hybride hvac with cv and airco
Posted: Saturday 03 January 2026 15:53
I have a hybrid hvac system running with mitsh.heavy airco and remeha avanta CV with thermostat (NEST in my case, but the brand does not matter) To use it you need your thermostat and airco values available and create an extra virtual housesetpoint
my external helperfunction tdiff :
why an extra setpoint : well this way it keeps running even if the cloud is down. You always have your local housesetpoint that you can use.
The only thing youll miss is the link between thermostat and airco setpoint when cloud is down (CV still works and airco also sill works, just not linked) this way its failsafe as long as you have power to feed the airco. I also have a virtual mode switch "normal", "turbo", "turbo+"
Normal = self explaining.
Turbo -> airco livingroom is turned on together with cv to reduce gas use.
Turbo+ -> same as turbo but also turns on airco on 1st and 2th floor.
Max = also switch on electric heater ( i never use it)
x = always on. decoupled keep airco always on in heating mode.
I have a couple of redundant things : i check also "Cv koud" and cv and airco power usage, those are just expirimental (seem to work with my poweplugs) just in case something fails as a "late backup" but it should run without it. Maybe couple of things not as nice as i have running it
Dont think this is an out of the box routine, i adjusted the offset values to my home, you have a warmup curve for cv and airco + an the heatbuffer in every home wich is very specific. So you'll need to adjust till you have the comfort you want.
(a good reader notices i have a sensor "Cv koud" what is kaku doorsensor with a 30*C clickson mounted at the place of the reed contact. It was just for testing and diagnostic, but since i have i keep using it as backup).
What is that part at the beginning with the table at the beginning ? Well i have a lot of devices in domoticz, this is my common way to have script parts only running and using time if relevant sensors are triggering the event system. I want to reduce cpu use as much as possible to keep things smooth and fast. (i have about 80 devices a minute that trigger the event system, so a lot & i need to keep up performance)
Why plain lua ? because i know the language and use lua also on other things. So just to lazy to learn dzevents (sorry)
So not out of the box working but a source of inspiration that needs tweaking and adjustment ... Have fun with it.
p.s. I also have my curtains opening when solar >1000W to let sunwarmt in and closing when <400W with a min. timewindow.
function Aircoverwarming()
if otherdevices["Airco Master"]=="On" then
local buiten = otherdevices_temperature["Buiten"]
local binnen = otherdevices_temperature["Binnen"]
-- hoofdblok
local od = otherdevices
local dc = devicechanged or {}
local uv = uservariables or {}
local timenow = os.date("*t")
-- Allowed devices check (CPU sparen)
local allowed_devices_list = {
["Binnen"] = true, ["Buiten"] = true, ["Woonkamer tmp"] = true,
["Heating mode"] = true, ["Cv koud"] = true, ["Cv koud 2"] = true,
["Target Setpoint Beneden"] = true,
["Target Setpoint 1e"] = true, ["Target Setpoint Zolder"] = true,
["Airco Power Beneden"] = true, ["Airco Power 1e"] = true,
["Airco Power Zolder"] = true, ["Operation Mode Beneden"] = true,
["Operation Mode 1e"] = true, ["Operation Mode Zolder"] = true,
["Swing Up/Down Beneden"] = true, ["Swing Up/Down 1e"] = true,
["Swing Up/Down Zolder"] = true, ["LivingFlame"] = true,
["Huis Setpoint"] = true
local skip = false
if device ~= nil and not allowed_devices_list[device] then skip = true end
if skip == false then
local function AircoExtraLogging()
-- MHI DEFROST DETECTOR (robust, 1 uservar)
local usage = tonumber(otherdevices_utility["Airco Beneden Usage"] or "0")
local defrost_active = 0
-- Detectie defrost actief (13–50 W)
if od["Airco Power Beneden"] == "On" and usage >= 13 and usage <= 50 then
defrost_active = 1
if dc["Binnen"] then print("❄️ DEFROST (Usage="..usage.."W)") end
-- PLUGIN REFRESH DETECTOR (haunted house edition)
--if dc["Target Setpoint Beneden"] ~= nil then print("👻 Plugin refresh: Target Setpoint Beneden = "..tostring(dc["Target Setpoint Beneden"])) end
--if dc["Target Setpoint 1e"] ~= nil then print("👻 Plugin refresh: Target Setpoint 1e = "..tostring(dc["Target Setpoint 1e"])) end
--if dc["Target Setpoint Zolder"] ~= nil then print("👻 Plugin refresh: Target Setpoint Zolder = "..tostring(dc["Target Setpoint Zolder"])) end
-- helpers
local abort_airco_logic = false
local function set_if_needed(dev, value, reden)
if otherdevices[dev] ~= value then
commandArray[dev] = value
if dev=="Airco Power Beneden" then set_var_if_needed("AircoHardGuard", "1", "HardGuard on") set_var_if_needed("AircoHardGuard_since", tostring(now), "HardGuard timestamp set") end
if debugprint==true then print("🔥❄️ Airco&Nest: "..dev.." = "..value.." -> "..tostring(reden)) printdone=true end
local function set_var_if_needed(var, value, reden)
if uservariables[var] ~= value then
commandArray["Variable:"..var] = value
if debugprint==true then print("🔥❄️ Airco&Nest: "..var.." = "..value.." -> "..tostring(reden)) printdone=true end
-- Setpoint helper:
-- - gebruikt één centrale uservariable (airco_heating_setpoint)
-- - alleen Beneden (idx 6352) MAG die variable updaten
-- - 1e en Zolder LEZEN alleen de variable om te volgen
local function set_setpoint_if_needed(idx, target_sp, reden)
local target_str = tostring(target_sp)
-- Alleen iets doen als het centrale setpoint wijzigt
if uservariables["airco_heating_setpoint"] ~= target_str then
commandArray["SetSetPoint:"..idx] = target_str
-- Alleen Beneden schrijft de centrale uservariable
if idx == "6352" then commandArray["Variable:airco_heating_setpoint"] = target_str end
if debugprint==true then print("🔥❄️ Airco&Nest: "..idx.." = "..target_sp.." -> "..tostring(reden)) printdone=true end
local function timing_helper(dev)
local status=od[dev]
local duration = 9999
local v1, d1, v2, d2, v3, d3 = showHistory(dev, 3, false)
if v1 == status then duration = d1 elseif v2 == status then duration = d2 end
return duration
local function robust_tdiff(dev)
local t = TDiff(dev) if t > 5 then return t else return timing_helper(dev) end
-- Loop preventie: radiator vents blokkeren
if device and string.find(device,"radiator vent") ~= nil then abort_airco_logic = true end
-- CV usage
local CV_usage = od["CV Usage"]
CV_usage = tonumber(string.sub(CV_usage,1,string.find(CV_usage,";")-1))
-- Setpoint
local Setpoint = od["Huis Setpoint"]
-- diversen
local debugprint = false
local debugprinttotal = false
local Setpoint_offset = 0.5
local Setpoint_offset_start = 4
local current_temp = round((tonumber(otherdevices_temperature["Woonkamer tmp"]) + tonumber(otherdevices_temperature["Binnen"])) / 2, 1)
local Heating = (od["Cv koud"] == "Off" or od["NEST heating"] == "On")
local HeatingMode = od["Heating mode"] or "Off"
local airco_heating_startup = uv["airco_heating_startup"]
local Cvlu = controleer("Cv koud") or TDiff("Cv koud")
local radlu = controleer("radiator vent rechts") or TDiff("radiator vent rechts")
local aircolu = controleer("Airco Power Beneden") or robust_tdiff("Airco Power Beneden")
local aircolu2 = controleer("Airco Power 1e") or robust_tdiff("Airco Power 1e")
local aircolu3 = controleer("Airco Power Zolder") or robust_tdiff("Airco Power Zolder")
-- Setpoint mirror
local SetpointHuis = round(otherdevices_svalues["Huis Setpoint"],1)
local SetpointNest = round(otherdevices_svalues["NEST setpoint"],1)
local varHuis=tonumber(uservariables["Airco_setpoint"])
local varNest=tonumber(uservariables["Nest_setpoint"])
--local transfer_offset = math.abs(round(current_temp-otherdevices_temperature["NEST temp"],1)) + 0.1
local transfer_offset = 0.9 -- match sensoren offset met NEST
local NestChanged=(tonumber(SetpointNest)~=tonumber(varNest))
local HuisChanged=(tonumber(SetpointHuis)~=tonumber(varHuis))
if NestChanged then
print("Nestchanged - old:"..varNest.." new:"..SetpointNest)
commandArray["Variable:Nest_setpoint"]=tostring(SetpointNest)
print("Huissetpoint aangepassen naar: "..tostring(tonumber(SetpointNest)+transfer_offset))
commandArray["SetSetPoint:8599"] = tostring(SetpointNest+transfer_offset)
if HuisChanged then
print("HuisChanged - old:"..varHuis.." new:"..SetpointHuis)
commandArray["Variable:Airco_setpoint"]=tostring(SetpointHuis)
-- Thresholds
local airco_on_threshold = Setpoint + 0.1
local airco_hold_threshold = Setpoint + 0.3
local airco_off_threshold = Setpoint + 0.7
local airco_hard_guard = airco_off_threshold + 0.7 -- overshoot-correctie
local airco_Min_time_On = 1200
local airco_Min_time_Off = 900
--local airco_Max_runtime = 21600
if debugprint then AircoExtraLogging() end
-- SETPOINT REALIGNMENT (mode-agnostisch, HVAC-safe)
-- Wordt uitgevoerd zodra Huis Setpoint is gewijzigd.
-- Doel: alle airco-targets opnieuw afleiden uit HuisSetpoint,
-- zonder on/off, zonder HardGuard-conflict.
if HuisChanged then
local desired_b, desired_1e, desired_z
-- BENEDEN (leidend toestel)
if od["Airco Power Beneden"] == "On" then
if HeatingMode == "X" then
desired_b = Setpoint -- exact volgen
elseif HeatingMode == "Normal" or HeatingMode == "Turbo" then
desired_b = Setpoint + Setpoint_offset_start
elseif HeatingMode == "Turb+" or HeatingMode == "Max" then
-- 1e VERDIEPING
if od["Airco Power 1e"] == "On" then
desired_1e = Setpoint - 1
desired_1e = Setpoint + Setpoint_offset_start
-- In Normal/Turbo volgt 1e alleen als hij aan staat
-- ZOLDER
if od["Airco Power Zolder"] == "On" then
desired_z = Setpoint - 2
desired_z = Setpoint + Setpoint_offset_start
-- APPLY (alleen setpoints, nooit power!)
if desired_b then set_setpoint_if_needed("6352", desired_b, "Realign Beneden") print("setpointB doen") end
if desired_1e then set_setpoint_if_needed("6361", desired_1e, "Realign 1e") print("setpoint1e doen") end
if desired_z then set_setpoint_if_needed("6367", desired_z, "Realign Zolder") print("setpointZ doen") end
-- HARD GUARD (100% HVAC-safe, onafhankelijk van TDiff)
local now = os.time()
local hg_since = tonumber(uservariables["AircoHardGuard_since"] or "0") or 0
local elapsed = now - hg_since
-- Detecteer wijziging van Airco Power Beneden (intern of extern)
if dc["Airco Power Beneden"] ~= nil then
set_var_if_needed("AircoHardGuard", "1", "HardGuard on (change detected)")
hg_since = now
elapsed = 0
-- Guard actief zolang <300 sec
if elapsed < 300 then
set_var_if_needed("AircoHardGuard", "1", "HardGuard active (<300s)")
if dc["Binnen"] then print("🔥❄️ Airco&Nest: HardGuard actief !") end
return -- return: script mag niet verder
set_var_if_needed("AircoHardGuard", "0", "HardGuard released (>300s)")
--extra guard : clickson rf433 "uit" gemist
if TDiff("Cv koud")>3600 and od["Cv koud"]=="Off" and od["NEST heating"] == "Off" then
commandArray["Cv koud"]="On"
print("🔥❄️ Airco&Nest: CV koud correctie na 3600 sec")
-- compressor protection timers (op basis van TDiff)
local Min_On_b = (TDiff("Airco Power Beneden") > airco_Min_time_On and od["Airco Power Beneden"]=="On")
local Min_On_1e = (TDiff("Airco Power 1e") > airco_Min_time_On and od["Airco Power 1e"]=="On")
local Min_On_z = (TDiff("Airco Power Zolder") > airco_Min_time_On and od["Airco Power Zolder"]=="On")
local Min_Off_b = (TDiff("Airco Power Beneden") > airco_Min_time_Off and od["Airco Power Beneden"]=="Off")
local Min_Off_1e= (TDiff("Airco Power 1e") > airco_Min_time_Off and od["Airco Power 1e"]=="Off")
local Min_Off_z = (TDiff("Airco Power Zolder") > airco_Min_time_Off and od["Airco Power Zolder"]=="Off")
-- koude dag
local tempbuiten = otherdevices_temperature["Buiten"]
local tempbinnen = otherdevices_temperature["Binnen"]
local deltatemp = tempbinnen - tempbuiten
local coldday = (tempbuiten < 10 and deltatemp > 10 and timenow.hour >= 8 and timenow.hour < 22)
-- cv "real on" guard
local CV_On = od["CV ingebruik"]=="On"
local CV_On_lu = TDiff("CV ingebruik") > 1800
if CV_On and CV_On_lu then Heating = Heating and (CV_usage > 50) end
-- startup offset resetten naar normale offset als Airco beneden uit
reden="startup offset resetten naar normale offset "
if od["Airco Power Beneden"]=="Off" then set_var_if_needed("airco_heating_setpoint", "0",reden) end
-- Radiatorventilatoren
if Heating and od["Radiator vent Master"]=="On" then
if od["radiator vent achter"] == "Off" then
commandArray["radiator vent achter"] = "On REPEAT 2 INTERVAL 10"
if debugprint==true then print("Airco&Nest: Radiatorvent = On") end
if od["radiator vent rechts"] == "Off" then commandArray["radiator vent rechts"] = "On REPEAT 2 INTERVAL 11" end
if od["radiator vent links"] == "Off" then commandArray["radiator vent links"] = "On REPEAT 2 INTERVAL 12" end
elseif Cvlu >= 1200 and od["Radiator vent Master"]=="On" then
if od["radiator vent achter"] == "On" then commandArray["radiator vent achter"] = "Off REPEAT 2 INTERVAL 10" end
if od["radiator vent rechts"] == "On" then commandArray["radiator vent rechts"] = "Off REPEAT 2 INTERVAL 11" end
if od["radiator vent links"] == "On" then commandArray["radiator vent links"] = "Off REPEAT 2 INTERVAL 12" end
-- Startup / Keepon / coldday / mode logica voorbereiden
local startup_flag = tonumber(uv["airco_heating_startup"] or "0") or 0
local ontime_b = controleer("Airco Power Beneden") or 0
local ontime_1e = controleer("Airco Power 1e") or 0
local ontime_z = controleer("Airco Power Zolder") or 0
local offtime_b = TDiff("Airco Power Beneden") or 0 if od["Airco Power Beneden"]=="On" then offtime_b=0 end
local offtime_1e = TDiff("Airco Power 1e") or 0 if od["Airco Power 1e"]=="On" then offtime_1e=0 end
local offtime_z = TDiff("Airco Power Zolder") or 0 if od["Airco Power Zolder"]=="On" then offtime_z=0 end
local KeepOn_b = (ontime_b > 0 and ontime_b < 1800)
local KeepOn_1e = (ontime_1e > 0 and ontime_1e < 1800)
local KeepOn_z = (ontime_z > 0 and ontime_z < 1800)
if current_temp >= airco_off_threshold then
KeepOn_b = false
KeepOn_1e = false
KeepOn_z = false
-- Startup reset (10 min) alleen voor beneden
if startup_flag == 1 and od["Airco Power Beneden"]=="On" and ontime_b > 600 then
reden="Startup reset (10 min)"
set_setpoint_if_needed("6352", Setpoint + Setpoint_offset,reden)
set_var_if_needed("airco_heating_startup", "0",reden)
-- Heating mode Off → alles uit
if dc["Heating mode"]=="Off" then
reden="Heating mode Off"
if od["Airco Power Beneden"] ~= "Off" and Min_On_b then set_if_needed("Airco Power Beneden","Off",reden) end
if od["Airco Power 1e"] ~= "Off" and Min_On_1e then set_if_needed("Airco Power 1e","Off",reden) end
if od["Airco Power Zolder"] ~= "Off" and Min_On_z then set_if_needed("Airco Power Zolder","Off",reden) end
if debugprint==true then print("Airco&Nest: heatingmode off gezet") end
-- HARDE VEILIGHEID (A2)
-- current_temp > airco_hard_guard → airco mag NIET starten
-- airco moet UIT zodra Min_On gehaald is
if current_temp > airco_hard_guard then
reden="current_temp > airco_hard_guard"
if od["Airco Power Beneden"]=="On" and Min_On_b then set_if_needed("Airco Power Beneden","Off",reden) set_var_if_needed("AircoHardGuard", "1", "HardGuard on") set_var_if_needed("AircoHardGuard_since", tostring(now), "HardGuard timestamp set") end
if od["Airco Power 1e"]=="On" and Min_On_1e then set_if_needed("Airco Power 1e","Off",reden) end
if od["Airco Power Zolder"]=="On" and Min_On_z then set_if_needed("Airco Power Zolder","Off",reden) end
-- LivingFlame uit
if od["LivingFlame"]=="On" then
commandArray[#commandArray+1] = { ["LivingFlame"] = "Set level 30" }
commandArray[#commandArray+1] = { ["LivingFlame"] = "Set level 10 AFTER 10" }
-- Fan naar Auto (Off)
reden="Fan naar Auto"
set_if_needed("Fan Beneden","Off",reden)
set_if_needed("Fan 1e","Off",reden)
set_if_needed("Fan Zolder","Off",reden)
-- Mode-logica overslaan
-- MODE-LOGICA (alleen uitvoeren als niet geaborteerd)
-- Allow-flags alvast declareren voor debugscope
local allow_start_b = false
local allow_start_1e = false
local allow_start_z = false
if not abort_airco_logic then
-- MINIMUM OFF-TIME GUARD (voorkomt directe herstart)
allow_start_b = (od["Airco Power Beneden"]=="Off" and Min_Off_b and commandArray["Airco Power Beneden"] ~= "Off")
allow_start_1e = (od["Airco Power 1e"]=="Off" and Min_Off_1e and commandArray["Airco Power 1e"] ~= "Off")
allow_start_z = (od["Airco Power Zolder"]=="Off" and Min_Off_z and commandArray["Airco Power Zolder"] ~= "Off")
-- NORMAL MODE
if HeatingMode == "Normal" then
-- Start vlak voor setpoint (airco voor CV)
if current_temp <= airco_on_threshold then
reden="Normal: Start vlak voor setpoint"
if allow_start_b then
set_if_needed("Airco Power Beneden", "On",reden)
set_setpoint_if_needed("6352", Setpoint + Setpoint_offset_start,reden)
set_var_if_needed("airco_heating_startup", "1",reden)
set_if_needed("Swing Up/Down Beneden", "Set Level 50",reden)
set_if_needed("Operation Mode Beneden", "Set Level 20",reden)
-- Coldday hold: airco zachtjes aan om CV te ontlasten
if coldday and current_temp >= airco_hold_threshold and not Heating then
reden="Normal: Coldday hold: airco zachtjes aan om CV te ontlasten"
set_if_needed("Fan Beneden", "Off",reden)
set_setpoint_if_needed("6352", airco_hold_threshold,reden)
-- Normale uitschakelconditie (boven setpoint, CV niet meer warm)
if current_temp >= airco_off_threshold and not Heating then
reden="Normal: Normale uitschakelconditie (boven setpoint, CV niet meer warm)"
if od["Airco Power Beneden"] == "On" and Min_On_b then
if not KeepOn_b then set_if_needed("Airco Power Beneden", "Off", reden) end
-- TURBO MODE
elseif HeatingMode == "Turbo" then
if Heating then
reden="Turbo: Opstarten met heating"
if current_temp >= airco_off_threshold and not KeepOn_b then
reden="Turbo: current_temp >= airco_off_threshold and not KeepOn_b"
set_if_needed("Airco Power Beneden", "Off",reden)
elseif coldday and current_temp >= airco_off_threshold then
reden="Turbo: coldday and current_temp >= airco_off_threshold"
elseif ontime_b >= 1800 and not KeepOn_b then
reden="Turbo: ontime_b >= 1800 and not KeepOn_b"
-- TURB+ MODE (alle airco’s volgen CV, met boost boven)
elseif HeatingMode == "Turb+" then
if Heating then
-- Beneden (met startup-boost via airco_heating_startup)
set_if_needed("Airco Power Beneden", "On")
set_setpoint_if_needed("6352", Setpoint + Setpoint_offset_start)
set_var_if_needed("airco_heating_startup", "1")
set_if_needed("Swing Up/Down Beneden", "Set Level 50")
set_if_needed("Fan Beneden", "Off")
set_if_needed("Operation Mode Beneden", "Set Level 20")
-- 1e (startup-boost via ontime_1e)
if allow_start_1e then
set_if_needed("Airco Power 1e", "On")
set_if_needed("Swing Up/Down 1e", "Set Level 50")
set_if_needed("Operation Mode 1e", "Set Level 20")
set_if_needed("Fan 1e", "Off")
if od["Airco Power 1e"] == "On" and commandArray["Airco Power 1e"] ~= "Off" then
if ontime_1e < 600 then
set_setpoint_if_needed("6361", Setpoint + Setpoint_offset_start)
set_setpoint_if_needed("6361", Setpoint + Setpoint_offset)
-- Zolder (startup-boost via ontime_z)
if allow_start_z then
set_if_needed("Airco Power Zolder", "On")
set_if_needed("Swing Up/Down Zolder", "Set Level 50")
set_if_needed("Operation Mode Zolder", "Set Level 20")
set_if_needed("Fan Zolder", "Off")
if od["Airco Power Zolder"] == "On" and commandArray["Airco Power Zolder"] ~= "Off" then
if ontime_z < 600 then
set_setpoint_if_needed("6367", Setpoint + Setpoint_offset_start)
set_setpoint_if_needed("6367", Setpoint + Setpoint_offset)
if od["Airco Power Beneden"] == "On" and Min_On_b and not KeepOn_b then set_if_needed("Airco Power Beneden", "Off") end
if od["Airco Power 1e"] == "On" and Min_On_1e and not KeepOn_1e then set_if_needed("Airco Power 1e", "Off") end
if od["Airco Power Zolder"] == "On" and Min_On_z and not KeepOn_z then set_if_needed("Airco Power Zolder", "Off") end
-- MAX MODE (Turb+ + LivingFlame)
elseif HeatingMode == "Max" then
if Heating then
-- LivingFlame aan (alleen in Max)
if od["LivingFlame"] == "Off" then
commandArray[#commandArray+1] = { ["LivingFlame"] = "Set level 20" }
commandArray[#commandArray+1] = { ["LivingFlame"] = "Set level 50 AFTER 10" }
-- LivingFlame uit (alleen in Max)
if od["LivingFlame"] == "On" then
-- X MODE (permanent aan, maar harde guard OVERRULET)
elseif HeatingMode == "X" then
-- Beneden
set_setpoint_if_needed("6352", Setpoint)
set_var_if_needed("airco_heating_startup", "0")
set_if_needed("Fan Beneden", "Set Level 10")
-- 1e
if allow_start_1e then set_if_needed("Airco Power 1e", "On") end
if od["Airco Power 1e"]=="On" and commandArray["Airco Power 1e"] ~= "Off" then
set_setpoint_if_needed("6361", Setpoint - 1)
-- Zolder
if allow_start_z then set_if_needed("Airco Power Zolder", "On") end
if od["Airco Power Zolder"]=="On" and commandArray["Airco Power Zolder"] ~= "Off" then
set_setpoint_if_needed("6367", Setpoint - 2)
end -- einde mode-logica
end -- einde abort_airco_logic
-- EINDE SCRIPT (GEEN return!)
if (debugprinttotal== true and dc["Binnen"]) or printdone then
print(
"🔥❄️ HVAC Airco&Nest",
" | NestTemp="..round(otherdevices_temperature["NEST temp"],1).."*C"..
" | NestSp="..round(otherdevices_svalues["NEST setpoint"],1).."*C"..
" | TransferOffset="..round(transfer_offset,1).."*C",
" | Mode="..HeatingMode..
" | Temp="..current_temp.."*C"..
" | SP="..Setpoint.."*C"..
" | ThrOn="..airco_on_threshold.."*C"..
" | ThrHold="..airco_hold_threshold.."*C"..
" | ThrOff="..airco_off_threshold.."*C"..
" | Hard="..airco_hard_guard.."*C",
" | Heating="..tostring(Heating)..
" | CVuse="..CV_usage.."W"..
" | Coldday="..tostring(coldday)..
" | Guard="..tostring(current_temp > airco_hard_guard)..
" | Hold="..tostring(coldday and current_temp >= airco_hold_threshold and not Heating),
-- Runtimes ON
" | onB="..ontime_b.." sec"..
" | on1e="..ontime_1e.." sec"..
" | onZ="..ontime_z.." sec"..
-- Runtimes OFF
" | offB="..offtime_b.." sec"..
" | off1e="..offtime_1e.." sec"..
" | offZ="..offtime_z.." sec",
-- Boost
" | BoostB="..tostring(startup_flag==1 and od["Airco Power Beneden"]=="On" and ontime_b < 600)..
" | Boost1e="..tostring(od["Airco Power 1e"]=="On" and ontime_1e < 600)..
" | BoostZ="..tostring(od["Airco Power Zolder"]=="On" and ontime_z < 600)..
-- KeepOn
" | KeepB="..tostring(KeepOn_b)..
" | Keep1e="..tostring(KeepOn_1e)..
" | KeepZ="..tostring(KeepOn_z),
-- Min_On
" | MinOnB="..tostring(Min_On_b)..
" | MinOn1e="..tostring(Min_On_1e)..
" | MinOnZ="..tostring(Min_On_z)..
-- Min_Off
" | MinOffB="..tostring(Min_Off_b)..
" | MinOff1e="..tostring(Min_Off_1e)..
" | MinOffZ="..tostring(Min_Off_z),
-- Allow start (Min_Off guard)
" | AllowB="..tostring(allow_start_b)..
" | Allow1e="..tostring(allow_start_1e)..
" | AllowZ="..tostring(allow_start_z),
-- Airco status
" | B="..od["Airco Power Beneden"]..
" | 1e="..od["Airco Power 1e"]..
" | Z="..od["Airco Power Zolder"]
end -- skip
end -- master
end -- function
function TDiff(input)
local prev = difference
local name, idx
for i, v in pairs(otherdevices_idx) do
if v == input or i == input then
name = i; idx = v
if name == nil then name = input end
local s = otherdevices_lastupdate and otherdevices_lastupdate[name]
if s ~= nil and name ~= "" then
local t2 = _parse_ts(s)
if t2 then
local t1 = _time()
if type(round) == "function" then
difference = round(_difftime(t1, t2), 0)
difference = math.floor(_difftime(t1, t2) + 0.5)
-- keep 'difference' unchanged if parse failed (matches original behavior)
print("TDIFF " .. tostring(input) .. " -- " .. tostring(name) .. "=nil")
-- keep 'difference' unchanged (matches original)
return difference