Fish pond pump script
Anyone here knows if there is a Fish pond pump script that deals with time and weather data?
i searched everywhere and also tried making my own from some heating scripts but without any luck and working script....
what i'm looking for is a script that sets on the pond pump x time (for example 2 hours and then off) at a x interval (example 2 hours on and 1 hours off and repeats that )
and if the temperature is below a x variable (like 0 degrees) it will not turn in on at all of turns is on continuously
i truly hope some of you could help me out or can give me some examples to work with.
(made serveral bash and python scripts, but i can't seem too figure out this one)
thanks alot
i searched everywhere and also tried making my own from some heating scripts but without any luck and working script....
what i'm looking for is a script that sets on the pond pump x time (for example 2 hours and then off) at a x interval (example 2 hours on and 1 hours off and repeats that )
and if the temperature is below a x variable (like 0 degrees) it will not turn in on at all of turns is on continuously
i truly hope some of you could help me out or can give me some examples to work with.
(made serveral bash and python scripts, but i can't seem too figure out this one)
thanks alot
-
- Posts: 272
- Joined: Sunday 11 May 2014 11:09
- Target OS: Windows
- Domoticz version: 2023.1+
- Location: NL
- Contact:
Re: Fish pond pump script
In Lua, just give youre some idea;s to get you started with the timing :
put the time/date table in variable time
time.hour contains the hours of time.
time.min contains the minite of time
would run every 2 minutes, this can also be done with time.hour.
Dont forget to load the table in time (first sentence)
Code: Select all
time = os.date("*t")
Code: Select all
if (time.hour==7 or time.hour==19) and time.min==0 then ....pump on or off ..... end
time.min contains the minite of time
Code: Select all
if ((time.min% 2)==0) then ..... end
Dont forget to load the table in time (first sentence)
Rpi & Win x64. Using : cam's,RFXCom, LaCrosse, RFY, HuE, google, standard Lua, Tasker, Waze traveltime, NLAlert&grip2+,curtains, vacuum, audioreceiver, smart-heating&cooling + many more (= automate all repetitive simple tasks)
-
- Posts: 24
- Joined: Monday 15 July 2013 2:37
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 3.8153
- Location: Twente
- Contact:
Re: Fish pond pump script
thanks for the push in right direction.. will give it a shot tonight.. is it okay if i post my progress here.. so you can maybe help me out a little?
-
- Posts: 272
- Joined: Sunday 11 May 2014 11:09
- Target OS: Windows
- Domoticz version: 2023.1+
- Location: NL
- Contact:
Re: Fish pond pump script
See PM and yes you can post it here if you made something, that way others can benefit or think together with you
Rpi & Win x64. Using : cam's,RFXCom, LaCrosse, RFY, HuE, google, standard Lua, Tasker, Waze traveltime, NLAlert&grip2+,curtains, vacuum, audioreceiver, smart-heating&cooling + many more (= automate all repetitive simple tasks)
- Egregius
- Posts: 2589
- Joined: Thursday 09 April 2015 12:19
- Target OS: Linux
- Domoticz version: v2024.7
- Location: Beitem, BE
- Contact:
Re: Fish pond pump script
With pass2php times are quite easy:
Code: Select all
<?php
$temp=status('temperature');
$pump=status('pump');
if($temp>25){
//To hot, let's pump continuosly
if($pump!='On')sw('pump','On');
}elseif($temp>0){
//Normal temp
if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off');
elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On');
}else{
//It's freezing cold, don't pump at all
if($pump!='Off')sw('pump','Off');
}
-
- Posts: 24
- Joined: Monday 15 July 2013 2:37
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 3.8153
- Location: Twente
- Contact:
Re: Fish pond pump script
that looks very good indeed, but how does it get the var temp and pump? are those the names in domoticz ?Egregius wrote: ↑Monday 25 September 2017 6:13 With pass2php times are quite easy:Code: Select all
<?php $temp=status('temperature'); $pump=status('pump'); if($temp>25){ //To hot, let's pump continuosly if($pump!='On')sw('pump','On'); }elseif($temp>0){ //Normal temp if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off'); elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On'); }else{ //It's freezing cold, don't pump at all if($pump!='Off')sw('pump','Off'); }
i can read the script and understand it.. but can you explain the "timestamp".. is that a persistant value? or does it read the time variables from domoticz? ("last seen")
How do i implement it?
- Egregius
- Posts: 2589
- Joined: Thursday 09 April 2015 12:19
- Target OS: Linux
- Domoticz version: v2024.7
- Location: Beitem, BE
- Contact:
Re: Fish pond pump script
Yes, the names of Domoticz.
You'll need to get pass2php running. All the magic happens there.
You'll need to get pass2php running. All the magic happens there.
-
- Posts: 24
- Joined: Monday 15 July 2013 2:37
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 3.8153
- Location: Twente
- Contact:
Re: Fish pond pump script
thats no problem, please help me understand the script (timestamps) as i have no php knowledge.
is it also possible to store values? because for example if it freezes for 2 days, and temp gets above 0 again.. it takes for example 5 days before the pump can start again because the ice needs to melddown.
is it also possible to store values? because for example if it freezes for 2 days, and temp gets above 0 again.. it takes for example 5 days before the pump can start again because the ice needs to melddown.
-
- Posts: 24
- Joined: Monday 15 July 2013 2:37
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 3.8153
- Location: Twente
- Contact:
Re: Fish pond pump script
realy hope you or someone willing to make this a working script... i just don't have the knowledge..yet.. 

- Egregius
- Posts: 2589
- Joined: Thursday 09 April 2015 12:19
- Target OS: Linux
- Domoticz version: v2024.7
- Location: Beitem, BE
- Contact:
Re: Fish pond pump script
you can store custom variables with the setstatus() function and read them with the status() function of pass2php.
You could (for example) set a variable 'hasfrozen' to the lowest frost temperature. pass2php automatically remembers the last set time of a var.
Didn't test this, but something like this could be a good direction:
A lot of information of pass2php can be found at http://www.domoticz.com/forum/viewtopic ... 64&t=12343
You could (for example) set a variable 'hasfrozen' to the lowest frost temperature. pass2php automatically remembers the last set time of a var.
Didn't test this, but something like this could be a good direction:
Code: Select all
<?php
$temp=status('temperature');
$pump=status('pump');
if($temp>25){
//To hot, let's pump continuosly
if($pump!='On')sw('pump','On');
}elseif($temp>8){
//Normal temp, let's cycle 2 hours on, 1 hour off
if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off');
elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On');
}elseif($temp>0){
//It's cold, did it freeze lately?
$hasfrozen=status('hasfrozen');
$hasfrozentime=timestamp('hasfrozen');
if($hasfrozen<-20){
//damned that was cold, lets wait 10 days
if($hasfrozentime<time-(86400*10)){
if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off');
elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On');
}
}elseif($hasfrozen<-10){
//damned that was cold, lets wait 5 days
if($hasfrozentime<time-(86400*5)){
if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off');
elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On');
}
}elseif($hasfrozen<-5){
//damned that was cold, lets wait 2 days
if($hasfrozentime<time-(86400*2)){
if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off');
elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On');
}
}elseif($hasfrozen<0){
//Just a litle frost, one day will do
if($hasfrozentime<time-86400){
if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off');
elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On');
}
}else{
//It didn't freeze, lets cycle
if($pump=='On'&×tamp('pump')<time-7200)sw('pump','Off');
elseif($pump=='Off'&×tamp('pump')<time-3600)sw('pump','On');
}
}else{
//It's freezing cold, don't pump at all
if($pump!='Off')sw('pump','Off');
$hasfrozen=status('hasfrozen');
if($temp<$hasfrozen)setstatus('hasfrozen',$temp);
}
-
- Posts: 24
- Joined: Monday 15 July 2013 2:37
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 3.8153
- Location: Twente
- Contact:
Re: Fish pond pump script
Thank you very much Egregius.. will give it a try
what will happen if it's -11 2 days in a row? it will just stay 5 days with every extra day its still freezing -11 ?
what will happen if it's -11 2 days in a row? it will just stay 5 days with every extra day its still freezing -11 ?
-
- Posts: 24
- Joined: Monday 15 July 2013 2:37
- Target OS: Raspberry Pi / ODroid
- Domoticz version: 3.8153
- Location: Twente
- Contact:
Re: Fish pond pump script
Anyone willing to help debug and improve this script?
thanks in advance
thanks in advance
Code: Select all
-- start lua commandarray = schakel tabel waarin we opdrachten gaan geven
commandArray = {}
------------------------------------------------------------
-- functie timedifference = functie di we verderop aanroepen om te zien hoe lang pomp aan is of uit is.
------------------------------------------------------------
function timedifference (s) --- tijdverschil bepalen sinds laatste schakeling in sec
yearx=string.sub(s, 1, 4) monthx=string.sub(s, 6, 7) dayx=string.sub(s, 9, 10)
hourx=string.sub(s, 12, 13) minutesx=string.sub(s, 15, 16) secondsx=string.sub(s, 18, 19)
t1=os.time()
t2=os.time{year=yearx, month=monthx, day=dayx, hour=hourx, min=minutesx, sec=secondsx}
difference=os.difftime (t1, t2)
--print(s.." "..tostring(t).." "..tostring(difference))
return difference
end
------------------------------------------------------------
-- zet de temperatuur in variable zodat we deze later als vooraarde kunnen laten dienen-- bepaal wat er moet gebeuren
------------------------------------------------------------
local temp = otherdevices_temperature['Temp Ground / Humidity (Twente)'] -- zet temp in waarde, en maak er n getal van ipv string
local laag= 0 -- min temp
local hoog= 25 -- max temp
local timediff=timedifference(otherdevices_lastupdate['vijver-pomp'])
local pompstatus=otherdevices['vijver-pomp']
local pompbeveiliging=false
------------------------------------------------------------
-- bepaal wat er moet gebeuren
------------------------------------------------------------
-- normaal
if temp>laag and temp<hoog then
max_uit = 3600 -- 3600 sec (1 uur)
max_aan = 7200 -- 7200 sec (2uur)
end
-- warm
if temp>laag and temp>hoog then
max_uit = 1800 -- 1800 sec (30 min)
max_aan = 10800 -- 10800 sec (3uur)
end
-- koud
if temp<laag and temp<hoog then
pompbeveiliging=true
else
pompbeveiliging=false
end
------------------------------------------------------------
-- Doe wat er moet gebeuren normaal en warm
------------------------------------------------------------
if pompbeveiliging==false then -- alleen schakelen als de pompbeveiliging niet actief is
if otherdevices['pompstatus'] == 'Off' and timediff>max_uit then -- aanzetten als uit en te lang uit
commandarray['pompstatus']='On'
end
if otherdevices['pompstatus']== 'On' and timediff>max_aan then -- uitzetten als aan en te lang aan.
commandarray['pompstatus']='Off'
end
end
------------------------------------------------------------
-- Doe wat er moet gebeuren bij vorst
------------------------------------------------------------
if pompbeveiliging==true and otherdevices['pompstatus']=='On' then -- als pompbeveiliging actief is en pomp aan dan pomp uitzetten
commandarray['pompstatus']='Off'
end
return commandArray -- nu gaat domoticz wat we in commandarray hebben geplaatst ook werkelijk uitvoeren