Ive updated the wiki to the best of my knowledge.. Maybe you guys can make a quick go through to check if its ok!
Hi, it looks betters now. In my flat I have only 5 Radiator Thermostat without wall thermostat.
I`m able to read only Percentage. What is needed to be able to read Setpoint and Temperature? Or is it possible?
Device status
Valve Loznice-Rad Setpoint=22.5 Temp=0 Valve pos=10 Battery=OK Mode=Auto
Valve Koupelna-Rad Setpoint=22 Temp=25.1 Valve pos=0 Battery=OK Mode=Auto
Valve Kuchyn-Rad Setpoint=24 Temp=0 Valve pos=46 Battery=OK Mode=Auto
Valve Obyvak-Rad Setpoint=24 Temp=25.4 Valve pos=61 Battery=OK Mode=Auto
Valve Predsin-Rad Setpoint=20 Temp=0 Valve pos=0 Battery=OK Mode=Auto
- l0gic
- Domoticz version: Latest
Hi Sean,blackdog65 wrote:Hi kevin,
What's in script_time_EQ3_Cube.lua?
Did you try the test script to do a basic read?
Sean
yeah the test code pulls out all the data as expected.
I just have issues with this specific code piece.
Googling seems to indicate either issues with paths / env settings (which I've checked) or version checks.
'tis weird
Kevin
Non credus crepitus
- blackdog65
Hi Kevin,
most of us linux users found issues with where lua5.2 installs as it was different to previous versions. This may be the same or similar with windows.
Sean
Sean
CubieTruck Master
RasPi slaves
EQ3 MAX!
TKB Sockets
RFXCOM
MySensors
ESPEasy ESP8266-12E
RasPi slaves
EQ3 MAX!
TKB Sockets
RFXCOM
MySensors
ESPEasy ESP8266-12E
Please put all devices in manual mode with the max app.hasan wrote:Hi, it looks betters now. In my flat I have only 5 Radiator Thermostat without wall thermostat.Code: Select all
Device status ------------- Valve Loznice-Rad Setpoint=22.5 Temp=0 Valve pos=10 Battery=OK Mode=Auto Valve Koupelna-Rad Setpoint=22 Temp=25.1 Valve pos=0 Battery=OK Mode=Auto Valve Kuchyn-Rad Setpoint=24 Temp=0 Valve pos=46 Battery=OK Mode=Auto Valve Obyvak-Rad Setpoint=24 Temp=25.4 Valve pos=61 Battery=OK Mode=Auto Valve Predsin-Rad Setpoint=20 Temp=0 Valve pos=0 Battery=OK Mode=Auto
You need to create thermostat setpoint dummy devices in domoticz with the following name: Loznice-Stat
Also make sure you've set the use wall mount thermostat to false!
Thanks! I changed parts of the text explaining the naming scheme, as it was not 100% corrrect, and added a bit more explanation on how to configure things if you don't have wall mounted thermostats.Skippiemanz wrote:Ive updated the wiki to the best of my knowledge.. Maybe you guys can make a quick go through to check if its ok!
Many thanks for your help, i have the round TRV's, all temps are now working with the add on line you recommended (subject to standard reading issues if valve hasnt moved). also, i needed to reboot the MAX! (i think all the testing confused it) i only have 1 thermostat currently in my setup (will add the other's after xmas).mvzut wrote:
Temperature will indeed not be updated if you don't have wall thermostats. Earlier versions of the script updated the Domoticz temperature device(s) with the actual temperature(s) received from the valves, but I removed that since the valves only send the current temperature when the motor is running. That didn't give very usable day graphs for the room temperature. We still need to explain this in the Wiki, actually you don't even have to create temperature devices in Domoticz if you don't have wall thermostats.
Apart from that, it seems you have everything set up correctly. The log says the Domoticz setpoints are updated, and it seems to send the commands. At least I assume so, because it says "Fetching url...", which is the expected message since I use API calls to do this. That is because of a bug Domoticz where updating setpoints via lua "UpdateDevice" commands results in script timeouts). Only the commands apparently never reach the setpoint devices. Are you using the right port number for the API calls to Domoticz?
You could try and replace (twice)withCode: Select all
table.insert(commandArray, { ['OpenURL'] = 'http://127.0.0.1:'..DomoticzPort..'/json.htm?type=command¶m=udevice&idx='..otherdevices_idx[name]..'&nvalue=0&svalue='..setpoint})
which could give the notorious timeout messages but should work regardlessly.Code: Select all
table.insert(commandArray, { ['UpdateDevice'] = otherdevices_idx[name]..'|0|'..setpoint})
P.S. I now see all your valves seem to report an actual temperature... This would contradict my story above. Can you maybe check, e.g. by running the lua test script a couple of times, if those temperatures are actually updated regularly? Maybe you have other valves than myself (I use the basic model)?!
If your valve temperatures are updated regularly, or if you don't have a problem with virtual Domoticz temperature sensors that are only updated every now and then, you can get temperature reading back into the script again by adding this line:directly below the "if not useWMT then" line. This will update the virtual temperature sensor(s) named after the room name(s), using the current temperature as reported by each valve.Code: Select all
table.insert(commandArray, { ['UpdateDevice'] = otherdevices_idx[room]..'|0|'..temp})
again, many thanks to you all for your work and code, this code has not only made my life easier but now the wife dosnt complain about being too hot or cold - YAY!!
Hello everyone
Im expieriencing exactly the same problem, module bassex not found. returns
gives me
Maybe just an addition, I had to install in order to install luasec, as this is the only thing that resolved the "openssl" not found issue during the build process.
I followed the wiki step by step last night, but am stuck at this point right now. Does anyone see where I'm going wrong ?
luarocks list
Installed rocks:
basexx
0.3.0-1 (installed) - /usr/local/lib/luarocks/rocks
luasec
0.6-1 (installed) - /usr/local/lib/luarocks/rocks
luasocket
3.0rc1-2 (installed) - /usr/local/lib/luarocks/rocks
lua
Lua 5.2.3 Copyright (C) 1994-2013 Lua.org, PUC-Rio
sudo apt-get install libssl-dev
I found solution yesterday. I'll update Wiki during today and let you know
Odesláno z mého LG-D855 pomocí Tapatalk
FYI:Skippiemanz wrote:The Window sensors are not(yet) seen in domoticz so no devices are Needed
I have ordered a window sensor myself today, since I would like to understand how they can be read and integrated into the script.
I am also experimenting with am alternative version of the script that automatically generates the devices for you the first time it is used. No guarantees that this is going to work reliably of course...
Martijn
Great news! I know the first maxbuddy script made the devices automatic. Maybe you can get some inspiration from that?
- blackdog65
Wow! This project has really grown legs and is off and running
I'm really pleased to have been along for the ride
Sean
Sean
CubieTruck Master
RasPi slaves
EQ3 MAX!
TKB Sockets
RFXCOM
MySensors
ESPEasy ESP8266-12E
RasPi slaves
EQ3 MAX!
TKB Sockets
RFXCOM
MySensors
ESPEasy ESP8266-12E
Hi, I did some adjustment of Wiki, so you should try it. You will need these two files:toffel969 wrote:Hello everyone
Im expieriencing exactly the same problem, module bassex not found.returnsCode: Select all
luarocks list
Installed rocks: ---------------- basexx 0.3.0-1 (installed) - /usr/local/lib/luarocks/rocks luasec 0.6-1 (installed) - /usr/local/lib/luarocks/rocks luasocket 3.0rc1-2 (installed) - /usr/local/lib/luarocks/rocks
gives meCode: Select all
lua
Maybe just an addition, I had to installCode: Select all
Lua 5.2.3 Copyright (C) 1994-2013 Lua.org, PUC-Rio >
in order to install luasec, as this is the only thing that resolved the "openssl" not found issue during the build process.Code: Select all
Thanks so much, will only be home tomorrow night to try and give feedback
- l0gic
I've had a sign today, my Windows PC locked up.
So, due to this thread I've decided to swing back over to a Pi setup.
Don't let me down guys.
I will be running the Pi on a HDD set up as having SD cards corrupting put me off using a Pi last time.
As soon as the order arrives I'll be on the case.
Looking at the code I'm guessing it will not be too hard to invoke a 'all rads open' for when my woodburner is on.
I'm guessing this function should do all I need, just send a manual mode with a high temperature to all rads while we are burning wood.
With a bit of code wrapped around it.
Just as well the Domoticz database is lift and drop between OS's.
Cheers guys
Kevin
function MaxCmdSend(id, room, mode, setpoint)
bits = setpoint * 2
smode = string.upper(mode)
if smode == 'MANUAL' then
bits = 64 + bits
elseif smode == 'BOOST' then
bits = 192 + bits
elseif smode == 'VACATION' then
bits = 128 + bits
hex = "000440000000"..id..room..string.format("%x",bits)
sendStr = Basexx.to_base64(Basexx.from_hex(hex))
i, status = tcp:send("s:"..sendStr.."\r\n")
if not i then
print("MAX TCP send failed - "..status)
return
Cheers guys
Kevin
Non credus crepitus
That is indeed where I got my inspiration from. I know the JSON commands to do this for temperature and percentage sensors, and I think I can also get it if to work for thermostats. I'll let you know when I have some success.Skippiemanz wrote:Great news! I know the first maxbuddy script made the devices automatic. Maybe you can get some inspiration from that?
UPDATE 12-11-2016 15:30 - Some changes to code
Is anybody willing to test this alternative script_time_max.lua script?
It should automatically create devices for all your MAX! modules: a virtual thermostat for each wall mounted thermostat (or for each valve if you have set "useWMT" to false), a temperature sensor for each wall mounted thermostat, and a percentage device for each valve.
Note that they will be invisible at first, you have to add them to the used devices in Domoticz via Settings > Devices. In principle, you can give them any name that you want when adding them, but I suggest to still use the naming scheme as agreed (i.e. use the "-Ras" and "-Stat" suffixes) to make sure the second script keeps working. It can be a bit confusing to know which is which, since by default all newly created devices are called "Unknown". I suggest you check the current temperatures, setpoints etc. on the displays, so that you can recognize the devices by their values.
The script adds a new hardware module called "MAX!" which is an instance of the dummy hardware module (unless you already had one with that name).
Let me know your results. It works at my side!
UPDATE:
I almost forgot to mention, but this version uses JSON decoding via an external library (JSON.lua). You can download one at https://www.domoticz.com/wiki/Lua_-_json.lua. Copy the JSON.lua file in your domoticz/scripts/lua folder.
package.loadlib("core.so", "*")
Socket = require "socket"
Basexx = require "basexx"
json = (loadfile "/home/pi/domoticz/scripts/lua/JSON.lua")() -- for Linux
--json = (loadfile "D:\\Domoticz\\scripts\\lua\\json.lua")() -- for Windows
http = require "socket.http"
MaxIP='192.168.178.46'
MaxPort = 62910
DomoticzPort = 8080
useWMT = true --Set to true if there is a wall mounted thermostat in every room
interval = 5 --Polling interval in minutes, possible range 1-59. Cube doesn't seem to like too frequent communication, 5 minutes is a safe value
Rooms = {}
Devices = {}
Room_nums = {}
function get_MAX_ID()
result, statuscode, content = http.request('http://127.0.0.1:'..DomoticzPort..'/json.htm?type=hardware')
r,e = json:decode(result)
if r.status == "OK" then
for k,v in pairs(r.result) do
if v.Name == "MAX!" then return v.idx end
function Thermostat(DID)
result, statuscode, content = http.request('http://127.0.0.1:'..DomoticzPort..'/json.htm?type=devices')
if v.ID == DID then return v.SetPoint,v.LastUpdate end
return 0, '2016-01-01 00:00:00' -- value to return if device was not found
function age(timestring)
t = {}
t.year = string.sub(timestring,1,4)
t.month = string.sub(timestring,6,7)
t.day = string.sub(timestring,9,10)
t.hour = string.sub(timestring,12,13)
t.min = string.sub(timestring,15,16)
t.sec = string.sub(timestring,18,19)
return os.difftime(os.time(),os.time(t))
function maxCmd_H(data)
-- print('H='..data)
function maxCmd_M(data)
i = 0
j = 0
while true do -- find next comma
i = string.find(data, ",", i+1)
if not i then break end
j = i
s = data:sub(j+1)
dec = Basexx.from_base64(s)
num_rooms = string.byte(dec,3)
if num_rooms == 0 or num_rooms == nil then table.insert(commandArray, {['SendNotification'] = 'MAX! problem#Configuration lost?#1'}) end
pos=4
for i=1, num_rooms do
room_num = string.byte(dec, pos)
name_len = string.byte(dec, pos+1)
pos = pos+2
name = dec:sub(pos, pos+name_len-1)
pos = pos+name_len
adr = Basexx.to_hex(dec:sub(pos, pos+2))
Rooms[room_num] = name
pos = pos+3
num_devs = string.byte(dec, pos)
for i=1, num_devs do
dtype = string.byte(dec, pos+1)
adr = Basexx.to_hex(dec:sub(pos+2, pos+4))
snum = dec:sub(pos+5, pos+14)
name_len = string.byte(dec, pos+15)
pos = pos+16
pos = pos+name_len
Room_nums[adr] = room_num
Devices[adr] = name
function maxCmd_C(data)
-- print('C='..data)
function maxCmd_L(data)
pos = 1
dec = Basexx.from_base64(data)
L_hex = Basexx.to_hex(dec)
L_len = string.len(L_hex)
while (pos < L_len) do
s = L_hex:sub(pos,(pos+1))
data_len = tonumber(s,16) + 1
hex = L_hex:sub(pos,pos+(data_len*2))
adr = hex:sub(3,8)
room_num = string.format("%02X", Room_nums[adr])
room = Rooms[Room_nums[adr]]
name = Devices[adr]
if not name then name=adr end
valve_info = tonumber(hex:sub(13,14),16)
batt = bit32.extract(valve_info,7,1)
bst = bit32.extract(valve_info,3,1)
mode = bit32.extract(valve_info,0,2)
if (batt==0) then sbat="OK" else sbat="Low" end
if (mode==0) then smode="Auto" elseif (mode==1) then smode="Manual"
elseif (mode==2) then smode="Holiday" elseif (mode==3) then smode="Boost" end
if (data_len == 13) then -- WallMountedThermostat (dev_type 3)
valve_pos = -1
s = hex:sub(17,18)
setpoint = tonumber(s,16) / 2
s = hex:sub(23,26)
temp = tonumber(s,16) / 10
dtype = "Thermostat"
elseif (data_len == 12) then -- HeatingThermostat (dev_type 1 or 2)
s = hex:sub(15,16)
valve_pos = tonumber(s,16)
s = hex:sub(17,18)
if (mode ~= 2) then
s = hex:sub(19,22)
temp = 0
dtype = "Valve"
--Following two lines correct temperatures over 25.5 degrees, since e.g. 26 degrees is reported as 0.5 degrees
--This is due to the fact that temperatures seem to be stored as two Hex characters only (= max 255 in decimal)
--Pending better solution
if temp < 5 then temp = temp + 25.5 end
if setpoint > 50 then setpoint = setpoint - 64 end
-- Update virtual devices in Domoticz and update MAX! setpoints if necessary
--print(dtype.." "..name.." Setpoint="..setpoint.." Temp="..temp.." Valve pos="..valve_pos)
if dtype == "Valve" then
table.insert(commandArray, {['OpenURL'] = 'http://127.0.0.1:'..DomoticzPort..'/json.htm?type=command¶m=udevice&hid='..MAX_ID..'&did='..adr..'&dunit=1&dtype=243&dsubtype=6&nvalue=0&svalue='..valve_pos})
if not useWMT then --Use valve to check setpoint mismatch
if temp ~=25.5 then
table.insert(commandArray, {['OpenURL'] = 'http://127.0.0.1:'..DomoticzPort..'/json.htm?type=command¶m=udevice&hid='..MAX_ID..'&did='..adr..'&dunit=1&dtype=80&dsubtype=5&nvalue=0&svalue='..temp})
setpoint_Domoticz, LastUpdate = Thermostat('0'..adr)
if tonumber(setpoint_Domoticz) ~= setpoint then
if age(LastUpdate) > interval * 60 then --Domoticz thermostat value must be updated
table.insert(commandArray, {['OpenURL'] = 'http://127.0.0.1:'..DomoticzPort..'/json.htm?type=command¶m=udevice&hid='..MAX_ID..'&did=0'..adr..'&dunit=1&dtype=242&dsubtype=1&nvalue=0&svalue='..setpoint})
print('Domoticz setpoint ' .. name .. ' updated')
else --Max! setpoint must be updated
MaxCmdSend(adr, room_num, "manual", setpoint_Domoticz)
print('MAX! setpoint ' .. name .. ' updated')
elseif dtype == "Thermostat" and smode ~= 'Auto' then
pos = pos + (data_len*2)
bits = setpoint * 2
bits = 64 + bits
bits = 192 + bits
bits = 128 + bits
if not i then
return
m = tonumber(os.date('%M'))
if (m % interval == 0) and (m ~= 0) and (m ~= 30) then
--Get ID of MAX hardware in Domoticz, create if it doesn't exist
MAX_ID = get_MAX_ID()
if MAX_ID == nil then -- "MAX!" dummy hardware not yet created, create it
table.insert(commandArray, {['OpenURL'] = 'http://127.0.0.1:'..DomoticzPort..'/json.htm?type=command¶m=addhardware&htype=15&port=1&name=MAX!&enabled=true'})
tcp = Socket.connect(MaxIP, MaxPort)
if not tcp then
print("Socket connect failed for "..MaxIP..':'..MaxPort)
return
tcp:settimeout(2)
while true do
s, status, partial = tcp:receive()
if (status) then
print("TCP receive - "..status)
break
local line = (s or partial)
local cmd = line:sub(1,1)
local data = line:sub(3)
if (cmd == 'H') then
status = maxCmd_H(data)
if status == 'Error' then break end
elseif (cmd == 'M') then
maxCmd_M(data)
elseif (cmd == 'C') then
maxCmd_C(data)
elseif (cmd == 'L') then
maxCmd_L(data)
break
tcp:close()
UPDATE:
Last edited by mvzut on Saturday 12 November 2016 15:27, edited 24 times in total.
Great! Wil test this morning! Where on a roll here hehe... Next stop a hardware plugin?
- Domoticz version: 3.5877
I tryed that script and got
2016-11-10 07:55:01.524 Error: EventSystem: in /home/pi/domoticz/scripts/lua/script_time_max.lua: /home/pi/domoticz/scripts/lua/script_time_max.lua:158: attempt to concatenate global 'MAX_ID' (a nil value)
Before trying script I updated my old version of json.lua.
I have one room with wall thermostat and one room without so I changed useWMT=false.
Do you use the standard Domoticz port of 8080? At two locations in the script, I forgot to change the default port into the variable "DomoticzPort" which is defined at the start of the script. I uploaded the script in the previous post, maybe you can try that. Unless you are using the default 8080, then it shouldn't make a difference for you. If that's the case, I will need to dive into your issue later.Teatech wrote:I tryed that script and got