Continuously changing setpoint
Alain
Domoticz version: 2022.1
Post by Alain »
I finally got Modbus working in Domoticz to communicate with my two heat pumps. I modified the script (which only allowed writing an on or off status) to write the setpoint to the heat pumps from a Domoticz thermostat setpoint.
As the heat pump setpoint needs to change according to demand, I want to continuously update the setpoint according to a boiler water setpoint shown to me by my Plugwise Anna thermostat. This thermostat creates a device in Domoticz which shows the current boiler setpoint. I want to relay that to the heat pumps so that they are producing the same water temperature. I can't work out a script to do this.
Does anyone have any idea's?
Hue | Zigbee2Mqtt | MQTT | P1 | Xiaomi | RFXCom | Modbus | TP-Link | Node-Red | Grafana |
psubiaco
Re: Continuously changing setpoint
Post by psubiaco »
Hi Alain,
I'm also interested to command my heat pump by Modbus: what are you using to send commands by RS485/Modbus?
In Domoticz you have a virtual device type "Thermostat Setpoint" that you can use to manual set the temperature, or to change it by a script.
To create the device, Setup -> Hardware, and if you haven't, create a new hardware type "Dummy", then you'll see the button Create a virtual sensor -> Thermostat Setpoint
Maybe you have to set the fluid temperature automatically, according to
1. external minimum and maximum temperature
2. difference from room setpoint and real temperature
3. availability of power from solar photovoltaic, if available, or other renewable energy
I'm using a script that compute the fluid temperature according to the 3 points above, but actually regulate the heat pump using 3 inputs:
1. on/off
2. radiant/coil temperature
3. 50% power, 100% power
It will be easy to modify the script to use ModBus, for this reason I'm interested to know what script/program/plugin you're using to communicate with the heat pump.
My lua scripts are available at https://github.com/CreasolTech/domoticz_lua_scripts
Thanks. Paolo
Paolo
Alain
Post by Alain »
Hi Paolo,
I installed the repository from S. Ebeltjes (Domoticx) on https://github.com/DomoticX/domoticz-modbus
I changed the script in the ModbusWrite plugin.py to write the value from a Thermostat which is created as a device by the modified plugin. I did, however, only change the code for RTU, not for TCP (as Im only using RTU). It would be easy to copy paste it to the other sections. The code is here:
# Modbus RTU / ASCII / TCP/IP - Universal READ Plugin for Domoticz
# Tested on domoticz 2020.2 (stable) with Python v3.7.3 and pymodbus v2.3.0
# Author: Sebastiaan Ebeltjes / DomoticX.nl
# RTU Serial HW: USB RS485-Serial Stick, like https://webshop.domoticx.nl/index.php?route=product/search&search=RS485%20RTU%20USB
# Dependancies:
# - pymodbus AND pymodbusTCP:
#   - Install for python3 with: sudo pip3 install -U pymodbus pymodbusTCP
<plugin key="ModbusWRITE" name="Modbus RTU / ASCII / TCP/IP - WRITE v2021.2" author="S. Ebeltjes / DomoticX.nl" version="2021.2" externallink="http://domoticx.nl" wikilink="https://github.com/DomoticX/domoticz-modbus">
    <description>
        <h3>Modbus RTU / ASCII / TCP/IP - WRITE</h3>
        With this plugin you can write to RS485 Modbus devices with methods RTU/ASCII/TCP<br/>
        <br/>
        <h4>RTU</h4>
        The serial binary communication protocol. It is the communication standard that<br/>
        became widely used and all series of PLC's and other device producers support it.<br/>
        It goes about the network protocol of the 1Master x nSlave type. The Slave devices can be 254 at the most.<br/>
        <h4>ASCII</h4>
        This protocol is similar to Modbus RTU, but the binary content is transformed to common ASCII characters.<br/>
        It is not used as frequently as Modbus RTU.<br/>
        <h4>RTU over TCP</h4>
        Means a MODBUS RTU packet wrapped in a TCP packet. The message bytes are modified to add the 6 byte MBAP header and remove the two byte CRC.
        <h4>TCP/IP</h4>
        It is a network protocol - classic Ethernet TCP/IP with the 10/100 Mbit/s speed rate, a standard net HW Ethernet card is sufficient.<br/>
        The communication principle (1Master x nSlave) is the same as for Modbus RTU. used port is most likely: 502<br/>
        <br/>
        <h3>Set-up and Configuration:</h3>
        See wiki link above.<br/>
    </description>
    <params>
        <param field="Mode1" label="Communication Mode" width="160px" required="true">
            <options>
                <option label="RTU" value="rtu:rtu" default="true"/>
                <option label="RTU (+DEBUG)" value="rtu:debug"/>
                <option label="RTU ASCII" value="ascii:ascii"/>
                <option label="RTU ASCII (+DEBUG)" value="ascii:debug"/>
                <option label="RTU over TCP" value="rtutcp:rtutcp"/>
                <option label="RTU over TCP (+DEBUG)" value="rtutcp:debug"/>
                <option label="TCP/IP" value="tcpip:tcpip"/>
                <option label="TCP/IP (+DEBUG)" value="tcpip:debug"/>
            </options>
        </param>
        <param field="SerialPort" label="RTU - Serial Port" width="120px"/>
        <param field="Mode3" label="RTU - Port settings" width="260px">
            <options>
                <option label="StopBits 1 / ByteSize 7 / Parity: None" value="S1B7PN"/>
                <option label="StopBits 1 / ByteSize 7 / Parity: Even" value="S1B7PE"/>
                <option label="StopBits 1 / ByteSize 7 / Parity: Odd" value="S1B7PO"/>
                <option label="StopBits 1 / ByteSize 8 / Parity: None" value="S1B8PN" default="true"/>
                <option label="StopBits 1 / ByteSize 8 / Parity: Even" value="S1B8PE"/>
                <option label="StopBits 1 / ByteSize 8 / Parity: Odd" value="S1B8PO"/>
                <option label="StopBits 2 / ByteSize 7 / Parity: None" value="S2B7PN"/>
                <option label="StopBits 2 / ByteSize 7 / Parity: Even" value="S2B7PE"/>
                <option label="StopBits 2 / ByteSize 7 / Parity: Odd" value="S2B7PO"/>
                <option label="StopBits 2 / ByteSize 8 / Parity: None" value="S2B8PN"/>
                <option label="StopBits 2 / ByteSize 8 / Parity: Even" value="S2B8PE"/>
                <option label="StopBits 2 / ByteSize 8 / Parity: Odd" value="S2B8PO"/>
            </options>
        </param>
        <param field="Mode2" label="RTU - Baudrate" width="70px">
            <options>
                <option label="1200" value="1200"/>
                <option label="2400" value="2400"/>
                <option label="4800" value="4800"/>
                <option label="9600" value="9600" default="true"/>
                <option label="14400" value="14400"/>
                <option label="19200" value="19200"/>
                <option label="38400" value="38400"/>
                <option label="57600" value="57600"/>
                <option label="115200" value="115200"/>
            </options>
        </param>
        <param field="Address" label="TCP/IP - IP:Port" width="140px" default="192.168.2.1:502"/>
        <param field="Password" label="Device ID" width="50px" default="1" required="true"/>
        <param field="Username" label="Modbus Function" width="280px" required="true">
             <options>
                <option label="Write Single Coil (Function 5)" value="5"/>
                <option label="Write Single Holding Register (Function 6)" value="6" default="true"/>
                <option label="Write Multiple Coils (Function 15)" value="15"/>
                <option label="Write Registers (Function 16)" value="16"/>
            </options>
        </param>
        <param field="Port" label="Register number" width="50px" default="1" required="true"/>
     </params>
</plugin>
import Domoticz
import sys
import pymodbus
import requests
import json
from pymodbus.client.sync import ModbusSerialClient # RTU
from pymodbus.client.sync import ModbusTcpClient    # RTU over TCP
from pymodbus.transaction import ModbusRtuFramer    # RTU over TCP
from pyModbusTCP.client import ModbusClient         # TCP/IP
from pymodbus.constants import Endian
from pymodbus.payload import BinaryPayloadDecoder
result=""
class BasePlugin:
    enabled = False
    def __init__(self):
        return
    def onStart(self):
        Domoticz.Log("onStart called")
        try:
          Domoticz.Log("Modbus RTU/ASCII/TCP - Universal WRITE loaded!, using python v" + sys.version[:6] + " and pymodbus v" + pymodbus.__version__)
        except:
          Domoticz.Log("Modbus RTU/ASCII/TCP - Universal WRITE loaded!")
        # Dependancies notification
        try:
          if (float(Parameters["DomoticzVersion"][:6]) < float("2020.2")): Domoticz.Error("WARNING: Domoticz version is outdated/not supported, please update!")
          if (float(sys.version[:1]) < 3): Domoticz.Error("WARNING: Python3 should be used!")
          if (float(pymodbus.__version__[:3]) < float("2.3")): Domoticz.Error("WARNING: Pymodbus version is outdated, please update!")
        except:
          Domoticz.Error("WARNING: Dependancies could not be checked!")
        # READ-IN OPTIONS AND SETTINGS
        # Convert "option names" to variables for easy reading and debugging.
        # Note: Parameters["Port"] cannot accept other value then int! (e.g. 192.168.0.0 will result in 192)
        Domoticz_Setting_Communication_MODDEB = Parameters["Mode1"].split(":") # Split MODE and DEBUG setting MODE:DEBUG
        self.Domoticz_Setting_Communication_Mode = Domoticz_Setting_Communication_MODDEB[0]
        self.Domoticz_Setting_Serial_Port = Parameters["SerialPort"]
        self.Domoticz_Setting_Baudrate = Parameters["Mode2"]
        self.Domoticz_Setting_Port_Mode = Parameters["Mode3"]
        self.Domoticz_Setting_Modbus_Function = Parameters["Username"]
        self.Domoticz_Setting_Register_Number = Parameters["Port"]
#        self.Domoticz_Setting_Payload_ON = Parameters["Mode4"]
#        self.Domoticz_Setting_Payload_OFF = Parameters["Mode5"]
        self.Domoticz_Setting_Device_ID = Parameters["Password"]
        self.Domoticz_Setting_TCP_IPPORT = Parameters["Address"].split(":") # Split address and port setting TCP:IP
        self.Domoticz_Setting_TCP_IP = 0 # Default
        if len(self.Domoticz_Setting_TCP_IPPORT) > 0: self.Domoticz_Setting_TCP_IP = self.Domoticz_Setting_TCP_IPPORT[0]
        self.Domoticz_Setting_TCP_PORT = 0 # Default
        if len(self.Domoticz_Setting_TCP_IPPORT) > 1: self.Domoticz_Setting_TCP_PORT = self.Domoticz_Setting_TCP_IPPORT[1]
        # Set debug yes/no
        if (Domoticz_Setting_Communication_MODDEB[1] == "debug"):
          Domoticz.Debugging(1) # Enable debugging
          DumpConfigToLog()
          Domoticz.Debug("***** NOTIFICATION: Debug enabled!")
        else:
          Domoticz.Debugging(0) # Disable debugging
        # RTU - Serial port settings
        if (self.Domoticz_Setting_Port_Mode == "S1B7PN"): self.StopBits, self.ByteSize, self.Parity = 1, 7, "N"
        if (self.Domoticz_Setting_Port_Mode == "S1B7PE"): self.StopBits, self.ByteSize, self.Parity = 1, 7, "E"
        if (self.Domoticz_Setting_Port_Mode == "S1B7PO"): self.StopBits, self.ByteSize, self.Parity = 1, 7, "O"
        if (self.Domoticz_Setting_Port_Mode == "S1B8PN"): self.StopBits, self.ByteSize, self.Parity = 1, 8, "N"
        if (self.Domoticz_Setting_Port_Mode == "S1B8PE"): self.StopBits, self.ByteSize, self.Parity = 1, 8, "E"
        if (self.Domoticz_Setting_Port_Mode == "S1B8PO"): self.StopBits, self.ByteSize, self.Parity = 1, 8, "O"
        if (self.Domoticz_Setting_Port_Mode == "S2B7PN"): self.StopBits, self.ByteSize, self.Parity = 2, 7, "N"
        if (self.Domoticz_Setting_Port_Mode == "S2B7PE"): self.StopBits, self.ByteSize, self.Parity = 2, 7, "E"
        if (self.Domoticz_Setting_Port_Mode == "S2B7PO"): self.StopBits, self.ByteSize, self.Parity = 2, 7, "O"
        if (self.Domoticz_Setting_Port_Mode == "S2B8PN"): self.StopBits, self.ByteSize, self.Parity = 2, 8, "N"
        if (self.Domoticz_Setting_Port_Mode == "S2B8PE"): self.StopBits, self.ByteSize, self.Parity = 2, 8, "E"
        if (self.Domoticz_Setting_Port_Mode == "S2B8PO"): self.StopBits, self.ByteSize, self.Parity = 2, 8, "O"
        if (len(Devices) == 0): Domoticz.Device(Name="Thermostat", Unit=1, Type=242, Subtype=1, Used=1).Create() # Used=1 to add a switch immediatly!
    def onStop(self):
        Domoticz.Log("onStop called")
    def onConnect(self, Connection, Status, Description):
        Domoticz.Log("onConnect called")
        return
    def onMessage(self, Connection, Data, Status, Extra):
        Domoticz.Log("onMessage called")
    def onCommand(self, Unit, Command, Level, Hue):
        Domoticz.Log("onCommand called for Unit " + str(Unit) + ": Parameter '" + str(Command) + "', Level: " + str(Level))
        # ON/OFF payload value
        payload = str(Level) # Set payload from Thermostat
        if Level > 58:
            Level = 58
        elif Level < 25:
            Level = 25
        percentage = Level*10
#        device.apply()
        Devices[1].Update(nValue=0, sValue=str(Level))
 #       response = requests.get("http://192.168.0.136:8080/json.htm?type=command&param=getuservariable&idx="+str(Parameters["Mode4"]))
 #       todos = json.loads(response.text)
 #       VariableValue = todos['result'][0]['Value']
 #       NewSetpoint = int(VariableValue)*10
 #       Domoticz.Log("User Variable: "+VariableValue)
        # Set payload if a button has been pressed
 #       if (str(Command) == "On"): payload = self.Domoticz_Setting_Payload_ON
 #       if (str(Command) == "Off"): payload = self.Domoticz_Setting_Payload_OFF
        # SET HARDWARE - pymodbus: RTU / ASCII
        if (self.Domoticz_Setting_Communication_Mode == "rtu" or self.Domoticz_Setting_Communication_Mode == "ascii"):
          Domoticz.Debug("MODBUS DEBUG - INTERFACE: Port="+self.Domoticz_Setting_Serial_Port+", BaudRate="+self.Domoticz_Setting_Baudrate+", StopBits="+str(self.StopBits)+", ByteSize="+str(self.ByteSize)+" Parity="+self.Parity)
          Domoticz.Debug("MODBUS DEBUG - SETTINGS: Method="+self.Domoticz_Setting_Communication_Mode+", Device ID="+self.Domoticz_Setting_Device_ID+", Register="+self.Domoticz_Setting_Register_Number+", Function="+self.Domoticz_Setting_Modbus_Function+", Payload="+payload)
          try:
            client = ModbusSerialClient(method=self.Domoticz_Setting_Communication_Mode, port=self.Domoticz_Setting_Serial_Port, stopbits=self.StopBits, bytesize=self.ByteSize, parity=self.Parity, baudrate=int(self.Domoticz_Setting_Baudrate), timeout=2, retries=2)
          except:
            Domoticz.Error("Error opening Serial interface on "+self.Domoticz_Setting_Serial_Port)
            Devices[1].Update(1, "0") # Set value to 0 (error)
        # SET HARDWARE - pymodbus: RTU over TCP
        if (self.Domoticz_Setting_Communication_Mode == "rtutcp"):
          Domoticz.Debug("MODBUS DEBUG - INTERFACE: IP="+self.Domoticz_Setting_TCP_IP+", Port="+self.Domoticz_Setting_TCP_PORT)
          try:
            client = ModbusTcpClient(host=self.Domoticz_Setting_TCP_IP, port=int(self.Domoticz_Setting_TCP_PORT), framer=ModbusRtuFramer, auto_open=True, auto_close=True, timeout=2)
          except:
            Domoticz.Error("Error opening RTU over TCP interface on address: "+self.Domoticz_Setting_TCP_IPPORT)
        # SET HARDWARE - pymodbusTCP: TCP/IP
        if (self.Domoticz_Setting_Communication_Mode == "tcpip"):
          Domoticz.Debug("MODBUS DEBUG - SETTINGS: Method="+self.Domoticz_Setting_Communication_Mode+", Device ID="+self.Domoticz_Setting_Device_ID+", Register="+self.Domoticz_Setting_Register_Number+", Function"+self.Domoticz_Setting_Modbus_Function+", Payload="+payload)
          try:
            client = ModbusClient(host=self.Domoticz_Setting_TCP_IP, port=int(self.Domoticz_Setting_TCP_PORT), unit_id=int(self.Domoticz_Setting_Device_ID), auto_open=True, auto_close=True, timeout=2)
          except:
            Domoticz.Error("Error opening TCP/IP interface on address: "+self.Domoticz_Setting_TCP_IPPORT)
        # WRITE PAYLOAD - pymodbus: RTU / ASCII / RTU over TCP
        if (self.Domoticz_Setting_Communication_Mode == "rtu" or self.Domoticz_Setting_Communication_Mode == "ascii" or self.Domoticz_Setting_Communication_Mode == "rtutcp"):
          try:
            # Function to execute
            if (self.Domoticz_Setting_Modbus_Function == "5"): result = client.write_coil(int(self.Domoticz_Setting_Register_Number), int(percentage), unit=int(self.Domoticz_Setting_Device_ID))
            if (self.Domoticz_Setting_Modbus_Function == "6"): result = client.write_register(int(self.Domoticz_Setting_Register_Number), int(percentage), unit=int(self.Domoticz_Setting_Device_ID))
            if (self.Domoticz_Setting_Modbus_Function == "15"): result = client.write_coils(int(self.Domoticz_Setting_Register_Number), int(percentage), unit=int(self.Domoticz_Setting_Device_ID))
            if (self.Domoticz_Setting_Modbus_Function == "16"): result = client.write_registers(int(self.Domoticz_Setting_Register_Number), int(percentage), unit=int(self.Domoticz_Setting_Device_ID))
            client.close()
            Domoticz.Debug("MODBUS DEBUG - RESULT: " + str(result))
            if (str(Command) == "On"): Devices[1].Update(1, "1") # Update device to ON
            if (str(Command) == "Off"): Devices[1].Update(0, "0") # Update device to OFF
          except:
            Domoticz.Error("Modbus error communicating! (RTU/ASCII/RTU over TCP), check your settings!")
        # SET PAYLOAD - pymodbusTCP: TCP/IP
          try:
            if (self.Domoticz_Setting_Modbus_Function == "5"): result = client.write_single_coil(int(self.Domoticz_Setting_Register_Number), int(payload))
            if (self.Domoticz_Setting_Modbus_Function == "6"): result = client.write_single_register(int(self.Domoticz_Setting_Register_Number), int(payload))
            if (self.Domoticz_Setting_Modbus_Function == "15"): result = client.write_multiple_coils(int(self.Domoticz_Setting_Register_Number), [payload])     # TODO split up multiple bytes to proper array.
            if (self.Domoticz_Setting_Modbus_Function == "16"): result = client.write_multiple_registers(int(self.Domoticz_Setting_Register_Number), [payload]) # TODO split up multiple bytes to proper array.
            client.close()
          except:
            Domoticz.Error("Modbus error communicating! (TCP/IP), check your settings!")
    def onNotification(self, Name, Subject, Text, Status, Priority, Sound, ImageFile):
        Domoticz.Log("Notification: " + Name + "," + Subject + "," + Text + "," + Status + "," + str(Priority) + "," + Sound + "," + ImageFile)
    def onDisconnect(self, Connection):
        Domoticz.Log("onDisconnect called")
    def onHeartbeat(self):
        # Domoticz.Log("onHeartbeat called")
        return
    def UpdateDevice(Unit, nValue, sValue):
        # Make sure that the Domoticz device still exists (they can be deleted) before updating it
        if (Unit in Devices):
          if (Devices[Unit].nValue != nValue) or (Devices[Unit].sValue != sValue):
            Devices[Unit].Update(nValue, str(sValue))
            Domoticz.Log("Update "+str(nValue)+":'"+str(sValue)+"' ("+Devices[Unit].Name+")")
        return
global _plugin
_plugin = BasePlugin()
def onStart():
    global _plugin
    _plugin.onStart()
def onStop():
    global _plugin
    _plugin.onStop()
def onConnect(Connection, Status, Description):
    global _plugin
    _plugin.onConnect(Connection, Status, Description)
def onMessage(Connection, Data, Status, Extra):
    global _plugin
    _plugin.onMessage(Connection, Data, Status, Extra)
def onCommand(Unit, Command, Level, Hue):
    global _plugin
    _plugin.onCommand(Unit, Command, Level, Hue)
def onNotification(Name, Subject, Text, Status, Priority, Sound, ImageFile):
    global _plugin
    _plugin.onNotification(Name, Subject, Text, Status, Priority, Sound, ImageFile)
def onDisconnect(Connection):
    global _plugin
    _plugin.onDisconnect(Connection)
def onHeartbeat():
    global _plugin
    _plugin.onHeartbeat()
    # Generic helper functions
def DumpConfigToLog():
    for x in Parameters:
        if Parameters[x] != "":
            Domoticz.Debug( "'" + x + "':'" + str(Parameters[x]) + "'")
    for x in Devices:
        Domoticz.Debug("Device:           " + str(x) + " - " + str(Devices[x]))
        Domoticz.Debug("Device ID:       '" + str(Devices[x].ID) + "'")
        Domoticz.Debug("Device Name:     '" + Devices[x].Name + "'")
        Domoticz.Debug("Device nValue:    " + str(Devices[x].nValue))
        Domoticz.Debug("Device sValue:   '" + Devices[x].sValue + "'")
        Domoticz.Debug("Device LastLevel: " + str(Devices[x].LastLevel))
    return
I will have a look at your script and see if I can use it. That would be great.
psubiaco
Post by psubiaco »
Thanks for the info.
That's a nice feature!
Have a nice day.
Paolo
Paolo
Cheryl83
Post by Cheryl83 »
I am just curious to know how would one design a PID controller or any other form of controller for a system which has a reference signal that varies with time. The controller I have known and have designed (for many applications) works on the basis of fixed reference value, but now I want to know the design approach for a controller with a system that has time changing reference value ?