR,
			SETPOINT_DEVICE
		}
	},
	data = {
		temperatureReadings = { history = true, maxItems = SMOOTH_FACTOR }
	},
	active = true,
	execute = function(domoticz, device, triggerInfo)

		local avgTemp
		local temperatureReadings = domoticz.data.temperatureReadings
		local sensor = domoticz.devices(TEMPERATURE_SENSOR)
		local current = sensor.temperature
		local boiler = domoticz.devices(BOILER_DEVICE)
		local setpoint = domoticz.devices(SETPOINT_DEVICE)

		-- first check if the sensor got a new reading or the setpoint was changed:
		if (triggerInfo.type == domoticz.EVENT_TYPE_DEVICE) then

			if (sensor.changed) then
				-- sensor just reported a new reading
				-- add it to the readings table

				if (current ~= 0 and current ~= nil) then
					temperatureReadings.add(current)
				else
					-- no need to be here, weird state detected
					domoticz.log('Strange sensor reading.. skiping', domoticz.LOG_ERROR)
					return
				end

			elseif (domoticz.devices(SETPOINT_DEVICE).changed) then
				-- a new setpoint was set
				if LOGGING then domoticz.log('Setpoint was set to ' .. device.state) end
			else
				-- no business here, bail out...
				return
			end
		end

		-- now determine what to do
		if (setpoint.state == nil or setpoint.state == 'Off') then
			boiler.switchOff()
			return -- we're done here
		end

		local setpointValue = tonumber(setpoint.state)

		-- determine at which temperature the boiler should be
		-- switched on
		local switchOnTemp = setpointValue - HYSTERESIS

		-- don't use the current reading but average it out over
		-- the past <SMOOTH_FACTOR> readings (data smoothing) to get rid of noise, wrong readings etc
		local avgTemp = temperatureReadings.avg(1, SMOOTH_FACTOR, current) -- fallback to current when history is empty

		if LOGGING then
			domoticz.log('Average: ' .. avgTemp, domoticz.LOG_INFO)
			domoticz.log('Setpoint: ' .. setpointValue, domoticz.LOG_INFO)
			domoticz.log('Current boiler state: ' .. boiler.state, domoticz.LOG_INFO)
			domoticz.log('Switch-on temperature: ' .. switchOnTemp, domoticz.LOG_INFO)
		end

		if (avgTemp >= setpointValue and boiler.state == 'On') then
			if LOGGING then domoticz.log('Target temperature reached, boiler off') end
			boiler.switchOff()
		end

		if (avgTemp < setpointValue and boiler.state == 'Off') then
			if (avgTemp < switchOnTemp) then
				if LOGGING then domoticz.log('Heating is required, boiler switched on') end
				boiler.switchOn()
			else
				if LOGGING then domoticz.log('Average temperature below setpoint but within hysteresis range, waiting for temperature to drop to ' .. switchOnTemp) end
			end
		end
	end
}
Try to find the differences ;)
Creator dzVents - RPi3, loads of zwave devices, esp8266, evohome.
jkimmel
Posts: 129
Joined: Monday 25 November 2013 17:51
Target OS: Raspberry Pi / ODroid
Domoticz version: 2021.1
Location: Mallorca
Contact:

Re: Heating control Script not switching

Post by jkimmel »

Only difference I found is about averaging. So because I didn't understand the logic behind I deleted averaging.
I also changed from dummy selector to thermostat hoping this won't spoil anything.
Anyway there still is no switching, log entries don't show up as well as debugging (using MS Edge)

Seems to me I haven't seen the differences :?

Code: Select all

local BOILER_DEVICE = 'FB 21 Heizkreis Salon' -- switch device
local SETPOINT_DEVICE = 'Setpoint Salon' -- Setpoint thermostat
local TEMPERATURE_SENSOR = 'Salon'
local HYSTERESIS = 0.5 -- temp has to drop this value below setpoint before boiler is on again
local SMOOTH_FACTOR = 3
local LOGGING = true

return {
   on = {
      ['timer'] = {
         'every minute',
      },
      devices = {
         TEMPERATURE_SENSOR,
         SETPOINT_DEVICE
      }
   },
  
   active = true,
   execute = function(domoticz, device, triggerInfo)

      local sensor = domoticz.devices(TEMPERATURE_SENSOR)
      local tcurrent --= sensor.temperature
      local boiler = domoticz.devices(BOILER_DEVICE)
      local setpoint --= domoticz.devices(SETPOINT_DEVICE)

      -- first check if the sensor got a new reading or the setpoint was changed:
      if (triggerInfo.type == domoticz.EVENT_TYPE_DEVICE) then

         if (sensor.changed) then
            -- sensor just reported a new reading
       		tcurrent = sensor.temperature
			domoticz.log('Temp was set to ' .. tcurrent)
           
         elseif (setpoint.changed) then
            -- a new setpoint was set
		scurrent = setpoint.setPoint
             domoticz.log('Setpoint was set to ' .. scurrent)
         else
            -- no business here, bail out...
            return
         end
      end

      -- now determine what to do
      if (scurrent == nil ) then
         boiler.switchOff()
         return -- we're done here
      end

      -- determine at which temperature the boiler should be
      -- switched on
      local switchOnTemp = scurrent - HYSTERESIS

     

      if LOGGING then
        
         domoticz.log('Setpoint: ' .. scurrent, domoticz.LOG_INFO)
         domoticz.log('Current boiler state: ' .. boiler.state, domoticz.LOG_INFO)
         domoticz.log('Switch-on temperature: ' .. switchOnTemp, domoticz.LOG_INFO)
      end

      if (tcurrent >= scurrent and boiler.state == 'On') then
         if LOGGING then domoticz.log('Target temperature reached, boiler off') end
         boiler.switchOff()
      end

      if (tcurrent < scurrent and boiler.state == 'Off') then
         if (tcurrent < switchOnTemp) then
            if LOGGING then domoticz.log('Heating is required, boiler switched on') end
            boiler.switchOn()
         else
            if LOGGING then domoticz.log(' temperature below setpoint but within hysteresis range, waiting for temperature to drop to ' .. switchOnTemp) end
         end
      end
   end
}
Edit:


Is this

Code: Select all

['timer'] = {
still allowed?

Obviously scurrent is nil although I used

Code: Select all

Thermostat set point[edit]
setPoint: Number.
from the Wiki, because when I change

Code: Select all

if (scurrent == nil or scurrent == 0) then
			boiler.switchOff()
to

Code: Select all

if (scurrent == nil and boiler.state == 'On' ) then
			boiler.switchOff()
there is no permanent swichOff command anymore as I realized in the log of the switches
Rfxcom
Raspi 4
jkimmel
Posts: 129
Joined: Monday 25 November 2013 17:51
Target OS: Raspberry Pi / ODroid
Domoticz version: 2021.1
Location: Mallorca
Contact:

Re: Heating control Script not switching

Post by jkimmel »

This one is switching now, tried to be closer to danyblue's example

Code: Select all

local BOILER_DEVICE = 'FB 21 Heizkreis Salon' -- switch device
local TEMPERATURE_SENSOR = 'Salon'
local RUECKLAUF_SENSOR = 'WP Ruecklauf'
local SMOOTH_FACTOR = 3
local HYSTERESIS = 0.005
local LOGGING = true

return {
	on = {
		timer = {
			'every 1 minute',
		},
		devices = {
			TEMPERATURE_SENSOR,
			}
	},
	data = {
		temperatureReadings = { history = true, maxItems = SMOOTH_FACTOR }
	},
	active = true,
	execute = function(domoticz, device, triggerInfo)
	
	  local avgTemp
      local temperatureReadings = domoticz.data.temperatureReadings
      local sensor = domoticz.devices(TEMPERATURE_SENSOR)
      local current = sensor.temperature
      local boiler = domoticz.devices(BOILER_DEVICE)
	  local ruecklauf = domoticz.devices(RUECKLAUF_SENSOR)
      -- experimenting with ruecklauf.temperature purpose avoiding wet walls
      local ruecklaufT = ruecklauf.temperature + 2
		
		-- first check if the sensor got a new reading or the setpoint was changed:
		if (triggerInfo.type == domoticz.EVENT_TYPE_DEVICE) then
		
		if (sensor.changed) then
            -- sensor just reported a new reading
            -- add it to the readings table

            if (current ~= 0 and current ~= nil) then
               temperatureReadings.add(current)
            else
               -- no need to be here, weird state detected
               domoticz.log('Strange sensor reading.. skiping', domoticz.LOG_ERROR)
               return
            end
    
		-- now determine what to do

			local dewpoint = sensor.dewPoint

		-- determine at which temperature the boiler should be
		-- switched on
		local switchOnTemp = dewpoint + HYSTERESIS

		-- don't use the current reading but average it out over
		-- the past <SMOOTH_FACTOR> readings (data smoothing) to get rid of noise, wrong readings etc
		local avgTemp = temperatureReadings.avg(1, SMOOTH_FACTOR, current)

		if LOGGING then
			domoticz.log('Average: ' .. avgTemp, domoticz.LOG_INFO)
			domoticz.log('Current boiler state: ' .. boiler.state, domoticz.LOG_INFO)
			domoticz.log('Switch-on temperature: ' .. switchOnTemp, domoticz.LOG_INFO)
			domoticz.log('Dewpoint: ' ..dewpoint, domoticz.LOG_INFO)
			
		end

		if ((avgTemp <= dewpoint or ruecklaufT <= dewpoint) and boiler.state == 'On') then
			if LOGGING then domoticz.log('Target temperature reached, boiler off') end
			boiler.switchOff()
	    
        else 
            boiler.switchOn()
            	if LOGGING then domoticz.log('Temperature to high cooling, boiler on') end
		    
				end
		end
	end
end
}
Rfxcom
Raspi 4
HvdW
Posts: 664
Joined: Sunday 01 November 2015 22:45
Target OS: Raspberry Pi / ODroid
Domoticz version: 2023.2
Location: Twente
Contact:

Re: Heating control Script not switching

Post by HvdW »

Hi,

I tried the original script from Github.
It stumbles on line 30 of the script.

I did try the script @dannybloe posted 3 posts before (Friday 14 July 2017 8:02 )

Then I changed

Code: Select all

on = {
		['timer'] = 'every minute',
		TEMPERATURE_SENSOR,
		SETPOINT_DEVICE
},
to

Code: Select all

on = {
        devices = {TEMPERATURE_SENSOR, SETPOINT_DEVICE},
        timer = {'every 10 minutes'}
    },
(don't even know if this change is necessary for dzVents 2.4)

It's running perfect now.

Code: Select all

 2019-05-13 23:27:41.651 Status: EventSystem: reset all device statuses...
2019-05-13 23:27:41.748 Status: dzVents: Info: Handling events for: "Thermostaat-setpoint", value: "20.80"
2019-05-13 23:27:41.748 Status: dzVents: Info: ------ Start internal script: Verwarming: Device: "Thermostaat-setpoint (Dummy)", Index: 184
2019-05-13 23:27:41.750 Status: dzVents: Info: Setpoint was set to 20.80
2019-05-13 23:27:41.750 Status: dzVents: Info: Average: 20.89999961853
2019-05-13 23:27:41.750 Status: dzVents: Info: Setpoint: 20.8
2019-05-13 23:27:41.750 Status: dzVents: Info: Current boiler state: On
2019-05-13 23:27:41.750 Status: dzVents: Info: Switch-on temperature: 20.3
2019-05-13 23:27:41.750 Status: dzVents: Info: Target temperature reached, boiler off
2019-05-13 23:27:41.751 Status: dzVents: Info: ------ Finished Verwarming
2019-05-13 23:27:41.752 Status: EventSystem: Script event triggered: /home/pi/domoticz/dzVents/runtime/dzVents.lua 
Thankyous and praises given hereby to @dannyblue
Last edited by HvdW on Tuesday 14 May 2019 1:41, edited 1 time in total.
Bugs bug me.
HvdW
Posts: 664
Joined: Sunday 01 November 2015 22:45
Target OS: Raspberry Pi / ODroid
Domoticz version: 2023.2
Location: Twente
Contact:

Re: Heating control Script not switching

Post by HvdW »

Hi,
Now that @dannybloe's thermostat is running fine I want to ask for some help.

I checked this project because I want to make our 20 year old Nefit Ecomline HR a 'smart' boiler.
A VPN connection from outside is established and then Domoticz is accessed.
Editing the Thermostat setpoint every time to switch on or off the boiler is a bit difficult.

How can the code be adapted or the Thermostat setpoint be changed that I can switch off the boiler easily.
A slider or some presets like 12, 14, 16, 18, 19, 20, 21, 22 would be perfect.
Bugs bug me.
rrozema
Posts: 470
Joined: Thursday 26 October 2017 13:37
Target OS: Raspberry Pi / ODroid
Domoticz version: beta
Location: Delft
Contact:

Re: Heating control Script not switching

Post by rrozema »

You have probably figured it out by now, but for anyone still looking how to make the thermostat script 'look and feel' as good as it controls your boiler: Add a dummy thermostat setpoint to your domoticz devices and use this from the script. Here are the steps:

1 - Add the 'Dummy' hardware (if you haven't got it installed yet):
Add dummy hardware & start adding a dummy device.png
Add dummy hardware & start adding a dummy device.png (81.28 KiB) Viewed 577 times
  • Click Instellingen (Setup)
  • Click Hardware
  • If your hardware list already contains the Dummy hardware, go to (2). You only need it installed once.
  • In the bottom half of the screen, enter a name for your hardware. I suggest to use 'Dummy'.
  • Behind 'Type', select "Dummy (Does nothing, use for virtual switches only)".
  • Click the Toevoegen (Add) button.
2 - Add a thermostat setpoint device
Add dummy thermostat setpoint device.png
Add dummy thermostat setpoint device.png (12.23 KiB) Viewed 577 times
  • On the hardware list, find the line for your Dummy hardware.
  • Click the button 'Maak virtuele sensoren' (Create virtual sensor). A dialog 'Create Virtual Sensor' opens.
  • In the "Naam:" (Name) field, enter a name for your setpoint device. Remember this name -exactly, including any capitals and spaces-. You'll need it in your script later on.
  • In the "Sensor Type" field, select "Thermostat Setpoint".
  • Click "OK"
3 - Use your new device in the script
Thermostat device name.png
Thermostat device name.png (3.48 KiB) Viewed 577 times
  • On the line that says "local SETPOINT_DEVICE = 'Setpoint'", change the text SetPoint into the name you entered for your virtual sensor.
  • Click the "Opslaan" (Save) button
4 - Change the temperature for your room/house
  • Click the "Overige" (Others) tab
  • Find your thermostat device (It's probably in the bottom if you haven't dragged it yet)
  • Click the flame icon
  • Enter the new value or use the up and down arrows to select one
  • Click "Instellen" (Set)