dzVents 1.0 released
dannybloe
Re: dzVents 1.0 released
Post by dannybloe »
well, problem solved :) (for now)
dhanjel
Domoticz version: 3.5146
Post by dhanjel »
yup
still hoping for dzVents to be part of the main code base though, would make life so much easier :)
dannybloe
Post by dannybloe »
We are working on it :-)
fergalom
Post by fergalom »
Query on my code:
I have a number (39) of user variables being populated from an alarm system with the values "ok" or "alarm"
I want to monitor them for the "alarm" value and if "alarm" I want to turn on a switch in domoticz and send a notification
This is my code:
    active = true ,
    on = { 'timer' },
    execute = function(domoticz)
    domoticz.variables.forEach(function(variable)
        print(variable.Value)
        if (variable.Value == 'alarm') then
            domoticz.devices['Alarm Triggered'].switchOn()
            domoticz.notify('Alarm triggered Event Test!', '', domoticz.PRIORITY_EMERGENCY)
            domoticz.devices['Alarm Triggered'].switchOff()
    end)
Below is the json call output from one of the user variables
http://domoticz.server.net:8080/json.ht ... ble&idx=63
result: [
LastUpdate: "2016-07-06 13:56:37",
Type: "2",
Value: "alarm",
idx: "63"
status: "OK",
title: "GetUserVariable"
From domoticz log:
2016-07-06 15:08:41.309 (RaZberry) Temp (HW Tank Temp)
2016-07-06 15:09:00.579 LUA: =====================================================
2016-07-06 15:09:00.579 LUA: >>> Handler: spc_alarm
2016-07-06 15:09:00.579 LUA: .....................................................
2016-07-06 15:09:00.582 LUA: .....................................................
2016-07-06 15:09:00.582 LUA: <<< Done
2016-07-06 15:09:00.582 LUA: -----------------------------------------------------
2016-07-06 15:09:00.582 LUA: [1] = Alarm Triggered: Off
2016-07-06 15:09:00.582 LUA: [2] = Alarm Triggered: Off
2016-07-06 15:09:00.582 LUA: [3] = Alarm Triggered: Off
2016-07-06 15:09:00.582 LUA: [4] = Alarm Triggered: Off
2016-07-06 15:09:00.582 LUA: [5] = Alarm Triggered: Off
2016-07-06 15:09:00.582 LUA: [6] = Alarm Triggered: Off
2016-07-06 15:09:00.582 LUA: [7] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [8] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [9] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [10] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [11] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [12] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [13] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [14] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [15] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [16] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [17] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [18] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [19] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [20] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [21] = Alarm Triggered: Off
2016-07-06 15:09:00.583 LUA: [22] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [23] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [24] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [25] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [26] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [27] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [28] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [29] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [30] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [31] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [32] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [33] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [34] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [35] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [36] = Alarm Triggered: Off
2016-07-06 15:09:00.584 LUA: [37] = Alarm Triggered: Off
2016-07-06 15:09:00.585 LUA: [38] = Alarm Triggered: Off
2016-07-06 15:09:00.585 LUA: [39] = Alarm Triggered: Off
2016-07-06 15:09:00.585 LUA: =====================================================
2016-07-06 15:09:00.610 EventSystem: Script event triggered: /home/pi/domoticz/scripts/lua/script_time_main.lua
2016-07-06 15:09:00.843 (DUMMY) Lighting 1 (Alarm Triggered)
It does not seem to be picking up a test user variable in "alarm" and switching 'Alarm Triggered' switch on and sending the notification.
Any pointers on what is wrong with my code?
dannybloe
Post by dannybloe »
fergalom wrote:Query on my code:
This is my code:
    active = true ,
    on = { 'timer' },
    	local switched = false
            print(variable.value)
            if (switched == false) then
	            switched = true
    end)
Ah, it took me a little but it should be variable.value (lowercase)
And I would alter the script a bit not to flood Domoticz with unnecessary commands:
	active = true ,
	on = { 'timer' },
		local alarmTrigger = domoticz.devices['Alarm Triggered']
		local switchCmd = 'Off'
			if (variable.value == 'alarm') then
				switchCmd = 'On'
		end)
		if (switchCmd == 'On' and alarmTrigger.state == 'Off') then
			alarmTrigger.switchOn()
		elseif (alarmTrigger.state == 'On') then
			-- only switchOff if it was On
			alarmTrigger.switchOff()
fergalom
Post by fergalom »
Thanks for that and the improvements!
One final question, instead of checking every minute using timer, can this work with Uservariables similar to devices?
   active = true ,
   on = { 'G_SPC_ZONE_STATUS_*'},
   etc
   etc
dannybloe
Post by dannybloe »
Unfortunately not. Domoticz doesn't throw an event and triggers scripts when a variable changes. Only if you change the variable from the UI.
I do have plans though to have this work for dzVents persistent variables and have other scripts create triggers for when global variables change.
What triggers the updating of these variables in your case? Coz if your alarm system could toggle a dummy switch instead of setting a variable, then you'r done. You can have a script that is triggered if any of these dummy switches is toggled.
fergalom
Post by fergalom »
I have a node.js script that talks to the alarm panel and dynamically creates the uservariables for each zone / pir / contact etc.
You are right, I could get the node.js script to set a switch if there is an alarm.
I think Domoticz does trigger scripts on variable changes - I currently have it changing switches depending on a door contact or alarm set/unset uservariables changing.
In my normal lua directory ~/domoticz/scripts/lua/
script_variable_spc.lua
logging = true
if (uservariablechanged['G_SPC_AREA_House'] == 'unset') then
   commandArray['House Alarm Set/Unset']='Off'
elseif (uservariablechanged['G_SPC_AREA_House'] == 'set') then
   commandArray['House Alarm Set/Unset']='On'
if (uservariablechanged['G_SPC_ZONE_INPUT_Front_Door'] == 'open' and  otherdevices['Front Door']=='Closed') then
   commandArray['UpdateDevice']='122|1|Open'
   print('Front Door Open')
elseif (uservariablechanged['G_SPC_ZONE_INPUT_Front_Door'] == 'closed' and  otherdevices['Front Door']=='Open') then
   commandArray['UpdateDevice']='122|0|Closed'
   print('Front Door Closed')
dzvents is useful for me because of the foreach function.
dannybloe
Post by dannybloe »
Maybe it triggers it indeed because changing the variable through a url is basically the same as doing it in the Domoticz UI. The thing is that it doesn't work if you do an update through the commandArray.
I think I can make dzVents work with variable events (and security).
jkimmel
Domoticz version: 2021.1
Post by jkimmel »
Nice.
I just added an example script in the dev branch that controls heating in one room where a setpoint device, a temp-sensor and a boiler switch work together with some basic hysteresis control. You could duplicate the script for all device or adapt it to support multi-rooms. It uses one hystorical variable to catch unwanted peaks in the temperature readings. The script is triggered by device events and timer events all in one.
@dannyblue
please have a look at your example
	local avgTemp = temperatureReadings.avg(1, SMOOTH_FACTOR)
leads to
lua:76: attempt to concatenate local 'avgTemp' (a nil value)
Rfxcom
Raspi 4
dannybloe
Post by dannybloe »
jkimmel wrote:
Nice.
@dannyblue
leads to
That surely isn't what it should do ;-)
I'll look into it. Thanks for testing.
Will after the weekend though... going for a weekend trip to Berlin.
jkimmel
Post by jkimmel »
dannybloe wrote:
jkimmel wrote:
Nice.
@dannyblue
leads to
Any news?
Rfxcom
Raspi 4
dannybloe
Post by dannybloe »
jkimmel wrote:
dannybloe wrote:
jkimmel wrote:
Any news?
So sorry but my house is a construction area right now (renovation and isolation) which will take at least one or two weeks so I don't have time to fix that I think. I will try but no promises. On the other hand... pull requests are always welcome ;-) Again sorry.
jkimmel
Post by jkimmel »
dannybloe wrote:
jkimmel wrote:
Solved. There had been not enough values
Rfxcom
Raspi 4
jkimmel
Post by jkimmel »
dannybloe wrote:
jkimmel wrote:
Take you time, but here is my next question concerning the following code
-- assumptions:
-- the setpoint is set by a selector dummy device where the values are numeric temperatures
-- but you can easily change it to a setpoint device
local BOILER_DEVICE = 'FB 41 Heizkreis Gaestebad' -- switch device
local SETPOINT_DEVICE = 'Setpoint Gaestebad' -- selector dummy device
local TEMPERATURE_SENSOR = 'Gaestebad'
local HYSTERESIS = 0.5 -- temp has to drop this value below setpoint before boiler is on again
local SMOOTH_FACTOR = 3
local LOGGING = true
		['timer'] = 'every minute',
		TEMPERATURE_SENSOR,
		SETPOINT_DEVICE
	data = {
		temperatureReadings = { history = true, maxItems = SMOOTH_FACTOR }
	active = true,
	execute = function(domoticz, device, triggerInfo)
		local avgTemp
		local temperatureReadings = domoticz.data.temperatureReadings
		-- first check if the sensor got a new reading or the setpoint was changed:
		if (triggerInfo.type == domoticz.EVENT_TYPE_DEVICE) then
			local sensor = domoticz.devices[TEMPERATURE_SENSOR]
			if (sensor.changed and sensor.attributeChanged('temperature')) then
				-- sensor just reported a new reading
				-- add it to the readings table
				local current = sensor.temperature
				if (current ~= 0 and current ~= nil) then
					temperatureReadings.add(current)
					-- no need to be here, weird state detected
					domoticz.log('Strange sensor reading.. skiping', domoticz.LOG_ERROR)
					return
			elseif (domoticz.devices[SETPOINT_DEVICE].changed) then
				-- a new setpoint was set
				if LOGGING then domoticz.log('Setpoint was set to ' .. device.state) end
				-- no business here, bail out...
				return
		-- now determine what to do
		local boiler = domoticz.devices[BOILER_DEVICE]
		local setpoint = domoticz.devices[SETPOINT_DEVICE]
		if (setpoint.state == nil or setpoint.state == 'Off') then
			boiler.switchOff()
			return -- we're done here
		local setpointValue = tonumber(setpoint.state)
		-- determine at which temperature the boiler should be
		-- switched on
		local switchOnTemp = setpointValue - HYSTERESIS
		-- don't use the current reading but average it out over
		-- the past <SMOOTH_FACTOR> readings (data smoothing) to get rid of noise, wrong readings etc
		if LOGGING then
			domoticz.log('Average: ' .. avgTemp, domoticz.LOG_INFO)
			domoticz.log('Setpoint: ' .. setpointValue, domoticz.LOG_INFO)
			domoticz.log('Current boiler state: ' .. boiler.state, domoticz.LOG_INFO)
			domoticz.log('Switch-on temperature: ' .. switchOnTemp, domoticz.LOG_INFO)
		if (avgTemp >= setpointValue and boiler.state == 'On') then
			if LOGGING then domoticz.log('Target temperature reached, boiler off') end
			boiler.switchOff()
		if (avgTemp < setpointValue and boiler.state == 'Off') then
			if (avgTemp < switchOnTemp) then
				if LOGGING then domoticz.log('Heating is required, boiler switched on') end
				boiler.switchOn()
				if LOGGING then domoticz.log('Average temperature below setpoint but within hysteresis range, waiting for temperature to drop to ' .. switchOnTemp) end
the protocol shows different outcomes
2016-11-07 20:20:38.697 LUA: Handling events for: "Gaestebad_Dewpoint", value: "12.422341346741"
2016-11-07 20:20:38.698 LUA: =====================================================
2016-11-07 20:20:38.698 LUA: >>> Handler: Heizung Gaestebad
2016-11-07 20:20:38.698 LUA: >>> Device: "Gaestebad" Index: 280
2016-11-07 20:20:38.698 LUA: .....................................................
2016-11-07 20:20:38.707 LUA: Average: 21
2016-11-07 20:20:38.708 LUA: Setpoint: 15
2016-11-07 20:20:38.708 LUA: Current boiler state: Off
2016-11-07 20:20:38.709 LUA: Switch-on temperature: 14.5
2016-11-07 20:20:38.713 LUA: .....................................................
2016-11-07 20:20:38.713 LUA: <<< Done
2016-11-07 20:20:38.714 LUA: -----------------------------------------------------
2016-11-07 20:21:00.718 LUA: >>> Handler: Heizung Gaestebad
2016-11-07 20:21:00.718 LUA: .....................................................
2016-11-07 20:21:00.725 LUA: Average: 21
2016-11-07 20:21:00.725 LUA: Setpoint: 15
2016-11-07 20:21:00.725 LUA: Current boiler state: Off
2016-11-07 20:21:00.726 LUA: Switch-on temperature: 14.5
2016-11-07 20:21:00.731 LUA: .....................................................
2016-11-07 20:21:00.731 LUA: <<< Done
2016-11-07 20:21:00.731 LUA: -----------------------------------------------------
2016-11-07 20:21:00.732 LUA: =====================================================
2016-11-07 20:21:21.555 LUA: Handling events for: "Gaestebad_Temperature", value: "21"
2016-11-07 20:21:21.556 LUA: =====================================================
2016-11-07 20:21:21.556 LUA: >>> Handler: Heizung Gaestebad
2016-11-07 20:21:21.556 LUA: >>> Device: "Gaestebad" Index: 280
2016-11-07 20:21:21.556 LUA: .....................................................
2016-11-07 20:21:21.565 LUA: Average: 21
2016-11-07 20:21:21.566 LUA: Setpoint: 15
2016-11-07 20:21:21.566 LUA: Current boiler state: Off
2016-11-07 20:21:21.566 LUA: Switch-on temperature: 14.5
2016-11-07 20:21:21.571 LUA: .....................................................
2016-11-07 20:21:21.571 LUA: <<< Done
2016-11-07 20:21:21.571 LUA: -----------------------------------------------------
2016-11-07 20:22:00.839 LUA: -----------------------------------------------------
2016-11-07 20:22:04.556 LUA: Handling events for: "Gaestebad_Humidity", value: "58"
2016-11-07 20:22:04.556 LUA: =====================================================
2016-11-07 20:22:04.556 LUA: >>> Handler: Heizung Gaestebad
2016-11-07 20:22:04.557 LUA: >>> Device: "Gaestebad" Index: 280
2016-11-07 20:22:04.557 LUA: .....................................................
2016-11-07 20:22:04.565 LUA: Average: 21
2016-11-07 20:22:04.566 LUA: Setpoint: 15
2016-11-07 20:22:04.566 LUA: Current boiler state: Off
2016-11-07 20:22:04.566 LUA: Switch-on temperature: 14.5
2016-11-07 20:22:04.571 LUA: .....................................................
2016-11-07 20:22:04.571 LUA: <<< Done
2016-11-07 20:22:04.571 LUA: -----------------------------------------------------
2016-11-07 20:22:47.556 LUA: Handling events for: "Gaestebad", value: "21.0;58;1"
2016-11-07 20:22:47.556 LUA: =====================================================
2016-11-07 20:22:47.556 LUA: >>> Handler: Heizung Gaestebad
2016-11-07 20:22:47.557 LUA: >>> Device: "Gaestebad" Index: 280
2016-11-07 20:22:47.557 LUA: .....................................................
2016-11-07 20:22:47.566 LUA: Average: 21
2016-11-07 20:22:47.566 LUA: Setpoint: 15
2016-11-07 20:22:47.566 LUA: Current boiler state: Off
2016-11-07 20:22:47.567 LUA: Switch-on temperature: 14.5
2016-11-07 20:22:47.571 LUA: .....................................................
2016-11-07 20:22:47.571 LUA: <<< Done
2016-11-07 20:22:47.572 LUA: -----------------------------------------------------
2016-11-07 20:26:22.553 LUA: Handling events for: "Gaestebad_Dewpoint", value: "12.422341346741"
2016-11-07 20:26:22.554 LUA: =====================================================
2016-11-07 20:26:22.554 LUA: >>> Handler: Heizung Gaestebad
2016-11-07 20:26:22.554 LUA: >>> Device: "Gaestebad" Index: 280
2016-11-07 20:26:22.554 LUA: .....................................................
2016-11-07 20:26:22.563 LUA: Average: 21
2016-11-07 20:26:22.563 LUA: Setpoint: 15
2016-11-07 20:26:22.564 LUA: Current boiler state: Off
2016-11-07 20:26:22.564 LUA: Switch-on temperature: 14.5
2016-11-07 20:26:22.568 LUA: .....................................................
2016-11-07 20:26:22.569 LUA: <<< Done
2016-11-07 20:26:22.569 LUA: -----------------------------------------------------
Why are all values questioned?
Rfxcom
Raspi 4
guiguid
Post by guiguid »
just pushing a pull request for leaking detection.
-- Water leak detection
-- assumptions:
-- need 2 devices :
-- a Water Flow devices name "Water_Flow"
-- a Dummy Device type percentage "Leakage_Percent"
-- 1 / leakage "open valve"
-- Every minute if a non-zero water flow is present, it incerments a counter (Leakage_Percent)
-- If the water flow is zero is that it leaks more continuously.
-- A notification can be put on "Leakage_Percent" if >80% (80% = 80 minutes of continuous flow)
-- 2 / "micro continuous flow" (drip)
-- in 24 hours one must have at least 2 hours without flow (detection 0.5 liters / hour is 4.5m3 / year)
-- if not, "Leakage_Percent" is forced at 100%.
local FLOW_DEVICE = 'Water_Flow' -- Flow device
local LEAK_DEVICE = 'Leakage_Percent' -- percent dummy device
    active = true,
    data = {
		time_0_flow = { initial = 0 },
		total_time = { initial = 0 },
    	-- Flow in liter/minute
        local flow = tonumber(domoticz.devices[FLOW_DEVICE].rawData[1])
        -- Dummy device in %
        local leakage = domoticz.devices[LEAK_DEVICE]
        local time_with_flow = tonumber(leakage.rawData[1])
        local new_time_with_flow = time_with_flow
        if (flow > 0) then
           domoticz.data.time_0_flow = 0  -- there is a flow
           new_time_with_flow = new_time_with_flow + 1 -- time with flow
           if (new_time_with_flow > 100) then
             	new_time_with_flow = 100
           new_time_with_flow = 0
           domoticz.data.time_0_flow = domoticz.data.time_0_flow + 1 -- time without flow
-- 2 / flight type "micro continuous flow" (drip)
        domoticz.data.total_time = domoticz.data.total_time + 1 -- time without since last 2 hours with no flow
        if (domoticz.data.time_0_flow > 120) then
            -- 2 hours with no flow
            domoticz.data.total_time = 0
        elseif (domoticz.data.total_time > (60*24)) then
        	-- 24 heures since last 2 hours with no flow
-- log
        domoticz.log(new_time_with_flow .. ' minutes with flow ')
        domoticz.log(domoticz.data.time_0_flow .. ' minutes without flow ')
        domoticz.log(domoticz.data.total_time .. ' minutes witout 2hrs witout flow ')
 -- update dummy device %
        if (time_with_flow ~= new_time_with_flow) then
         leakage.update(0,new_time_with_flow)
I hope it'll be usefull for someone
guiguid
