dzVents 2.0 simple heating script editted for room control
mcmikev
Post by mcmikev »
Hi Danny,
It thought that it would be better to do this in an own topic.
The problem: script for room heating is editted and works fine with old version dzventz. Then the 2.x version came intergrated in domoticz and I changed the lines that needed to be compatible for the 2.x version to work.
That part I have figured out i hope , but the temp reading has some issues i think or some code is not as it should now to work with the 2.x version.
the code
-- assumptions:
-- the setpoint is set by a selector dummy device where the values are numeric temperatures
-- but you can easily change it to a setpoint device
local BOILER_DEVICE = 'State-CV-Badkamer' -- switch device
local SETPOINT_DEVICE = 'Thermostaat Badkamer' -- selector dummy device
local TEMPERATURE_SENSOR = 'TH-Badkamer'
local HYSTERESIS = 0.1 -- temp has to drop this value below setpoint before boiler is on again
local SMOOTH_FACTOR = 3
local LOGGING = true
local OVERRIDE_SWITCH = 'CV-Badkamer-Override' -- override switch
      timer = { 'every minute'},
      device = { TEMPERATURE_SENSOR, SETPOINT_DEVICE}
	data = {
		temperatureReadings = { history = true, maxItems = SMOOTH_FACTOR }
	active = true,
	execute = function(domoticz, device, triggerInfo)
		local avgTemp
		local temperatureReadings = domoticz.data.temperatureReadings
		-- first check if the sensor got a new reading or the setpoint was changed:
		if (triggerInfo.type == domoticz.EVENT_TYPE_DEVICE) then
			local sensor = domoticz.devices(TEMPERATURE_SENSOR)
			if (sensor.changed and sensor.attributeChanged('temperature')) then
				-- sensor just reported a new reading
				-- add it to the readings table
				local current = sensor.temperature
				if (current ~= 0 and current ~= nil) then
					temperatureReadings.add(current)
					-- no need to be here, weird state detected
					domoticz.log('Strange sensor reading.. skiping', domoticz.LOG_ERROR)
					return
			elseif (domoticz.devices(SETPOINT_DEVICE).changed) then
				-- a new setpoint was set
				if LOGGING then domoticz.log('Setpoint was set to ' .. device.state) end
				-- no business here, bail out...
				return
		-- now determine what to do
		local boiler = domoticz.devices(BOILER_DEVICE)
		local setpoint = domoticz.devices(SETPOINT_DEVICE)
		local override = domoticz.devices(OVERRIDE_SWITCH)
		if (setpoint.state == nil or setpoint.state == 'Off') then
			boiler.switchOff()
			return -- we're done here
		local setpointValue = tonumber(setpoint.state)
		-- determine at which temperature the boiler should be
		-- switched on
		local switchOnTemp = setpointValue - HYSTERESIS
		-- don't use the current reading but average it out over
		-- the past <SMOOTH_FACTOR> readings (data smoothing) to get rid of noise, wrong readings etc
		--local avgTemp = temperatureReadings.avg(1, SMOOTH_FACTOR)
		local avgTemp = temperatureReadings.avg(1, SMOOTH_FACTOR, 0) -- when there's no average, return 0 (or whatever you want it to return)
		if LOGGING then
			domoticz.log('Average: ' .. avgTemp, domoticz.LOG_INFO)
			domoticz.log('Setpoint: ' .. setpointValue, domoticz.LOG_INFO)
			domoticz.log('Current boiler state: ' .. boiler.state, domoticz.LOG_INFO)
			domoticz.log('Switch-on temperature: ' .. switchOnTemp, domoticz.LOG_INFO)
		if (avgTemp >= setpointValue and boiler.state == 'On') then
			if LOGGING then domoticz.log('Target temperature reached, boiler off') end
			boiler.switchOff()
			boiler.switchOff().afterMin(2)
		if (avgTemp < setpointValue and boiler.state == 'Off' and override.state == 'Off') then
			if (avgTemp < switchOnTemp) then
				if LOGGING then domoticz.log('Heating is required, boiler switched on') end
				boiler.switchOn()
				boiler.switchOn().afterMin(2)
				if LOGGING then domoticz.log('Average temperature below setpoint but within hysteresis range, waiting for temperature to drop to ' .. switchOnTemp) end
		if (boiler.state == 'On' and override.state == 'On') then
			if LOGGING then domoticz.log('Override is aan, CV Badkamer UIT') end
			boiler.switchOff()
He does not use the avg anymore and that gives the compare to nil error.
With the line you gave me to try, the avg is now 0 so the "temp" in the room is 0 so the heating always keeps turning on even though the setpoint is low.
Hope you can help out here ;)
dannybloe
Re: dzVents 2.0 simple heating script editted for room control
Post by dannybloe »
Yes, just dawned to me that it really resembles my own heating script that I used a while ago. Hahaha.
So, as I have been running that script for quite some time it should work (famous last words).
Anyway,
boiler.switchOff()
This looks weird. I don't know what Domoticz will do with these two commands.
But, what I would do is put print statements in the various locations and see if you get to the proper if-branches and what the values are. And I'd get rid of those weird double switch commands.
mcmikev
Post by mcmikev »
the double switch commands are needed because although the valves are zwave they seem to mis the commands now and then and then keep heating the room until tropical temps. (LC13 valves)
So the wakeup time is 180 seconds so by repeating the command after 2 minutes (most of the timesit works) they will do what I want. open or close.
Can you help out with the print statements?
dannybloe
Post by dannybloe »
oh, ok.
Oh, I see there are already logging statements every where. Make sure you have set the logging level in the settings to at least 'Errors + minimal execution info + generic info' and check the domoticz log. It should give you hints as to where the logic of you script is taking you.
mcmikev
Post by mcmikev »
2017-07-07 20:36:01.295  dzVents: Info:  ------ Start internal script: dz_cv_badkamer:, trigger: every minute
2017-07-07 20:36:01.297  dzVents: Debug: Device-adapter found for State-CV-Badkamer: Switch device adapter
2017-07-07 20:36:01.297  dzVents: Debug: Processing device-adapter for State-CV-Badkamer: Switch device adapter
2017-07-07 20:36:01.298  dzVents: Debug: Device-adapter found for Thermostaat Badkamer: Thermostat setpoint device adapter
2017-07-07 20:36:01.298  dzVents: Debug: Processing device-adapter for Thermostaat Badkamer: Thermostat setpoint device adapter
2017-07-07 20:36:01.298  dzVents: Debug: Device-adapter found for CV-Badkamer-Override: Switch device adapter
2017-07-07 20:36:01.298  dzVents: Debug: Processing device-adapter for CV-Badkamer-Override: Switch device adapter
2017-07-07 20:36:01.298  dzVents: Info:  Average: 0
2017-07-07 20:36:01.299  dzVents: Info:  Setpoint: 18
2017-07-07 20:36:01.299  dzVents: Info:  Current boiler state: Off
2017-07-07 20:36:01.299  dzVents: Info:  Switch-on temperature: 17.9
This is the logging. Have dzventz in debug mode
The avg temp = 0 and setpoint 18. Script does a if avg<setpoint do boiler on.
So right now the boiler always gets turned on :-(
My override switch is the only thing prevening it from doing it actualy :-)
If I remove the ,0 in the line you gave me so the script is "original" again i get the compare to nil again.
dannybloe
Post by dannybloe »
Ah, I think I see what's going on here. You don't have the latest code from the example. The idea is simple:
You do a sensor reading and put it into the storage (temperatureReadings.add(current)). Then, if you do an avg() later on, you always get at least the first reading as the average value. However, in your if-statement on line 32 you still have sensor.attributeChanged. That doesn't exist anymore in 2.0. You have to remove that:
if (sensor.changed) then
You see, in your version that if statement was never true so the current reading was never added to the history so your avg() was always calculating the average of 0 readings. My suggestion to add ,0 didn't help of course :).
Give it a try.. again
mcmikev
Post by mcmikev »
I have removed the ,0 from the line and changed the other line like you suggest.
2017-07-07 20:58:01.175  dzVents: Info:  ------ Start internal script: dz_cv_badkamer:, trigger: every minute
2017-07-07 20:58:01.177  dzVents: Debug: Device-adapter found for State-CV-Badkamer: Switch device adapter
2017-07-07 20:58:01.177  dzVents: Debug: Processing device-adapter for State-CV-Badkamer: Switch device adapter
2017-07-07 20:58:01.178  dzVents: Debug: Device-adapter found for Thermostaat Badkamer: Thermostat setpoint device adapter
2017-07-07 20:58:01.178  dzVents: Debug: Processing device-adapter for Thermostaat Badkamer: Thermostat setpoint device adapter
2017-07-07 20:58:01.178  dzVents: Debug: Device-adapter found for CV-Badkamer-Override: Switch device adapter
2017-07-07 20:58:01.179  dzVents: Debug: Processing device-adapter for CV-Badkamer-Override: Switch device adapter
2017-07-07 20:58:01.179  Error: dzVents: Error: An error occured when calling event handler dz_cv_badkamer
2017-07-07 20:58:01.179  Error: dzVents: Error: ...icz/scripts/dzVents/generated_scripts/dz_cv_badkamer.lua:78: attempt to concatenate local 'avgTemp' (a nil value)
line 78 is :
dannybloe
Post by dannybloe »
Ok, try this. I modified it a bit. Previously, if there hasn't been any reading yet, your history is empty and so the avg() is nil. Then the timer fires, and it tries to get the avg() on an empty history so there you have your error. So, I did a temp reading at the beginning of the script and have that as fallback (third param to avg) so you always have an avg():
(and I moved some declarations to the beginning as well)
-- assumptions:
		timer = { 'every minute' },
		device = { TEMPERATURE_SENSOR, SETPOINT_DEVICE }
	data = {
	active = true,
		local avgTemp
					return
				return
			boiler.switchOff()
		-- switched on
		local avgTemp = temperatureReadings.avg(1, SMOOTH_FACTOR, current)
		if LOGGING then
			boiler.switchOff()
				boiler.switchOn()
			boiler.switchOff()
mcmikev
Post by mcmikev »
seems to have done it ! APPLAUSE!!!
Dank je Danny!
I will test some more tomorrow. I see an average now
2017-07-07 21:22:01.124 dzVents: Info: ------ Start internal script: dz_cv_badkamer:, trigger: every minute
2017-07-07 21:22:01.126 dzVents: Debug: Device-adapter found for State-CV-Badkamer: Switch device adapter
2017-07-07 21:22:01.126 dzVents: Debug: Processing device-adapter for State-CV-Badkamer: Switch device adapter
2017-07-07 21:22:01.127 dzVents: Debug: Device-adapter found for Thermostaat Badkamer: Thermostat setpoint device adapter
2017-07-07 21:22:01.127 dzVents: Debug: Processing device-adapter for Thermostaat Badkamer: Thermostat setpoint device adapter
2017-07-07 21:22:01.128 dzVents: Debug: Device-adapter found for CV-Badkamer-Override: Switch device adapter
2017-07-07 21:22:01.128 dzVents: Debug: Processing device-adapter for CV-Badkamer-Override: Switch device adapter
2017-07-07 21:22:01.128 dzVents: Info: Average: 24.5
2017-07-07 21:22:01.128 dzVents: Info: Setpoint: 18
2017-07-07 21:22:01.128 dzVents: Info: Current boiler state: Off
2017-07-07 21:22:01.128 dzVents: Info: Switch-on temperature: 17.9
dannybloe
Post by dannybloe »
Logic always wins :-)
dannybloe
Post by dannybloe »
Oh and no need to keep debugging mode active as it will fill you logs quite easily.
mcmikev
Post by mcmikev »
I have disabled debug and execution and minimal info for now.
Morgen meer tijd om te testen maar zag er goed uit!
mcmikev
Post by mcmikev »
Hi Danny,
Well been testing and it looks to be fine again. Changed all my room scripts and tested with high setpoint temp to turn on the heating and that worked. Low setpoint temp turned it off again.
Now lets wait for winter to come :-)
PS: A lot of the example scripts are the "old version". Maybe wise to remove them from the integrated part????
dannybloe
Post by dannybloe »
I thought I converted all examples. But I'll look again.
Skippiemanz
Domoticz version: 4.10233
Post by Skippiemanz »
Dannybloe and Mcmikev,
I've used your script for switching on/off my boiler.
But i have several rooms with several valves.
If i now create multiple scripts and for example room 1 needs heat and room 2 is ok the boiler is switched on by room 1 and 1 min later switched off by the script of room 2.
How could this be solved?
Can there be more rooms/devices added? on https://github.com/bobkersten/domoticz- ... arming.lua
i saw the lua option like underneath:
local aThermostatDeviceNames = { 'Woonkamer Thermostaat', 'Badkamer Thermostaat', 'Entree Thermostaat' }			-- An array with the names of the thermostat pseudo devices above
local aThermostatWeights = { 12, 4, 1 }																				-- The priorities for the thermostats
local aTemperatureDeviceNames = { 'Woonkamer Temperatuur', 'Badkamer Temperatuur', 'Entree Sensor Temperatuur' }	-- An array with temperature sensor names that correspond to the thermostats above
local aValvesDeviceNames = { 'Vloerverwarming Pomp Schakelaar', nil, nil }											-- An array with comma separated valve device names.
local aPreHeat = { true, true, false }																				-- Wether or not to pre-heat the zone
local sTemperatureOutsideDeviceName = 'Buiten Temperatuur'															-- The name of an outside temperature sensor
local sHeatingDeviceName = 'CV Aansturing'																			-- The name of the on/off heating device
local fMeasureDeltaMinimum = 0.3																					-- Minimum temperatature delta measured to determine pre-heat duration
local iHeaterMinimumDuration = 3.5																					-- Minimum duration in minutes the heater is off or off to prevent to excessive switching
local iValveMinimumDuration = 4.5
Could this be usefull?
Also i have some windows sensors. Would be nice to integrate this also, so that it will be a complete multi zone solution.
mcmikev
Post by mcmikev »
Hi.
I don’t have boiler. I have city heating so the main valve is always open and I have temp sensor in every room that opens of closes the radiator
madrian
Post by madrian »
Thanks for this script, I am using it now 2 years back and it's working great.
In the last week I switched to Xiaomi Gateway & sensors and there is a little problem. These sensors send new temperature only when is a significant change in the temperature, that's sometimes takes long 10-15 minutes. With my "old" DIY sensor I red values at every 5 minutes so the "avgTemp" changed quickly. Not with the Xiaomi sensors...I must wait much longer to get "avgTemp" over the set value -> my heating running is running unnecessary.
Do you have any recommendation how to get "avgTemp" update more quickly/lower the smooth factor?
funnybu
Domoticz version: 3.9272
Post by funnybu »
It works perfect! But i don't understand, why you power off boiler twice?
boiler.switchOff()
dannybloe wrote: Friday 07 July 2017 21:14 Ok, try this. I modified it a bit. Previously, if there hasn't been any reading yet, your history is empty and so the avg() is nil. Then the timer fires, and it tries to get the avg() on an empty history so there you have your error. So, I did a temp reading at the beginning of the script and have that as fallback (third param to avg) so you always have an avg():
-- assumptions:
	data = {
	active = true,
		local avgTemp
					return
				return
			boiler.switchOff()
		-- switched on
		if LOGGING then
			boiler.switchOff()
				boiler.switchOn()
			boiler.switchOff()
mcmikev
Post by mcmikev »
The reason for switching on or off after 2 minutes was because sometimes the danfoss misses the off or on command the room stays cold or gets too hot.
Users browsing this forum: gvhoofst and 1 guest