Hi Team,
As a next exercise, I want to create a script that shows the COP of my heatpump in a Domoticz device. The COP is not readily available from my heatpump interface. The related alternative input data is 'meter heating' and 'energy heating', These are total/accumulating values, not daily, monthly or alike. The COP can (likely) be calculated using this input data. So, it should be straightforward to create a script that shows this calculated COP. However, I would (also) like to see the COP 'in the day/week/month/year' or similar. The 'cumulative COP' will even out to some value and not give any information on 'how the system worked last day/week/...".
Question: what is the most practical way to do that? Would I need to use persistent variable with the 'History' feature? Is there a specific device supporting this?
Practical way to script COP calculation?
Moderator: leecollings
- waltervl
- Posts: 5842
- Joined: Monday 28 January 2019 18:48
- Target OS: Linux
- Domoticz version: 2024.7
- Location: NL
- Contact:
Re: Practical way to script COP calculation?
Put it in a custom sensor https://wiki.domoticz.com/Dummy_for_vir ... tom_Sensor
You probably have one in your environment so you can see how the data looks like.
You probably have one in your environment so you can see how the data looks like.
Domoticz running on Udoo X86 (on Ubuntu)
Devices/plugins: ZigbeeforDomoticz (with Xiaomi, Ikea, Tuya devices), Nefit Easy, Midea Airco, Omnik Solar, Goodwe Solar
Devices/plugins: ZigbeeforDomoticz (with Xiaomi, Ikea, Tuya devices), Nefit Easy, Midea Airco, Omnik Solar, Goodwe Solar
-
- Posts: 612
- Joined: Sunday 01 November 2015 22:45
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 2023.2
- Location: Twente
- Contact:
Re: Practical way to script COP calculation?
I asked our new friend Deep Seek for a solution
Here is Deep's script. You can translate the Durch for yourself if needed.
Here is Deep's script. You can translate the Durch for yourself if needed.
Code: Select all
Hier is een **dzVents-script** dat de gegevens verzamelt wanneer de airco wordt uitgeschakeld, deze gegevens opslaat in een bestand, en aan het einde van de maand de COP (Coefficient of Performance) berekent over de afgelopen maand. Het script maakt gebruik van de volgende aannames:
- Het stroomverbruik van de airco wordt bijgehouden door een device genaamd **Airco**.
- De buitentemperatuur wordt bijgehouden door een device genaamd **Buitentemperatuur**.
- De gewenste binnentemperatuur is **21°C**.
### Script:
```lua
-- Script om COP van de airco te berekenen en gegevens op te slaan
return {
on = {
devices = {
'Airco' -- Luister naar het Airco-device
}
},
data = {
aircoData = { history = {} } -- Opslag voor historische gegevens
},
execute = function(domoticz, device)
local airco = domoticz.devices('Airco')
local buitenTemp = domoticz.devices('Buitentemperatuur')
local gewensteTemp = 21 -- Gewenste binnentemperatuur
-- Controleer of de airco is uitgeschakeld
if airco.state == 'Off' then
-- Verzamel gegevens
local stroomVerbruik = airco.usage -- Stroomverbruik in kWh
local buitenTemperatuur = buitenTemp.temperature -- Buitentemperatuur in °C
-- Bereken de warmte-uitwisseling (Q)
-- Q = stroomVerbruik * COP (schatting, COP wordt later berekend)
-- Voor nu slaan we alleen de ruwe gegevens op
local gegevens = {
tijdstip = domoticz.time.rawTime, -- Tijdstip van uitschakelen
stroomVerbruik = stroomVerbruik,
buitenTemperatuur = buitenTemperatuur,
gewensteTemp = gewensteTemp
}
-- Voeg gegevens toe aan de geschiedenis
table.insert(domoticz.data.aircoData.history, gegevens)
-- Schrijf gegevens naar een bestand (optioneel)
local bestandsNaam = 'airco_data.txt'
local bestand = io.open(bestandsNaam, 'a') -- Open het bestand in append-modus
if bestand then
bestand:write('Tijdstip: ' .. gegevens.tijdstip .. ', ')
bestand:write('Stroomverbruik: ' .. gegevens.stroomVerbruik .. ' kWh, ')
bestand:write('Buitentemperatuur: ' .. gegevens.buitenTemperatuur .. ' °C\n')
bestand:close()
else
domoticz.log('Kan bestand niet openen om gegevens op te slaan', domoticz.LOG_ERROR)
end
end
-- Aan het einde van de maand de COP berekenen
if domoticz.time.day == 1 and domoticz.time.hour == 0 and domoticz.time.minute == 0 then
local totaalStroomVerbruik = 0
local totaalWarmteUitwisseling = 0
-- Loop door de geschiedenis om totale waarden te berekenen
for _, gegevens in ipairs(domoticz.data.aircoData.history) do
totaalStroomVerbruik = totaalStroomVerbruik + gegevens.stroomVerbruik
-- Schat de warmte-uitwisseling (Q) op basis van temperatuurverschil
local deltaT = gegevens.buitenTemperatuur - gegevens.geweneTemp
totaalWarmteUitwisseling = totaalWarmteUitwisseling + (gegevens.stroomVerbruik * deltaT)
end
-- Bereken de COP
local COP = totaalWarmteUitwisseling / totaalStroomVerbruik
-- Log de COP
domoticz.log('COP over de afgelopen maand: ' .. COP, domoticz.LOG_INFO)
-- Wis de geschiedenis voor de nieuwe maand
domoticz.data.aircoData.history = {}
end
end
}
```
---
### Uitleg van het script:
1. **Trigger:**
- Het script wordt geactiveerd wanneer de status van het **Airco**-device verandert.
- Het controleert of de airco is uitgeschakeld (`state == 'Off'`).
2. **Gegevens verzamelen:**
- Het script verzamelt het stroomverbruik van de airco en de buitentemperatuur op het moment van uitschakelen.
- Deze gegevens worden opgeslagen in een tabel (`domoticz.data.aircoData.history`).
3. **Opslaan in een bestand:**
- De gegevens worden ook weggeschreven naar een tekstbestand (`airco_data.txt`) voor langdurige opslag.
4. **COP berekenen aan het einde van de maand:**
- Op de eerste dag van de maand om middernacht wordt de COP berekend over de afgelopen maand.
- Het script berekent het totale stroomverbruik en de geschatte warmte-uitwisseling.
- De COP wordt berekend als de verhouding tussen de totale warmte-uitwisseling en het totale stroomverbruik.
5. **Geschiedenis wissen:**
- Na het berekenen van de COP wordt de geschiedenis gewist om klaar te zijn voor de nieuwe maand.
---
### Opmerkingen:
- **Schatting van warmte-uitwisseling (Q):** Het script schat de warmte-uitwisseling op basis van het temperatuurverschil tussen binnen en buiten. Dit is een vereenvoudiging en kan worden verfijnd als je meer gegevens hebt (bijv. luchtdebiet).
- **Bestandsopslag:** Het script schrijft gegevens naar een tekstbestand. Zorg ervoor dat Domoticz toegang heeft tot het bestandssysteem.
- **Testen:** Test het script grondig om ervoor te zorgen dat het correct werkt in jouw Domoticz-omgeving.
Laat het weten als je verdere aanpassingen nodig hebt! 😊
Bugs bug me.
- waltervl
- Posts: 5842
- Joined: Monday 28 January 2019 18:48
- Target OS: Linux
- Domoticz version: 2024.7
- Location: NL
- Contact:
Re: Practical way to script COP calculation?
When airco is off measure energy usage of airco?
Trigger is only on airco device not on time. So monthly COP calculation will most likely be shipped. Or you send data at least every minute to the airco device.....
The estimated heat transfer calculations as base for the COP seems to be a joke, at least I do not understand it.
Trigger is only on airco device not on time. So monthly COP calculation will most likely be shipped. Or you send data at least every minute to the airco device.....
The estimated heat transfer calculations as base for the COP seems to be a joke, at least I do not understand it.
Domoticz running on Udoo X86 (on Ubuntu)
Devices/plugins: ZigbeeforDomoticz (with Xiaomi, Ikea, Tuya devices), Nefit Easy, Midea Airco, Omnik Solar, Goodwe Solar
Devices/plugins: ZigbeeforDomoticz (with Xiaomi, Ikea, Tuya devices), Nefit Easy, Midea Airco, Omnik Solar, Goodwe Solar
- Domoberry
- Posts: 121
- Joined: Tuesday 30 May 2017 19:00
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 2024.7
- Contact:
Re: Practical way to script COP calculation?
Thanks for the feedback! It contains relevant information!
in the meantime (apologies for not responding earlier), I created a Dzvents script that takes two key parameters generated by my heat pump (via the EMS-ESP "BBQ-kees" gateway): 'meter heating' ("eIn", the energy consumption for heating purposes) and 'energy heating' ("eOut", the energy generated by the heat pump). These are accumulating numbers updated every minute.
I found on https://www.gridx.ai/knowledge/coeffici ... rmance-cop and on https://en.wikipedia.org/wiki/Coefficie ... erformance that for a heat pump, used to heat a space, one could use:
COP = (eOut + eIn) / (eIn)
(for cooling a space the article suggests COP = (eOut) / (eIn)). That makes sense.
In order to calculate the COP, I need to decide over which time period I want determine the COP. I have taken 10 minutes for now (adjustable), I'm not sure how much time makes most sense yet. The script keeps track of the eOut and eIn and determines delta's for both over 10 minutes and calculates the COP over that period. The result is sent to a Custom Sensor virtual device. The sensor provides as usual in its log averages over days/months/years. The 10-minute-COP's averaged over -say- a week is obviously not the same as the COP calculated over that same week.
Some further care is taken to ensure the 'eIn' and 'eOut' originate from the same data message from the heatpump, it is not guaranteed that both eIn and eOut are updated at the same time in Domoticz, neither do I know which of them if first/last updated.
This is a (very) first working version (updated 250203):
in the meantime (apologies for not responding earlier), I created a Dzvents script that takes two key parameters generated by my heat pump (via the EMS-ESP "BBQ-kees" gateway): 'meter heating' ("eIn", the energy consumption for heating purposes) and 'energy heating' ("eOut", the energy generated by the heat pump). These are accumulating numbers updated every minute.
I found on https://www.gridx.ai/knowledge/coeffici ... rmance-cop and on https://en.wikipedia.org/wiki/Coefficie ... erformance that for a heat pump, used to heat a space, one could use:
COP = (eOut + eIn) / (eIn)
(for cooling a space the article suggests COP = (eOut) / (eIn)). That makes sense.
In order to calculate the COP, I need to decide over which time period I want determine the COP. I have taken 10 minutes for now (adjustable), I'm not sure how much time makes most sense yet. The script keeps track of the eOut and eIn and determines delta's for both over 10 minutes and calculates the COP over that period. The result is sent to a Custom Sensor virtual device. The sensor provides as usual in its log averages over days/months/years. The 10-minute-COP's averaged over -say- a week is obviously not the same as the COP calculated over that same week.
Some further care is taken to ensure the 'eIn' and 'eOut' originate from the same data message from the heatpump, it is not guaranteed that both eIn and eOut are updated at the same time in Domoticz, neither do I know which of them if first/last updated.
This is a (very) first working version (updated 250203):
Code: Select all
-- COP calculator
-- 250127.1/250128/250129.2
-- v2: rounding cop to 3 decimals, catch error when cop divide by zero, counter "== 1" replaced by '<=1' for COP calculation
-- 250130: if eInDelta is 0 over the sample period, a "COP" does not make sense (and would yield divide by 0), in that case, no COP is reported.
--[[
** Description
Objective of this script is to show the COP of my heat pump on a Domoticz device.
The script calculates the COP based in two parameters provided by the ems-esp gateway between my
heat pump and Domoticz: 'meter heating' ("eIn", the energy consumption for heating purposes) and
'energy heating' ("eOut", the energy generated by the heat pump). These are accumulating numbers
updated every minute.
As found on https://www.gridx.ai/knowledge/coefficient-of-performance-cop, you can use
COP = (eOut + eIn) / (eIn) to calculate the COP.
The script is triggered by updates of the eOut device. As I cannot be sure that eIn is updated before
eOut (or vice verse), the script triggers itself again a few seconds after the eOut trigger using
a Custom Event. This ensures both eOut and eIn originate from the same heat pump data sample.
The COP is calculated over several updates of eOut/eIn, for example spanning a period of 10 mins. An
internal sample counter is used for this.
The value of eOut and eIn is stored using a persistent variable. The script has some means to
reinitialize these values.
The COP values are sent to a dummy device of type general/custom counter. this device proides the
usual Domoticz averages 7 days, month, year, compare years. Note that for example the months COP
average is not the same as the COP calculated over a period of a month.
Installing and requirements
- 'meter heating' and 'energy heating' are available as Domoticz devices and updated each minute
- a dummy/virtual device type general/custom counter has been created with label "COP"
** Testing
-To start from 'zero'
- set local variable 'initializeOnly' to true
- start the script
- at the first trigger, all persistent variables will be reinitialized
- stop the script and set 'initializeOnly' to false again for normal used
- Debug logging
- set local var logLevel to domoticz.LOG_DEBUG, default to domoticz.LOG_INFO
- More triggering
- add "timer = { 'every minute' }," to run the script anyhow every minute
** Notes
- I'm not sure about the best time span (number of samples) to wait before a practical COP calculation
- during deicing, the heat pump uses heat from inside, so eOut will decrease, COP will be <1 or even
this could lead to negative COP if deicing during sample period takes more energy then eIn over same period
** Improvements
- add input validation on some local parameters? or just add noe to the comment?
** Abbreviations
dz = Dz = Domoticz
eOut = accumulated energy (e.g. heat) generated by the heatpump for heating purposes
eIn = accumulated energy (e.g. electrical) used by the heatpump for heating purposes
--]]
-- local variables
local logMarker = 'COP calc' -- [string] same as the title to make it clear in the Domoticz log
local logLevel = domoticz.LOG_DEBUG -- use domoticz.LOG_DEBUG for debugging, otherwise use domoticz.LOG_INFO
local eOutIdx = 1093 -- [idx] eOut Dz device (a general/kWh device), holds the accumulated heatpump output for heating
local eInIdx = 1100 -- [idx] eIn Dz device (a general/kWh device), holds the accumulate heatpump energy used for heating
local copSensorIdx = 1169 -- [idx] cop Dz dummy device, to show the COP this scropt determines
local copCustomEvent = 'waitAbit' -- [string] name of the custom event used to trigger this script
local delay = 2 -- [s] number of seconds to wait before retrieving second value
local initCounter = 10 -- [int] number of samples to wait between calculating CoP (e.g. calculate cop over 10 x sample time = 10 x 1 min = 10 mins)
local initializeOnly = false -- [boolean] default: false. if set to true, the script will *only* reinitialize persistent variables when triggered
-- end local variables
-- functions go here
function reinitPersisVar(dz)
dz.log('The initializeOnly local variable has been set to: ' .. tostring(initializeOnly), dz.LOG_DEBUG)
dz.log('Re-initializing persistent variables is all that will happen!', dz.LOG_DEBUG)
dz.log('counter = ' .. tostring(dz.data.counter), dz.LOG_DEBUG)
dz.log('eOutPrv = ' .. tostring(dz.data.eOutPrv), dz.LOG_DEBUG)
dz.log('eInPrv = ' .. tostring(dz.data.eInPrv), dz.LOG_DEBUG)
dz.log('eOutNow = ' .. tostring(dz.data.eOutNow), dz.LOG_DEBUG)
dz.log('re-initilizing persistent variables...', dz.LOG_DEBUG)
dz.data.initialize('eOutPrv')
dz.data.initialize('eInPrv')
dz.data.initialize('counter')
dz.data.initialize('eOutNow')
dz.log('counter = ' .. tostring(dz.data.counter), dz.LOG_DEBUG)
dz.log('eOutPrv = ' .. tostring(dz.data.eOutPrv), dz.LOG_DEBUG)
dz.log('eInPrv = ' .. tostring(dz.data.eInPrv), dz.LOG_DEBUG)
dz.log('eOutNow = ' .. tostring(dz.data.eOutNow), dz.LOG_DEBUG)
dz.log('All persistent variables have been reinitilized.', dz.LOG_STATUS)
return
end -- ReinitPersisVar
-- end functions
-- MAIN CODE BLOCK
return {
-- active
active = {
true, -- either true or false, or you can specify a function returning true or false
},
-- trigger
on = {
-- device triggers
devices = { eOutIdx, -- triggered by the eOut device
},
customEvents = {
copCustomEvent,
}
},
-- persistent data
data = {
counter = { initial = 10 }, -- counter to keep track of samples between cop calculation
eOutPrv = { initial = 0 }, -- to store the eOut for use in the next script run
eInPrv = { initial = 0 }, -- to store the eIn for use in the next script run
eOutNow = {initial = 0 }, -- to store new eOut value during script calculating COP run
}, -- end of persistent data section
-- logging
logging = {
-- level = domoticz.LOG_DEBUG, -- use LOG_DEBUG if you want more logging, LOG_INFO as default is OK
level = logLevel,
marker = logMarker
},
-- end of logging section
-- actual event code
execute = function(dz, item)
-- for testing only: reset all persistent vars back to initial values
if initializeOnly then
reinitPersisVar(dz)
return -- exit the script here
end
-- end testing
-- some shortcuts here
counter = dz.data.counter
eOutPrv = dz.data.eOutPrv
eInPrv = dz.data.eInPrv
eOutNow = dz.data.eOutNow
-- end shortcuts
dz.log('Remaining sample counter: ' .. tostring (counter),dz.LOG_DEBUG)
-- address one of these cases only (high level):
-- (1) get start values eOut and eIn if not available
-- (2) calculate COP if collected enough samples
-- (3) otherwise decrement the samples counter
--
-- (1)
if ( eOutPrv == 0 or eInPrv == 0 ) then -- if not set, get the first eOut and eIn values ever
dz.log('Persistent variables eOutPrv and/or eInPrv are 0, get start values first', dz.LOG_DEBUG)
if item.isDevice then -- if triggered by device update
eOutNow = dz.devices(eOutIdx).WhTotal -- get current value of Dz device for eOut
dz.data.eOutPrv = eOutNow -- store the first value in persistent variable eInPrv
dz.log('Retrieved current eOut (' .. tostring(eOutNow) .. ' [W]) and stored in persistent variable "eOutPrv"', dz.LOG_DEBUG)
dz.emitEvent(copCustomEvent,'some tbd data').afterSec(delay) -- can delete data part unless you find practical use for it
dz.log('Custom Event "' .. copCustomEvent .. '" will be raised afer ' .. tostring(delay) .. ' seconds', dz.LOG_DEBUG)
end -- from if triggered by item.isDevice (device update)
if item.isCustomEvent then -- if triggered by CustomEvent
-- log will mention what triggered this script run, no need to add to log again
eInNow = dz.devices(eInIdx).WhTotal -- get curreny value of Dz device for eIn
dz.data.eInPrv = eInNow -- store the first value in persistent variable eInPrv
dz.log('Retrieved current eIn (' .. tostring(eInNow) .. ' [W]) and stored in persistent variable "eInPrv"', dz.LOG_DEBUG)
end -- from if triggered by item.isCustomEvent
-- end catching the need to initialize eOutPrv and eInPrv persistent variable
--
-- (2)
elseif counter <= 1 then -- get the last sample and calculate COP
-- calculate COP
dz.log('Get last eOut and eIn samples and calculate CoP',dz.LOG_DEBUG)
-- get first value (eOut)
if item.isDevice then -- if triggered by device update
eOutNow = dz.devices(eOutIdx).WhTotal -- get current value of Dz device for eOut
dz.data.eOutNow = eOutNow -- store the first value in persistent variable eOutNow
dz.log('Retrieved current eOut (' .. tostring(eOutNow) .. ' [W]) and stored this in a persistent variable "eOutNow"', dz.LOG_DEBUG)
dz.emitEvent(copCustomEvent,'some tbd data').afterSec(delay) -- can delete data part unless you find practical use for it
dz.log('Custom Event "' .. copCustomEvent .. '" will be triggered afer ' .. tostring(delay) .. ' seconds', dz.LOG_DEBUG)
return -- abort script, no reason to continue now
end -- from if triggered by item.isDevice (device update)
-- get second value (eIn)
if item.isCustomEvent then -- if triggered by CustomEvent
-- log will mention what triggered this script run, no need to add that to log again
eInNow = dz.devices(eInIdx).WhTotal -- get curreny value of Dz device for eIn
dz.log('Retrieved current eIn (' .. tostring(eInNow) .. ' [W])', dz.LOG_DEBUG) -- no need to store it in a persistent variable, will be used directly
end -- from if triggered by item.isCustomEvent
--
-- do the math
eOutDelta = eOutNow - eOutPrv -- energy delivered during the time determined by the counter
eInDelta = eInNow - eInPrv -- energy used during the time determined by the counter
dz.log('eOutDelta = ' .. tostring(eOutNow) .. ' - ' .. tostring(eOutPrv) .. ' = ' .. tostring(eOutDelta) .. ' [W]', dz.LOG_DEBUG)
dz.log('eInDelta = ' .. tostring(eInNow) .. ' - ' .. tostring(eInPrv) .. ' = ' .. tostring(eInDelta) .. ' [W]', dz.LOG_DEBUG)
-- check for no energy used, in which case reporting a COP does not make sense (and would lead ot divide by 0)
if eInDelta == 0 then -- no energy used
dz.log('eInDelta = ' .. tostring(eInNow) .. ' - ' .. tostring(eInPrv) .. ' = ' .. tostring(eInDelta) .. ' [W] => no energy used, COP not updated',dz.LOG_STATUS)
else -- report COP and send update to device
cop = ( eOutDelta + eInDelta ) / eInDelta
dz.log('Calculated COP = ' .. tostring(cop), dz.LOG_STATUS)
cop = dz.utils.round(cop,3) -- round cop to 3 decimals, looks better on the device
dz.devices(copSensorIdx).updateCustomSensor(cop)
end
--
-- some further testing to find out what causes a negative COP
-- noted that eOutDelta can be negative, perhaps when heat pump is de-icing?
if (eOutDelta < 0) or (eInDelta < 0) then
dz.log('One of these was negative: eOutDelta = ' .. tostring(eOutDelta) .. ' eInDelta = ' .. tostring(eInDelta), dz.LOG_ERROR)
end
--
-- update previous values stored in persistent variables
dz.data.eOutPrv = eOutNow
dz.data.eInPrv = eInNow
dz.log('Updated the values stored in persistent data: eOut: ' .. tostring(dz.data.eOutPrv) .. ' [W] and eIn: ' .. tostring(dz.data.eInPrv) .. ' [W]', dz.LOG_DEBUG)
--
-- reset the counter
dz.data.counter = initCounter
--
--
-- (3)
else -- not the time yet to calculate COP
dz.data.counter = dz.data.counter - 1 -- decrement counter
dz.log('Earlier stored persistent values for eOut: ' .. tostring(eOutPrv) .. ' [W] and eIn: ' .. tostring(eInPrv) .. ' [W]', dz.LOG_DEBUG)
end -- from processing the cases
end
-- end actual event code
}
-- END MAIN CODE BLOCK
Last edited by Domoberry on Monday 03 February 2025 18:07, edited 4 times in total.
-
- Posts: 35
- Joined: Wednesday 22 July 2015 21:39
- Target OS: Raspberry Pi / ODroid
- Domoticz version:
- Contact:
Re: Practical way to script COP calculation?
Code: Select all
return {
on = {
timer = { 'every minute'}
},
logging =
{
--level = domoticz.LOG_DEBUG, -- for debugging
--level = domoticz.LOG_INFO,
marker = "COP berekening"
},
execute = function(dz)
local verbruik = dz.devices(38).WhToday
local opgewekt = dz.devices(39).WhToday
local Cop = dz.utils.round(opgewekt / verbruik,2)
-- dz.log ('Verbruik is ' .. verbruik)
-- dz.log ('Opgewekt is ' .. opgewekt)
dz.log ('COP is ' .. Cop)
dz.devices(213).updateCustomSensor(Cop)
end
}
- Domoberry
- Posts: 121
- Joined: Tuesday 30 May 2017 19:00
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 2024.7
- Contact:
Re: Practical way to script COP calculation?
That is in essence the same!
Based on what I found using Google (links in the earlier post), I'm using CoP = (energy-out + energy-in)/(energy-in), e.g. exactly 1 more than above. I understood this is because I'm looking at a CoP for heating, not cooling. However, I'm not an expert! Also, I think you need to consider the energy in/out over a certain time period, yet I do not know how much time is optimal. In the attached example, Energie-out/in are calculated over 10 mins (my heat pump provides the accumulated energy out/in every minute), yet the result is still quite 'noisy', so I probably need a longer period. Lastly, if the heat pump is not running, energy-in is obviously zero (divide by zero), so I capture that (by not giving an update on CoP in that case). Also noted that in some cases energy-out can be negative, which is probably when the system is deicing. Even to the extend that the CoP itself becomes negative. Unfortunately, the position of the 4-way valve in the heat pump (e.g. heating or cooling/deicing) seems not to be exposed via the EMS-ESP gateway.
Note that the Domoticz graph takes the 10-minute CoP updates and interpolates every 5 minutes for the graph. Perhaps I should rather use a bar-graph. (the script code in my earlier is updated to what I'm currently testing with)
Based on what I found using Google (links in the earlier post), I'm using CoP = (energy-out + energy-in)/(energy-in), e.g. exactly 1 more than above. I understood this is because I'm looking at a CoP for heating, not cooling. However, I'm not an expert! Also, I think you need to consider the energy in/out over a certain time period, yet I do not know how much time is optimal. In the attached example, Energie-out/in are calculated over 10 mins (my heat pump provides the accumulated energy out/in every minute), yet the result is still quite 'noisy', so I probably need a longer period. Lastly, if the heat pump is not running, energy-in is obviously zero (divide by zero), so I capture that (by not giving an update on CoP in that case). Also noted that in some cases energy-out can be negative, which is probably when the system is deicing. Even to the extend that the CoP itself becomes negative. Unfortunately, the position of the 4-way valve in the heat pump (e.g. heating or cooling/deicing) seems not to be exposed via the EMS-ESP gateway.
Note that the Domoticz graph takes the 10-minute CoP updates and interpolates every 5 minutes for the graph. Perhaps I should rather use a bar-graph. (the script code in my earlier is updated to what I'm currently testing with)