[Solved] Zigate controller and firmware upgrade to 031a
JanZorz
Post by JanZorz »
Today I upgraded my Zigate USB controller to 031a (from 030e) - I did everything as described in manual and upgrade was executed without problems. Zigate plugin web interface tells me that Zigate was properly initialized with new firmware and is running fine. Domoticz Zigate version is 4.5.9, hardware is old one (blue).
Domoticz still tells me that there are 33 devices in inventory, but non of them is reporting anything. Scan of the network shows 0 devices connected.
Domoticz version is 4.11597, build hash: 70664be92
If I enable "Accept new hardware" - lights on controller does not start blinking. I also pressed the "Erase" button on web interface to "erase the permanent data memory of Zigate" in secret hope that I'll be able to re-pair - but to no avail. If I put it into "accept new hardware" mode and try to pair old devices - nothing happens.
Here is the part of log file:
2020-01-09 13:33:29.216 Status: (Zigate) Initialized version 4.5, author 'zaraki673 pipiche38'
2020-01-09 13:33:29.217 Status: (Zigate) Zigate plugin stable-4.5.9 started
2020-01-09 13:33:29.217 (Zigate) Debug: 0
2020-01-09 13:33:29.217 Status: (Zigate) Python Version - 3.7.3 (default, Oct 7 2019, 12:56:13)
2020-01-09 13:33:29.217 Status: (Zigate) Switching Heartbeat to 5 s interval
2020-01-09 13:33:29.217 Status: (Zigate) DomoticzVersion: 4.11597
2020-01-09 13:33:29.217 Status: (Zigate) DomoticzHash: 70664be92
2020-01-09 13:33:29.217 Status: (Zigate) DomoticzBuildTime: 2019-12-30 00:14:56
2020-01-09 13:33:29.217 Status: (Zigate) load PluginConf
2020-01-09 13:33:29.218 Status: (Zigate) enableReadAttributes set to 1
2020-01-09 13:33:29.218 Status: (Zigate) allowOTA set to 1
2020-01-09 13:33:29.218 Status: (Zigate) batteryOTA set to 1
2020-01-09 13:33:29.218 Status: (Zigate) filename set to /opt/domoticz/plugins/Domoticz-Zigate/Conf/PluginConf-07.json
2020-01-09 13:33:29.218 Status: (Zigate) pluginHome set to /opt/domoticz/plugins/Domoticz-Zigate/
2020-01-09 13:33:29.218 Status: (Zigate) homedirectory set to /opt/domoticz/plugins/Domoticz-Zigate/
2020-01-09 13:33:29.218 Status: (Zigate) pluginData set to /opt/domoticz/plugins/Domoticz-Zigate/Data/
2020-01-09 13:33:29.218 Status: (Zigate) pluginConfig set to /opt/domoticz/plugins/Domoticz-Zigate/Conf/
2020-01-09 13:33:29.218 Status: (Zigate) pluginOTAFirmware set to /opt/domoticz/plugins/Domoticz-Zigate/OTAFirmware/
2020-01-09 13:33:29.218 Status: (Zigate) pluginReports set to /opt/domoticz/plugins/Domoticz-Zigate/Reports/
2020-01-09 13:33:29.218 Status: (Zigate) pluginWWW set to /opt/domoticz/plugins/Domoticz-Zigate/www/
2020-01-09 13:33:29.218 Status: (Zigate) Opening DomoticzDB in raw
2020-01-09 13:33:29.218 Status: (Zigate) Plugin Database: DeviceList-7.txt
2020-01-09 13:33:29.221 Status: (Zigate) DeviceConf loaded
2020-01-09 13:33:29.221 Status: (Zigate) load ListOfDevice
2020-01-09 13:33:29.227 Status: (Zigate) Entries loaded from /opt/domoticz/plugins/Domoticz-Zigate/Data/DeviceList-7.txt : 11
2020-01-09 13:33:29.227 Error: (Zigate) checkListOfDevice2Devices - Okrogel switch - 00158d0003496dfd not found in Plugin Database
2020-01-09 13:33:29.227 Status: (Zigate) Transport mode: USB
2020-01-09 13:33:29.227 Status: (Zigate) Connection Name: Zigate, Transport: Serial, Address: /dev/ttyUSB0
2020-01-09 13:33:29.228 Status: (Zigate) Zigate set Time Server
2020-01-09 13:33:29.228 (Zigate) setTimeServer - Setting UTC Time to : 631892009
2020-01-09 13:33:29.228 Status: (Zigate) Software reset
2020-01-09 13:33:29.229 Status: (Zigate) ZigateConf setting Channel(s) to: 0
2020-01-09 13:33:29.229 Status: (Zigate) setChannel - Channel set to : 00000000
2020-01-09 13:33:29.229 Status: (Zigate) Set Zigate as a Coordinator
2020-01-09 13:33:29.229 (Zigate) setTimeServer - Setting UTC Time to : 631892009
2020-01-09 13:33:29.229 Status: (Zigate) Start network
2020-01-09 13:33:29.229 Status: (Zigate) Configure Permit To Join
2020-01-09 13:33:29.229 Status: (Zigate) Request Accepting new Hardware for 254 seconds
2020-01-09 13:33:29.229 Status: (Zigate) Trigger a Topology Scan
2020-01-09 13:33:29.229 Status: (Zigate) Trigger a Energy Level Scan
2020-01-09 13:33:29.229 Status: (Zigate) Network Energy Level Report: 0000
2020-01-09 13:33:29.229 Status: (Zigate) -----------------------------------------------
2020-01-09 13:33:29.229 Status: (Zigate) router <- nwkid Tx Failure 11 15 19 20 25 26
2020-01-09 13:33:29.330 Status: (Zigate) Major Version Num: 0003
2020-01-09 13:33:29.330 Status: (Zigate) Installer Version Number: 031a
2020-01-09 13:33:29.632 Status: (Zigate) 'Factory new' Restart status: NFN_START
2020-01-09 13:33:29.934 Status: (Zigate) Busy Node
2020-01-09 13:33:29.934 (Zigate) Start Network status : Success
2020-01-09 13:33:30.035 (Zigate) Permit Join status: 00
2020-01-09 13:33:30.035 (Zigate) ---> self.permitTojoin['Starttime']: 1578573209
2020-01-09 13:33:30.035 (Zigate) ---> Current time : 1578573210
2020-01-09 13:33:30.035 (Zigate) ---> self.Ping['Permit'] (prev) : None
2020-01-09 13:33:30.035 Status: (Zigate) Accepting new Hardware: Disable
2020-01-09 13:33:30.035 (Zigate) ---> self.Ping['Permit'] (new ) : Off
2020-01-09 13:33:30.141 Status: (Zigate) Zigate addresses ieee: 00158d0001ee04c9 , short addr: 0000
2020-01-09 13:33:30.141 Status: (Zigate) Network state UP, PANID: d9d7 extPANID: 0xf7261c14f504723c Channel: 11
2020-01-09 13:33:30.381 (Zigate) Permit Join status: 01
2020-01-09 13:33:30.381 (Zigate) ---> self.permitTojoin['Starttime']: 1578573209
2020-01-09 13:33:30.381 (Zigate) ---> Current time : 1578573210
2020-01-09 13:33:30.381 (Zigate) ---> self.Ping['Permit'] (prev) : Off
2020-01-09 13:33:30.381 Status: (Zigate) Accepting new Hardware: On
2020-01-09 13:33:30.381 (Zigate) ---> self.Ping['Permit'] (new ) : On
2020-01-09 13:33:30.482 Status: (Zigate) Zigate addresses ieee: 00158d0001ee04c9 , short addr: 0000
2020-01-09 13:33:30.482 Status: (Zigate) Network state UP, PANID: d9d7 extPANID: 0xf7261c14f504723c Channel: 11
2020-01-09 13:33:30.657 Status: (Zigate) Number of devices recently active in Zigate = 33
2020-01-09 13:33:30.657 Status: (Zigate) [00] DevID = 00 Network addr = bbb4 IEEE = 00158d0003496dfd LQI = 098 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.657 Status: (Zigate) [01] DevID = 01 Network addr = 0800 IEEE = 0000000000000000 LQI = 016 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.657 Status: (Zigate) [02] DevID = 02 Network addr = 0000 IEEE = 0000000000000000 LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.657 Status: (Zigate) [03] DevID = 03 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 004 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [05] DevID = 05 Network addr = 0800 IEEE = 0000000000000000 LQI = 016 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [06] DevID = 06 Network addr = 0000 IEEE = 0000000000000000 LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [07] DevID = 07 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 009 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [09] DevID = 09 Network addr = 0800 IEEE = 0000000000000000 LQI = 016 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [10] DevID = 0a Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [11] DevID = 0b Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [12] DevID = 0d Network addr = ff00 IEEE = 00158d0003496dfd LQI = 000 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [13] DevID = 0e Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [14] DevID = 0f Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [15] DevID = 11 Network addr = ff00 IEEE = 00158d0003496dfd LQI = 000 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [16] DevID = 12 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [17] DevID = 13 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [18] DevID = 15 Network addr = ff00 IEEE = 00158d0003496dfd LQI = 000 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.658 Status: (Zigate) [19] DevID = 16 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [20] DevID = 17 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [21] DevID = 19 Network addr = ff00 IEEE = 00158d0003496dfd LQI = 000 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [22] DevID = 1a Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [23] DevID = 1b Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [24] DevID = 1d Network addr = ff00 IEEE = 00158d0003496dfd LQI = 000 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [25] DevID = 1e Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [26] DevID = 1f Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [27] DevID = 21 Network addr = ff00 IEEE = 00158d0003496dfd LQI = 000 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [28] DevID = 22 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [29] DevID = 23 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [30] DevID = 25 Network addr = ff00 IEEE = 00158d0003496dfd LQI = 000 Power = 01 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [31] DevID = 26 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 000 Power = 00 not found in ListOfDevices
2020-01-09 13:33:30.659 Status: (Zigate) [32] DevID = 27 Network addr = 0000 IEEE = 00158d0003496dfd LQI = 255 Power = 00 not found in ListOfDevices
2020-01-09 13:33:39.230 Status: (Zigate) Zigate set to Certification : CE
2020-01-09 13:33:39.230 Status: (Zigate) Start Web Server connection
2020-01-09 13:33:39.236 Status: (Zigate) Web backend for Web User Interface started on port: 9440
2020-01-09 13:33:39.236 Status: (Zigate) Plugin with Zigate firmware 031a correctly initialized
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 16897 version: 12217572 - filename: 159698-TRADFRI-driver-lp-1.2.217.ota.ota size: 173246 Bytes
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 10241 version: 13009572 - filename: 10035515-TRADFRI-bulb-cws-1.3.009.ota.ota size: 178366 Bytes
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 8449 version: 12214572 - filename: 159696-TRADFRI-bulb-w-1000lm-1.2.214.ota.ota size: 168318 Bytes
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 16641 version: 12245572 - filename: 159495-TRADFRI-transformer-1.2.245.ota.ota size: 181118 Bytes
2020-01-09 13:33:39.236 (Zigate) ota_decode_new_image - Image 1004764-TRADFRI-bulb-cws-1.3.009.ota.ota already imported. Type: 10241 with better version 13009572 versus 13009572
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 4548 version: 12214572 - filename: 159700-TRADFRI-motion-sensor-1.2.214.ota.ota size: 157822 Bytes
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 8707 version: 12221572 - filename: 10035534-TRADFRI-bulb-ws-gu10-1.2.221.ota.ota size: 172734 Bytes
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 4546 version: 12248572 - filename: 159701-TRADFRI-wireless-dimmer-1.2.248.ota.ota size: 172926 Bytes
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 4549 version: 22008631 - filename: 10005778-4.1-TRADFRI-onoff-shortcut-control-2.2.008.ota.ota size: 179582 Bytes
2020-01-09 13:33:39.236 Status: (Zigate) Available Firmware Type: 4353 version: 20022623 - filename: 10005777-4.1-TRADFRI-control-outlet-2.0.022.ota.ota.signed size: 204222 Bytes
2020-01-09 13:33:39.237 Status: (Zigate) Available Firmware Type: 8705 version: 12221572 - filename: 10035514-TRADFRI-bulb-ws-1.2.221.ota.ota size: 172734 Bytes
2020-01-09 13:33:39.237 Status: (Zigate) Available Firmware Type: 16900 version: 20022623 - filename: 10038562-TRADFRI-sy5882-bulb-ws-2.0.022.ota.ota.signed size: 209790 Bytes
2020-01-09 13:33:39.237 Status: (Zigate) Available Firmware Type: 8706 version: 12217572 - filename: 159695-TRADFRI-bulb-ws-1000lm-1.2.217.ota.ota size: 173246 Bytes
2020-01-09 13:33:39.237 Status: (Zigate) Available Firmware Type: 4545 version: 12223573 - filename: 159699-2.1-TRADFRI-remote-control-1.2.223.ota.ota.signed size: 159806 Bytes
2020-01-09 13:33:39.237 Status: (Zigate) Available Firmware Type: 16898 version: 12217572 - filename: 159697-TRADFRI-driver-hp-1.2.217.ota.ota size: 173246 Bytes
2020-01-09 13:33:47.432 (Zigate) TxPower set to: 00
Any idea how to get my devices back?
Please, help! :)
Cheers and thnx, Jan Zorz
pipiche
Re: Zigate controller and firmware upgrade to 031a
Post by pipiche »
What the log said is that you have miss-match between what is defined in the plugin DB ( /opt/domoticz/plugins/Domoticz-Zigate/Data/DeviceList-7.txt ) 11 devices and 33 were recently active in Zigate and what is in Domoticz.
So from here, I cannot really comment more than there is an inconsistency between the plugin DB and the Domoticz DB. The fct that you have done an ErasePDM, will require you to redo the pairing, but FIRST you need to fix the inconsistency. Either by removing all Zigate related devices in Domoticz and to start from scratch
Having the possibility to restart from a backup where there is Domoticz and Plugin consistency would help.
Did you upgrade the plugin ? if so from which version to which version ?
JanZorz
Post by JanZorz »
pipiche wrote: Thursday 09 January 2020 13:47 Having the possibility to restart from a backup where there is Domoticz and Plugin consistency would help.
I did not upgrade the plugin meantime... I did "git pull", but no change of plugin version.
I'll try with restoring the backup and see if that works. Thank you a lot!
Cheers, Jan
JanZorz
Post by JanZorz »
pipiche wrote: Thursday 09 January 2020 13:47 Either by removing all Zigate related devices in Domoticz and to start from scratch
Restored a backup from yesterday evening and same problem - no devices found. I even tried to pair new device, but to no avail. I tried to remove one device in Domoticz and re-pair it - also nothing... When I put controller in "Allow new hardware", led light on controller does not go into blinking mode. Is that a normal behavior?
pipiche
Post by pipiche »
To allow the pairing you need to enable it from the plugin.
When you start the plugin you can say permit to join for a number of seconds ( 255 means for ever )
JanZorz
Post by JanZorz »
pipiche wrote: Thursday 09 January 2020 15:01 To allow the pairing you need to enable it from the plugin.
Hey, thnx for your time and help.
It's set to 254, that's how I paired all zigbee devices up to now... I also have restart-on-save, but it doesn't matter how I restart or start the module - the controller does not go into blinking mode that up to now indicated that it is allowing new hardware.
Serial port is properly set and from log files it seems that the module initializes the controller - just not into "pairing" mode...
Any hint?
JanZorz
Post by JanZorz »
ok, I removed all devices bound to Zigate controller from Domoticz, did a "Erase Persistent Data" from plugin setup screen, removed a plugin from Domoticz, shut down Domoticz, removed a Domoticz-Zigate directory from plugins directory, did again a git clone, started Domoticz, added Zigate plugin and now I have new "issues":
2020-01-09 20:54:45.747 Status: (Zigate) Started.
2020-01-09 20:54:45.900 Status: (Zigate) Entering work loop.
2020-01-09 20:54:45.900 Status: (Zigate) Initialized version 4.5, author 'zaraki673 pipiche38'
2020-01-09 20:54:45.901 Status: (Zigate) Zigate plugin stable-4.5.9 started
2020-01-09 20:54:45.901 (Zigate) Debug: 14
2020-01-09 20:54:45.901 Status: (Zigate) Python Version - 3.7.3 (default, Oct 7 2019, 12:56:13)
2020-01-09 20:54:45.901 Status: (Zigate) Switching Heartbeat to 5 s interval
2020-01-09 20:54:45.901 Status: (Zigate) DomoticzVersion: 4.11597
2020-01-09 20:54:45.901 Status: (Zigate) DomoticzHash: 70664be92
2020-01-09 20:54:45.901 Status: (Zigate) DomoticzBuildTime: 2019-12-30 00:14:56
2020-01-09 20:54:45.901 Status: (Zigate) load PluginConf
2020-01-09 20:54:45.901 Status: (Zigate) filename set to /opt/domoticz/plugins/Domoticz-Zigate/Conf/PluginConf-09.json
2020-01-09 20:54:45.901 Status: (Zigate) pluginHome set to /opt/domoticz/plugins/Domoticz-Zigate/
2020-01-09 20:54:45.901 Status: (Zigate) homedirectory set to /opt/domoticz/plugins/Domoticz-Zigate/
2020-01-09 20:54:45.901 Status: (Zigate) pluginData set to /opt/domoticz/plugins/Domoticz-Zigate/Data/
2020-01-09 20:54:45.901 Status: (Zigate) pluginConfig set to /opt/domoticz/plugins/Domoticz-Zigate/Conf/
2020-01-09 20:54:45.901 Status: (Zigate) pluginOTAFirmware set to /opt/domoticz/plugins/Domoticz-Zigate/OTAFirmware/
2020-01-09 20:54:45.901 Status: (Zigate) pluginReports set to /opt/domoticz/plugins/Domoticz-Zigate/Reports/
2020-01-09 20:54:45.901 Status: (Zigate) pluginWWW set to /opt/domoticz/plugins/Domoticz-Zigate/www/
2020-01-09 20:54:45.901 Status: (Zigate) Opening DomoticzDB in raw
2020-01-09 20:54:45.902 Status: (Zigate) Plugin Database: DeviceList-9.txt
2020-01-09 20:54:45.904 Status: (Zigate) DeviceConf loaded
2020-01-09 20:54:45.904 Status: (Zigate) load ListOfDevice
2020-01-09 20:54:45.904 Status: (Zigate) Transport mode: USB
2020-01-09 20:54:45.904 Status: (Zigate) Connection Name: Zigate, Transport: Serial, Address: /dev/ttyUSB0
2020-01-09 20:54:45.972 Status: (Zigate) Zigate set Time Server
2020-01-09 20:54:45.972 (Zigate) setTimeServer - Setting UTC Time to : 631918485
2020-01-09 20:54:45.972 Status: (Zigate) Software reset
2020-01-09 20:54:45.972 Status: (Zigate) ZigateConf setting Channel(s) to: 0
2020-01-09 20:54:45.972 Status: (Zigate) setChannel - Channel set to : 00000000
2020-01-09 20:54:45.972 Status: (Zigate) Set Zigate as a Coordinator
2020-01-09 20:54:45.972 Status: (Zigate) Start network
2020-01-09 20:54:45.973 Status: (Zigate) Configure Permit To Join
2020-01-09 20:54:45.973 Status: (Zigate) Request Accepting new Hardware for 254 seconds
2020-01-09 20:54:45.973 Status: (Zigate) Trigger a Topology Scan
2020-01-09 20:54:45.973 Status: (Zigate) Trigger a Energy Level Scan
2020-01-09 20:54:45.973 Status: (Zigate) Network Energy Level Report: 0000
2020-01-09 20:54:45.973 Status: (Zigate) -----------------------------------------------
2020-01-09 20:54:45.973 Status: (Zigate) router <- nwkid Tx Failure 11 15 19 20 25 26
2020-01-09 20:54:46.074 Status: (Zigate) Major Version Num: 0003
2020-01-09 20:54:46.074 Status: (Zigate) Installer Version Number: 031a
2020-01-09 20:54:46.376 Status: (Zigate) 'Factory new' Restart status: STARTUP
2020-01-09 20:54:46.678 (Zigate) Start Network status : Success
2020-01-09 20:54:55.949 Status: (Zigate) Zigate set to Certification : CE
2020-01-09 20:54:55.950 Status: (Zigate) Start Web Server connection
2020-01-09 20:54:55.955 Status: (Zigate) Web backend for Web User Interface started on port: 9440
2020-01-09 20:54:55.955 Status: (Zigate) Plugin with Zigate firmware 031a correctly initialized
2020-01-09 20:54:56.102 (Zigate) Permit Join status: 00
2020-01-09 20:54:56.102 (Zigate) ---> self.permitTojoin['Starttime']: 1578599685
2020-01-09 20:54:56.102 (Zigate) ---> Current time : 1578599696
2020-01-09 20:54:56.102 (Zigate) ---> self.Ping['Permit'] (prev) : None
2020-01-09 20:54:56.102 Status: (Zigate) Accepting new Hardware: Disable
2020-01-09 20:54:56.102 (Zigate) ---> self.Ping['Permit'] (new ) : Off
2020-01-09 20:54:56.204 Error: (Zigate) Zigate not correctly initialized
2020-01-09 20:54:56.204 Status: (Zigate) Zigate addresses ieee: 00158d0001ee04c9 , short addr: ffff
2020-01-09 20:54:56.204 Status: (Zigate) Network state UP, PANID: 9ea9 extPANID: 0x9b95d6dc09c12c64 Channel: 11
2020-01-09 20:54:56.406 (Zigate) Permit Join status: 01
2020-01-09 20:54:56.406 (Zigate) ---> self.permitTojoin['Starttime']: 1578599685
2020-01-09 20:54:56.406 (Zigate) ---> Current time : 1578599696
2020-01-09 20:54:56.406 (Zigate) ---> self.Ping['Permit'] (prev) : Off
2020-01-09 20:54:56.406 Status: (Zigate) Accepting new Hardware: On
2020-01-09 20:54:56.406 (Zigate) ---> self.Ping['Permit'] (new ) : On
2020-01-09 20:54:56.507 Error: (Zigate) Zigate not correctly initialized
2020-01-09 20:54:56.507 Status: (Zigate) Zigate addresses ieee: 00158d0001ee04c9 , short addr: ffff
2020-01-09 20:54:56.507 Status: (Zigate) Network state UP, PANID: 9ea9 extPANID: 0x9b95d6dc09c12c64 Channel: 11
2020-01-09 20:54:56.608 Status: (Zigate) Number of devices recently active in Zigate = 0
2020-01-09 20:55:01.021 (Zigate) TxPower set to: 00
2020-01-09 20:55:01.222 Error: (Zigate) Zigate not correctly initialized
2020-01-09 20:55:01.222 Status: (Zigate) Zigate addresses ieee: 00158d0001ee04c9 , short addr: ffff
2020-01-09 20:55:01.222 Status: (Zigate) Network state UP, PANID: 9ea9 extPANID: 0x9b95d6dc09c12c64 Channel: 11
2020-01-09 20:55:11.046 Error: (Zigate) Zigate not correctly initialized
2020-01-09 20:55:11.046 Status: (Zigate) Zigate addresses ieee: 00158d0001ee04c9 , short addr: ffff
2020-01-09 20:55:11.046 Status: (Zigate) Network state UP, PANID: 9ea9 extPANID: 0x9b95d6dc09c12c64 Channel: 11
2020-01-09 20:55:15.913 Status: (Zigate) ZigateConf setting Channel(s) to: 0
2020-01-09 20:55:15.913 Status: (Zigate) setChannel - Channel set to : 00000000
2020-01-09 20:55:15.913 Status: (Zigate) Set Zigate as a Coordinator
2020-01-09 20:55:15.913 (Zigate) setTimeServer - Setting UTC Time to : 631918515
2020-01-09 20:55:15.913 Status: (Zigate) Start network
2020-01-09 20:55:16.316 (Zigate) Network joined / formed Status: 06: Address parameter is out-of-range (fatal error), e.g. broadcast address when calling unicast function
2020-01-09 20:55:16.316 (Zigate) Start Network status : Success
2020-01-09 20:55:16.417 (Zigate) Permit Join status: 01
2020-01-09 20:55:16.417 (Zigate) ---> self.permitTojoin['Starttime']: 1578599685
2020-01-09 20:55:16.417 (Zigate) ---> Current time : 1578599716
2020-01-09 20:55:16.417 (Zigate) ---> self.Ping['Permit'] (prev) : On
2020-01-09 20:55:16.417 Status: (Zigate) Accepting new Hardware: On
2020-01-09 20:55:16.417 (Zigate) ---> self.Ping['Permit'] (new ) : On
2020-01-09 20:55:16.518 Error: (Zigate) Zigate not correctly initialized
2020-01-09 20:55:16.518 Status: (Zigate) Zigate addresses ieee: 00158d0001ee04c9 , short addr: ffff
2020-01-09 20:55:16.518 Status: (Zigate) Network state UP, PANID: 9ea9 extPANID: 0x9b95d6dc09c12c64 Channel: 11
2020-01-09 21:00:51.001 Error: (Zigate) processConfigureReporting - no 'Status' flag for device ffff !!!
2020-01-09 21:01:51.040 Error: (Zigate) processConfigureReporting - no 'Status' flag for device ffff !!!
2020-01-09 21:02:51.027 Error: (Zigate) processConfigureReporting - no 'Status' flag for device ffff !!!
I'm currently not at the place where controller is so I can't try to include anything (will do that tomorrow morning), but as seen from logs - the whole thing is now not properly initialized :(
Linux is Ubuntu 19.04.
Any idea?
Thnx a lot!
Cheers, Jan
JanZorz
Post by JanZorz »
I did again the flashing...
root@home:~/Zigate# ./JennicModuleProgrammer -V 6 -P 115200 -f ZiGate_Coordinator_v3.1a.bin -s /dev/ttyUSB0
JennicModuleProgrammer Version: 0.6 (r56124)
Setting baudrate: 115200
Detected Chip: Unknown
MAC Address: 00:15:8D:00:01:EE:04:C9
Opened firmware file size 206728
Module uses Bootloader v2 Header
Erasing: 100%
Writing Program to Flash
Writing: 100%
Verifying Program in Flash
Verifying: 100%
Success
Pull USB out and back in...
Ran the Zigate module with "Erase Persistent Data" to "True" for the first time after reflashing. Still same errors :(
Anyone?
Cheers, Jan
pipiche
Post by pipiche »
From the log I do not see the Erase PDM, so could you try once more the Erase and then if still you have a problem share the logs
JanZorz
Post by JanZorz »
pipiche wrote: Friday 10 January 2020 17:15 From the log I do not see the Erase PDM, so could you try once more the Erase and then if still you have a problem share the logs
Problem fixed. I found a Windows machine and followed the process with Windows flashing application, including Erase EEPROM plus Complete EEPROM and everything and all of a sudden the thing started working in Domoticz.
Apparently Linux flashing app does not erase EEPROM succesfully - not if you follow the upgrade process from zigate.fr web site.
All in all - 031a works much better than original one, inclusion of devices is much faster and much more reliable. That's my first impression, let's see over time how it behaves.
Thank you very much for all your help!
Cheers, Jan
pipiche
Re: [Solved] Zigate controller and firmware upgrade to 031a
Post by pipiche »
Lovely and glad that you succeed ...
JanZorz
Post by JanZorz »
pipiche wrote: Friday 10 January 2020 21:11 Lovely and glad that you succeed ...
The thing that I learned from all this was that Domoticz Zigate module does not erase EEPROM when you configure it, neither does it do over it's web interface. Tried both many times, with no success.
Cheers, Jan
pipiche
Post by pipiche »
Correct over the Web Interface it is not yet enabled. It works only via the Domoticz Hardware plugin menu
JanZorz
Post by JanZorz »
pipiche wrote: Saturday 11 January 2020 15:28 Correct over the Web Interface it is not yet enabled. It works only via the Domoticz Hardware plugin menu
I tried through Domoticz Hardware plugin menu, many times - didn't work :(
On the other note - now all of a sudden my Zigate TTL USB controller died in the middle of a day... All lights went off and it doesn't matter to which USB on which machine I connect it - there is no lights whatsoever and no detection in OS that something connected. I think it's a HW failure.
Problem that I have is that there is no contact info on zigate.fr to contact them regarding the HW failure and possible replacement of device. I also can't register on their forum to ask a question there - so if you have any direct contact with Zigate folx - if you can give it to me to check if they honour the 2-year guarantee and replace my device. Maybe it's just a TTL USB module and the Zigbee part is ok...
Still wondering - if I replace just TTL USB part (blue in my case, red are the new ones) - would all my devices still be there and they'll just reconnect or will I have to do the whole pairing dance again?
Thank you very much for all your help, Jan Zorz
pipiche
Post by pipiche »
On the web site : https://zigate.fr/ you have a Contact Form which can be used to contact
this is at the bottom of the page
JanZorz
Post by JanZorz »
pipiche wrote: Friday 17 January 2020 9:55 On the web site : https://zigate.fr/ you have a Contact Form which can be used to contact
Did that yesterday - no reply yet... Thank you very much anyway ;)
Cheers, Jan
pipiche
Post by pipiche »
JanZorz wrote: Friday 17 January 2020 14:23
Cheers, Jan
Can you MP me your email address ?