Heating finally automated using HomeEasy HE105
Moderator: leecollings
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Re: Heating finally automated using HomeEasy HE105
Latest Version of the code updated : 10/03/2015 V0.4 <- Latest version updated to support new temperature set point switch. this removes the need for lots of the code and additional switches. Enjoy
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 6
- Joined: Sunday 02 February 2014 19:13
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
Nice one.
while reading this I noticed that the HE105 looked exactly like the Boiler switch that I have in my house which is branded as a 'Horstmann HRFS1' - Like this one http://www.screwfix.com/p/horstmann-hrf ... stat/93829.
It turns out that it is the same receiver/switch unit as the HE105 and that I can also switch it with rfxmgr and have just managed to add a switch in my domoticz to control it
I have had this thermostat for years (using the seperate LCD display to control it), and never realised that the 'thermostat' tab was there in rfxmgr or that I could control it! Now I can start playing with it!
while reading this I noticed that the HE105 looked exactly like the Boiler switch that I have in my house which is branded as a 'Horstmann HRFS1' - Like this one http://www.screwfix.com/p/horstmann-hrf ... stat/93829.
It turns out that it is the same receiver/switch unit as the HE105 and that I can also switch it with rfxmgr and have just managed to add a switch in my domoticz to control it
I have had this thermostat for years (using the seperate LCD display to control it), and never realised that the 'thermostat' tab was there in rfxmgr or that I could control it! Now I can start playing with it!
-
- Posts: 1
- Joined: Thursday 07 May 2015 16:48
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
I've just implemented this script and have been having problems with the heating switching on and off too frequently. Even increasing the heatercommanddelay you then have to balance introducing artificial latency into the system so it still switches on when you want it to but doesn't switch on/off too frequently. With an aging oil fired boiler I was keen to avoid too frequent switching but to also optimise runtime to save oil consumption. As such I've made some modifications to the excellent work done by thebeetleuk. This version samples the three thermostats I have scattered around the house and takes an average but more importantly adds some hysteresis to the switching process. It takes the set point and then establishes a range either side, the lower point of which is the trigger to switch the heating on and the top point to switch the heating off. If the measured temperature is anywhere between the top and bottom it will leave the system as is (we assume that the system is either running to warm the house up towards the top threshold or cooling down towards the lower threshold). I've found that 0.5 degrees either side of the set point isn't noticeable from a comfort perspective, boiler firing times are in the 20 - 30 min range which allows the system to heat all radiators evenly around the house and because they aren't being governed by the heatercommanddelay value I can drop this value down to a couple of minutes meaning the script reacts promptly to valid changes in temperature. Hope all that makes sense. Updated to v0.4.1
Code: Select all
-----------------------------------------------------------------------------------------------
-- Heating Control
-- Version 0.4.1
-- Author - Martin Rourke
-- This library is free software: you can redistribute it and/or modify it under the terms of
-- the GNU Lesser General Public License as published by the Free Software Foundation, either
-- version 3 of the License, or (at your option) any later version. This library is distributed
-- in the hope that it will be useful, but WITHOUT ANY WARRANTY; without even the implied
-- warranty of MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE. See the GNU Lesser General
-- Public License for more details. You should have received a copy of the GNU Lesser General
-- Public License along with this library. If not, see <http://www.gnu.org/licenses/>.
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-- Setup
-----------------------------------------------------------------------------------------------
-- To use this script you need to have a few devices already setup in Domoticz
-- 1. A physical switch to operate (On/Off Switch)
-- 2. A physical temperature sensor (Temperature)
-- 3. A virtual switch to tun on and off the heating (On/Off Switch)
-- 4. A virtual switch to set the target temperature (Temperature)
-- 5. Define a User Variable as 'Debug', Integer and set to 1 or 0 to show/hide entries in the log
-----------------------------------------------------------------------------------------------
-- 1. A physical switch to operate (On/Off Switch)
-----------------------------------------------------------------------------------------------
local physicalheater = 'Heating House (Boiler)'
-----------------------------------------------------------------------------------------------
-- 2. A physical temperature sensor (Temperature)
-----------------------------------------------------------------------------------------------
local currenttemperature = 'Lounge temp'
local currenttemperature1 = 'Lounge temp'
local currenttemperature2 = 'Bedroom2'
local currenttemperature3 = 'Bedroom1'
-----------------------------------------------------------------------------------------------
-- 3. A virtual switch to tun on and off the heating (On/Off Switch)
-----------------------------------------------------------------------------------------------
local virtualheater = 'Heating House'
-----------------------------------------------------------------------------------------------
-- 4. A virtual switch to set the target temperature (Temperature)
-- Assumes you are using a dummy switch "Thermostat Setpoint" to move temperature up and down
-----------------------------------------------------------------------------------------------
local targettemperature = 'Thermostat House'
-----------------------------------------------------------------------------------------------
-- 5. UserVariable - Set debug to 1 for testing. 0 for live running.
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-- OPTIONS
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-- After this time the heating will automatically turn off as a temperature was not detected
-- from the temperature sensor. this helps protect against the heating being left on all the
-- time if the signal is lost.
-----------------------------------------------------------------------------------------------
local lostsignaltime = 3600 -- 60 minutes
-----------------------------------------------------------------------------------------------
-- Helps protect against multiple quick changes to the physical switch
-----------------------------------------------------------------------------------------------
local heatercommanddelay = 120 -- 2 minutes
-----------------------------------------------------------------------------------------------
-- Repeats the On or Off command after a set time for devices that don't have a handshake
-- Should always be bigger than heatercommanddelay
-----------------------------------------------------------------------------------------------
local heaterrepeatdelay = 300 -- 5 minutes
-----------------------------------------------------------------------------------------------
-- Defines the temperature range above and below the set point where the heating will left in
-- the current state to avoid frequent switching
-----------------------------------------------------------------------------------------------
local temprange = 0.5 -- 0.5 degrees
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-- NOTHING SHOULD NEED TO CHANGE BELOW THIS LINE
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
-----------------------------------------------------------------------------------------------
local thermostatchgnagedetected = 0
commandArray = {}
function debuglog (s)
if uservariables["Debug"] == 1 then print("DEBUG - THERMOSTAT " .. physicalheater .. s) end
return true
end
function timedifference (s)
year = string.sub(s, 1, 4)
month = string.sub(s, 6, 7)
day = string.sub(s, 9, 10)
hour = string.sub(s, 12, 13)
minutes = string.sub(s, 15, 16)
seconds = string.sub(s, 18, 19)
t1 = os.time()
t2 = os.time{year=year, month=month, day=day, hour=hour, min=minutes, sec=seconds}
difference = os.difftime (t1, t2)
return difference
end
function round(num, idp)
local mult = 10^(idp or 0)
return math.floor(num * mult + 0.5) / mult
end
-----------------------------------------------------------------------------------------------
-- Controls the heating based on the target and current temperatures
-----------------------------------------------------------------------------------------------
-- Is the heating scheduled to be on?
if (otherdevices[virtualheater]=='On') then
debuglog('Heating - Heating Is Scheduled To Be On: ' .. virtualheater )
-- what is the target temperature and the top/bottom range?
target = round(tonumber(otherdevices_svalues[targettemperature]), 1)
targethigh = (target + tonumber(temprange))
targetlow = (target - tonumber(temprange))
-- test to see if we can still see the thermostat. If not force the heating off
if ( timedifference(otherdevices_lastupdate[currenttemperature]) > lostsignaltime ) then
-- this section to handle loss of signal with thermostat and turns off boiler
debuglog('Heating - WARNING: Last seen temperature sensor: '.. currenttemperature ..' ' .. tostring(otherdevices_lastupdate[currenttemperature]))
debuglog('Heating - WARNING: Signal Lost with temperature sensor for over '.. lostsignaltime ..' seconds: '.. currenttemperature)
debuglog('Heating - WARNING: forcing Heating OFF : '.. physicalheater)
if( timedifference(otherdevices_lastupdate[physicalheater]) > heaterrepeatdelay) then -- checks to see if the command needs to be repeated
if (otherdevices[physicalheater]=='Off') then
debuglog('Heating - WARNING - Turning Physical Heater On: '.. physicalheater)
else
debuglog('Heating - WARNING - Turning Physical Heater On (Repeat Command): '.. physicalheater)
end
commandArray[physicalheater] = 'On'
else
debuglog('Heating - INFO: Not enough time has passed before issuing repeat command to switch: Only '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heaterrepeatdelay .. ' seconds')
end
-- end of section for turning off boiler if no comms with thermostat
else
-- this section runs only if we have received temp info from the stat
debuglog('Heating - Last seen temperature sensor: '.. currenttemperature ..' ' .. tostring(otherdevices_lastupdate[currenttemperature]))
-- What is the current temperature? We sample three stats and take an average and round to one DP
-- As some temperature devices also return other values as humidity this assumes the first value is the temperature in all cases
current1 = tonumber(string.gmatch(otherdevices_svalues[currenttemperature1], '([^;]+)')(1))
current2 = tonumber(string.gmatch(otherdevices_svalues[currenttemperature2], '([^;]+)')(1))
current3 = tonumber(string.gmatch(otherdevices_svalues[currenttemperature3], '([^;]+)')(1))
current = round(((current1 + current2 + current3) / 3), 1)
debuglog('Heating - Lounge temperature: ' .. tostring(current1))
debuglog('Heating - Bedroom2 temperature: ' .. tostring(current2))
debuglog('Heating - Bedroom1 temperature: ' .. tostring(current3))
debuglog('Heating - Average temperature: ' .. tostring(current))
debuglog('Heating - Target: ' .. tostring(target) .. ' Current: ' .. tostring(current))
debuglog('Heating - TargetHigh: ' .. tostring(targethigh) .. ' TargetLow: ' .. tostring(targetlow))
if( timedifference(otherdevices_lastupdate[physicalheater]) > heatercommanddelay ) then -- checks to see if the heater has been turned off recently
debuglog('Heating - Enough time has passed since last change to switch: '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heatercommanddelay .. ' seconds')
if (current < targetlow) then -- test if current temp is below target low threshold - need to turn heater on
debuglog('Heating - Current temp is below TargetLow. Turning Physical Heater On: '.. physicalheater)
if( timedifference(otherdevices_lastupdate[physicalheater]) > heaterrepeatdelay or devicechanged[remoteup] or devicechanged[remotedown] or devicechanged[virtualheater]) then -- checks to see if the command needs to be repeated
if (otherdevices[physicalheater]=='Off') then
debuglog('Heating - Current below TargetLow. Turning Physical Heater On: '.. physicalheater)
else
debuglog('Heating - Current below TargetLow. Turning Physical Heater On (Repeat Command): '.. physicalheater)
end
commandArray[physicalheater] = 'On'
else
debuglog('Heating - INFO: Not enough time has passed before issuing repeat command to switch: Only '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heaterrepeatdelay .. ' seconds')
end
else
if (current > targethigh) then -- test if current temp is above top threshold - need to turn heater off
debuglog('Heating - Current temp is above Targethigh. Turning Physical Heater Off: '.. physicalheater)
if( timedifference(otherdevices_lastupdate[physicalheater]) > heaterrepeatdelay or devicechanged[remoteup] or devicechanged[remotedown] or devicechanged[virtualheater]) then -- checks to see if the command needs to be repeated
if (otherdevices[physicalheater]=='On') then
debuglog('Heating - Current above TargetHigh. Turning Physical Heater Off: '.. physicalheater)
else
debuglog('Heating - Current above TargetHigh. Turning Physical Heater Off (Repeat Command): '.. physicalheater)
end
commandArray[physicalheater] = 'Off'
else
debuglog('Heating - INFO: Not enough time has passed before issuing repeat command to switch: Only '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heaterrepeatdelay .. ' seconds')
end
else
debuglog('Heating - Current temp between TargetHigh and Targetlow. Leaving boiler in current state') -- leave boiler either on as house warms up or off as house cools down
end
end
else
debuglog('Heating - INFO: Not enough time has passed before issuing command to switch: Only '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heatercommanddelay .. ' seconds')
end
end
else
debuglog('Heating - Turning Heating Off As Scheduled To Be Off')
if( timedifference(otherdevices_lastupdate[physicalheater]) > heatercommanddelay ) then
debuglog('Heating - Enough time has passed before issuing command to switch: '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heatercommanddelay .. ' seconds')
if( timedifference(otherdevices_lastupdate[physicalheater]) > heaterrepeatdelay or devicechanged[remoteup] or devicechanged[remotedown] or devicechanged[virtualheater]) then -- checks to see if the command needs to be repeated
if (otherdevices[physicalheater]=='On') then
debuglog('Heating - Turning Physical Heater Off: '.. physicalheater)
else
debuglog('Heating - Turning Physical Heater Off (Repeat Command): '.. physicalheater)
end
commandArray[physicalheater] = 'Off'
else
debuglog('Heating - INFO: Not enough time has passed before issuing repeat command to switch: Only '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heaterrepeatdelay .. ' seconds')
end
else
debuglog('Heating - INFO: Not enough time has passed before issuing command to switch: Only '.. timedifference(otherdevices_lastupdate[physicalheater]) .. ' seconds out of ' .. heatercommanddelay .. ' seconds')
end
end
-
- Posts: 23
- Joined: Tuesday 03 September 2013 21:33
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
Evening, could someone please explain how to enable debug for this script?
The instructions say to add a user variable but I do not know what this looks like, or where in the code to add it.
Is it simply:
And once enabled where is the debug log located?
Many thanks in advance
The instructions say to add a user variable but I do not know what this looks like, or where in the code to add it.
Is it simply:
Code: Select all
-----------------------------------------------------------------------------------------------
-- 5. UserVariable - Set debug to 1 for testing. 0 for live running.
-----------------------------------------------------------------------------------------------
debug = 1
Many thanks in advance
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Re: Heating finally automated using HomeEasy HE105
Hi Mike,
the function calls the "Debug" variable which isnt sent within the lua script itself. Its set within domoticz. From the Web interface go to Setup->More Options->User Variables. From here just create a new entry called Debug as an integer and set it to 1 to tun on the debugging.
Hope this helps!!
the function calls the "Debug" variable which isnt sent within the lua script itself. Its set within domoticz. From the Web interface go to Setup->More Options->User Variables. From here just create a new entry called Debug as an integer and set it to 1 to tun on the debugging.
Code: Select all
function debuglog (s)
if uservariables["Debug"] == 1 then print("DEBUG - THERMOSTAT " .. physicalheater .. s) end
return true
end
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 23
- Joined: Tuesday 03 September 2013 21:33
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
It does! That was the missing piece of the puzzle. Thank you for your help and script.thebeetleuk wrote:Hi Mike,
the function calls the "Debug" variable which isnt sent within the lua script itself. Its set within domoticz. From the Web interface go to Setup->More Options->User Variables. From here just create a new entry called Debug as an integer and set it to 1 to tun on the debugging.
Hope this helps!!Code: Select all
function debuglog (s) if uservariables["Debug"] == 1 then print("DEBUG - THERMOSTAT " .. physicalheater .. s) end return true end
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Re: Heating finally automated using HomeEasy HE105
Np. I'll update the notes at some point to make it clearer.
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 43
- Joined: Thursday 22 October 2015 21:15
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 2023.2
- Location: The Netherlands
- Contact:
Re: Heating finally automated using HomeEasy HE105
Hello Martin,
I used the 4.0 script and at first it could not understand why the status was not chaging.
Then I found out in the sript there is a typo which confused me
local heaterrepeatdelay = 600 -- 1 minute where 600 secs is certainly not 1 minute
So I changed the 600 to 60 and voila we have 1 minute.
My other question is how you get the yellow marked dropdown menu in the top right hand corner that says " Room ; Heating House " ?
I assume you have the dashboard devided in several pages?
Paco
I used the 4.0 script and at first it could not understand why the status was not chaging.
Then I found out in the sript there is a typo which confused me
local heaterrepeatdelay = 600 -- 1 minute where 600 secs is certainly not 1 minute
So I changed the 600 to 60 and voila we have 1 minute.
My other question is how you get the yellow marked dropdown menu in the top right hand corner that says " Room ; Heating House " ?
I assume you have the dashboard devided in several pages?
Paco
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Heating finally automated using HomeEasy HE105
To setup rooms just go to the following location in the web interface
Setup-->More Options-->Plans-->Room Plan
Now just create a room and add items to it
P.s. I'll change the 600
Setup-->More Options-->Plans-->Room Plan
Now just create a room and add items to it
P.s. I'll change the 600
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 43
- Joined: Thursday 22 October 2015 21:15
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 2023.2
- Location: The Netherlands
- Contact:
Re: Heating finally automated using HomeEasy HE105
Thanks Martin,
Roomplans now added....
Paco
Roomplans now added....
Paco
-
- Posts: 3
- Joined: Friday 04 December 2015 10:33
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
So, been having a go at trying to get v0.4.1 to work but getting some errors in the log file. It's probably me not RTFM-ing but if anyone could help.....
I *think* this is due to this line
and the and
what are the remoteup and remotedown and where are they defined? I couldn't find any definitions....?
Thanks
Andy
Code: Select all
2015-12-04 09:41:00.413 Error: EventSystem: /home/pi/domoticz/scripts/lua/script_time_heating-0.1.lua:165: attempt to index global 'devicechanged' (a nil value)
Code: Select all
if( timedifference(otherdevices_lastupdate[physicalheater]) > heaterrepeatdelay or devicechanged[remoteup] or devicechanged[remotedown] or devicechanged[virtualheater]) then -- checks to see if the command needs to be repeated
Code: Select all
devicechanged[remoteup]
Code: Select all
devicechanged[remotedown]
Thanks
Andy
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Re: Heating finally automated using HomeEasy HE105
Andy, looks like you have found some redundant code! Bad me!!
"Latest Version of the code updated : 10/03/2015 V0.4 <- Latest version updated to support new temperature set point switch. this removes the need for lots of the code and additional switches. Enjoy "
I have made some additional changes over the last month so will upload the latest version when I get home.
Strange thing however is that I am not getting the same error (I don't think!). This makes me wonder if the code is ever getting to that point to throw the error (investigation required).
Out of interest have you created the virtual switch as defined in step 4?
"Latest Version of the code updated : 10/03/2015 V0.4 <- Latest version updated to support new temperature set point switch. this removes the need for lots of the code and additional switches. Enjoy "
I have made some additional changes over the last month so will upload the latest version when I get home.
Strange thing however is that I am not getting the same error (I don't think!). This makes me wonder if the code is ever getting to that point to throw the error (investigation required).
Out of interest have you created the virtual switch as defined in step 4?
-- 4. A virtual switch to set the target temperature (Temperature)
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 3
- Joined: Friday 04 December 2015 10:33
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
Ah that may explain it
I suspect my setup maybe one of the 'edge cases' (I always seem to be a bit odd...) but I thought I'd followed all the instructions.
I do have a virtual switch (but not sure how or what it's used for). I think need to read the code in a bit more detail.
Thanks for taking the time and effort to post!
Andy
I suspect my setup maybe one of the 'edge cases' (I always seem to be a bit odd...) but I thought I'd followed all the instructions.
I do have a virtual switch (but not sure how or what it's used for). I think need to read the code in a bit more detail.
Thanks for taking the time and effort to post!
Andy
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Re: Heating finally automated using HomeEasy HE105
I have checked my latest code tonight and I do still have the redundant code in place
I was in the process of updating to run off some variables and if possible set itself up automatically (so you don't need to read all the instructions)
Looks like I need to be slightly more detailed in the instructions. I'll post the latest code asap once I have remove the errors.
I was in the process of updating to run off some variables and if possible set itself up automatically (so you don't need to read all the instructions)
Looks like I need to be slightly more detailed in the instructions. I'll post the latest code asap once I have remove the errors.
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Re: Heating finally automated using HomeEasy HE105
-----------------------------------------------------------------------------------------------MajorJ wrote:
I do have a virtual switch (but not sure how or what it's used for). I think need to read the code in a bit more detail.
-- 4. A virtual switch to set the target temperature (Temperature)
-- Assumes you are using a dummy switch "Thermostat Setpoint" to move temperature up and down
-----------------------------------------------------------------------------------------------
local targettemperature = 'Thermostat House'
This is used for moving the target temperature. See the first post in the thread.
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 3
- Joined: Friday 04 December 2015 10:33
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
It was this one I was confused about
-----------------------------------------------------------------------------------------------
-- 3. A virtual switch to tun on and off the heating (On/Off Switch)
-----------------------------------------------------------------------------------------------
local virtualheater = '(CH) Virtual'
If I've got a 'real' switch to control my Central Heating why do I need a virtual one too?
-----------------------------------------------------------------------------------------------
-- 3. A virtual switch to tun on and off the heating (On/Off Switch)
-----------------------------------------------------------------------------------------------
local virtualheater = '(CH) Virtual'
If I've got a 'real' switch to control my Central Heating why do I need a virtual one too?
-
- Posts: 115
- Joined: Saturday 21 December 2013 23:50
- Target OS: Linux
- Domoticz version:
- Location: Scotland
- Contact:
Re: Heating finally automated using HomeEasy HE105
The virtual switch is just to say you want the heating on and off. While the heating might be on (via the virtual switch) the physical switch might be off as the temperature might have reached the value you want to get to. when the temperature drops then the script will turn the physical heater back on.
My Setup: Pi, RFXtrx433, HomeEasy: 13 Dimmers & 4 Sockets, 2 motion-sensors, 3 magnetic switches, 1 OWL Electricity Sensor, 3 Oregon Temp Sensor.
-
- Posts: 3
- Joined: Wednesday 13 January 2016 23:14
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Heating finally automated using HomeEasy HE105
Hallo i have some problem in the log
2016-01-13 23:04:56.901 Domoticz V2.4078 (c)2012-2016 GizMoCuz
2016-01-13 23:04:56.902 Build Hash: 7f07293, Date: 2016-01-10 08:33:58
2016-01-13 23:04:56.922 Sunrise: 07:50:00 SunSet:16:31:00
2016-01-13 23:04:56.922 EventSystem: reset all events...
2016-01-13 23:04:56.937 Active notification subsystems: (0/10)
2016-01-13 23:04:57.031 Webserver(HTTP) started on port: 8080
2016-01-13 23:04:57.047 Incoming connection from: 127.0.0.1
2016-01-13 23:04:57.047 Webserver(SSL) started on port: 443
2016-01-13 23:04:57.047 Proxymanager started.
2016-01-13 23:04:57.047 Starting shared server on: :::6144
2016-01-13 23:04:57.047 TCPServer: shared server started...
2016-01-13 23:04:57.047 RxQueue: queue worker started...
2016-01-13 23:04:59.066 EventSystem: reset all events...
2016-01-13 23:04:59.066 EventSystem: reset all device statuses...
2016-01-13 23:04:59.067 EventSystem: Started
2016-01-13 23:05:00.165 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:213: attempt to index global 'devicechanged' (a nil value)
2016-01-13 23:06:00.081 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:213: attempt to index global 'devicechanged' (a nil value)
2016-01-13 23:07:00.485 EventSystem: Script event triggered: C:\Program Files (x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua
2016-01-13 23:07:00.769 (Wohnzimmer licht) Lighting 2 (Heating House (Boiler))
2016-01-13 23:09:34.599 User: Admin initiated a switch command
2016-01-13 23:09:34.600 (Wohnzimmer Schalter1) Lighting 2 (Heating House)
2016-01-13 23:09:35.489 User: Admin initiated a switch command
2016-01-13 23:09:35.489 (Wohnzimmer licht) Lighting 2 (Heating House (Boiler))
2016-01-13 23:09:49.706 (Wohnzimmer Schalter1) Thermostat (Thermostat House)
2016-01-13 23:09:51.810 User: Admin initiated a switch command
2016-01-13 23:09:51.810 (Wohnzimmer licht) Lighting 2 (Heating House (Boiler))
2016-01-13 23:10:00.388 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:10:54.785 (Wohnzimmer Schalter1) Thermostat (Thermostat House)
2016-01-13 23:11:00.260 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:11:29.236 (Wohnzimmer Schalter1) Thermostat (Thermostat House)
2016-01-13 23:12:00.330 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:13:00.085 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:14:00.480 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:15:00.371 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
Please Help me
Best regard Mike
2016-01-13 23:04:56.901 Domoticz V2.4078 (c)2012-2016 GizMoCuz
2016-01-13 23:04:56.902 Build Hash: 7f07293, Date: 2016-01-10 08:33:58
2016-01-13 23:04:56.922 Sunrise: 07:50:00 SunSet:16:31:00
2016-01-13 23:04:56.922 EventSystem: reset all events...
2016-01-13 23:04:56.937 Active notification subsystems: (0/10)
2016-01-13 23:04:57.031 Webserver(HTTP) started on port: 8080
2016-01-13 23:04:57.047 Incoming connection from: 127.0.0.1
2016-01-13 23:04:57.047 Webserver(SSL) started on port: 443
2016-01-13 23:04:57.047 Proxymanager started.
2016-01-13 23:04:57.047 Starting shared server on: :::6144
2016-01-13 23:04:57.047 TCPServer: shared server started...
2016-01-13 23:04:57.047 RxQueue: queue worker started...
2016-01-13 23:04:59.066 EventSystem: reset all events...
2016-01-13 23:04:59.066 EventSystem: reset all device statuses...
2016-01-13 23:04:59.067 EventSystem: Started
2016-01-13 23:05:00.165 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:213: attempt to index global 'devicechanged' (a nil value)
2016-01-13 23:06:00.081 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:213: attempt to index global 'devicechanged' (a nil value)
2016-01-13 23:07:00.485 EventSystem: Script event triggered: C:\Program Files (x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua
2016-01-13 23:07:00.769 (Wohnzimmer licht) Lighting 2 (Heating House (Boiler))
2016-01-13 23:09:34.599 User: Admin initiated a switch command
2016-01-13 23:09:34.600 (Wohnzimmer Schalter1) Lighting 2 (Heating House)
2016-01-13 23:09:35.489 User: Admin initiated a switch command
2016-01-13 23:09:35.489 (Wohnzimmer licht) Lighting 2 (Heating House (Boiler))
2016-01-13 23:09:49.706 (Wohnzimmer Schalter1) Thermostat (Thermostat House)
2016-01-13 23:09:51.810 User: Admin initiated a switch command
2016-01-13 23:09:51.810 (Wohnzimmer licht) Lighting 2 (Heating House (Boiler))
2016-01-13 23:10:00.388 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:10:54.785 (Wohnzimmer Schalter1) Thermostat (Thermostat House)
2016-01-13 23:11:00.260 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:11:29.236 (Wohnzimmer Schalter1) Thermostat (Thermostat House)
2016-01-13 23:12:00.330 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:13:00.085 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:14:00.480 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
2016-01-13 23:15:00.371 Error: EventSystem: ...(x86)\Domoticz\scripts\lua\script_time_heating-0.4.1.lua:102: bad argument #1 to 'sub' (string expected, got nil)
Please Help me
Best regard Mike
-
- Posts: 63
- Joined: Sunday 14 July 2013 11:19
- Target OS: Raspberry Pi / ODroid
- Domoticz version: Beta
- Location: Ipswich, UK
- Contact:
dzVents home heating using HomeEasy HE105
Thanks for the inspiration for deploying my HE105. I've used the code already listed in this thread as a model upon which to write my own, but this time using the dzVents add-on.
The code allows for a list of thermometers which are averaged to get the current temperature. Thermometers which have not updated recently are ignored. To prevent the boiler from cycling too frequently, you can specify a tolerance value to force some hysteresis into the workings, you can also specify a maximum rate by which the boiler can be switched.
It also allows you to list door and window sensors which are checked. If any are found open then heating is disabled.
My implementation uses a dzVents script to detect presence based on successfully pinging our android phones - if neither of the phones are present then heating is temporarily disabled. I've yet to see how well this works in practice .
Optionally, a timer runs to update the boiler setting every so often.
At present I use a simple dimmer to specify the set point, this'll change when my plumber get involved. Suggestions for improvements welcome.
Enjoy, Peter
The code allows for a list of thermometers which are averaged to get the current temperature. Thermometers which have not updated recently are ignored. To prevent the boiler from cycling too frequently, you can specify a tolerance value to force some hysteresis into the workings, you can also specify a maximum rate by which the boiler can be switched.
It also allows you to list door and window sensors which are checked. If any are found open then heating is disabled.
My implementation uses a dzVents script to detect presence based on successfully pinging our android phones - if neither of the phones are present then heating is temporarily disabled. I've yet to see how well this works in practice .
Optionally, a timer runs to update the boiler setting every so often.
At present I use a simple dimmer to specify the set point, this'll change when my plumber get involved. Suggestions for improvements welcome.
Code: Select all
-- /lua/scripts/heating.lua adapted for dzVents by commodore white
local doors = {"foo"} -- list of doors
local windows = {"bar"} -- list of windows
local thermometers = { -- list of thermometers to average out
"envKitchen" }
local thermostat = "Bedroom" -- name of the control used to select the temperature
local boiler = "boiler" -- name of the switch that controls the boiler
local heating = "heating" -- name of the switch used to turn heating on and off
local thermometer_timeout = 60 -- minutes to prevent relying on a broken thermometer
local max_temperature = 25 -- degrees to detect heating over-run
local min_temperature = 15 -- degress for target if house is unoccupied
local frost_protect = 10 -- degrees for target to protect against a freeze (un-implemented)
local boiler_switch_delay = 10 -- seconds to prevent boiler being switched too frequently (negative to disable)
local tolerance = 0.5 -- degrees of thermal hysteresis to avoid frequent cycling
local keep_alive = 15 -- minutes between repeated commands (9999 to efectively disable)
local debug = true
-------------------- break the seal to void the warrenty -------------------------
-- build the on= list
local onlist = {['timer'] = 'every ' .. keep_alive .. ' minutes', thermostat, heating}
for _,j in ipairs(thermometers) do onlist[#onlist+1] = j end
for _,j in ipairs(doors ) do onlist[#onlist+1] = j end
for _,j in ipairs(windows ) do onlist[#onlist+1] = j end
if false then for i,j in ipairs(onlist) do print(i..' '..j) end end
--
return {
active = true, on=onlist,
execute = function(domoticz,_device)
local printf = function(s,...) if debug then print('heating: ' .. s:format(...)) end end
local _thermometer = domoticz.devices[thermometer]
local _thermostat = domoticz.devices[thermostat]
local _boiler = domoticz.devices[boiler]
local _heating = domoticz.devices[heating]
printf("Heating: %s ...... Boiler: %s ", _heating.state, _boiler.state)
-- re-issue most recent boiler command depending on keep_alive timer
local demand = ""
if _device == nil -- scheduled script execution ?
then
demand = _boiler.state
printf('Resend most recent boiler command: %s', demand)
_boiler.setState(demand)
return
end
-- Calculate temperature by averaging those listed. Ignore any that have not responded recently.
local count = 0
local sum = 0
for _,thermometer in ipairs(thermometers)
do
_therm = domoticz.devices[thermometer]
if _therm ~= nil -- check the device exists
then -- if so
age = _therm.lastUpdate.minutesAgo
temp = domoticz.devices[thermometer].temperature
printf("Thermometer %s (updated %sm ago) is %2.1f", thermometer, age, temp)
if age < thermometer_timeout -- if thermometer still responding
then
count = count + 1 -- accumulate the temperatures
sum = sum + temp -- and the number included
if temp > max_temperature then -- if temperature is too high
boiler_switch_delay = 0 -- send command immediately
demand = "Off"
_heating.switchOff()
domoticz.notify("Room temperature of " .. t .. "deg is too high","Shutting down")
end
else
printf("Thermometer device %s is unresponsive - skipping", thermometer)
end
else
printf("Thermometer device %s not found - skipping", thermometer)
end
end
if count == 0
and _heating.state == "On"
then
printf("No viable thermometers found - turning heating Off")
_boiler.switchOff()
_heating.switchOff()
return
end
local current = sum/count -- calculate average across all thermometers
-- set the target temperature depending on house occupancy
local is_occupied = domoticz.devices["AnyPhone"].state == "On"
local target
if is_occupied
then
target = _thermostat.rawData[1]
else
print("House is unoccupied")
target = min_temperature
end
printf('target temp: %s', target)
printf('Average current temp: %2.1f (average of %1d measurement(s))', current,count)
-- check if any doors or windows are open
local is_open = false -- assume no doors or windows are open
for _,door in ipairs(doors) do
local ptr = domoticz.devices[door]
if ptr == nil then
printf("No such door sensor as %s - skipping it", door)
else
if ptr.state == "Alarm" then
printf("Door %s is open", door)
is_open = true
end
end
end
for _,window in ipairs(windows) do
local ptr = domoticz.devices[window]
if ptr == nil then
printf("No such window sensor as %s - skipping it", window)
else
if ptr.state == "Alarm" then
printf("Window %s is open", window)
is_open = true
end
end
end
if is_open
then
print("One or more doors or windows open - heating is disabled")
_boiler.switchOff()
return
end
-- if the doors and windows are closed and the house is occupied, then
-- heat the room if it's cold, don't if it's not
local is_heatingScheduled = _heating.state == "On"
if is_heatingScheduled
and not is_open -- doors/windows closed
then
is_toohot = current > target + tolerance
is_toocool = current < target - tolerance
if is_toohot
and _boiler.state == "On"
then demand = "Off"
printf('Too hot! Switching boiler Off') end
if is_toocool
and _boiler.state == "Off"
then demand = "On"
printf('Too cold! Switching boiler On') end
else
if _boiler.state == "On"
then
printf("Switching boiler Off")
demand = "Off" -- turn off boiler if heating is off or if doors/windows are open
end
end
-- send the boiler the command ensuring there's a reasonable delay since the last one
local age = _boiler.lastUpdate.secondsAgo printf("Boiler previously updated %ss ago", age)
local delay = boiler_switch_delay - age
if demand ~= ""
then
if age >= boiler_switch_delay
then
_boiler.setState(demand)
else
if boiler_switch_delay >= 0 then
_boiler.setState(demand).after_sec(delay)
end
end
end
end -- execute
}
- pieman
- Posts: 5
- Joined: Thursday 23 October 2014 22:30
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Location: Cyprus
- Contact:
Re: Heating finally automated using HomeEasy HE105