Making groups and association
Posted: Monday 04 January 2016 0:07
by kritjuu
Hello there,
I hope someone can explain me how I have to make Z wave group and association between different nodes.
I am new with Domoticz.
I use Raspberry pi with Razberry Zwave controller. I want to make an association between 2 nodes: Everspring ST814 humidity detector and Fibaro relay-switch who is switching my bathroom fan. When the humidity is 90 % and 82% the sensor is triggered and the fan should go on and of automatically.
What steps do I have to take to make this working in Domoticz. I now can only switch manually.
Re: Making groups and association
Posted: Monday 04 January 2016 10:22
by almirhod
Hardware -> Setup (Your controller) -> Node Management -> Groups & Networks.
There you will see all the nodes & groups. You need to add the Fibaro Relay Switch NODE to correct group in the Everspring hum. detector. If there are several groups under the Everspring node you need to read the manual to see which group is the correct. Then the Evespring will switch on/off the Fibaro node.
All of the above assumes that you have associated the swithc & sensor with the main controller. So that they are visible in Domoticz.
Re: Making groups and association
Posted: Monday 04 January 2016 10:41
by kritjuu
Thanks for your answer. Very simple. It works.
Re: Making groups and association
Posted: Monday 04 January 2016 14:08
by almirhod
No problem. Just wondering something, Isnt 90% Rh a bit high?

Re: Making groups and association
Posted: Saturday 16 July 2016 10:02
by RikkieB
Hi,
Just wondering why this does not work with the fibaro smoke sensor in combination with the Fibaro Roller shutter. I put the roller shutter in group 2 of the smoke sensor. According to the manual I can use this group. The smoke sensor will sent basic on and off commands to that group. But still does not work. Any ideas?
Rik
Re: Making groups and association
Posted: Sunday 17 July 2016 9:37
by RikkieB
Nobody?
Re: Making groups and association
Posted: Monday 18 July 2016 10:09
by RikkieB
My bad! A test alarm is NOT a real alarm. When testing with real smoke, Fibaro Roller Shutter works (through the controller), although I can't seem to understand if the smoke alarm is really a smoke alarm in Domoticz, as for 2 roller shutters I changed the parameter for smoke alarm to 'no reaction', but still these roller gates go open when a real alarm is triggered. When the alarm stops, the roller gates go down again.
Re: Making groups and association
Posted: Monday 18 July 2016 19:10
by RikkieB
I figured it out. In the smoke sensor, disable alarm broadcast and make appropriate settings in each roller shutter.