dzVents script for heating control [SOLVED]
Re: dzVents script for heating control
Does the scrtipt calculate the heating start point in order to reach the setpoint as soon as the required time zone starts?
Or is it just working during the selected time zone?
in other words: Does this script 'think ahead'?
It does not think ahead. Depending on the time zone set and setpoint it tries to keep the temperature in the hysteresis range.
-- switching the boiler on or off if the set temperature has been reached
local temp_to_compare = domoticz.devices(devHEAT).state
local switchOnTemp = temp_set - HISTERESIS
local switchOffTemp = temp_set + HISTERESIS
- Domoticz version: 3.9272
What is happen (with mode switched) if i just click on "Fire icon" on "Workin mode" device?
- Domoticz version: 4.10717
hello:
thank you very much for this good script, with all my respect towards the author, I have translated it into my usual language.
But the object of this message is the error that appears to me and that I have highlighted it in red.
What can be the cause?
2018-10-31 16:10:00.659 Status: dzVents: Info: ------ Start internal script: BEROGAILU dzvents:, trigger: every 2 minutes
2018-10-31 16:10:00.659 Status: dzVents: !Info:
2018-10-31 16:10:00.660 Status: dzVents: !Info: **************************************************************************
2018-10-31 16:10:00.660 Status: dzVents: !Info: 1. Control de calefacción - iniciar la depuración versión -> 2.3
2018-10-31 16:10:00.660 Status: dzVents: !Info: En el momento de inicio del script:
2018-10-31 16:10:00.660 Status: dzVents: !Info: --------------------------------------------------------------------------
2018-10-31 16:10:00.760 Status: dzVents: !Info: > RELE -1- -> Off
2018-10-31 16:10:00.769 Status: dzVents: !Info: > TEMPERATURA SALA -> 20.1
2018-10-31 16:10:00.772 Status: dzVents: !Info: > Current working status CO -> >AUTO< Heating temp.: 19.5 dg.
2018-10-31 16:10:00.787 Status: dzVents: !Info: > Temperatura Confort -> 19.50
2018-10-31 16:10:00.790 Status: dzVents: !Info: > Temperatura Económica -> 18.70
2018-10-31 16:10:00.793 Status: dzVents: !Info: > Temperatura Modo Manual -> 20.00
2018-10-31 16:10:00.807 Status: dzVents: !Info: > Temperatura FESTIVOS -> 19.50
2018-10-31 16:10:00.810 Status: dzVents: !Info: > CALEFACCION -dias laborables -> 10-13/14.30-22.30
2018-10-31 16:10:00.819 Status: dzVents: !Info: > CALEFACCION -festivos -> 10-13/14.30-22.30
2018-10-31 16:10:00.819 Status: dzVents: !Info: > HISTERESIS -> 0.3
2018-10-31 16:10:00.819 Status: dzVents: !Info: --------------------------------------------------------------------------
2018-10-31 16:10:00.823 Status: dzVents: !Info: Ajustes de funcionamiento de la caldera para el modo. AUTO:
2018-10-31 16:10:00.823 Status: dzVents: !Info: --------------------------------------------------------------------------
2018-10-31 16:10:00.823 Status: dzVents: !Info: > 13. Franja horaria de calefacción: días laborables - calefacción desde 10:00-13:00
2018-10-31 16:10:00.824 Status: dzVents: !Info: > 14. Franja horaria de calefacción: días laborables - calefacción desde 14:30-22:30
2018-10-31 16:10:00.824 Status: dzVents: !Info: > 15. Franja horaria de calefacción: Fines de semana - calefacción. 10:00-13:00
2018-10-31 16:10:00.837 Status: dzVents: !Info: > 20. Modo de funcionamiento actual de la caldera: Día de calefacción.
2018-10-31 16:10:00.837 Status: dzVents: !Info: > 22. Enciendo la caldera para una temperatura uniforme o más baja: 19.2 Temperatura actual: 20.1
2018-10-31 16:10:00.838 Status: dzVents: !Info: > 23. Apago la caldera para una temperatura uniforme o más alta: 19.8 Temperatura actual: 20.1
2018-10-31 16:10:00.838 Status: dzVents: !Info: --------------------------------------------------------------------------
2018-10-31 16:10:00.838 Status: dzVents: Error (2.4.6): There is no uservariable with that name or id: HeatWorkCondition
2018-10-31 16:10:00.838 Status: dzVents: Error (2.4.6): An error occured when calling event handler BEROGAILU dzvents
2018-10-31 16:10:00.838 Status: dzVents: Error (2.4.6): .../scripts/dzVents/generated_scripts/BEROGAILU dzvents.lua:96: attempt to index a nil value
2018-10-31 16:10:00.839 Status: dzVents: Info: ------ Finished BEROGAILU dzvents
Script from line 38 start like this.uzturre wrote: ↑Wednesday 31 October 2018 16:15 2018-10-31 16:10:00.838 Status: dzVents: !Info: --------------------------------------------------------------------------
-- USER VARIABLES // name of user variables in Domoticz ( Setup > More options > User variables).
local usrStateWorkHEAT = 'HeatWorkCondition' -- helper variable to work script
local usrLastStatement = 'HeatStatement' -- helper variable last statemen
Of course You can change name of variable according to your own needs in this line of script and domoticz's "user variables".
By the way, a slightly newer version of the Polish-language objects names.
-- Heat control
local version = '2.5' -- current version of script
local LOGGING = false -- true or false LOGGING info to domoticz log.
-- DEVICES // name of devices in Domoticz
-- HEAT
local devHEAT = 'Kocioł C.O.' -- switch that will be turned OFF and ON
local devAUTO = 'Automatyka' -- switch that will be turned OFF and ON autmatic of scrpt
-- thermometers
local devThermometer_main = 'Temperatura Babcia' -- main thermometer to control switch
local devThermometer_second = 'Temperatura Jacek' -- backup thermometer to control switch when main thermometer dont work (lastUpdate > max_time_last_seen)
-- DUMMY DEVICES // your name of devices create in Domoticz for this script
-- setpoints
local devSetpoint_comfort = 'Temperatura komfortowa' -- setpoint: comfort temperature
local devSetpoint_night = 'Temperatura na noc' -- setpoint: eco temperature for night
local devSetpoint_custom = 'Temperatura dla trybu ręcznego' -- setpoint: temperature for manual mode
local devSetpoint_holidays = 'Temperatura WYJAZD' -- setpoint: eco temperature for holidays mode
-- selectors
local devSelector_heat_work_day = 'Grzanie - dni robocze' -- heat work day with buttons for zone of hours exp: [5-22] or [5,30-22,30] or [5,30-7 i 14,00-22]
local devSelector_heat_weekend = 'Grzanie - weekendy' -- heat weekend with buttons for zone of hours exp: [5-22] or [5,30-22,30] or [5,30-7 i 14,00-22]
local devSelector_mode = 'Wybierz tryb pracy' -- work mode with 4 buttons as below:
local devSelector_mode_auto = 'AUTO'
local devSelector_mode_manual = 'RĘCZNY'
local devSelector_mode_holidays = 'WYJAZD'
local devSelector_mode_off = 'OFF'
-- text
local devText_work_state = 'DODATKOWO - CO' -- text device witch displayed current status
local devText_temp_state = 'DODATKOWO - T'
local usrStateWorkHEAT = 'StanPracyCO' -- helper variable to work script
local usrLastStatement = 'komunikatCO' -- helper variable last statemen
-- OTHER
-- conditions of TIME ZONE
local NOTIFY_TIME = 'at 07:00-22:00' -- matchesRule when notify will be send. (default - PUSHOVER)
local BACK_TO_AUTO = 'at 23:30-23:40 on mon,tue,wed,thu,fri,sat,sun' -- matchesRule to back to 'AUTO' mode from 'MANUAL' mode.
-- auxiliary variables
local HISTERESIS = 0.1 -- deviation from the set temperature
local max_time_last_seen = 60 -- the maximum time in minutes when main thermometer have to report (lastUpdate) or we change on backup
local min_time_to_change = 30 -- the minimum time in minutes to do change of state devHEAT
local min_time_to_notify = 60 -- the minimum time in minutes to repeat the unchanged notifycation.
local temp_default = 20 -- default temperature when both termometers dont work.
local description_heat ='Grzanie ' -- label "HEAT" to info for text device
local description_break ='Przerwa ' -- label "BREAK" to info for text device
local descriptionPrefix = ' Ust. temp.: ' -- label "PREFIX" to info for text device
local descriptionSufix = ' st.' -- label "SUFIX" to info for text device
-- FUNCTION: helpers
function notify(domoticz, text1, text2)
if domoticz.variables(usrLastStatement).value ~= text2 or domoticz.variables(usrLastStatement).lastUpdate.minutesAgo > min_time_to_notify then
domoticz.variables(usrLastStatement).set(text2)
if domoticz.time.matchesRule(NOTIFY_TIME) then
domoticz.notify(text1,text2, domoticz.PRIORITY_HIGH, domoticz.SOUND_PUSHOVER, '', domoticz.NSS_PUSHOVER) -- notify system default - PUSHOVER
function log(domoticz, text, lvlError)
local lvlLog = domoticz.LOG_FORCE
if lvlError ~= nil and lvlError == true then lvlLog = domoticz.LOG_ERROR end
if LOGGING then domoticz.log(text , lvlLog) end
function round(num, numDecimalPlaces)
local mult = 10^(numDecimalPlaces or 0)
return math.floor(num * mult + 0.5) / mult
function rtrim(s)
local n = #s
while n > 0 and s:find("^%s", n) do n = n - 1 end
return s:sub(1, n)
function updateTextInfoDevice(domoticz, text_content)
if domoticz.devices(devText_work_state).state ~= text_content then domoticz.devices(devText_work_state).updateText(text_content) end
if domoticz.variables(usrStateWorkHEAT).value ~= text_content then
domoticz.variables(usrStateWorkHEAT).set(text_content)
notify(domoticz,'Sterowanie CO - zmiana trybu pracy', 'Zmiana trybu: '..text_content)
-- domoticz.log(text_content, domoticz.LOG_FORCE);
-- domoticz.log(domoticz.variables(usrStateWorkHEAT).value, domoticz.LOG_FORCE);
function getHourFromSelector(state,nZone)
-- separators in buttons with hours exp: [5-22] or [5.30-22.15] or [5.30-7/14.20-22]
local hourSplit = '-'
local minSplit = '.'
local zoneSplit = '/'
local ret = ''
local hour1 =''
local hour2 =''
if minSplit == '.' then minSplit = '%.' end
local nZoneSplit= string.find(state, zoneSplit)
if nZone == 1 then nFrom = 0 end
nLenZoneSplit=string.len(zoneSplit)
if nZone == 2 and nZoneSplit ~= nil then
nFrom = nZoneSplit + nLenZoneSplit
if nZone == 2 then return nil end
if nFrom == nil then return nil end
local nHourSplit= string.find(state, hourSplit, nFrom,true)
if nHourSplit > 0 then
local hour1 = string.sub(state,nFrom,nHourSplit-1)
if string.len(hour1) == 0 then hour1='00' end
if string.len(hour1) == 1 then hour1='0'..hour1 end
local nMin=string.find(hour1,minSplit,1)
if nMin == nil then
hour1 = hour1..':00'
hour1 = string.gsub(hour1,minSplit,':')
local nZoneSplit2 = string.find(state, zoneSplit, nHourSplit+1)
if nZoneSplit2 == nil then hour2 = string.sub(state,nHourSplit+1) else
hour2 = string.sub(state,nHourSplit+1,nZoneSplit2-1)
hour2=rtrim(hour2)
if string.len(hour2) == 0 then hour2='00' end
if string.len(hour2) == 1 then hour2='0'..hour2 end
nMin=string.find(hour2,minSplit,1)
if nMin == nil then
hour2 = hour2..':00'
hour2 = string.gsub(hour2,minSplit,':')
ret = hour1..'-'..hour2
return ret
-- MAIN dzVent's SCRIPT
active = true,
devices = {devSetpoint_comfort, devSetpoint_night, devSetpoint_custom, devSetpoint_holidays, devSelector_heat_work_day, devSelector_heat_weekend, devSelector_mode, devThermometer_main },
timer = {'every 2 minutes'},
execute = function(domoticz,device,triggerInfo)
-- BLOCK INFO TO DEBUG
log(domoticz,'')
log(domoticz,' **************************************************************************')
log(domoticz,'1. STEROWANIE CO - rozpoczynam debugowanie ver -> '.. version)
-------------- STATE ON BEGIN RUN OF SCRIPT
log(domoticz,' Stany na wejściu do skryptu:')
log(domoticz,' --------------------------------------------------------------------------')
log(domoticz,' > '..domoticz.devices(devHEAT).name .. ' -> '.. domoticz.devices(devHEAT).state)
log(domoticz,' > '..domoticz.devices(devThermometer_main).name .. ' -> '.. round(domoticz.devices(devThermometer_main).temperature,1))
log(domoticz,' > '..domoticz.devices(devText_work_state).name .. ' -> '.. domoticz.devices(devText_work_state).state)
log(domoticz,' > '..domoticz.devices(devSetpoint_comfort).name .. ' -> '.. domoticz.devices(devSetpoint_comfort).state)
log(domoticz,' > '..domoticz.devices(devSetpoint_night).name .. ' -> '.. domoticz.devices(devSetpoint_night).state)
log(domoticz,' > '..domoticz.devices(devSetpoint_custom).name .. ' -> '.. domoticz.devices(devSetpoint_custom).state)
log(domoticz,' > '..domoticz.devices(devSetpoint_holidays).name .. ' -> '.. domoticz.devices(devSetpoint_holidays).state)
log(domoticz,' > '..domoticz.devices(devSelector_heat_work_day).name .. ' -> '.. domoticz.devices(devSelector_heat_work_day).state)
log(domoticz,' > '..domoticz.devices(devSelector_heat_weekend).name .. ' -> '.. domoticz.devices(devSelector_heat_weekend).state)
log(domoticz,' > HISTERESIS' .. ' -> '.. HISTERESIS)
-- variables
local Time = require('Time')
local stateworkHEAT = ''
local stateworkMODE = ''
local temp_current = 0
local temp_set = 0
local temp_night = 0
local temp_comfort = 0
-- BLOCK OF selectors
if ((domoticz.devices(devSelector_mode).changed) and (domoticz.devices(devSelector_mode).state == devSelector_mode_off)) then
local text_content = 'SYSTEM OFF'
domoticz.devices(devHEAT).switchOff()
log(domoticz,' > 3. USTAWIONY TRYB PRACY: [' .. text_content .. ']',true)
return
if domoticz.devices(devSelector_mode).state == devSelector_mode_holidays then stateworkMODE = '>'..devSelector_mode_holidays..'<' end
if domoticz.devices(devSelector_mode).state == devSelector_mode_auto then stateworkMODE = '>'..devSelector_mode_auto..'<' end
if domoticz.devices(devSelector_mode).state == devSelector_mode_manual then stateworkMODE = '>'..devSelector_mode_manual..'<' end
if domoticz.devices(devSelector_mode).state == devSelector_mode_off then return end --- because system is OFF.
-- BLOCK return from MANUAL to AUTO
-- automatic return to AUTO mode when the time condition described in the parameters is met, the event is triggered by a thermometer (ie automatically and not manually)
if domoticz.time.matchesRule(BACK_TO_AUTO) and domoticz.devices(devSelector_mode).state == devSelector_mode_manual then
domoticz.devices(devSelector_mode).dimTo(10)
notify(domoticz,'Sterowanie CO - powrót do trybu '..devSelector_mode_auto, 'Jest spełniony warunek dla przełączenia automatycznego w tryb '..devSelector_mode_auto)
log(domoticz,' > 2. Automatyczny powrót do trybu '..devSelector_mode_auto..' -> Włączam tryb '..devSelector_mode_auto..' -> '..BACK_TO_AUTO)
log(domoticz,'')
return --exit from the script, because it will trigger a second event which will enter the new service for auto mode.
-- BLOCK OF setpoints
-- notifications of changes in the status of important control parameters
local llnotify=false
if (domoticz.devices(devSetpoint_comfort).changed) then
notify(domoticz,'Sterowanie CO - zmiana parametru', 'Zmieniono ustawienie temp. dla strefy komfortu na wart.: '..domoticz.devices(devSetpoint_comfort).state)
log(domoticz,' > 4. Wysłano powiadomienie ->'..' Zmieniono ustawienie temp. dla strefy komfortu na wart.: '..domoticz.devices(devSetpoint_comfort).state)
llnotify = true
if (domoticz.devices(devSetpoint_night).changed) then
notify(domoticz,'Sterowanie CO - zmiana parametru', 'Zmieniono ustawienie temp. nocnej na wart.: '..domoticz.devices(devSetpoint_night).state)
log(domoticz,' > 5. Wysłano powiadomienie ->'..' Zmieniono ustawienie temp. nocnej na wart.: '..domoticz.devices(devSetpoint_night).state)
llnotify = true
if (domoticz.devices(devSetpoint_custom).changed) then
notify(domoticz,'Sterowanie CO - zmiana parametru', 'Zmieniono ustawienie temp. użytkownika na wart.: '..domoticz.devices(devSetpoint_custom).state)
log(domoticz,' > 6. Wysłano powiadomienie ->'..'Zmieniono ustawienie temp. użytkownika na wart.: '..domoticz.devices(devSetpoint_custom).state)
llnotify = true
if (domoticz.devices(devSetpoint_holidays).changed) then
notify(domoticz,'Sterowanie CO - zmiana parametru', 'Zmieniono ustawienie temp. dla trybu '..devSelector_mode_holidays..' na wart.: '..domoticz.devices(devSetpoint_holidays).state)
log(domoticz,' > 7. Wysłano powiadomienie ->'..'Zmieniono ustawienie temp. dla trybu '..devSelector_mode_holidays..' na wart.: '..domoticz.devices(devSetpoint_holidays).state)
llnotify = true
if (domoticz.devices(devSelector_heat_work_day).changed) then
notify(domoticz,'Sterowanie CO - zmiana parametru', 'Zmieniono ustawienie stref grzania w dni rob. na wart: '..domoticz.devices(devSelector_heat_work_day).state)
log(domoticz,' > 8. Wysłano powiadomienie ->'..' Zmieniono ustawienie stref grzania w dni rob. na wart: '..domoticz.devices(devSelector_heat_work_day).state)
llnotify = true
if (domoticz.devices(devSelector_heat_weekend).changed) then
notify(domoticz,'Sterowanie CO - zmiana parametru', 'Zmieniono ustawienie stref grzania w weekendy. na wart: '..domoticz.devices(devSelector_heat_weekend).state)
log(domoticz,' > 9. Wysłano powiadomienie ->'..'Zmieniono ustawienie stref grzania w weekendy. na wart: '..domoticz.devices(devSelector_heat_weekend).state)
llnotify = true
if llnotify then log(domoticz,' ------------------------------------------------------------------------') end
-- BLOCK OF CHECKS termometers :
local devHeatMinAgo = domoticz.devices(devHEAT).lastUpdate.minutesAgo
--- its time event so user dont click any push button, below we check condition to not offen change state of devHEAT.
if (triggerInfo.type == domoticz.EVENT_TYPE_TIMER or device.name == devThermometer_main) and devHeatMinAgo < min_time_to_change then
log(domoticz,' > 10. Nic do zmiany bo ostatnia była -> '.. tostring(devHeatMinAgo) .. ' minut temu. WYCHODZĘ')
log(domoticz,'')
-- Determining the current temperature in the living room [this is a reference point for heating control] but if the thermometer does not work, we assume the temperature of the spare thermometer
if domoticz.devices(devThermometer_main).lastUpdate.minutesAgo < max_time_last_seen then temp_current = round(domoticz.devices(devThermometer_main).temperature,2) end
if (domoticz.devices(devThermometer_main).lastUpdate.minutesAgo >= max_time_last_seen) then
notify(domoticz,'Sterowanie CO - ALERT!!!', 'Termometr nie zgłasza się od 60min, system pobiera temp. z alternatywnego termometru!')
log(domoticz,'10a. Termometr nie zgłasza się od 60min, system pobiera temp. z alternatywnego termometru!')
if (domoticz.devices(devThermometer_second).lastUpdate.minutesAgo < max_time_last_seen) then
temp_current = round(domoticz.devices(devThermometer_second).temperature,2)
temp_current = temp_default
notify(domoticz,'Sterowanie CO - ALERT!!!', 'Alternatywny termometr też nie działa, przyjmuję jako temp_current 20 st.')
log(domoticz,'10b. Alternatywny termometr też nie działa, przyjmuję jako temp_current 20 st.!')
-- BLOCK CONTROL: <holidays> i <MANUAL>
if ((domoticz.devices(devSelector_mode).state == devSelector_mode_holidays) or (domoticz.devices(devSelector_mode).state == devSelector_mode_manual)) then
temp_set = tonumber(domoticz.devices(devSetpoint_holidays).state)
log(domoticz,' > Wybrano tryb pracy >'..devSelector_mode_holidays..'<, sprawdzanie czy praca kotła jest potrzebna ')
temp_set = tonumber(domoticz.devices(devSetpoint_custom).state)
log(domoticz,' > Wybrano tryb pracy >'..devSelector_mode_manual..'<, sprawdzanie czy praca kotła jest potrzebna ')
log(domoticz,' Reakcja kotła na nowe ustawienia: ')
if temp_set > temp_current then
domoticz.devices(devHEAT).switchOn()
log(domoticz,' >11. ' .. devHEAT .. ' Włączony bo aktualna temperatura '.. tostring(temp_current)..' niższa niż wymagana '..tostring(temp_set),true)
log(domoticz,' > 11a. '.. devHEAT .. ' Wyłączony bo aktualna temperatura '..tostring(temp_current)..' nie jest niższa niż wymagana '..tostring(temp_set),true)
-- contentet of text info
local text_content = stateworkMODE ..' '..stateworkHEAT..' Ust.temp: '..temp_set..' st.'
log(domoticz,' > 11b. Ustawiam info o stanie pracy na: [' .. text_content .. ']')
log(domoticz,'')
return
-- BLOCK CONTROL: <AUTO>
-- determination of heating zones: on what days in which times the comfort temperature should be maintained, and when it should be lowered
--- WORK DAY
log(domoticz,' Ustawienia pracy kotła dla trybu '..devSelector_mode_auto..': ')
local HEAT_MORNING = ''
local HEAT_AFTERNOON = ''
local HEAT_WEEKEND = ''
if domoticz.devices(devAUTO).state=='Off' then
if domoticz.devices(devHEAT).state=='On' then
local text_content = ' AUTO SYSTEM OFF !!!'
log(domoticz,text_content,true);
log(domoticz,' > 11c. Ustawiam info o stanie pracy na: AUTO OFF ')
log(domoticz,'')
return
-- devSelector_heat_work_day
stateDevSelector_heat_work_day=domoticz.devices(devSelector_heat_work_day).state
strHEAT_morning = getHourFromSelector(stateDevSelector_heat_work_day, 1)
if strHEAT_morning ~= nil then
HEAT_MORNING = 'at '.. strHEAT_morning ..' on mon,tue,wed,thu,fri'
log(domoticz,' > 13. Ustawiam strefę grzania: Dni robocze - grzanie od '.. strHEAT_morning)
local text_content = ' SYSTEM OFF !!!'
log(domoticz,'')
return
strHEAT_afternoon = getHourFromSelector(stateDevSelector_heat_work_day, 2)
if strHEAT_afternoon ~= nil then
HEAT_AFTERNOON = 'at '.. strHEAT_afternoon ..' on mon,tue,wed,thu,fri'
log(domoticz,' > 14. Ustawiam strefę grzania: Dni robocze - grzanie od '.. strHEAT_afternoon)
HEAT_AFTERNOON = HEAT_MORNING
--- WEEKEND;
stateDevSelector_heat_work_weekend=domoticz.devices(devSelector_heat_weekend).state
strHEAT_weekend = getHourFromSelector(stateDevSelector_heat_work_weekend, 1)
if strHEAT_weekend ~= nil then
HEAT_WEEKEND = 'at ' .. strHEAT_weekend .. ' on sat, sun'
log(domoticz,' > 15. Ustawiam strefę grzania: Weekendy - grzanie '..strHEAT_weekend)
log(domoticz,'')
return
-- log(domoticz,' > 16. Aktualne reguły : ')
-- log(domoticz,' > 17. ...HEAT_MORNING -> '.. HEAT_MORNING )
-- log(domoticz,' > 18. ...HEAT_AFTERNOON -> '.. HEAT_AFTERNOON )
-- log(domoticz,' > 19. ...HEAT_WEEKEND -> '.. HEAT_WEEKEND )
-- determination of comfortable and overnight temperature
if (domoticz.time.matchesRule(HEAT_MORNING) or domoticz.time.matchesRule(HEAT_AFTERNOON) or domoticz.time.matchesRule(HEAT_WEEKEND)) then
temp_comfort = tonumber(domoticz.devices(devSetpoint_comfort).state)
temp_set = temp_comfort
stateworkHEAT = description_heat
log(domoticz,' > 20. Aktualny tryb pracy kotła: Grzanie dzień')
temp_night = domoticz.devices(devSetpoint_night).state
temp_set = tonumber(temp_night)
stateworkHEAT = description_break
log(domoticz,' > 21. Aktualny tryb pracy kotła: Strefa chłodna')
log(domoticz,' > 22. Wlaczam piec dla temperatury równej lub mniejszej: ' .. switchOnTemp ..' Akt temp: '..tostring(temp_current))
log(domoticz,' > 23. Wylaczam piec dla temperatury równej lub większej: ' .. switchOffTemp ..' Akt temp: '..tostring(temp_current))
if (temp_current >= switchOffTemp and domoticz.devices(devHEAT).state == 'On') then
log(domoticz,' Reakcja kotła na nowe ustawienia (lub wywołanie skrytpu przez czujnik temp.): ')
log(domoticz,' > 24. Docelowa temperature osiagnieta, Piec-Status => off',true)
if (temp_current <= switchOnTemp and domoticz.devices(devHEAT).state == 'Off') then
log(domoticz,' > 25. Ogrzewanie jest potrzebne, Piec-Status => on',true)
local text_content = stateworkMODE ..' '..stateworkHEAT..descriptionPrefix..temp_set..descriptionSufix
local text_content2 = tostring(temp_current)..' on: '..switchOnTemp..' off: '..switchOffTemp
if domoticz.devices(devText_temp_state).state ~= text_content2 then
domoticz.devices(devText_temp_state).updateText(text_content2)
log(domoticz,' > 26. Temperatura przełączania kotła: [' .. text_content .. ']')
log(domoticz,' > 27. Ustawiam info o stanie pracy na: [' .. text_content .. ']')
log(domoticz,' ************************************************************************** ')
log(domoticz,'')
-- end of script
Eoreh wrote: ↑Wednesday 31 October 2018 19:11***************************************************uzturre wrote: ↑Wednesday 31 October 2018 16:15"HeatWorkCondition" is the name of the variable you must manually create in "Domoticz". As You see above is also second variable "HeatStatement" which of course You also have to create.Code: Select all
--======================================================= -- USER VARIABLES // name of user variables in Domoticz ( Setup > More options > User variables). --======================================================= local usrStateWorkHEAT = 'HeatWorkCondition' -- helper variable to work script local usrLastStatement = 'HeatStatement' -- helper variable last statemen
This is the code on line 38..***************************************************Code: Select all
--======================================================= -- VARIABLES DE USUARIO // nombre de las variables de usuario en Domoticz (Configuración> Más opciones> Variables de usuario). --======================================================= local usrStateWorkHEAT = 'HeatWorkCondition' -- Variable auxiliar para trabajar script local usrLastStatement = 'HeatStatement' -- variable de ayuda último estado
the log tells me the following:Code: Select all
2018-11-01 12:46:00.405 Status: dzVents: Error (2.4.6): There is no uservariable with that name or id: HeatWorkCondition 2018-11-01 12:46:00.405 Status: dzVents: Error (2.4.6): An error occured when calling event handler BEROGAILU dzvents 2018-11-01 12:46:00.405 Status: dzVents: Error (2.4.6): .../scripts/dzVents/generated_scripts/BEROGAILU dzvents.lua:96: attempt to index a nil value
I continue with the same error detailed above, but the script is working correctly. I do not know why the log gives me that error. The error in line 96 calls my attention.
Thank you very much for your answer.
Last edited by uzturre on Thursday 01 November 2018 12:51, edited 3 times in total.
I tell you my installation, I have two pi zero w, one pi zero for the temperature probe installed in the room and the other pi zero with the relay modules next to the boiler, in this pi zero I have a module with 2 relays (relay 1 and relay 3) when the relay 1 is activated its contact closes to give way to the current and activate the relay 3. The relay 3 is subject to the start of the relay 1. This I did because it used blockly and in this way I could do the boiler operated at certain times activating relay 1 (relay 1 with time condition) and this way activate relay 3 which in turn had to meet the temperature condition of the room probe.
As you see in your script, I have changed line 12 and it works for me that way, but only relay 1 remains OFF, relay 3 always remains activated, I do not know how to do it in the correct way.
If you read line 13, if I put it in active mode, the script does not work.
Thank you.
Thank you.
CONTROL DE CALEFACCION
local version = '2.3' -- current version of script
local LOGGING = true -- true or false LOGGING info to domoticz log.
-- HEAT
local devHEAT = 'RELE -3-' and 'RELE -1-' -- switch that will be turned OFF and ON
--- local devHEAT = 'RELE -1-' -- interruptor OFF - ON
This script cant be used with 2 relays. A lot of line used syntex like egz. " domoticz.devices(devHEAT).switchOff()"uzturre wrote: ↑Thursday 01 November 2018 12:19 I tell you my installation, I have two pi zero w, one pi zero for the temperature probe installed in the room and the other pi zero with the relay modules next to the boiler, in this pi zero I have a module with 2 relays (relay 1 and relay 3) when the relay 1 is activated its contact closes to give way to the current and activate the relay 3. The relay 3 is subject to the start of the relay 1. This I did because it used blockly and in this way I could do the boiler operated at certain times activating relay 1 (relay 1 with time condition) and this way activate relay 3 which in turn had to meet the temperature condition of the room probe.
Thank you.Code: Select all
CONTROL DE CALEFACCION -- ------------------------------------------------------------------------ local version = '2.3' -- current version of script ------------------------------------------------------------------------ local LOGGING = true -- true or false LOGGING info to domoticz log. --======================================================= -- DEVICES // name of devices in Domoticz --======================================================= -- HEAT local devHEAT = 'RELE -3-' and 'RELE -1-' -- switch that will be turned OFF and ON --- local devHEAT = 'RELE -1-' -- interruptor OFF - ON
so
If you want still use this script and you have 2 relays, you can use it with one relay and in another script "dzVents" or even blockly do action depending on the condition second and link the actions of these relays.
Thank you very much, the problem is that I do not know how to write code...
So You can do this in blockly, but i recomnends write script in dzVents. It not very hard to learn and in future you will have more posibilities. Is very good documentation on wiki with a lot of egzamples. See https://www.domoticz.com/wiki/DzVents:_ ... _scripting
Hello, I am using this script for regulating de heating in our house, but unfortunately the ' Holiday' function does not work.
We are on holiday now and I noticed that de heating was still working.
At for now I lowered the ' Comfort temperature' to holiday-level, so the heating is ok, but I would like to make the script work also when we are on holiday.
Any suggestions to solve this?
Does "name" in line nr 25 is the same as SetPoint ?.corthebor wrote: ↑Monday 01 April 2019 21:27 Hello, I am using this script for regulating de heating in our house, but unfortunately the ' Holiday' function does not work.
local devSetpoint_holidays = 'Temperature HOLIDAYS' -- setpoint: eco temperature for holidays mode
Problem solved: Edited the selector switch ' Working mode' . Changed HOLIDAY into HOLIDAYS. And now it's working.
thanks a lot, Very nice and useful script.
greetings
Cor
greetings
Cor
- Domoticz version: 2020.1
After updating Domoticz to version 2020.1, errors began to appear in the logs: (Polish version)
Can i have some help?
2020-03-31 09:30:34.541 Error: dzVents: Error: (3.0.1) >11. Baxi Włączony bo aktualna temperatura 20.2 niższa niż wymagana 22.0
2020-03-31 09:31:25.949 Error: dzVents: Error: (3.0.1) > 24. Docelowa temperature osiagnieta, Piec-Status => off
2020-03-31 09:31:34.081 Error: dzVents: Error: (3.0.1) > 25. Ogrzewanie jest potrzebne, Piec-Status => on
- waaren
These are just messages from the script but send with a loglevel that is recognized by domoticz as an Error. You can change that by changing the lines which are producing these messages and remove the last ,true.elpaul wrote: ↑Tuesday 31 March 2020 9:32 After updating Domoticz to version 2020.1, errors began to appear in the logs: (Polish version)Can i have some help?Code: Select all
2020-03-31 09:30:34.541 Error: dzVents: Error: (3.0.1) >11. Baxi Włączony bo aktualna temperatura 20.2 niższa niż wymagana 22.0 2020-03-31 09:31:25.949 Error: dzVents: Error: (3.0.1) > 24. Docelowa temperature osiagnieta, Piec-Status => off 2020-03-31 09:31:34.081 Error: dzVents: Error: (3.0.1) > 25. Ogrzewanie jest potrzebne, Piec-Status => on
As example change line:
log(domoticz,' > 24. Target temperature reached, Status => off',true)
log(domoticz,' > 24. Target temperature reached, Status => off')
Thx a lot! it's work fine!waaren wrote: ↑Tuesday 31 March 2020 10:30These are just messages from the script but send with a loglevel that is recognized by domoticz as an Error. You can change that by changing the lines which are producing these messages and remove the last ,true.elpaul wrote: ↑Tuesday 31 March 2020 9:32 After updating Domoticz to version 2020.1, errors began to appear in the logs: (Polish version)Can i have some help?Code: Select all
toCode: Select all
