Error executing script command returned: 256 Topic is solved
JanvdW
Post by JanvdW »
A Domoticz Blockly starts a python script to set the Evohome temperature of rooms.
This starts the following script:
#!/usr/bin/env python
import evoconfig
import sys
import requests
from evohomeclient2 import EvohomeClient
from datetime import datetime
import datetime
import time
# Zet de systeem status op 'Normal' als hij op 'Away' is ingesteld
client = EvohomeClient(evoconfig.usr, evoconfig.pw)
status=client.locations[0].status()
tcs=status['gateways'][0]['temperatureControlSystems'][0]
zones=tcs['zones']
# Wait to avoid that previous script is still running
time.sleep( 10 )
# Set system in the normal mode if that is not the case
currentmode = tcs['systemModeStatus']['mode']
if currentmode == "Away":
   client.set_status_normal()
# Wijzigingen doorvoeren tussen 06:00 en 21:30 uur
dt = datetime.datetime.now()
start_time = "06:00"
end_time = "21:30"
if start_time < dt.strftime("%H:%M") < end_time:
   # Aanpassen radiator temperatuur
   kamer=sys.argv[1]
   if kamer <> "aanwezig":
      temp=sys.argv[2]
      zone = client.locations[0]._gateways[0]._control_systems[0].zones[kamer]
      zone.set_temperature(temp)
This worked excellent for a long time, but suddenly Domoticz logs an error message when the scrips is called:
Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
I am not aware of relevant changes to my system that triggered this. To solve the issue I have tried a lot of things that are suggested in similar issues:
  • I checked that the absolute path to the script is defined in Domoticz
  • I checked rights and ownership: -rwxrwxrwx 1 pi pi 1142 Feb 3 10:36 radiator_temp.py
  • I tested different suggestions for the first line of the pyhton script
#!/usr/bin/env python -> original one, which returned 256
#!/bin/bash -> returned 512
#!/usr/bin/python -> returned 256
#!/bin/sh -> returned 512
  • edited script with vi
  • Running the script (in this case starting with #!/bin/sh) in putty works fine: python radiator_temp.py Voorkamer 19
What else can I change to solve this issue?
erem
Domoticz version: 2021.1
Re: Error executing script command returned: 256
Post by erem »
#!/usr/bin/env python is the correct shebang.
or use #!/usr/bin/python3
try adding exit() at the end of your script.
Regards,
Rob
FireWizard
Post by FireWizard »
Hi, @JanvdW
Hello Jan, this is an ever returning topic.
Have a look at this discussion: viewtopic.php?f=6&t=30657&p=231907#p231907
Maybe the solution in @DewGew 's post will help you.
JanvdW
Post by JanvdW »
erem wrote: Wednesday 03 February 2021 12:23 #!/usr/bin/env python is the correct shebang.
I thought so, and was using that shebang. I have added exit() at the end of the script, but the error is still there.
The strange thing is that the script is executed properly, but gives an error every time.
JanvdW
Post by JanvdW »
FireWizard wrote: Wednesday 03 February 2021 12:36 Hi, @JanvdW
Seems a good suggestion in case the script is started with the wrong account. I changes the script (this is how it's should be done, right?):
import evoconfig
import sys
import requests
import datetime
import time
# make sure we're running as the user
RUN_AS="pi" # Enter username here
if [ "$USER" != "$RUN_AS" ]
then
    echo ""
    echo " This script must run as $RUN_AS, trying to change user..."
    exec sudo -u $RUN_AS $0 $1
fi
zones=tcs['zones']
time.sleep( 10 )
end_time = "21:30"
   kamer=sys.argv[1]
      temp=sys.argv[2]
exit()
Unfortunately the error is still in the Domoticz log
FireWizard
@JanvdW
I don't know.
@DewGew ´s solution has been made in a Bash shell script and not a Python script.
From the shell script, you can call the Python script.
@DewGew said also:
I don't know if it has same problem with python scripts. Maybe a bash script like above to call python script might work.
I forgot mention in last post that the bash script need to be executable.
You can try, at least.
erem
Post by erem »
you can find more info on the various exit modes here
https://www.geeksforgeeks.org/python-ex ... -os-_exit/
what version of python do you use, 2 or 3?
Regards,
Rob
JanvdW
Post by JanvdW »
erem wrote: Wednesday 03 February 2021 13:42 you can find more info on the various exit modes here
I tried sys.exit() as well; same result.
erem wrote: Wednesday 03 February 2021 13:42 what version of python do you use, 2 or 3?
Evohome client (which is included in my script) works with Python 2, in my case 2.7.16
JanvdW
Post by JanvdW »
FireWizard wrote: Wednesday 03 February 2021 13:39 @JanvdW
I don't know.
@DewGew said also:
I am not sure how to do this. My python script is started with two parameters and I don't know how I can pass them from the shell script to the python script.
erem
Post by erem »
i dumbed the code down to this blocky,
03-02-2021 15-21-18.jpg (18.44 KiB) Viewed 5024 times
and the script
-rwxr-xr-x 1 pi pi 448 Feb 3 15:16 py2test.py
with code
#!/usr/bin/python2
import sys
import requests
import datetime
import time
print "test python2 starts"
time.sleep( 5 )
end_time = "21:30"
   print "test python2 ran"
#exit()
output in domoticz log
2021-02-03 15:17:00.213 EventSystem: Event triggered: py2test_1
2021-02-03 15:17:00.442 Status: Executing script: //home/pi/py2test.py
2021-02-03 15:18:00.234 EventSystem: Event triggered: py2test_1
2021-02-03 15:18:00.473 Status: Executing script: //home/pi/py2test.py
2021-02-03 15:19:00.247 EventSystem: Event triggered: py2test_1
2021-02-03 15:19:00.460 Status: Executing script: //home/pi/py2test.py
2021-02-03 15:20:00.261 EventSystem: Event triggered: py2test_1
2021-02-03 15:21:00.275 EventSystem: Event triggered: py2test_1
2021-02-03 15:21:18.487 (Buienradar) General/Custom Sensor (Next Rainshower Leadtime)
2021-02-03 15:21:18.495 (Buienradar) General/Custom Sensor (Next Rainshower Duration)
2021-02-03 15:21:18.504 (Buienradar) General/Custom Sensor (Next Rainshower Avg Rainrate)
2021-02-03 15:21:18.512 (Buienradar) General/Custom Sensor (Next Rainshower Max Rainrate)
2021-02-03 15:21:18.520 (Buienradar) General/Percentage (Rain Intensity)
2021-02-03 15:21:18.528 (Buienradar) General/Custom Sensor (Rainfall next Hour)
2021-02-03 15:22:00.287 EventSystem: Event triggered: py2test_1
2021-02-03 15:23:00.300 EventSystem: Event triggered: py2test_1
2021-02-03 15:23:00.530 Status: Executing script: //home/pi/py2test.py
2021-02-03 15:24:00.313 EventSystem: Event triggered: py2test_1
2021-02-03 15:24:00.531 Status: Executing script: //home/pi/py2test.py
i did the same test with python3, same result.
can you see if that runs without the error on your system
you can see that i tried with and without exit(), both give no error on my system.
does your domoticz run as root?
if so, what happens if you execute the script from a root command line? any errors?
Regards,
Rob
JanvdW
Post by JanvdW »
erem wrote: Wednesday 03 February 2021 15:38 i dumbed the code down to this blocky,
and the script
with code
#!/usr/bin/python2
import sys
import requests
import datetime
import time
time.sleep( 5 )
end_time = "21:30"
#exit()
I need to use python2, because the Evohome scripts are not compliant with python3. When I run the script on the command line everything works fine; no errors appear.
I tested your setup and this works fine. I noticed some differences with my setup:
  • The test script was owned by root, while my script was owned by pi.
  • Different shebang
So I changed ownership and shebang of my script. Unfortunately the 256 errors are still there.
As far as I know this error normally means that the script is not executed. In my case the script is clearly executed, because the room temperature is changed as expected. But the 256 error appears in the log as well.
How can I check if domoticz run as root?
JanvdW
Post by JanvdW »
I found another confusing fact: in some cases the script results in an error and in some cases it doesn't. I can't recognize any pattern.
The log filtering of script execution between 20:50 and 21:20:
	2021-02-03 20:50:09.254 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 20:51:06.198 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 20:52:09.747 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 20:53:06.134 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 20:54:10.588 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 20:55:06.591 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 20:56:10.140 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 20:57:05.668 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 20:58:10.963 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 20:59:05.723 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 21:00:24.232 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 21:01:05.739 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 21:02:10.269 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 21:03:05.771 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 21:04:10.316 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 21:05:07.028 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 21:06:10.178 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
2021-02-03 21:07:05.817 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	021-02-03 21:08:10.302 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
	2021-02-03 21:09:05.850 Status: Executing script: //home/pi/evohome-client/radiator_temp.py
I indented the lines in this log that are correlated to an error message, as is shown in the log filtering of script errors between 20:50 and 21:20
2021-02-03 20:50:10.541 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 20:52:10.671 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 20:54:11.493 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 20:55:07.576 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 21:00:25.189 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 21:01:06.658 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 21:02:11.115 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 21:04:11.256 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 21:05:07.875 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 21:08:11.344 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
2021-02-03 21:09:06.762 Error: Error executing script command (//home/pi/evohome-client/radiator_temp.py). returned: 256
So possibly the conclusion in my previous message that, despite of the error, the script was clearly executed (because the room temperature changed) wasn't appropriate. Maybe this change was caused by an occasions which didn't end up in an 256 error.
FireWizard
Hi, @JanvdW,
Have you read this thread?
viewtopic.php?t=7465
Perhaps it is useful
JanvdW
Post by JanvdW »
FireWizard wrote: Wednesday 03 February 2021 23:29 Hi, @JanvdW,
Yes, I have seen that topic before. Most of the solutions mentioned here can't solve my problem, because other (quite similar) scripts work perfectly well. And some solutions are mentioned for Actions in Domoticz (like the three '/'). I have have tested the suggestion in this topic to end the script with 'exit 0', but that doesn't solve the issues either.
I have another script, that is called with a similar Blockly, stored in the same directory, using the same Evohome libraries, which run without trouble:
import evoconfig
import sys
import requests
zones=tcs['zones']
if currentmode != "Away":
   client.locations[0]._gateways[0]._control_systems[0].zones["Achterkamer"].set_temperature(15)
   client.locations[0]._gateways[0]._control_systems[0].zones["Tussenkamer"].set_temperature(15)
   client.locations[0]._gateways[0]._control_systems[0].zones["Voorkamer"].set_temperature(15)
   client.locations[0]._gateways[0]._control_systems[0].zones["Badkamer"].set_temperature(15)
I don't know what I'm overlooking, but at this moment don't understand this at all.
JanvdW wrote: Wednesday 03 February 2021 21:43 I found another confusing fact: in some cases the script results in an error and in some cases it doesn't. I can't recognize any pattern.
Maybe belows dzVents script does give you some insight what's going wrong.
return
    on =
        timer =
            'every minute',
    logging =
        level = domoticz.LOG_DEBUG,
        marker = 'Python script-starter',
    execute = function(dz)
        local function osCommand(cmd)
            dz.log('Executing Command: ' .. cmd,dz.LOG_DEBUG)
            local fileHandle = assert(io.popen(cmd .. ' 2>&1 || echo ::ERROR::', 'r'))
            local commandOutput = assert(fileHandle:read('*a'))
            local returnTable = {fileHandle:close()}
            if commandOutput:find '::ERROR::' then     -- something went wrong
                dz.log('Error ==>> ' .. tostring(commandOutput:match('^(.*)%s+::ERROR::') or ' ... but no error message ' ) ,dz.LOG_DEBUG)
            else -- all is fine!!
                dz.log('ReturnCode: ' .. returnTable[3] .. '\ncommandOutput:\n' .. commandOutput, dz.LOG_DEBUG)
            return commandOutput,returnTable[3] -- rc[3] contains returnCode
        local res, rc = osCommand ('/home/pi/evohome-client/radiator_temp.py Voorkamer "19" ' )
        dz.log('returnCode: ' .. (rc % 255) .. ' , result: ' .. res, dz.LOG_DEBUG)
JanvdW
Post by JanvdW »
waaren wrote: Thursday 04 February 2021 0:12
return
    on =
        timer =
            'every minute',
    logging =
I ran the script and script temperature setting is implemented. In the log
2021-02-04 08:42:21.329 Status: dzVents: Debug: Python script-starter: returnCode: 0 , result:
2021-02-04 08:43:00.295 Status: dzVents: Info: Python script-starter: ------ Start internal script: Script #2:, trigger: "every minute"
2021-02-04 08:43:00.295 Status: dzVents: Debug: Python script-starter: Executing Command: /home/pi/evohome-client/radiator_temp.py Voorkamer "10"
2021-02-04 08:43:14.177 Status: dzVents: Debug: Python script-starter: ReturnCode: 0
2021-02-04 08:43:14.177 commandOutput:
2021-02-04 08:43:14.177 Status: dzVents: Debug: Python script-starter: returnCode: 0 , result:
The only error that is logged is:
2021-02-04 08:42:20.436 Error: EventSystem: Warning!, lua script /home/pi/domoticz/dzVents/runtime/dzVents.lua has been running for more than 10 seconds
2021-02-04 08:42:21.331 Error: dzVents: Error: (3.1.4) Python script-starter: ------ Finished Script #2 after >16 seconds. (using 0.934 seconds CPU time !)
JanvdW
Post by JanvdW »
After some of these the following error was logged:
2021-02-04 08:46:06.324 Error: dzVents: Debug: Python script-starter: Error ==>> Traceback (most recent call last):
2021-02-04 08:46:06.324 File "/home/pi/evohome-client/radiator_temp.py", line 11, in <module>
2021-02-04 08:46:06.324 client = EvohomeClient(evoconfig.usr, evoconfig.pw)
2021-02-04 08:46:06.324 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 89, in __init__
2021-02-04 08:46:06.324 self._login()
2021-02-04 08:46:06.324 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 94, in _login
2021-02-04 08:46:06.324 self.user_account()
2021-02-04 08:46:06.324 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 228, in user_account
2021-02-04 08:46:06.324 response = requests.get(url, headers=self._headers())
2021-02-04 08:46:06.324 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 110, in _headers
2021-02-04 08:46:06.324 self._basic_login()
2021-02-04 08:46:06.324 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 150, in _basic_login
2021-02-04 08:46:06.324 self._obtain_access_token(credentials)
2021-02-04 08:46:06.324 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 180, in _obtain_access_token
2021-02-04 08:46:06.324 raise AuthenticationError(msg)
2021-02-04 08:46:06.324 evohomeclient2.AuthenticationError: Unable to obtain an Access Token, hint: {"error":"attempt_limit_exceeded"}
2021-02-04 08:46:06.325 Error: dzVents: Debug: Python script-starter: returnCode: 0 , result: Traceback (most recent call last):
2021-02-04 08:46:06.325 File "/home/pi/evohome-client/radiator_temp.py", line 11, in <module>
2021-02-04 08:46:06.325 client = EvohomeClient(evoconfig.usr, evoconfig.pw)
2021-02-04 08:46:06.325 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 89, in __init__
2021-02-04 08:46:06.325 self._login()
2021-02-04 08:46:06.325 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 94, in _login
2021-02-04 08:46:06.325 self.user_account()
2021-02-04 08:46:06.325 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 228, in user_account
2021-02-04 08:46:06.325 response = requests.get(url, headers=self._headers())
2021-02-04 08:46:06.325 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 110, in _headers
2021-02-04 08:46:06.325 self._basic_login()
2021-02-04 08:46:06.325 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 150, in _basic_login
2021-02-04 08:46:06.325 self._obtain_access_token(credentials)
2021-02-04 08:46:06.325 File "/home/pi/evohome-client/evohomeclient2/__init__.py", line 180, in _obtain_access_token
2021-02-04 08:46:06.325 raise AuthenticationError(msg)
2021-02-04 08:46:06.325 evohomeclient2.AuthenticationError: Unable to obtain an Access Token, hint: {"error":"attempt_limit_exceeded"}
2021-02-04 08:46:06.325 ::ERROR::
This explains why the error occurs not in all cases: the problem had nothing to do with the python script, but with exceeding Evohome access limits. In other words, it's caused by the Blocky timer (that I added for some tests) which fires the script every minute. I removed that and fired the script based on (manually triggered) smartphone presence only. No errors are logged now. So it seems to be solved. Rather confusing error message...
Thanks for your help and your script. It helps me to find the cause.
JanvdW wrote: Thursday 04 February 2021 8:55 Thanks for your help and your script. It helps me to find the cause.
Given that you are on a recent dzVents version, you can also use below script. This will process the evohome script async from domoticz and therewith not blocking the eventsystem for 10 seconds when evohome connection takes too long.
local scriptVar = 'pythonStarter'
return
    on =
        devices =
            ['Smartphone Jan'] =
                'at 08:00-21:00',
        shellCommandResponses =
            scriptVar,
    logging =
        marker = scriptVar
    execute = function(dz, item)
        if item.isDevice and item.active then
            dz.executeShellCommand(
                command = '/home/pi/evohome-client/radiator_temp.py Voorkamer "19" ' ,
                timeout = 30,
                callback = scriptVar,
        elseif item.isShellCommandResponse then
            local result = ''
            if item.data and item.data ~= '' then
                result = '\n' .. 'output: ' .. item.data
            dz.log('returnCode: '.. item.statusCode .. ' , error Text: ' .. item.errorText .. result , dz.LOG_DEBUG)
JanvdW
Post by JanvdW »
waaren wrote: Thursday 04 February 2021 22:21
return
    on =
        devices =
                'at 08:00-21:00',
            scriptVar,
    logging =
        marker = scriptVar
                timeout = 30,
            local result = ''
Thanks for thinking along; I really appreciate that! The script works perfect.
I was not aware that Blockly is working synchronous. Are Blockly scrips always running synchronous? In that case I will have a look at my other Blockly's as well.
JanvdW wrote: Thursday 04 February 2021 23:22 I was not aware that Blockly is working synchronous. Are Blockly scrips always running synchronous? In that case I will have a look at my other Blockly's as well.
Yes, classic Lua and Blockly commands like os.execute, io.popen are executed synchronous. The os commands can be forced to be executed in the background on linux systems by adding a trailing ampersand to the command and something similar can be done on windows.
Problem with that approach is that quite some extra code is needed to check if the commands were successful and to process any results.