3 point motorized mixing valve [Solved]
bitzy
- Domoticz version: 2023.2
hello. i have a circulation unit that is equipped with a mixing valve controlled by a 3 point signal actuator.
ESBE GRA 211 Circulation Unit equipped with ESBE ARA661 Actuator https://www.esbe.eu/group/products/circ ... 200-gra300
The goal is to control the flow temperature according to the outside temperature. Being new to domoticz and not having any programming experience, i have a hard time on doing the script to control the actuator.
The actuator is a 230 V one, controlled by 3 wires. i control it in domoticz with the help of 2 switches, switches that control 2 relays from a 4 channel relay module, one for clockwise motion and one for anticlockwise motion.
i need to keep the track for the position of the actuator (it is moving 45 degree in the clockwise direction in 60 seconds from the initial position and 45 degree anticlockwise in 60 sec from the initial position)
Can someone help me with the script to control this actuator? (at least for a fixed temperature of the flow)
If someone is willing to do this i can put more information about the setup i am using and any other information that is necessary.
And another thing: how can i use as a trigger for a script a device that change state in another script? (i have a switch that control the pump that is triggered by the inside thermostat. i have a script that start the pump when the thermostat ask for heat. then i need to make a script that start the comby gas boiler when the pump start. if i manually start the pump, the boiler will fire, but if the pump is started by the script then it will not trigger the script for the boiler (i uderstand that is because how dzvent works? but i don't know how to work around this))
bitzy
Re: 3 point motorized mixing valve
no one dare?
- jacobsentertainment
- Domoticz version: 2021-1
If I'm correct you have basically an open and a close function on this device you want to control with domoticz based on the temperature behind the valve.
So you are looking for: if temperature is below 25° then open valve, and if above 35° then close valve. Thats it or do you also wish to use a thermostat on this? If so have a look in to the Virtual thermostat of domoticz, I use this for my floorheating and it works fine!
bitzy
the initial position of the valve is at at the middle between half close and half open (actually half open for the flow and half open for return). i call that position 0.
the valve does 90° of movement in 120 sec so to fully close the flow (and fully open the return) from that position (45°), it needs 60 sec ,or 60 sec to fully close the return (and fully open the flow). something like 60 - 0 - 60. it can be put anywhere in between this position. so the only way of maintaining the position of the valve is by counting the time it move.
i assigned the 2 relays at 2 on/off switches but i manually control them with the help of a venetian blinds switch, because i have to be careful not to energize both relays at the same time. i have 2 scripts that close 1 switch if the other one is open, but to activate the script, the trigger is the other switch so for a bit, i end up with both relays energized. so i use a venetian blinds switch with a script that first close the switch if open then open the other one. (but i cant use it in the floorplan unfortunately)
i did a script that take the temperature of the flow, compare it with the desired one an move the valve accordingly by open the corresponding switch for n seconds and keeping count of the sec it moved in a global var. but i end up with the switch doing only 2 cycle and the var going all the way up to 60 cause for what i so in the log the dzvent do all the script and then sending the command to the switch so the var is quickly increased but the actual movement of the valve is way slower.
bottom line is that i kinda have to use some timers with some checking or don't know what to check if the command was executed and i have no idea how to do this.
i thought on keeping the position of the valve in 2 global variable so i can know the position even if i manually move the valve with the switch.
first i need a way of keeping the position of the valve in the interval 60 - 60 for the manual movement, every time i activate the UP switch, a cout_up var need to keep the seconds of movement and not allow the switch to be open for more than 60 sec UP when starting from the 0 position. same for Down movement. (even if the switch open and valve move for 1 sec or 5 sec or 10 ... 50 sec)
something like this (i take a 20 sec movement for this exemple)
the manual reset of the valve is always in this 0 - 0 position.
count_up+20------------count_down-20 if actual_temp < set_temp -->switchUP-on-for 1..60 sec (depending how far apart set and actual temp are)
60--40--20----count_up=0---0----0---0
0---0----0---count_dwn=0--20--40--60
count_up-20--------------countdown+20 if actual_temp > set_temp --> switchDOWN-on-for 1..60 sec .....
for the manual movement count_up/down +/- tine.sec.switch_is_open
and move up or down in this area until the actual_temp == set_temp
the valve need to move a little wait some minutes (3..5) for the temperature to settle, read again and move some more (up or down) if needed.
i did it like this (without the wait part ) but unfortunately doesn't work for the way dzvent does his thing, so time must be used so i have no clue what need to be done cause my programming skills are limited and the syntax and insides of dzvent will take me a lot of time to learn in detail.
if maybe someone help me with 1 switch to keep count of the position and not move over those 60 up and 60 sec down, i can start from there and bring both together depending on the flow temperature, then make the flow temperature dependent of the outside temperature.
i can't put a link to a youtube video to how the valve but look for
50% valve position in VRG valve or ARA manual and automatic operation
bitzy
This is my setup
i use a 4 module relay board to start/stop the comby, read if the comby is in block state, start/stop the pump for the underfloor heating and to try to control the actuator. (i use a thermostatic mixing valve to get a constant value for my motorized mixing valve to be able to set it in manual mode for the moment). is a work in progress so anything can be changed.
by the way, the controller for that valve with exterior compensation and interior reading for desired temperature is arround 700 euro.
for the thermostat and controlling the pump there is a simple script in the script/dzVent/examples folder
bitzy
i managed to do a little script. i need some help from someone who know dzvent and programming to take a look and see what is not write and what can be improved.
i put a auto switch and the switch that help me set the desired temperature as trigger but the switches only start opening after 1 minute. can someone tell me why and what i should change?
please keep in mind that i'm not a programmer.
is just to figure out how it works, and if someone correct it i will try to go ahead and do some change to move the valve for longer or shorter time, depending on how far the set_temp and actual_temp are and to try to regulate the actual_temp depending on the outside temperature.
thanks in advance !!
timer = {
'every 2 minutes'
devices = {
'Auto_TempAdjustment', -- dummy switch set the auto/manual
'Tur', -- the actual temperature after the valve
'Setare_temperatura_tur', -- dummy to set the dezired value for the temperature
variables = {
't_tur_setat',
't_DOWN_count',
't_UP_count',
execute = function(dz, devices)
local tauto = dz.devices('Auto_TempAdjustment')
local set_t = dz.variables('t_tur_setat') -- global var that keep the dezired value of the temperature
local actual_t = dz.devices('Tur')
local move_up = dz.devices('TadjustUP_(rLe3)') -- on/off switch that controll the relay for the up movement
local move_down = dz.devices('TadjustDOWN_(rLe4)') -- on/off switch that controll the relay for the down movement
if (devices.isTimer and tauto.state == 'On') then
if (actual_t.temperature > set_t.value) then
if (dz.variables('t_UP_count').value == 0 and dz.variables('t_DOWN_count').value ==0) then
move_down.switchOn().forSec(5)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 5)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value < 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 5)
elseif (actual_t.temperature < set_t.value) then
move_up.switchOn().forSec(5)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 5)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value < 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value >0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 5)
bitzy
it seems no one is interested in this subject. can someone point to another site where i can ask for help?
bitzy
i put together another script that moves the actuator more or less depending on how far the actual temperature is from the set value.
i really need someone more experienced to take a look and see what is not right and what can be improved, or if someone has another aproacs to this job a little simpler.
this one not working as intended. gets at the end then start another cicle into the same direction and not closing anymore !!!!!
timer = {
'every 1 minutes'
devices = {
'Tur',
variables = {
't_tur_setat',
't_DOWN_count',
't_UP_count',
if (actual_t.temperature >= set_t.value + 5) then
move_down.switchOn().forSec(30)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 30)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 30 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 30 > 60)) then
dz.variables('t_cam_setat').set(60 - dz.variables('t_DOWN_count').value)
move_down.switchOn().forSec(60 - dz.variables('t_DOWN_count').value)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + (60 - dz.variables('t_DOWN_count').value))
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -30 >= 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 30)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -30 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(30-(30-dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (30-(30-dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(30-(30-(30-dz.variables('t_UP_count').value))))
elseif ((actual_t.temperature < set_t.value + 5) and (actual_t.temperature >= set_t.value + 3)) then
move_down.switchOn().forSec(20)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 20)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 20 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 20 > 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 20 > 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 20)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -20 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(20-(20-dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (20-(20-dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(20-(20-(20-dz.variables('t_UP_count').value))))
elseif ((actual_t.temperature < set_t.value + 3) and (actual_t.temperature >= set_t.value + 2)) then
move_down.switchOn().forSec(15)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 15)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value>0 and dz.variables('t_DOWN_count').value + 15 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 15 > 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 15 > 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 15)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -15 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(15-(15-dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (15-(15-dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(15-(15-(15-dz.variables('t_UP_count').value))))
elseif ((actual_t.temperature < set_t.value + 2) and (actual_t.temperature >= set_t.value + 1)) then
move_down.switchOn().forSec(10)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 10)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value>0 and dz.variables('t_DOWN_count').value + 10 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 10 > 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 10 > 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 10)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -10 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(10-(10-dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (10-(10-dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(10-(10-(10-dz.variables('t_UP_count').value))))
elseif ((actual_t.temperature < set_t.value + 1) and (actual_t.temperature >= set_t.value + 0.5)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value>0 and dz.variables('t_DOWN_count').value + 5 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 5 > 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 5 > 0 and dz.variables('t_UP_count').value <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -5 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(5-(5-dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (5-(5-dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(5-(5-(5-dz.variables('t_UP_count').value))))
elseif ((actual_t.temperature < set_t.value + 0.5) and (actual_t.temperature > set_t.value)) then
move_down.switchOn().forSec(1)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 1)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value>0 and dz.variables('t_DOWN_count').value + 1 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 1 > 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 1 > 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 1)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -1 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(1-(1-dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (1-(1-dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(1-(1-(1-dz.variables('t_UP_count').value))))
elseif (actual_t.temperature <= set_t.value -5) then
if (dz.variables('t_DOWN_count').value == 0 and dz.variables('t_UP_count').value ==0) then
move_up.switchOn().forSec(30)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 30)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 30 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 30 > 60)) then
dz.variables('t_cam_setat').set(60 - dz.variables('t_UP_count').value)
move_up.switchOn().forSec(60 - dz.variables('t_UP_count').value)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + (60 - dz.variables('t_UP_count').value))
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -30 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 30)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -30 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(30-(30-dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (30-(30-dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(30-(30-(30-dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 5) and (actual_t.temperature <= set_t.value - 3)) then
move_up.switchOn().forSec(20)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 20)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 20 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 20 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -20 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 20)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -20 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(20-(20-dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (20-(20-dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(20-(20-(20-dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 3) and (actual_t.temperature <= set_t.value - 2)) then
move_up.switchOn().forSec(15)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 15)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 15 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 15 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -15 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 15)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -15 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(15-(15-dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (15-(15-dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(15-(15-(15-dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 2) and (actual_t.temperature <= set_t.value - 1)) then
move_up.switchOn().forSec(10)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 10)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 10 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 10 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -10 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 10)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -10 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(10-(10-dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (10-(10-dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(10-(10-(10-dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 1) and (actual_t.temperature <= set_t.value - 0.5)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 5 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 5 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -5 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -5 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(5-(5-dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (5-(5-dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(5-(5-(5-dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 0.5) and (actual_t.temperature < set_t.value)) then
move_up.switchOn().forSec(1)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 1)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 1 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 1 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -1 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 1)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value -1 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(1-(1-dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (1-(1-dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(1-(1-(1-dz.variables('t_DOWN_count').value))))
bitzy
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 30 > 60)) then-
bitzy
is see the subject is of no interest to no one.
i struggled and done this:
i dont know how to put it in a more simpler form. maybe someone else cane, but i doubt that since is no interest in the subject.
it will keep the temp like this:
the start, until the return settles a bit is very slow and all over the place. in the pictures above i manually changed the trigger time to 1min.
it needs a 1 min trigger and some time conditioning to move the actuator depending on the temp, at a faster rate at the beginning when the temp start to settle (something like 1/2 a min or 1 minute) and more and more slower when it brought the temp at the set point. need some time manipulation and i don't understand it yet. maybe in the future, or maybe someone else want to do something. and maybe in the future some code whit some corelation betwin flow and return, with some anticipation, cause with this, the actuator is always behind the temp.
over all, a +/- 0.5 degree i'l say it's very good for a improvisation.
timer = {
'every 2 minutes'
-- devices = {
-- 'Auto_TempAdjustment',
-- 'Tur',
-- 'Setare_temperatura_tur',
-- local move = dz.devices('Temp_UP/DOWN')
-- local count_up = dz.variables('t_UP_count')
-- local count_down = dz.variables('t_DOWN_count')
move_down.switchOn().forSec(60)
dz.variables('t_DOWN_count').set(60)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 60 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 60 > 60)) then
if ((dz.variables('t_DOWN_count').value-60) < 0) then
dz.log('The valve is at the end and the temperature is still to high')
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -60 >= 0 and dz.variables('t_UP_count').value <= 60)) then
move_down.switchOn().forSec(120-(60-dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(0)
dz.variables('t_DOWN_count').set(120-((60-dz.variables('t_UP_count').value)-dz.variables('t_UP_count').value))
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value -60 < 0 and dz.variables('t_UP_count').value < 60)) then
move_down.switchOn().forSec(60 + dz.variables('t_UP_count').value)
elseif ((actual_t.temperature < set_t.value + 5) and (actual_t.temperature >= set_t.value + 4)) then
if ((dz.variables('t_DOWN_count').value-60) ~= 0) then
elseif ((actual_t.temperature < set_t.value + 4) and (actual_t.temperature >= set_t.value + 3)) then
elseif ((actual_t.temperature < set_t.value + 2) and (actual_t.temperature >= set_t.value + 1.5)) then
elseif ((actual_t.temperature < set_t.value + 1.5) and (actual_t.temperature >= set_t.value + 1)) then
move_down.switchOn().forSec(2)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 2)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value>0 and dz.variables('t_DOWN_count').value + 2 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 2 > 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 2 > 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 2)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 2 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(2 - (2 - dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (2 - (2 - dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(2- (2 - (2 - dz.variables('t_UP_count').value))))
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 1 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_cam_setat').set(1 - (1 - dz.variables('t_UP_count').value))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (1 - (1 - dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(1- (1 - (1 - dz.variables('t_UP_count').value))))
elseif ((actual_t.temperature < set_t.value + 0.5) and (actual_t.temperature > set_t.value+0.02)) then
move_down.switchOn().forSec(0.5)
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value + 0.5)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value>0 and dz.variables('t_DOWN_count').value + 0.5 <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value > 0 and dz.variables('t_DOWN_count').value + 0.5 > 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 0.5 > 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - 0.5)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value - 0.5 < 0 and dz.variables('t_UP_count').value <= 60)) then
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value - (0.5 - (0.5 - dz.variables('t_UP_count').value)))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value +(0.5 - (0.5 - (0.5 - dz.variables('t_UP_count').value))))
elseif (actual_t.temperature <= set_t.value - 5) then
if ((dz.variables('t_UP_count').value-60) ~= 0) then
move_down.switchOn().forSec(60 - dz.variables('t_UP_count').value)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 15 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 15 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (15 - (15 - dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(15 - (15 - (15 - dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 5) and (actual_t.temperature <= set_t.value - 4)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 10 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 10 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (10 - (10 - dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(10 - (10 - (10 - dz.variables('t_DOWN_count').value))))
-- elseif ((actual_t.temperature > set_t.value - 4) and (actual_t.temperature <= set_t.value - 3)) then
-- if (dz.variables('t_DOWN_count').value == 0 and dz.variables('t_UP_count').value ==0) then
-- move_up.switchOn().forSec(15)
-- dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 15)
-- elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 15 <= 60)) then
-- elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 15 > 60)) then
-- if ((dz.variables('t_UP_count').value-60) ~= 0) then
-- move_down.switchOn().forSec(60 - dz.variables('t_UP_count').value)
-- dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + (60 - dz.variables('t_UP_count').value))
-- dz.variables('t_cam_setat').set(60 - dz.variables('t_DOWN_count').value)
-- else
-- dz.log('The valve is at the end and the temperature is still to high')
-- end
-- elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 15 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
-- dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 15)
-- elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 15 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
-- dz.variables('t_cam_setat').set(15 - (15 - dz.variables('t_DOWN_count').value))
-- dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (15 - (15 - dz.variables('t_DOWN_count').value)))
-- dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(15 - (15 - (15 - dz.variables('t_DOWN_count').value))))
-- end
elseif ((actual_t.temperature > set_t.value - 4) and (actual_t.temperature <= set_t.value - 2)) then
move_up.switchOn().forSec(7)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 7)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 7 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 7 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 7 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 7)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 7 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(7 - (7 - dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (7 - (7 - dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(7 - (7 - (7 - dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 2) and (actual_t.temperature <= set_t.value - 1.5)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 5 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (5 - (5 - dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(5 - (5 - (5 - dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 1.5) and (actual_t.temperature <= set_t.value - 1)) then
move_up.switchOn().forSec(3)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 3)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 3 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 3 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 3 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 3)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 3 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(3 - (3 - dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (3 - (3 - dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(3 - (3 - (3 - dz.variables('t_DOWN_count').value))))
move_up.switchOn().forSec(2)
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value + 2)
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 2 <= 60)) then
elseif (dz.variables('t_DOWN_count').value == 0 and (dz.variables('t_UP_count').value > 0 and dz.variables('t_UP_count').value + 2 > 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 2 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - 2)
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 2 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
dz.variables('t_cam_setat').set(2 - (2 -dz.variables('t_DOWN_count').value))
dz.variables('t_DOWN_count').set(dz.variables('t_DOWN_count').value - (2 - (2 -dz.variables('t_DOWN_count').value)))
dz.variables('t_UP_count').set(dz.variables('t_UP_count').value +(2 - (2 - (2 - dz.variables('t_DOWN_count').value))))
elseif ((actual_t.temperature > set_t.value - 0.5) and (actual_t.temperature < set_t.value - 0.02)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 1 >= 0 and dz.variables('t_DOWN_count').value <= 60)) then
elseif (dz.variables('t_UP_count').value == 0 and (dz.variables('t_DOWN_count').value - 1 < 0 and dz.variables('t_DOWN_count').value <= 60)) then
- Domoticz version: 2026.3
It has been a long time for me (school) to touch this topic but perhaps you should read on the topic: PID controller.
If you seach on this in relation with Domoticz you will get topics like:
viewtopic.php?t=15075
https://domoticz.com/forum/viewtopic.php?t=16216
And there is also a Plugin https://domoticz.com/forum/viewtopic.php?t=19418 Perhaps not what you need but could be interesting for information.
bitzy
this is not solved. i need someone to help me do a better job with the code i wrote.
and if someone understand the PID algorithm to help me understand it myself so i can try to improve
bitzy
Re: 3 point motorized mixing valve [Solved]
The same script to keep a constant flow temperature, a little cleaner and easier to follow and modify:
and the script for resetting the valve (moving it in the maxDown position when the heating is close or the automat temperature adjustement is tuned in manual.
The reset is good for puting back in sinc the actual valve with the variable that track the movement in case something happened and they got offset. if the heating is runing 24/7, a sink can be done every day at a desired hour in the script that keep the temperature.
i'm also trying to make a script to use some heating curve and to automatically set the flow temperature depending on the outside temperature. but if someone else already have this or know how to make it please post it. i have something but is not working. maybe someone can take a look and try a fix.
timer = { 'every 2 minutes' }, -- Triggers the script every 1 minute
devices = {
'Auto_TempAdjustment', -- Device 'Selector to switch between 'Auto' and 'Manual' for the temperature adjustment'
-- 'Tur', -- Device 'Flow temperature sensor'
'Setare_temperatura_tur', -- Device 'for setting the desired temperature'
logging = {
level = domoticz.LOG_INFO,
marker = "** Atoadjust Flow Temperatre: **", -- Marker for log entries
-- Get relevant devices and variables
local tauto = dz.devices('Auto_TempAdjustment') -- Selector Device to switch betwin 'Auto' and 'Manual' for the temperature adjustement. -'Auto_TempAdjustment'
local set_t = dz.variables('t_tur_setat') -- User Variable for keeping the desired temperature value for the flow. - 't_tur_setat'
local actual_t = dz.devices('Tur') -- Temperature Sensore. 'Tur'
local move_up = dz.devices('TadjustUP_(rLe3)') -- Reley for moving the actuator up. - 'TadjustUP_(rLe3)'
local move_down = dz.devices('TadjustDOWN_(rLe4)') -- Relay for moving the actuator down. - 'TadjustDOWN_(rLe4)'
local pompa = dz.devices('Pompa_On/OFF_(rLe2)') -- Relay for turning On/Off the heating pump. - 'Pompa_On/OFF_(rLe2)'
local valvePosition = dz.variables('valvePosition') -- User Variable for keepeng track of the mixing valve position. - 'valvePosition'
local valveResetDone = dz.variables('valveResetDone') -- User Variable for reseting the mixing valve (moving the max down position). 'valveResetDone'
-- Calculate the temperature difference betwin the actual flow temperature and the desired one
local diff = actual_t.temperature - set_t.value
-- Function to move the valve up (open - increase temperature)
local function moveValveUp(valvePosition, moveActuator, targetMovement)
-- Check if the actual valve position+targetMovement not surpass the maxUp position of the actuator
if valvePosition.value + targetMovement <= 60 then
-- Switch the actuator up and update the valve position
moveActuator.switchOn().forSec(targetMovement)
valvePosition.set(valvePosition.value + targetMovement)
print('********** Moving valve up by ' .. targetMovement .. ' seconds. ***********')
--Check to avoid using command .switchOn().forsec(0)
elseif valvePosition.value ~= 60 then
-- Calculate remaining movement, switch the actuator up, and update the valve position
local remainingMovement = 60 - valvePosition.value
moveActuator.switchOn().forSec(remainingMovement)
valvePosition.set(valvePosition.value + remainingMovement)
print('********** Moving valve up by ' .. remainingMovement .. ' seconds. ***********')
-- Function to move the valve down
local function moveValveDown(valvePosition, moveActuator, targetMovement)
-- Check if the actual valve position-targetMovement not reach the maxDown position of the actuator
if valvePosition.value - targetMovement >= -60 then
-- Check the direction of movement and switch the actuator down accordingly
if targetMovement > 0 then
-- Switch the actuator down and update the valve position
valvePosition.set(valvePosition.value - targetMovement)
print('********** Moving valve down by ' .. targetMovement .. ' seconds. ***********')
elseif targetMovement < 0 then
local poz_targetMovement = -targetMovement
moveActuator.switchOn().forSec(poz_targetMovement)
dz.log('********** Moving valve down by ' .. poz_targetMovement .. ' seconds. ***********')
-- Check if the valve is not in the minDown position
elseif valvePosition.value ~= -60 then
-- Calculate remaining movement and switch the actuator down
local remainingMovement = -60 - valvePosition.value
if remainingMovement >= 0 then
valvePosition.set(-60)
print('********** Moving valve down by ' .. remainingMovement .. ' seconds. ***********')
local poz_remainingMovement = -remainingMovement
moveActuator.switchOn().forSec(poz_remainingMovement)
print('********** Moving valve down by ' .. poz_remainingMovement .. ' seconds. ***********')
-- Function to perform valve adjustments
local function performValveAdjustments(dz, valvePosition, move_up, move_down, diff)
-- Check temperature difference and perform valve adjustments
if diff >= 30 then
moveValveDown(valvePosition, move_down, 100)
elseif diff < 30 and diff >= 20 then
moveValveDown(valvePosition, move_down, 80)
elseif diff < 20 and diff >= 10 then
moveValveDown(valvePosition, move_down, 60)
elseif diff < 10 and diff >= 8 then
moveValveDown(valvePosition, move_down, 50)
elseif diff < 8 and diff >= 6 then
moveValveDown(valvePosition, move_down, 40)
elseif diff < 6 and diff >= 5 then
moveValveDown(valvePosition, move_down, 30)
elseif diff < 5 and diff >= 3 then
moveValveDown(valvePosition, move_down, 20)
elseif diff < 3 and diff >= 2 then
moveValveDown(valvePosition, move_down, 10)
elseif diff < 2 and diff >= 1 then
moveValveDown(valvePosition, move_down, 5)
elseif diff < 1 and diff >= 0.5 then
moveValveDown(valvePosition, move_down, 2)
elseif diff < 0.5 and diff >= 0.1 then
moveValveDown(valvePosition, move_down, 0.5)
elseif diff <= -30 then
moveValveUp(valvePosition, move_up, 60)
elseif diff > -30 and diff <= -20 then
moveValveUp(valvePosition, move_up, 30)
elseif diff > -20 and diff <= -10 then
moveValveUp(valvePosition, move_up, 20)
elseif diff > -10 and diff <= -8 then
moveValveUp(valvePosition, move_up, 15)
elseif diff > -8 and diff <= -6 then
moveValveUp(valvePosition, move_up, 10)
elseif diff > -6 and diff <= -5 then
moveValveUp(valvePosition, move_up, 5)
elseif diff > -5 and diff <= -3 then
moveValveUp(valvePosition, move_up, 3)
elseif diff > -3 and diff <= -2 then
moveValveUp(valvePosition, move_up, 2.5)
elseif diff > -2 and diff <= -1 then
moveValveUp(valvePosition, move_up, 2)
elseif diff > -1 and diff <= -0.5 then
moveValveUp(valvePosition, move_up, 1)
elseif diff > -0.5 and diff <= -0.1 then
moveValveUp(valvePosition, move_up, 0.5)
-- If the script trigger and the pump is on and the temperature adjustement is in auto mode
if devices.isTimer and tauto.state == 'Auto' and pompa.state == 'On' then
print('********** Checking temperature difference and performing valve adjustments ***********')
-- Call the function to perform valve adjustments
--After moving the valve from the maxDown position
if valveResetDone.value == 'true' then
valveResetDone.set('false')
devices = {
'Pompa_On/OFF_(rLe2)',
logging = {
marker = "Valve Reset Script: "
execute = function(dz, trigger)
local initialSetupDone = dz.variables('initialSetupDone')
if trigger.isDevice and (pompa.state == 'Off' or tauto.state == 'Manual') and valveResetDone.value == 'false' then
-- Move the valve down for 120 seconds
dz.devices('TadjustDOWN_(rLe4)').switchOn().forSec(125)
-- Set valvePosition to -60
-- Set initialSetupDone to 'false'
initialSetupDone.set('false')
valveResetDone.set('true')
dz.log('Resetting valve position and initial setup flag.', dz.LOG_INFO)
devices = {
'Mod Incalzire', -- Selector for Heating mode: 'Auto', 'Manual'
'EXTERIOR', -- Exterior temperature sensore
'Setare_temperatura_tur', --Using thermostat for manually setting the desired flow temperature.
'Curba De Incalzire' -- Selector for chosing the desired heating curve: 'Manual', 'Curbe1', 'Curba2', ...
customEvents = {
'Setare_temp_tur'
logging = {
marker = "** Adjust Flow Temperature Script: **"
execute = function(domoticz, devices, customEvents)
local heatingMode = domoticz.devices('Mod Incalzire').state
local exteriorTemp = domoticz.devices('EXTERIOR').temperature
local heatingCurve = domoticz.devices('Curba De Incalzire').state
local tSetat = domoticz.variables('t_tur_setat') -- User variable for keeping the desired flow temperature
local FLOW_MIN_TEMP_CALORIF = 30 -- minimum temperature value for radiators heating
local FLOW_MAX_TEMP_CALORIF = 75 -- maximum temperature value for radiators heating
local FLOW_MIN_TEMP_PARD = 25 -- minimum temperature value for floor heating
local FLOW_MAX_TEMP_PARD = 45 -- maximum temperature value for floor heating
-- Define heating curves based on your requirements
local heatingCurves = {
Curba1 = {
{temp = 15, pardosealaFlow = 10, calorifereFlow = 15},
{temp = 14, pardosealaFlow = 10.5, calorifereFlow = 15.5},
{temp = 13, pardosealaFlow = 11, calorifereFlow = 16},
{temp = 12, pardosealaFlow = 21.5, calorifereFlow = 46.5},
{temp = 11, pardosealaFlow = 22, calorifereFlow = 47},
{temp = 10, pardosealaFlow = 22.5, calorifereFlow = 47.5},
{temp = 9, pardosealaFlow = 23, calorifereFlow = 48},
{temp = 8, pardosealaFlow = 23.5, calorifereFlow = 48.5},
{temp = 7, pardosealaFlow = 24, calorifereFlow = 49},
{temp = 6, pardosealaFlow = 24.5, calorifereFlow = 49.5},
{temp = 5, pardosealaFlow = 25, calorifereFlow = 50},
{temp = 4, pardosealaFlow = 25.5, calorifereFlow = 50.5},
{temp = 3, pardosealaFlow = 26, calorifereFlow = 51},
{temp = 2, pardosealaFlow = 26.5, calorifereFlow = 51.5},
{temp = 1, pardosealaFlow = 27, calorifereFlow = 52},
{temp = 0, pardosealaFlow = 27.5, calorifereFlow = 52.5},
{temp = -1, pardosealaFlow = 28, calorifereFlow = 53},
{temp = -2, pardosealaFlow = 28.5, calorifereFlow = 53.5},
{temp = -3, pardosealaFlow = 29, calorifereFlow = 54},
{temp = -4, pardosealaFlow = 29.5, calorifereFlow = 54.5},
{temp = -5, pardosealaFlow = 30, calorifereFlow = 55},
{temp = -6, pardosealaFlow = 30.5, calorifereFlow = 55.5},
{temp = -7, pardosealaFlow = 31, calorifereFlow = 56},
{temp = -8, pardosealaFlow = 31.5, calorifereFlow = 56.5},
{temp = -9, pardosealaFlow = 32, calorifereFlow = 57},
{temp = -10, pardosealaFlow = 32.5, calorifereFlow = 57.5},
{temp = -11, pardosealaFlow = 33, calorifereFlow = 58},
{temp = -12, pardosealaFlow = 33.5, calorifereFlow = 58.5},
{temp = -13, pardosealaFlow = 34, calorifereFlow = 59},
{temp = -14, pardosealaFlow = 34.5, calorifereFlow = 59.5},
{temp = -15, pardosealaFlow = 35, calorifereFlow = 60},
{temp = -16, pardosealaFlow = 35.5, calorifereFlow = 60.5},
{temp = -17, pardosealaFlow = 36, calorifereFlow = 61},
{temp = -18, pardosealaFlow = 36.5, calorifereFlow = 61.5},
{temp = -19, pardosealaFlow = 37, calorifereFlow = 62},
{temp = -20, pardosealaFlow = 37.5, calorifereFlow = 62.5},
{temp = -21, pardosealaFlow = 38, calorifereFlow = 63},
{temp = -22, pardosealaFlow = 38.5, calorifereFlow = 63.5},
{temp = -23, pardosealaFlow = 39, calorifereFlow = 64},
{temp = -24, pardosealaFlow = 39.5, calorifereFlow = 64.5},
{temp = -25, pardosealaFlow = 40, calorifereFlow = 65},
Curba2 = {
{temp = 15, pardosealaFlow = 25, calorifereFlow = 55},
{temp = 14, pardosealaFlow = 25.5, calorifereFlow = 55.5},
{temp = 13, pardosealaFlow = 21, calorifereFlow = 56},
{temp = 12, pardosealaFlow = 21.5, calorifereFlow = 56.5},
{temp = 11, pardosealaFlow = 22, calorifereFlow = 57},
{temp = 10, pardosealaFlow = 22, calorifereFlow = 57.5},
{temp = 9, pardosealaFlow = 23, calorifereFlow = 58},
{temp = 8, pardosealaFlow = 24, calorifereFlow = 58.5},
{temp = 7, pardosealaFlow = 24, calorifereFlow = 59},
{temp = 6, pardosealaFlow = 24, calorifereFlow = 59.5},
{temp = 5, pardosealaFlow = 24, calorifereFlow = 60},
{temp = 4, pardosealaFlow = 24, calorifereFlow = 60.5},
{temp = 3, pardosealaFlow = 24, calorifereFlow = 61},
{temp = 2, pardosealaFlow = 24, calorifereFlow = 61.5},
{temp = 1, pardosealaFlow = 24, calorifereFlow = 62},
{temp = 0, pardosealaFlow = 24, calorifereFlow = 62.5},
{temp = -1, pardosealaFlow = 24, calorifereFlow = 63},
{temp = -2, pardosealaFlow = 24, calorifereFlow = 63.5},
{temp = -3, pardosealaFlow = 24, calorifereFlow = 64},
{temp = -4, pardosealaFlow = 24, calorifereFlow = 64.5},
{temp = -5, pardosealaFlow = 25, calorifereFlow = 65},
{temp = -6, pardosealaFlow = 26, calorifereFlow = 65.5},
{temp = -7, pardosealaFlow = 27, calorifereFlow = 66},
{temp = -8, pardosealaFlow = 28, calorifereFlow = 66.5},
{temp = -9, pardosealaFlow = 29, calorifereFlow = 67},
{temp = -10, pardosealaFlow = 30, calorifereFlow = 67.5},
{temp = -11, pardosealaFlow = 31, calorifereFlow = 68},
{temp = -12, pardosealaFlow = 32, calorifereFlow = 68.5},
{temp = -13, pardosealaFlow = 33, calorifereFlow = 69},
{temp = -14, pardosealaFlow = 34, calorifereFlow = 69.5},
{temp = -15, pardosealaFlow = 35, calorifereFlow = 70},
{temp = -16, pardosealaFlow = 36, calorifereFlow = 70.5},
{temp = -17, pardosealaFlow = 37, calorifereFlow = 71},
{temp = -18, pardosealaFlow = 38, calorifereFlow = 71.5},
{temp = -19, pardosealaFlow = 39, calorifereFlow = 72},
{temp = -20, pardosealaFlow = 40, calorifereFlow = 72.5},
{temp = -21, pardosealaFlow = 41, calorifereFlow = 73},
{temp = -22, pardosealaFlow = 42, calorifereFlow = 73.5},
{temp = -23, pardosealaFlow = 43, calorifereFlow = 74},
{temp = -24, pardosealaFlow = 44.5, calorifereFlow = 74.5},
{temp = -25, pardosealaFlow = 45, calorifereFlow = 75},
Curba3 = {
-- Add temperature-flow rate pairs for Curba3
Manual = {}
-- Leave custom temperature-flow rate pairs for Manual mode free
if customEvents['Setare_temp_tur'] then
local setpointTemp = customEvents['Setare_temp_tur'].setPoint
local minLimit, maxLimit
-- Set the minimum and maximum limits based on the heating mode
if heatingMode == 'Pardoseala' then
minLimit = FLOW_MIN_TEMP_PARD
maxLimit = FLOW_MAX_TEMP_PARD
elseif heatingMode == 'Calorifere' then
minLimit = FLOW_MIN_TEMP_CALORIF
maxLimit = FLOW_MAX_TEMP_CALORIF
-- Limit the setpoint temperature within the specified range
setpointTemp = math.min(maxLimit, math.max(minLimit, setpointTemp)) --require modification
-- Update the thermostat setpoint device
domoticz.devices('Setare_temperatura_tur').updateSetPoint(setpointTemp)
tSetat.set(setpointTemp)
if heatingCurve ~= 'Manual' and heatingCurves[heatingCurve] then
for i = 1, #heatingCurves[heatingCurve] do
if exteriorTemp >= heatingCurves[heatingCurve][i].temp then
setpointTemp = heatingCurves[heatingCurve][i].pardosealaFlow
setpointTemp = heatingCurves[heatingCurve][i].calorifereFlow
break
Szmalu
Thx!bitzy wrote: Monday 16 October 2023 19:58 The same script to keep a constant flow temperature, a little cleaner and easier to follow and modify:
bitzy
keep in mind that u may need to modify this part for your needs and the system u have:
how is set here for my system is to move down in bigger steps, to prevent a to higher temperature fluid entering the underfloor heating.
if diff >= 30 then
end-
bitzy
i also made a PID algorithm to keep a constant temperature for who want it.
this is still a work in progress and there are some global persistent variables used in the PID script that are declarred in a script called:
global_data (see Global persistent variables in wiki: https://www.domoticz.com/wiki/DzVents:_ ... _variables
to call the rounding function in whatever script u want call it with:
domoticz.helpers.customRoundFunction(numberToRound, decimals)
or
local globalData = require('global_data')
local customRound = globalData.helpers.customRoundFunction
numberToRound = customRound(numberToRound, decimals)
and please if someone can remove the junk posts in this topic so that only useful information remain
devices = { -- Triggers when the listed devices or variables change
-- 'Auto_TempAdjustment', -- Device 'Auto_TempAdjustment'
-- 'Mod Incalzire',
-- 'Tur',
-- Device 'Setare_temperatura_tur'
logging = {
level = domoticz.LOG_INFO, -- Sets the logging level to INFO
marker = "&&&**## PID FOR TEMPERATURE IS ON &&&**## : ", -- Marker for log entries
local tauto = dz.devices('Auto_TempAdjustment') -- Device 'Auto_TempAdjustment'
local set_t = dz.variables('t_tur_setat') -- Variable 't_tur_setat'
local actual_t = dz.devices('Tur') -- Device 'Tur'
local move_up = dz.devices('TadjustUP_(rLe3)') -- Device 'TadjustUP_(rLe3)'
local move_down = dz.devices('TadjustDOWN_(rLe4)') -- Device 'TadjustDOWN_(rLe4)'
local pompa = dz.devices('Pompa_On/OFF_(rLe2)') -- Device 'Pompa_On/OFF_(rLe2)'
local valvePosition = dz.variables('valvePosition') -- Variable 'valvePosition'
local control_output1 = dz.variables('control_output')
local maxValvePosition = 60
local minValvePosition = -60
-- local trend = dz.variables('trend')
local valvePositionData = dz.globalData.valvePositionData
local valveResetDoneData = dz.globalData.valveResetDoneData
local previous_error = dz.globalData.previous_error
local integral = dz.globalData.integral
local derivative = dz.globalData.derivative
if valvePosition.value + targetMovement <= maxValvePosition then
valvePositionData = valvePositionData + targetMovement
dz.log('********** Moving valve up by ' .. targetMovement .. ' seconds. ***********')
elseif valvePosition.value ~= maxValvePosition then
local remainingMovement = maxValvePosition - valvePosition.value
valvePositionData = valvePositionData + remainingMovement
dz.log('********** Moving valve up by ' .. remainingMovement .. ' seconds. ***********')
if valvePosition.value - targetMovement >= minValvePosition then
dz.log('********** Moving valve down by ' .. targetMovement .. ' seconds. ***********')
elseif valvePosition.value ~= minValvePosition then
local remainingMovement = minValvePosition - valvePosition.value
valvePositionData = minValvePosition
valvePosition.set(minValvePosition)
dz.log('********** Moving valve down by ' .. remainingMovement .. ' seconds. ***********')
dz.log('********** Moving valve down by ' .. poz_remainingMovement .. ' seconds. ***********')
-- PID Constants
local Kp = 1.5
local Ki = 0.05
local Kd = 0.9
local control_output = 0
-- Initialize PID variables
if (valvePosition.value < maxValvePosition and actual_t.temperature <= set_t.value) or (valvePosition.value == maxValvePosition and actual_t.temperature >= set_t.value) or (valvePosition.value > minValvePosition and actual_t.temperature >= set_t.value) or (valvePosition.value == minValvePosition and actual_t.temperature <= set_t.value) or (valvePosition.value == minValvePosition and actual_t.temperature <= set_t.value and valveResetDone == 'true') then
--local previous_error = 0
--dz.variables('z1_prev_error').set(0)
--local integral = 0
--dz.variables('z2_integral').set(0)
if not devices.isTimer then
integral = 0.1 -- Adjust as needed
--dz.variables('z2_integral').set(0.1)
-- Calculate error
local error = math.floor((set_t.value - actual_t.temperature) * 10 + 0.5) / 10
--dz.variables('z1_error').set(error)
-- Calculate delta time (dt) assuming you have a timer event
local dt = 2 --actual_t.temperature -- You might need to adjust this based on your timer event
-- Update the integral term
integral = integral + error * dt
--dz.variables('z2_integral').set(integral)
-- Anti-windup: Limit the integral terms
local max_integral = 60 -- Set the maximum allowable integral term (adjust as needed)
if integral > max_integral then
integral = max_integral
elseif integral < -max_integral then
integral = -max_integral
-- Calculate the derivative term
derivative = (error - previous_error) / dt
--dz.variables('z3_derivative').set(derivative)
-- Calculate the control output
control_output = Kp * error + Ki * integral + Kd * derivative
control_output = math.floor(control_output * 10 + 0.5) / 10
-- Update the previous error for the next iteration
previous_error = error
--dz.variables('z1_prev_error').set(previous_error)
control_output = 0
-- Adjust the valve position based on control_output
-- print('********** Checking temperature difference and performing valve adjustments ***********')
-- if trend.value ~=2 and trend.value ~=3 then
if control_output ~= nill then
if control_output < 0 then
moveValveDown(valvePosition, move_down, control_output)
control_output1.set(control_output)
elseif control_output > 0 then
moveValveUp(valvePosition, move_up, control_output)
valveResetDoneData = 'false'
valveResetDone.set(valveResetDoneData)
if valvePosition.value == maxValvePosition then
dz.log('Valva este la maxim de cursa')
elseif valvePosition.value == minValvePosition then
dz.log('Valva este la minim de cursa')
--end
#global_data
helpers = {
customRoundFunction = function(number, decimalNumber)
local function roundToDecimals(numString, decimals)
local integralPart, fractionalPart = string.match(numString, "([^%.]+)%.?(%d*)")
local firstDecimal = tonumber(fractionalPart:sub(1, 1)) or 0
-- Funcție pentru verificarea zecimalelor ulterioare
local function checkNextDigits(startIndex)
for i = startIndex, #fractionalPart do
local currentDigit = tonumber(fractionalPart:sub(i, i)) or 0
if currentDigit > 5 then
return true -- Rotunjim în sus
elseif currentDigit < 5 then
return false -- Rotunjim în jos
return true -- Dacă toate sunt 5, rotunjim în sus
-- Dacă nu se doresc zecimale
if decimals == 0 then
-- Decidem rotunjirea
if firstDecimal < 5 then
return tonumber(integralPart) -- Partea întreagă rămâne neschimbată
elseif firstDecimal > 5 then
return tonumber(integralPart) + 1 -- Rotunjim în sus
else -- Dacă firstDecimal == 5
if checkNextDigits(2) then
return tonumber(integralPart) -- Rămâne neschimbată
-- Dacă numărul are mai puține zecimale decât se dorește, returnează numărul original
if #fractionalPart <= decimals then
return tonumber(numString)
-- Zecimala la care se face rotunjirea
local targetDigit = tonumber(fractionalPart:sub(decimals + 1, decimals + 1)) or 0
-- Determinăm noua valoare a ultimei zecimale
local roundedDigit
if targetDigit < 5 then
roundedDigit = tonumber(fractionalPart:sub(decimals, decimals))
elseif targetDigit > 5 then
roundedDigit = (tonumber(fractionalPart:sub(decimals, decimals)) or 0) + 1
else -- Dacă targetDigit == 5
if checkNextDigits(decimals + 2) then
-- Construim numărul rotunjit
local roundedNumber = integralPart .. "." .. fractionalPart:sub(1, decimals - 1) .. roundedDigit
return tonumber(roundedNumber)
local numString = tostring(number)
return roundToDecimals(numString, decimalNumber)
data = {
valvePositionData = { initial = -60 },
valveResetDoneData = { initial = 'false' },
pompaCaloriferLastUse = { initial = 0 },
previous_error = { initial = 0 },
integral = { initial = 0 },
derivative = { initial = 0 },
protectie_pufferData = { initial = false },
or
bitzy
- Domoticz version: 2023.2
this is my variant of a script that will set the flow temperature depending on the exterior temperature and the inside desired temperature:
the 'global_data' script contain some global persistent variable that i use in the scripts i made including this one (useful for the future modification of my setup) and also a rounding function that round a number depending on the amount of decimals someone desire (i made this because i didn't know what the correct function is (if exist) in dzvents. the way the rounding is done is like this: if u want to round at 1 decimal, we look at the 2 decimal and if that is under 5, the 1-st decimal will remain unchanged. if the second decimal is >5 then the 1-st decimal is increased by 1. if the second decimal ==5 we look at the 3-rd decimal and if is <5, first decimal remain the same if 3-rd decimal>5 then 1-st decimal is increased by 1 and so on. we can do that for 0, 1, 2, 3, ... n decimals.
if someone know the correct function in dzvents that does this kind of rounding please poste it here !!
-- This script will set the flow temperature of a heating system based on the external temperature and the
-- internal temperature of the room.This is done with the help of the heating curves that are defined based
-- on the desire and the needs of the room u wish.
-- Also the script will set the desire flow temperature based on the type of the heating system u have: underfloor or
-- radiators. In one of this states, the script will automatically keep a minimum and maximum flow temperature depending
-- on the state of your settings (underfloor or radiators). Also a manual state can be set where u set the temperature
-- at any value u want.
-- Define a threshold for exterior temperature change to trigger the script
-- U can set here how many degrees the outside temperature need to change before the flow temperature will be changed to the next value from the coresponding heating curve
local tempChangeThreshold = 2 -- Adjust this value as needed
local decimalNumber = 1 -- this is the noumber of decimal for the temperature sensors
-- The heating curves will be set as follow: temp - is the outside temperature; pardosealaFlow - is the underfloor temperature
-- u want for the coresponding outside temperature; calorifereFlow - is the radiator temperature.
C1 = {
{temp = 18, pardosealaFlow = 20.5, calorifereFlow = 28.3},
{temp = 17, pardosealaFlow = 21, calorifereFlow = 28.8},
{temp = 16, pardosealaFlow = 21.5, calorifereFlow = 29.4},
{temp = 15, pardosealaFlow = 22, calorifereFlow = 29.9},
{temp = 14, pardosealaFlow = 22.5, calorifereFlow = 30.4},
{temp = 13, pardosealaFlow = 23, calorifereFlow = 30.9},
{temp = 12, pardosealaFlow = 23.5, calorifereFlow = 31.3},
{temp = 11, pardosealaFlow = 24, calorifereFlow = 31.9},
{temp = 10, pardosealaFlow = 24.5, calorifereFlow = 32.3},
{temp = 9, pardosealaFlow = 25, calorifereFlow = 32.8},
{temp = 8, pardosealaFlow = 25.5, calorifereFlow = 32.3},
{temp = 7, pardosealaFlow = 26, calorifereFlow = 33.7},
{temp = 6, pardosealaFlow = 26.5, calorifereFlow = 34.2},
{temp = 5, pardosealaFlow = 27, calorifereFlow = 34.7},
{temp = 4, pardosealaFlow = 27.5, calorifereFlow = 35.1},
{temp = 3, pardosealaFlow = 28, calorifereFlow = 35.6},
{temp = 2, pardosealaFlow = 28.5, calorifereFlow = 36},
{temp = 1, pardosealaFlow = 29, calorifereFlow = 36.5},
{temp = 0, pardosealaFlow = 29.5, calorifereFlow = 37},
{temp = -1, pardosealaFlow = 30, calorifereFlow = 37.4},
{temp = -2, pardosealaFlow = 31.5, calorifereFlow = 37.9},
{temp = -3, pardosealaFlow = 32, calorifereFlow = 38.3},
{temp = -4, pardosealaFlow = 32.5, calorifereFlow = 38.7},
{temp = -5, pardosealaFlow = 33, calorifereFlow = 39.2},
{temp = -6, pardosealaFlow = 33.5, calorifereFlow = 39.6},
{temp = -7, pardosealaFlow = 34, calorifereFlow = 40},
{temp = -8, pardosealaFlow = 34.5, calorifereFlow = 40.5},
{temp = -9, pardosealaFlow = 35, calorifereFlow = 41},
{temp = -10, pardosealaFlow = 35.5, calorifereFlow = 41.4},
{temp = -11, pardosealaFlow = 36, calorifereFlow = 41.8},
{temp = -12, pardosealaFlow = 36.5, calorifereFlow = 42.2},
{temp = -13, pardosealaFlow = 37, calorifereFlow = 42.7},
{temp = -14, pardosealaFlow = 37.5, calorifereFlow = 43.1},
{temp = -15, pardosealaFlow = 38, calorifereFlow = 43.5},
{temp = -16, pardosealaFlow = 38.5, calorifereFlow = 44.9},
{temp = -17, pardosealaFlow = 39, calorifereFlow = 44.4},
{temp = -18, pardosealaFlow = 39.5, calorifereFlow = 45.8},
{temp = -19, pardosealaFlow = 40, calorifereFlow = 45.2},
{temp = -20, pardosealaFlow = 40.5, calorifereFlow = 45.6},
{temp = -21, pardosealaFlow = 41, calorifereFlow = 46.1},
{temp = -22, pardosealaFlow = 41.5, calorifereFlow = 46.5},
{temp = -23, pardosealaFlow = 42, calorifereFlow = 46.9},
{temp = -24, pardosealaFlow = 42.5, calorifereFlow = 47.3},
{temp = -25, pardosealaFlow = 43, calorifereFlow = 47.7},
{temp = -26, pardosealaFlow = 43.5, calorifereFlow = 48.1},
{temp = -27, pardosealaFlow = 44, calorifereFlow = 48.6},
{temp = -28, pardosealaFlow = 44.5, calorifereFlow = 49},
{temp = -29, pardosealaFlow = 45, calorifereFlow = 49.4},
{temp = -30, pardosealaFlow = 45.5, calorifereFlow = 50.8},
C2 = {
{temp = 18, pardosealaFlow = 20.5, calorifereFlow = 32.3},
{temp = 17, pardosealaFlow = 21, calorifereFlow = 32.8},
{temp = 16, pardosealaFlow = 21.5, calorifereFlow = 33.4},
{temp = 15, pardosealaFlow = 22, calorifereFlow = 33.9},
{temp = 14, pardosealaFlow = 22.5, calorifereFlow = 34.4},
{temp = 13, pardosealaFlow = 23, calorifereFlow = 34.9},
{temp = 12, pardosealaFlow = 23.5, calorifereFlow = 35.3},
{temp = 11, pardosealaFlow = 24, calorifereFlow = 35.9},
{temp = 10, pardosealaFlow = 24.5, calorifereFlow = 36.3},
{temp = 9, pardosealaFlow = 25, calorifereFlow = 36.8},
{temp = 8, pardosealaFlow = 25.5, calorifereFlow = 37.3},
{temp = 7, pardosealaFlow = 26, calorifereFlow = 37.7},
{temp = 6, pardosealaFlow = 26.5, calorifereFlow = 38.2},
{temp = 5, pardosealaFlow = 27, calorifereFlow = 38.7},
{temp = 4, pardosealaFlow = 27.5, calorifereFlow = 39.1},
{temp = 3, pardosealaFlow = 28, calorifereFlow = 39.6},
{temp = 2, pardosealaFlow = 28.5, calorifereFlow = 40},
{temp = 1, pardosealaFlow = 29, calorifereFlow = 40.5},
{temp = 0, pardosealaFlow = 29.5, calorifereFlow = 41},
{temp = -1, pardosealaFlow = 30, calorifereFlow = 41.4},
{temp = -2, pardosealaFlow = 31.5, calorifereFlow = 41.9},
{temp = -3, pardosealaFlow = 32, calorifereFlow = 42.3},
{temp = -4, pardosealaFlow = 32.5, calorifereFlow = 42.7},
{temp = -5, pardosealaFlow = 33, calorifereFlow = 43.2},
{temp = -6, pardosealaFlow = 33.5, calorifereFlow = 43.6},
{temp = -7, pardosealaFlow = 34, calorifereFlow = 44},
{temp = -8, pardosealaFlow = 34.5, calorifereFlow = 44.5},
{temp = -9, pardosealaFlow = 35, calorifereFlow = 45},
{temp = -10, pardosealaFlow = 35.5, calorifereFlow = 45.4},
{temp = -11, pardosealaFlow = 36, calorifereFlow = 45.8},
{temp = -12, pardosealaFlow = 36.5, calorifereFlow = 46.2},
{temp = -13, pardosealaFlow = 37, calorifereFlow = 46.7},
{temp = -14, pardosealaFlow = 37.5, calorifereFlow = 47.1},
{temp = -15, pardosealaFlow = 38, calorifereFlow = 47.5},
{temp = -16, pardosealaFlow = 38.5, calorifereFlow = 48.9},
{temp = -17, pardosealaFlow = 39, calorifereFlow = 48.4},
{temp = -18, pardosealaFlow = 39.5, calorifereFlow = 48.8},
{temp = -19, pardosealaFlow = 40, calorifereFlow = 49.2},
{temp = -20, pardosealaFlow = 40.5, calorifereFlow = 49.6},
{temp = -21, pardosealaFlow = 41, calorifereFlow = 50.1},
{temp = -22, pardosealaFlow = 41.5, calorifereFlow = 50.5},
{temp = -23, pardosealaFlow = 42, calorifereFlow = 50.9},
{temp = -24, pardosealaFlow = 42.5, calorifereFlow = 51.3},
{temp = -25, pardosealaFlow = 43, calorifereFlow = 51.7},
{temp = -26, pardosealaFlow = 43.5, calorifereFlow = 52.1},
{temp = -27, pardosealaFlow = 44, calorifereFlow = 52.6},
{temp = -28, pardosealaFlow = 44.5, calorifereFlow = 53},
{temp = -29, pardosealaFlow = 45, calorifereFlow = 53.4},
{temp = -30, pardosealaFlow = 45.5, calorifereFlow = 53.8},
C3 = {
{temp = 18, pardosealaFlow = 20.5, calorifereFlow = 36.3},
{temp = 17, pardosealaFlow = 21, calorifereFlow = 36.8},
{temp = 16, pardosealaFlow = 21.5, calorifereFlow = 37.4},
{temp = 15, pardosealaFlow = 22, calorifereFlow = 37.9},
{temp = 14, pardosealaFlow = 22.5, calorifereFlow = 38.4},
{temp = 13, pardosealaFlow = 23, calorifereFlow = 38.9},
{temp = 12, pardosealaFlow = 23.5, calorifereFlow = 39.3},
{temp = 11, pardosealaFlow = 24, calorifereFlow = 39.9},
{temp = 10, pardosealaFlow = 24.5, calorifereFlow = 40.3},
{temp = 9, pardosealaFlow = 25, calorifereFlow = 40.8},
{temp = 8, pardosealaFlow = 25.5, calorifereFlow = 41.3},
{temp = 7, pardosealaFlow = 26, calorifereFlow = 41.7},
{temp = 6, pardosealaFlow = 26.5, calorifereFlow = 42.2},
{temp = 5, pardosealaFlow = 27, calorifereFlow = 42.7},
{temp = 4, pardosealaFlow = 27.5, calorifereFlow = 43.1},
{temp = 3, pardosealaFlow = 28, calorifereFlow = 43.6},
{temp = 2, pardosealaFlow = 28.5, calorifereFlow = 44},
{temp = 1, pardosealaFlow = 29, calorifereFlow = 44.5},
{temp = 0, pardosealaFlow = 29.5, calorifereFlow = 45},
{temp = -1, pardosealaFlow = 30, calorifereFlow = 45.4},
{temp = -2, pardosealaFlow = 31.5, calorifereFlow = 45.9},
{temp = -3, pardosealaFlow = 32, calorifereFlow = 46.3},
{temp = -4, pardosealaFlow = 32.5, calorifereFlow = 46.7},
{temp = -5, pardosealaFlow = 33, calorifereFlow = 47.2},
{temp = -6, pardosealaFlow = 33.5, calorifereFlow = 47.6},
{temp = -7, pardosealaFlow = 34, calorifereFlow = 48},
{temp = -8, pardosealaFlow = 34.5, calorifereFlow = 48.5},
{temp = -9, pardosealaFlow = 35, calorifereFlow = 49},
{temp = -10, pardosealaFlow = 35.5, calorifereFlow = 49.4},
{temp = -11, pardosealaFlow = 36, calorifereFlow = 49.8},
{temp = -12, pardosealaFlow = 36.5, calorifereFlow = 50.2},
{temp = -13, pardosealaFlow = 37, calorifereFlow = 50.7},
{temp = -14, pardosealaFlow = 37.5, calorifereFlow = 51.1},
{temp = -15, pardosealaFlow = 38, calorifereFlow = 51.5},
{temp = -16, pardosealaFlow = 38.5, calorifereFlow = 51.9},
{temp = -17, pardosealaFlow = 39, calorifereFlow = 52.4},
{temp = -18, pardosealaFlow = 39.5, calorifereFlow = 52.8},
{temp = -19, pardosealaFlow = 40, calorifereFlow = 53.2},
{temp = -20, pardosealaFlow = 40.5, calorifereFlow = 53.6},
{temp = -21, pardosealaFlow = 41, calorifereFlow = 54.1},
{temp = -22, pardosealaFlow = 41.5, calorifereFlow = 54.5},
{temp = -23, pardosealaFlow = 42, calorifereFlow = 54.9},
{temp = -24, pardosealaFlow = 42.5, calorifereFlow = 55.3},
{temp = -25, pardosealaFlow = 43, calorifereFlow = 55.7},
{temp = -26, pardosealaFlow = 43.5, calorifereFlow = 56.1},
{temp = -27, pardosealaFlow = 44, calorifereFlow = 56.6},
{temp = -28, pardosealaFlow = 44.5, calorifereFlow = 57},
{temp = -29, pardosealaFlow = 45, calorifereFlow = 57.4},
{temp = -30, pardosealaFlow = 45.5, calorifereFlow = 57.8},
C4 = {
-- Add temperature-flow rate pairs for Curba4
Manual = {
local FLOW_MIN_TEMP_CALORIF = 20 -- the minimum flow temperature for radiators
local FLOW_MAX_TEMP_CALORIF = 75 -- the maximum flow temperature for radiators
local FLOW_MIN_TEMP_PARD = 20 -- the minimum flow temperature for underfloor
local FLOW_MAX_TEMP_PARD = 45.5 -- the maximum flow temperature for underfloor
devices = {
'Mod Incalzire', -- selector switch (Heating Mode) with Pardoseala(Underfloor), Calorifere(Radiators), Manual modes - (Pardoseala if the renamed Off mode of the selector in my case)
-- to switch betwin Underfloor, Radiators or Manual mode
'Setare_temperatura_tur', -- thermostat like device (Set_flow_temp) to set the desired flow temperature when in Manual mode or to show the set temperature in automatic mode
'Curba De Incalzire', -- selector switch (Heating Curve) to pick between the desired defined heting curves (C1, C2, C3, ...) or to put it in Manual mode.
-- The Manual is the renamed Off mode of the selector and allow u to manually set a desired flow temperature with the help of the 'Set_flow_temp' device
-- but forcing the minimum and maximum of the flow temperature at the set values
'EXTERIOR', -- exterior temperature sensor
'Setare_temperatura_camera',-- thermostat device (Room_Temp_Set)that set the disired room temperature.
logging = {
-- level = domoticz.LOG_DEBUG,
marker = "&&##**^^ Adjust Flow Temperature Script ^^**##&& "
local settempTur = domoticz.devices('Setare_temperatura_tur')
local tSetat = domoticz.variables('t_tur_setat') -- user variable that keep the set flow temperature to be shared amongst different scripts
local lastExteriorTemp = domoticz.variables('lastExteriorTemp') -- user variable that help keepeng the previous outside temperature that script used
local tCamSet = domoticz.variables('t_cam_setat') -- user variable that keep the desired set room temperature to be shared amongst different scripts
local thermostat = domoticz.devices('Setare_temperatura_camera')
local tempRoom = domoticz.devices('Baie')
local outTempDifference = thermostat.setPoint - 20 -- this is to calculate the difference between the actual room temperature and the ideal room temperature for what heating curves are defined
local roomTempDifference = tCamSet.value - tempRoom.temperature -- in this case the ideal temperature is 20 degrees Celsius. If your room temperature is set at 20 degrees, the flow temperature will be picked
-- from the desired heating curve. if u set the temperature at 19, the flow temperature will be set as
-- the temperature from the set curve for 20 degrees - tempDifference (19-20=-1 so the flow temperature will be -1 degree from the normal 20)
local t= 'false' -- this variable is used to determine if the outside temperature was changed for the 'tempChangeThreshold' ammount
-- if the script is triggered by the exterior temperature sensore we check to see if the outside temperature is changed from the last reading when we set the flow temperature
-- to this: 'tempChangeThreshold' ammount. if is changed, we will proceed to set a new flow temperature. if not the script will not run
if devices.name == 'EXTERIOR' then
local exteriorTempRound = domoticz.helpers.customRoundFunction(exteriorTemp, decimalNumber)
local diffTemp = lastExteriorTemp.value - exteriorTempRound
--domoticz.log('1.5 Temp difference : ' ..lastExteriorTemp.value..' - '..exteriorTempRound..' =' .. diffTemp)
-- Check if the exterior temperature has changed beyond the threshold
if math.abs(diffTemp) > tempChangeThreshold then
t = 'true'
domoticz.log(' ')
domoticz.log('1.1 THE SCRIPT WAS TRIGGERED BY : ' .. devices.name .. ' because:')
domoticz.log('1.3 Last exterior temperatre : ' .. lastExteriorTemp.value)
domoticz.log('2.1 Exterior temperature changed more than '.. tempChangeThreshold)
domoticz.log('2.2 Last exterior temperatre will be set to : ' .. exteriorTempRound)
lastExteriorTemp.set(exteriorTempRound)
t='false'
--domoticz.log('3.1 Exterior temperature did not changed more than '.. tempChangeThreshold)
--domoticz.log('3.2 Last exterior temperatre will remane : ' .. lastExteriorTemp.value)
-- we check to see if the script was triggered by the exterior temp sensor and if the outside temperature changed the 'tempChangeThreshold' ammount or
-- by the any other device from the trigger part of the script
if (devices.name == 'EXTERIOR' and t=='true') or devices.name == 'Mod Incalzire' or devices.name == 'Setare_temperatura_tur' or devices.name == 'Curba De Incalzire' or devices.name == 'Setare_temperatura_camera' then
domoticz.log(' ')
domoticz.log('1.1 THE SCRIPT WAS TRIGGERED BY : ' .. devices.name)
if heatingMode ~= 'Manual' then -- check to see if the Heating Mode is in the automatic (C1 ... Cn) mode so we can pick the flow temperature from the wanted heating curve
local targetTemp = FLOW_MIN_TEMP_PARD
targetTemp = heatingCurves[heatingCurve][i].pardosealaFlow
domoticz.log('(5.1.P) targetTemp for the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown') ..' should be set to : ' .. targetTemp)
break
targetTemp = heatingCurves[heatingCurve][i].calorifereFlow
domoticz.log('(5.2.C) targetTemp for the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown') ..' should be set to : ' .. targetTemp)
break
-- Handle other heating modes if necessary
domoticz.log('(5.3) Invalid heating mode: ' .. heatingMode)
return
-- if room temperature is ~= to 20, we adjust the flow temperature from the heating curve accordingly
if outTempDifference ~= 0 then
targetTemp = targetTemp + outTempDifference
local minLimit = FLOW_MIN_TEMP_PARD
local maxLimit = FLOW_MAX_TEMP_PARD
-- set the limits of the flow temperature depending on the Heating Mode chosen (Underfloor or Radiators)
-- Ensure that targetTemp is within the specified range
if targetTemp < minLimit then
targetTemp = minLimit
domoticz.log('(6.1) targetTemp is less than min for the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown')..'. Will be automatically set to minim : ' .. targetTemp)
elseif targetTemp > maxLimit then
targetTemp = maxLimit
domoticz.log('(6.2) targetTemp is over the maxim for the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown')..'. Will be automatically set to maxim : ' .. targetTemp)
settempTur.updateSetPoint(targetTemp).silent() -- Update the selecting flow temperature thermostat setpoint automatically
tSetat.set(targetTemp) -- updating the user variable with the new value
domoticz.log('(6.3) targetTemp fo the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown') ..' is set to : ' .. tostring(targetTemp))
elseif heatingCurve == 'Manual' then -- if the Heating Curve is set to Manual we can manually set the flow temperature, but not outside the min and max alowed by the Heating Mode (Underfloor or Radiators)
domoticz.log('(7.1) S-a intrat in logica devices.trigger and heatingCurve == Manual')
local setpointTemp = settempTur.setPoint
domoticz.log('(7.2) targetTemp for the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown') ..' should be set to : ' .. setpointTemp)
domoticz.log('(1.2) Invalid heating mode: ' .. heatingMode)
return
if setpointTemp < minLimit then
setpointTemp = minLimit
domoticz.log('(7.3) targetTemp is less than min for the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown')..'. Will be automatically set to minim : ' .. setpointTemp)
elseif setpointTemp > maxLimit then
setpointTemp = maxLimit
domoticz.log('(7.4) targetTemp is over the maxim for the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown')..'. Will be automatically set to maxim : ' .. setpointTemp)
-- Update the thermostat setpoint device if the manually set flow temperature is outside the min or max
settempTur.updateSetPoint(setpointTemp).silent()
domoticz.log('(7.5) targetTemp fo the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown') ..' is set to : ' .. setpointTemp)
domoticz.log(" (3) Invalid heating curve selected.")
return
else -- if Heating Mode is in Manual we can set whatever flow temperature we want, not taking into account the min and max value for the flow temperatures
tSetat.set(settempTur.setPoint)
domoticz.log('(7.6) targetTemp fo the curve ' ..(heatingCurves[heatingCurve] and heatingCurve or 'Unknown') ..' is set to : ' .. settempTur.setPoint)
--domoticz.log('Flow temperature did not changed')
bitzy
i've repaired the broken rounding function in global_data. now it works like i intended (i think)