Conditional timers and manual override
Spottyq
Domoticz version: 3.5877
Post by Spottyq »
Here is script used to make timers that can change dynamically and be overridden manually (until the next timer occurence.)
Take this snippet for instance :
{['device'] = 'Boiler Parents', ['schedule'] = {
  {['value'] = 'On',  ['condition'] = presence({'Invités'})},
  {['value'] = 'On',  ['timeInterval'] = {{ 4, 0},{ 7,15}}},
  {['value'] = 'On',  ['timeInterval'] = {{12, 0},{16, 0}}, ['wDays'] = {0,0,0,0,0,1,1}},
  {['value'] = 'On',  ['timeInterval'] = {{19, 0},{22, 0}}},
  {['value'] = 'Off'}
It will turn the water heater on whenever there are guests (‘Invités’) home (1st line).
During a normal day, it will turn on the morning (2) and evening (4), plus an extra period the afternoon (3).
Otherwise, it should be off (5).
presence() is a function that takes an array of strings. It checks if any virtual device named “Presence <someone>” is activated (the prefix and suffix of the virtual switch is configurable manually.)
I think it is pretty much human readable, while still allowing some complex schedules. :-)
I use this script with On/Off switches, dimmers (percentage) and thermostat setpoints (for these, please see my examples of how to set them up; the idx must be included.)
For thermostat, I have made a workaround for ugly graphs. It will set a value every 15 minutes, to ensure the graph line is horizontal. Activate it by changing the value of ‘thermostatGraphWorkaround’ to ‘true’.
I recommend you name the script ’Timers’ (otherwise, change the variable scriptName) and setting the script to run every minute (the ‘time’ option in Domoticz.)
    This script is intended to be run every minute ('time' setting in Domoticz).
    Device is the Domoticz name of the device you want to control. Ex: ['device'] = 'Relay 1'
    Schedule contains a table with the schedule
    First format must contain : value. May contain: time, timeInterval, wDays, condition (something not explicitely defined is considered to be always true)
    A time. DO NOT ADD A LEADING 0. Ex : ['time'] = {23, 9} DON'T WRITE : {23,09}
    A timeInterval. Ex: 1:00 to 13:30 : ['timeInterval'] = {{ 1,30},{13, 0}}
                        00:00 to 1:00 and 20:00 to 24:00 : {{20, 0},{ 1, 0}}
    A wDays : Ex: only the weekends : ['wDays'] = {0,0,0,0,0,1,1}
    Whether it is enabled or not (default is enabled). Ex : ['enabled'] = false
    A value. May be anything. Will be sent to domoticz via the commandArray
    A condition. True if this timer is supposed to be active. (I recommend writing a function.) Ex:['condition'] = checkPresence()
    For some domoticz devices, the 'normal' way to control them does not work. If it is the case (for ex. thermostat devices) use a workaround
        - UpdateDevice. Should specify the idx of the device. Ex : ['idx'] = '45', ['type'] = 'UpdateDevice'
    If you want the manual override to work, create a uservariale named 'Timer-<deviceName>-LastSetPoint'. Ex : 'Timer-HallLight-LastSetPoint of type String.
    If that variable does not exist, the timer will work but the manual override won't.
    Assumptions :   - the first day of the week is monday
                    - Device state in Domoticz == actual device state
                    - nil is used internally; should not be used by a device
    The first timer to match all his criterias is applied, without going further. A criteria that is not set is considered to be true
    If you don't set a value for a timer, the script won't update the device. Use if you want manual control.
    Known bugs :    - manual override only works if there were at least 2 minutes between automatic changes.
                    - manual override does not work with devices who use percentages
function initializeTimer()
    timers = {
        {['device'] = 'Boiler Aymeric', ['enabled'] = false, ['schedule'] = {
            {['value'] = 'On',  ['timeInterval'] = {{ 5,30},{ 8,30}}, ['condition'] = presence({'Aymeric', 'Quentin'})},
            {['value'] = 'On',  ['timeInterval'] = {{17, 0},{22, 0}}, ['condition'] = presence({'Aymeric', 'Quentin'})},
            {['value'] = 'Off'}
        {['device'] = 'Boiler Parents', ['enabled'] = false, ['schedule'] = {
            {['value'] = 'Off'}
        {['device'] = 'Presence Quentin', ['enabled'] = false, ['schedule'] = {
            {['value'] = 'On',  ['timeInterval'] = {{19, 0},{ 8, 0}}},
            {['value'] = 'Off'}
        {['device'] = 'Presence Aymeric', ['schedule'] = {
            {['value'] = 'On',  ['wDays'] = {0,0,0,0,0,1,1}},
            {['value'] = 'On',  ['timeInterval'] = {{17, 0},{23,59}}, ['wDays'] = {0,0,0,0,1,0,0}},
            {['value'] = 'Off'}
        {['device'] = 'Ventilation', ['enabled'] = false, ['type'] = 'Dimmer', ['schedule'] = {
            {['value'] = 90, ['condition'] = presence({'Quentin', 'Invités'})},
            {['value'] = 50, ['timeInterval'] = {{ 6,45},{ 7,45}}},
            {['value'] = 50, ['timeInterval'] = {{17, 0},{21, 0}}},
            {['value'] = 10}
        {['device'] = 'Consigne Salon', ['idx'] = '45', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 20, ['timeInterval'] = {{ 9, 0},{20, 0}}, ['condition'] = presence({'Invités'})},
            {['value'] = 20, ['condition'] = chauffageHeureDePointe()},
            {['value'] = 18}
        {['device'] = 'Consigne Cuisine', ['idx'] = '40', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 19, ['timeInterval'] = {{15,30},{20, 0}}},
            {['value'] = 17}
        {['device'] = 'Consigne Bureau', ['idx'] = '261', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 18, ['condition'] = chauffageHeureDePointe()},
            {['value'] = 15}
        {['device'] = 'Consigne Mezzanine', ['idx'] = '43', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 19, ['condition'] = chauffageHeureDePointe()},
            {['value'] = 18}
        {['device'] = 'Consigne Ch Parents', ['idx'] = '38', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 17, ['timeInterval'] = {{ 6, 0},{ 6,40}}},
            {['value'] = 17, ['timeInterval'] = {{19, 0},{22, 0}}},
            {['value'] = 15}
        {['device'] = 'Consigne Ch Quentin', ['idx'] = '46', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 19, ['timeInterval'] = {{ 7, 0},{19, 0}}, ['condition'] = presence({'Quentin'})},
            {['value'] = 17, ['timeInterval'] = {{19, 0},{ 7, 0}}, ['condition'] = presence({'Quentin'})},
            {['value'] = 10}
        {['device'] = 'Consigne Hall', ['idx'] = '44', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 16}
        {['device'] = 'Consigne SdB Parents', ['idx'] = '262', ['type'] = 'UpdateDevice', ['schedule'] = {
            {['value'] = 19, ['timeInterval'] = {{ 6, 0},{ 8, 0}}},
            {['value'] = 18, ['timeInterval'] = {{21, 0},{22, 0}}},
            {['value'] = 17}
-- User functions
function chauffageHeureDePointe()
    return isInTimeInterval({{15, 0},{21, 0}});
-- Variable declarations
scriptName = 'Timers'   --Used for debug messages
presencePrefix = 'Presence '
presenceSuffix = ''
thermostatGraphWorkaround = true    -- Sets the temperature every 15 minutes, even if it has not changed.
                                    -- Used to have better graphs in Domoticz.
                                    -- Will work only if the value is continually set (use timeInterval instead of time)
                                    -- !! Needs some uservariables
FirstDayOfWeekIsMonday = true --Maybe buggy. Has not been tested when false
domoticzIP='192.168.1.30'
now = {tonumber(os.date("%H")), tonumber(os.date("%M"))}
-- Helper functions
function needToActivateWorkaround(deviceName)
    if not thermostatGraphWorkaround then
        return false
    if deviceName == nil then
        return exitFailure('needToActivateWorkaround : received nil');
    if timeDifferenceInMin(otherdevices_lastupdate[deviceName]) >= 45 then
        return true
    return false
function timeDifferenceInMin(s)
   year = string.sub(s, 1, 4)
   month = string.sub(s, 6, 7)
   day = string.sub(s, 9, 10)
   hour = string.sub(s, 12, 13)
   difference = os.difftime (os.time(), t2)
   return math.floor(difference/60)
function getLastSetPointUserVarFromDeviceName(string)
    return 'Timer-' .. string .. '-LastSetPoint'
function setValueByUpdateDevice(deviceName, idx, value)
    if (deviceName == nil or idx == nil or value == nil) then
        return exitFailure('function setValueByUpdateDevice received some nil value')
    value = tostring(value)
    if tonumber(otherdevices[deviceName]) ~= tonumber(value) then
        if tonumber(value) ~= tonumber(uservariables[getLastSetPointUserVarFromDeviceName(deviceName)]) then --SetPoint has just changed
            commandArray['Variable:' .. getLastSetPointUserVarFromDeviceName(deviceName)] = value
            commandArray[#commandArray + 1] = {['UpdateDevice']=idx .. '|' .. value .. '|' .. value}
        elseif needToActivateWorkaround(deviceName) then --Manual override + graphWorkaround
            value = tostring(otherdevices[deviceName])
    elseif needToActivateWorkaround(deviceName) then --Graphworkaround
function checkDevice(device)
    if device.enabled ~= nil and not (device.enabled == true or device.enabled == 1 or device.enabled == 'true') then
        return true
    local value = getCurrentValue(device.schedule)
    if value == nil then
        return true
    if device.type == nil then
        setValue(device.device, value)
        return true
    elseif device.type == 'UpdateDevice' then
        if (device.idx == nil) then
            return exitFailure('function checkDevice : device ' .. device.device .. ' does not have an idx')
        setValueByUpdateDevice(device.device, device.idx, value)
        return true
    elseif device.type == 'Dimmer' then
        setValueForDimmer(device.device, value);
        return true
        return exitFailure('function checkDevice : device ' .. device.device .. ' has an unknow type : ' .. device.type)
function setValue(device, value)
    if value ~= uservariables[getLastSetPointUserVarFromDeviceName(device)] then --SetPoint has just changed
        commandArray['Variable:' .. getLastSetPointUserVarFromDeviceName(device)] = value
        if otherdevices[device] ~= value then
            commandArray[device] = value
function setValueForDimmer(device, value)
    if tostring(value) ~= tostring(uservariables[getLastSetPointUserVarFromDeviceName(device)]) then --SetPoint has just changed
        commandArray['Variable:' .. getLastSetPointUserVarFromDeviceName(device)] = tostring(value)
            commandArray[device] = 'Set Level ' .. tostring(value)
-- May return nil (if there is no valid timer. In that case, the device won't be updated)
function getCurrentValue(schedule)
    local value
    for key, timer in pairs(schedule) do
        local val = getCurrentValueFromTimer(timer)
        if val ~= nil then
            value = val
            break
    return value
function getWeekDayOfToday()
    local weekDayOffSet = 1
    if (FirstDayOfWeekIsMonday) then
        weekDayOffSet = 0
    wDay = tonumber(os.date('%w'))+weekDayOffSet
    if (wDay < 0 or wDay > 6) then
        return exitFailure('weekDayOffSet is wrongly set !')
    return wDay
function isInTimeInterval(interval)
    if not (type(interval) == "table" and #interval == 2 and isAValidTime(interval[1]) and isAValidTime(interval[2])) then
        return exitFailure('function isInTimeInterval(interval) : interval is not valid or time is not valid')
    if (compareTimes(interval[1], interval[2])) then
        return compareTimes(interval[2], now) or compareTimes(now, interval[1])
        return compareTimes(now, interval[1]) and compareTimes(interval[2], now)
function isItTime(time)
    if not isAValidTime(time) then
        return exitFailure('isItTime : received wrong time')
    if time[2] == tonumber(os.date('%M')) and time[1] == tonumber(os.date('%H')) then
        return true
        return false
function isInWeekDay(wDays)
    if wDays == nil or #wDays ~= 7 then
        return exitFailure('wDays is declared incorrectly')
    return wDays[getWeekDayOfToday()] == 1
function isAValidTime(time)
    if not (type(time) == 'table' and #time == 2) then
        return false
    hour = time[1]
    min = time[2]
    if not (type(hour) == 'number' and type(min) == 'number') then
        return false
    elseif (hour < 0 or hour > 23 or min < 0 or min > 59) then
        return false
    return true
-- Returns true if time1 is greater or equal to time2, false otherwise
function compareTimes(time1, time2)
    if (time1[1] > time2[1]) then
        return true
    elseif (time1[1] == time2[1]) then
        if (time1[2] >= time2[2]) then
            return true
    return false
-- Does not exit on its own… use return exitFailure(…)
function exitFailure(string)
    print(scriptName .. " failure ! Error : " .. string)
    return nil
function isempty(s)
  return s == nil or s == ''
-- Returns true if >= 1 person from the list is present; nil if there is an error
function presence(names)
    if (isempty(names)) then
        return exitFailure('function presence(...) : received nil')
    elseif (type(names) == 'array') then
        return exitFailure('function presence(...) : expecting a table')
    for key, name in pairs(names) do
        if otherdevices[presencePrefix .. name .. presenceSuffix] == nil then
            return exitFailure('function presence(...) : switch does not exist for ' .. name)
        if otherdevices[presencePrefix .. name .. presenceSuffix] == 'On' then
            return true
    return false
-- Returns the value or nil if the timer is not supposed to be active now
function getCurrentValueFromTimer(timer)
    valueSet = false
    for key, value in pairs(timer) do
        if key == 'value' then
            valueSet = true
        elseif key == 'time' then
            if not isItTime(timer.time) then
                return nil
        elseif key == 'timeInterval' then
            if not isInTimeInterval(timer.timeInterval) then
                return nil
        elseif key == 'wDays' then
            if not isInWeekDay(timer.wDays) then
                return nil
        elseif key == 'condition' then
            if not timer.condition then
                return nil
            return exitFailure('function getValueFromTimer : error in a key name for a timer or too many conditions')
    if valueSet then
        return timer.value
        return exitFailure('function getValueFromTimer : a timer has no value')
-- Main
initializeTimer()
for key, device in pairs(timers) do
    if checkDevice(device) == nil then
        return exitFailure('Main : checkDevice returned nil')
Let me know what you think of it !
zicht
Domoticz version: 2023.1+
Re: Conditional timers and manual override
Post by zicht »
Looks nice, but why not using the timers in the GUI ?
I cannot think of any additional benefit in my home for this, maybe you have some great ideas that inspire me too ?
Spottyq
Post by Spottyq »
The timers in the GUI are great as long as you don't need conditional timers. (Manual override works fine.)
In my hot water heater example, it is impossible to have the boiler always on when guests are home (when a virtual switch is turned on) using only GUI timers.
It also allow to edit all the timers in one place, rather than on each device. (Handy when you have 8 thermostats ! :) )