Page 1 of 3
Generic auto-off
Posted: Monday 04 June 2018 14:33
by rrozema
UPDATE: I have written 2 more scripts since I wrote this article: Auto-On and Auto-OnOff. All updates on all 3 of these scripts are now presented in this thread: https://www.domoticz.com/forum/viewtopi ... 72&t=32031.
In my house I have multiple switches that are either manually or automatically by some mechanism switched on and that I want to switch off after some time. Initially I had a separate script for each such device. But the amount of scripts kept on growing and it was not very clear anymore which script controlled what switch and when I wanted to change a setting change or a add switch I had to go into the scripts and alter them. Rather tedious and error prone. So came up with a generic solution to specify per device if it was to switched off automatically and if so, after how much time. Once I had this working I added the possibility to delay switching the light off for as long as someone is still in the room, as detected by a motion detector (a PIR). I wanted my switches to be easy configurable, and I don't think having to go into a script and add, update or remove devices names or even index values is very easy. So I wrote a single script that is executed once a minute and checks all devices to see if it needs to be switched off. This script reads for each device a setting, stored in the devices' description field, to see what to do for this device. If a device's description does not contain the values, that device is not switched off automatically. If it contains only an "auto_off_minutes" value, the device will be switched off if its state = 'On' and its LastUpdate is older than the number of minutes specified in the value. If it contains also a value for "auto_off_motion_device" and the switch is on for at least the "auto_off_minutes" value, the motion device by the name specified is interrogated to see if is currently off and its last update is more than the amount in auto_off_minutes old. If the motion is indeed off with lastupdate being old, the switch is switched off. If the motion device is On or lastUpdate is less than auto_off_minutes old, there must still be someone in the room and the switch is not switched off.
Here's an example of what to put in a device's description field to make it switch off automatically after two minutes:
"auto_off_minutes": 2
And here's an example of how to make a switch go off 1 minute after the last person has left the room:
"auto_off_minutes": 1,
"auto_off_motion_device": "Overloop 1: Motion"
Another example to show how to use multiple motion sensors for a single light. If either of the sensors still shows activity, the light remains on (thanks @waaren!):
"auto_off_motion_device": ["Overloop 1: Motion 1", "Overloop 1: Motion 2"]
If I want to make a new switch go off automatically, I don't need to go into my scripts any more, I simply enter the proper values in the device's description field and it will use the new settings.
Here's the script I wrote for this.
-- This script will run every minute and can automatically send an 'Off' command to turn off any device after
-- it has been on for some specified time. Each device can be individually configured by putting json coded
-- settings into the device's description field. The settings currently supported are:
-- - "auto_off_minutes" : <time in minutes>
-- - "auto_off_motion_device" : "<name of a motion detection device>"
-- If "auto_off_minutes" is not set, the device will never be turned off by this script. If
-- "auto_off_minutes" is set and <time in minutes> is a valid number, the device will be turned off when it
-- is found to be on plus the device's lastUpdate is at least <time in minutes> minutes old. This behavior
-- can be further modified by specifying a valid device name after "auto_off_motion_device". When a motion
-- device is specified and the device's lastUpdate is at least <time in minutes> old, the device will not
-- be turned off until the motion device is off and it's lastUpdate is also <time in minutes> old.
-- Specifying "auto_off_motion_device" without specifying "auto_off_minutes" does nothing.
-- Example 1: turn off the device after 2 minutes:
-- "auto_off_minutes": 2
-- Example 2: turn off the device when it has been on for 5 minutes and no motion has been detected for
-- at least 5 minutes:
-- "auto_off_minutes": 5,
-- "auto_off_motion_device": "Overloop: Motion"
		-- timer triggers
		timer = {
			'every minute'
	execute = function(domoticz, triggeredItem, info)
	    local cnt = 0
		domoticz.devices().forEach(
	        function(device)
	            cnt = cnt + 1
	            if device.state ~= 'Off' then
    	            local description = device.description
    	            if description ~= nil and description ~= '' then
    	                local ok, settings = pcall( domoticz.utils.fromJSON, description)
    	                if ok and settings ~= nil then
    	                    if settings.auto_off_minutes ~= nil and device.lastUpdate.minutesAgo >= settings.auto_off_minutes then
	                            if settings.auto_off_motion_device == nil then
            		                domoticz.log(device.name .. ' is switched off because it has been on for ' .. settings.auto_off_minutes .. ' minutes.', domoticz.LOG_INFO)
	                                device.switchOff()
	                            elseif type(settings.auto_off_motion_device) == "string" then
	                                local motion_device = domoticz.devices(settings.auto_off_motion_device)
                                    if motion_device.state == 'Off' and motion_device.lastUpdate.minutesAgo >= settings.auto_off_minutes then
                		                domoticz.log(device.name .. ' is switched off because no one was in the room for ' .. settings.auto_off_minutes .. ' minutes.', domoticz.LOG_INFO)
    	                                device.switchOff()
                                elseif type(settings.auto_off_motion_device) == "table" then
                                    local off = true
                                    for i,v in ipairs(settings.auto_off_motion_device) do
                                        local d = domoticz.devices(v)
                                        if d.state ~= 'Off' or d.lastUpdate.minutesAgo < settings.auto_off_minutes then
                                            off = false
                                    if off then
                                        device.switchOff()
                            domoticz.log( 'Device description for '.. device.name ..' is not in json format. Ignoring this device.', domoticz.LOG_ERROR)
        domoticz.log('Scanned ' .. tostring(cnt) .. ' devices.', domoticz.LOG_INFO)
Edit: updated to the latest version of the script. Plus pcall is now used correctly to catch invalid json description texts.
Re: Generic auto-off
Posted: Thursday 15 November 2018 0:01
by dizzeenl
Thanks a lot, it works like a charm!
Posted: Thursday 15 November 2018 6:48
by Stief
@rrozema Thanks man!
Was looking for something like this.
I'm not that knowledgeable in scripting, so this is a great help.
Any updates since your first post?
I'll try is later this week.
Posted: Thursday 15 November 2018 8:20
by emme
pure genius! :o
Posted: Wednesday 19 December 2018 2:24
by MarcoC
Thanks for this script, which was a great starting point for what I needed to do.
If anyone can tell me how to properly use pcall() to catch the error, I will be very thankful.
I found that you can use functions in the lodash utilities to make this work properly('_') here is an extract from my script where they are used - it should be easy to adapt to what you need. Hope this helps someone.
    local _ = dz.utils._
    dz.devices().forEach(function(device)
      if (_.isString(description) and description ~= '') then
        local settings = dz.utils.fromJSON(description)
        if (_.isTable(settings) and _.isNumber(settings.offline_timeout)) then
Posted: Saturday 29 December 2018 17:36
by wobbenl
Thanks man!
Posted: Sunday 30 December 2018 23:17
by rrozema
I've made some minor modifications to the auto-off script since my first post.
- fixed error handling when a devices description is not a json format,
- made it possible to specify multiple motion devices per switch; if at least one device has seen motion, the light will not be switched off yet.
I'm not completely sure if I should check the lastupdate on the motion device against the timeout period too. This version only checks if the motion device is 'Off' without an additional delay because the motion devices themselves also have a period they remain on, so adding my own period to that period would make the delay too long in my opinion. I've had this running for some weeks now and I like this best. Please see for yourself which version you like best.
-- Example 2: turn off the device when it has been on for 5 minutes and no motion has been detected by
-- the "Overloop: Motion" device:
-- Example 3: turn off the device when it has been on for 2 minutes and no motion has been detected by
-- either of the "Overloop: Motion" or the "Trap: Motion" devices:
-- "auto_off_minutes": 2,
-- "auto_off_motion_device": ["Overloop: Motion", "Trap: Motion"]
		-- timer triggers
		timer = {
			'every minute'
	-- custom logging level for this script
--	logging = {
--        level = domoticz.LOG_INFO,
--        marker = 'Auto Off'
	    local cnt = 0
	        function(device)
	            cnt = cnt + 1
                --domoticz.log( 'Device "' .. device.name .. '" is "' .. tostring(device.state) .. '".', domoticz.LOG_INFO)
    	                --domoticz.log( 'description = ' .. description .. '.', domoticz.LOG_INFO)
	                                device.switchOff()
                                    if motion_device.state == 'Off' then
    	                                device.switchOff()
                                    local off = true
                                        if domoticz.devices(v).state ~= 'Off' then
                                            off = false
                                    if off then
                                        device.switchOff()
Posted: Monday 28 January 2019 21:36
by papoo
emme wrote: Thursday 15 November 2018 8:20 pure genius! :o
yes, great!
Posted: Friday 01 March 2019 23:51
by raq24
is it possible to set the time after which it is supposed to switch off the last movement or only 1 minute
Posted: Saturday 02 March 2019 9:06
by rrozema
If you specify a motion detector, the light will not turn off for as long as the motion detector sees motion. The light will turn off x minutes after the motion detector has gone off or x minutes after the light was switched on, whichever is last.
Posted: Sunday 03 March 2019 11:54
by papoo
for my personal use I added news notifications features to this great script. If it helps someone
high, low, on, off and timeout threshold notification with quiet hours management and frequency notification for switch, temperature, hygrometry, percentage, custom and alert devices
original script by rrozema Generic auto-off : https://www.domoticz.com/forum/viewtopic.php?f=72&t=23717&p=205159&hilit=auto+off#p201976
author = papoo
maj : 06/05/2019
this version need a waaren script, Universal function notification :
https://www.domoticz.com/forum/viewtopic.php?f=59&t=26542#p204958
https://pon.fr/dzvents-fonction-de-notification-universelle/
blog url : https://pon.fr/dzvents-script-de-notification-ultime-mais-pas-que
forum url : https://easydomoticz.com/forum/viewtopic.php?f=17&t=8167
github url : https://github.com/papo-o/domoticz_scripts/blob/master/dzVents/scripts/JsonDescription.lua
Example 1:
turn off the device after 2 minutes :
Exemple 1 :
éteindre l'appareil après 2 minutes :
Example 2:
    the "Overloop: Motion" device :
Exemple 2 : éteindre l'appareil lorsqu'il est allumé depuis 5 minutes et qu'aucun mouvement n'a été détecté par
    le dispositif "Overloop: Motion":
exemple 3: éteindre l'appareil lorsqu'il est allumé depuis 2 minutes et qu'aucun mouvement n'a été détecté par
    l’un des dispositifs "Overloop: Motion" ou "Trap: Motion":
"auto_off_motion_device": ["Overloop": "Motion", "Trap": "Motion"]
With this new version you can :
    - be notified if temperature and or hygrometry exceed min or max threshold.
    - be notified if device is on, off or out
    you can mix the desired notifications, such as only the maximum temperature rise,
    or the minimum and maximum humidity, or do not set quiet hours, or minimum temperature and timout
    if you want to use the notification functions, the frequency of notifications is necessary
Avec cette nouvelle version vous pouvez :
    - être averti après le délai défini si la température et / ou l'hygrométrie dépassent le seuil minimal ou maximal.
    - être averti si un périphérique est allumé, éteint ou hors service
    vous pouvez mélanger les notifications souhaitées, telles que uniquement le dépassement de température maxi,
    ou  l'hygrométrie mini et maxi, ou ne pas définir d'heures calmes, ou température mini et timeout
    si vous souhaitez utiliser les fonctions de notification,  la fréquence de notifications est nécessaire
Example 4 : be notified if temperature or hygrometry exceed min or max threshold for a number of minutes
    with notifications frequency in minutes and quiet hours notification
Exemple 4 : être averti si la température ou l'hygrométrie dépasse les seuils minimal ou maximal pendant un certain nombre de minutes
    avec fréquence de notifications en minutes et notification des heures calmes
 "low_threshold_temp": 10,
 "high_threshold_temp": 40,
 "duration_exceeded_temp": 20,
 "low_threshold_hr": 25,
 "high_threshold_hr": 75,
 "duration_exceeded_hr": 20,
 "frequency_notifications": 60,
 "quiet_hours":"23:00-07:15"
Example 5 : be notified if device is on since x minutes
Exemple 5 : être averti si le périphérique est allumé depuis x minutes
 "time_active_notification": 120,
Example 6 : be notified if device is off since x minutes
Exemple 6 : être averti si le périphérique est éteint depuis x minutes
 "time_inactive_notification": 2,
Example 7 : be notified if device is out since x minutes
Exemple 7 : être averti si le périphérique est hors service depuis x minutes
"timeout_notification": 1440,
Example 8 : be notified if a device% exceeds the minimum or maximum thresholds
    with frequency of notifications in minutes and notification of quiet hours
Exemple 8 : être averti si un périphérique % dépasse les seuils minimal ou maximal
 "low_threshold_percent": 10,
 "high_threshold_percent": 40,
 "duration_exceeded_percent": 20,
Example 9 : be notified if a Custom Sensor device exceeds the minimum or maximum thresholds
Exemple 9 :être averti si un périphérique Custom Sensor dépasse les seuils minimal ou maximal
 "low_threshold_custom": 1000,
 "high_threshold_custom": 4000,
Example 10: Be notified if an Alert device exceeds a predefined threshold (1,2,3 or 4)
Exemple 10 : être averti si un périphérique Alert dépasse un seuil prédéfini (1,2,3 ou 4)
 "high_threshold_color": 4,
Fonctionnalités proposées par denis_brasseur
Example 11: Be notified if a device's battery is below a low threshold
Exemple 11 : être averti si la batterie d'un périphérique est inférieure un seuil bas
 "low_battery_level": 30,
 "high_threshold_temp": -15,
Example 12: Be notified if the signal level (zwave, rfxcom) of a device is below a low threshold
Exemple 12 : être averti si le niveau de signal (zwave, rfxcom) d'un périphérique est inférieure un seuil bas
 "low_signal_level": 2,
Example 13: Be notified if a power device exceeds a high threshold or a low threshold set
Exemple 13 : être averti si un périphérique puissance dépasse un seuil haut ou un seuil bas défini
 "low_watt_usage": 0,
 "high_watt_usage": 10000,
 Example 14: Be notified if an intensity device exceeds a high threshold or a low threshold set
 Exemple 14 : être averti si un périphérique intensité dépasse un seuil haut ou un seuil bas défini
 "low_current_usage": 0,
 "high_current_usage": 60,
  Example 15 : turn on the device after x minutes:
  Exemple 15 : allumer l'appareil après x minutes:
"auto_on_minutes": 1
Example 16 : be notified if device is off since x minutes
    with notifications frequency in minutes and quiet hours notification only on telegram notifications
    Notification systems available:
    GOOGLE_CLOUD_MESSAGING, HTTP, KODI, LOGITECH_MEDIASERVER, NMA, PROWL, PUSHALOT, PUSHBULLET,PUSHOVER, PUSHSAFER, TELEGRAM
Exemple 16 : être averti si le périphérique est éteint depuis x minutes
    avec fréquence de notifications en minutes et notification des heures calmes seulement via les notifications TELEGRAM
    Systèmes de notification disponibles :
  "subsystems" : "TELEGRAM",
Example 17 : be notified if device is off since x minutes
    with notifications frequency in minutes and quiet hours notification only on TELEGRAM and PUSHBULLET notifications
    For multi-system notification, separate the systems with a comma.
Exemple 17 : être averti si le périphérique est éteint depuis x minutes
    avec fréquence de notifications en minutes et notification des heures calmes seulement via les notifications TELEGRAM et PUSHBULLET
    Pour une notification sur plusieurs systèmes, séparez les systèmes par une virgule.
  "subsystems" : "TELEGRAM,PUSHBULLET",
--permet de lire les valeurs des périphériques avec "duration_exceeded_temp", "low_threshold_hr", "high_threshold_hr" ou  "duration_exceeded_hr"
function managed(dz, id, duration_exceeded, high_threshold, low_threshold)
    test_high_threshold = true
    test_low_threshold = true
    x = 0
    dz.data.managedId.forEach(
        function(item)
            x = x + 1
            if item.data == id then
                timeNotif = tonumber(item.time.minutesAgo)
                local value = dz.data.managedValue.get(x)
                if timeNotif < duration_exceeded then -- on test si l'ancienneté de la valeur est < à la valeur duration_exceeded_temp
                    if high_threshold ~= nil then -- si la value est < à la valeur de ref, on passe la variable à false => pas d'envoi de notification
                        if value.data <= high_threshold then test_high_threshold = false end
                    if low_threshold ~= nil then -- si la value est > à la valeur de ref, on passe la variable à false => pas d'envoi de notification
                        if value.data >= low_threshold then test_low_threshold = false end
    return test_high_threshold, test_low_threshold
local scriptName = 'Json Description'
local scriptVersion = '1.01'
    active = true,
        -- timer triggers
        timer = {
            'every minute'
    logging = {
                -- level    =   domoticz.LOG_DEBUG,
                -- level    =   domoticz.LOG_INFO,             -- Seulement un niveau peut être actif; commenter les autres
                -- level    =   domoticz.LOG_ERROR,            -- Only one level can be active; comment others
                -- level    =   domoticz.LOG_MODULE_EXEC_INFO,
                marker = scriptName..' v'..scriptVersion
    -- permet de stocker les valeurs des périphériques avec "duration_exceeded_" sous /home/pi/domoticz/scripts/dzVents/data/__data_JsonDescription.lua
   data = {
        managedValue = { history = true, maxItems = 3600, maxHours = 6 },
        managedId = { history = true, maxItems = 3600, maxHours = 6 },
        local cnt = 0
        function split(s, delimiter)
        if s ~= nil then
            result = {};
            for match in (s..delimiter):gmatch("(.-)"..delimiter) do
                table.insert(result, match);
            result = {""};
        return result;
        function notificationTable(str)
        --NSS_GOOGLE_CLOUD_MESSAGING, NSS_HTTP, NSS_KODI, NSS_LOGITECH_MEDIASERVER, NSS_NMA,NSS_PROWL, NSS_PUSHALOT, NSS_PUSHBULLET, NSS_PUSHOVER, NSS_PUSHSAFER, NSS_TELEGRAM
            if (str) then
            str = string.gsub (str,"GCM", domoticz.NSS_GOOGLE_CLOUD_MESSAGING)
            str = string.gsub (str,"GOOGLE_CLOUD_MESSAGING", domoticz.NSS_GOOGLE_CLOUD_MESSAGING)
            str = string.gsub (str,"HTTP", domoticz.NSS_HTTP)
            str = string.gsub (str,"LMS", domoticz.NSS_LOGITECH_MEDIASERVER)
            str = string.gsub (str,"LOGITECH_MEDIASERVER", domoticz.NSS_LOGITECH_MEDIASERVER)
            str = string.gsub (str,"NMA", domoticz.NSS_NMA)
            str = string.gsub (str,"PROWL", domoticz.NSS_PROWL)
            str = string.gsub (str,"PUSHALOT", domoticz.NSS_PUSHALOT)
            str = string.gsub (str,"PUSHOVER", domoticz.NSS_PUSHOVER)
            str = string.gsub (str,"PUSHSAFER", domoticz.NSS_PUSHSAFER)
            str = string.gsub (str,"PUSHBULLET", domoticz.NSS_PUSHBULLET)
            str = string.gsub (str,"TELEGRAM", domoticz.NSS_TELEGRAM)
        return (split(str,','))
        local subject               = "/!\\ Attention /!\\"           -- sujet des notifications
            function(device)
                cnt = cnt + 1
                local frequency_notifications = nil
                local quiet_hours = nil
                local message = nil
                local subSystems = nil
                local j = string.find(tostring(description), '^{.*}$')
                if description ~= nil and description ~= '' and j ~= nil then
                    if ok and settings then
                        if settings.subsystems ~= nil then -- systeme(s) de notification
                            subSystems = settings.subsystems
                            domoticz.log('le(s) systeme(s) de notification pour '.. device.name .. ' est(sont)  ' .. subSystems, domoticz.LOG_INFO)
                        if settings.frequency_notifications ~= nil then -- fréquence de notification
                            frequency_notifications = settings.frequency_notifications
                            domoticz.log('la fréquence de notification pour '.. device.name .. ' est de  ' .. settings.frequency_notifications.." minutes", domoticz.LOG_INFO)
                        if settings.quiet_hours ~= nil then -- période silencieuse
                            quiet_hours = settings.quiet_hours
                            domoticz.log('la période silencieuse de notification pour '.. device.name .. ' est définie entre  ' .. quiet_hours, domoticz.LOG_INFO)
                        if device.temperature ~= nil and settings.high_threshold_temp ~= nil then  -- seuil haut température
                            domoticz.log(device.name .. ' a un seuil temperature haute défini à  ' .. settings.high_threshold_temp..'°C', domoticz.LOG_INFO)
                        if device.temperature ~= nil and settings.low_threshold_temp ~= nil then  -- seuil bas température
                            domoticz.log(device.name .. ' a un seuil temperature basse défini à  ' .. settings.low_threshold_temp..'°C', domoticz.LOG_INFO)
                        if device.percentage ~= nil and settings.high_threshold_percent ~= nil then  -- seuil haut %
                            domoticz.log(device.name .. ' a un seuil % haut défini à  ' .. settings.high_threshold_percent..'%', domoticz.LOG_INFO)
                        if device.percentage ~= nil and settings.low_threshold_percent ~= nil then  -- seuil bas %
                            domoticz.log(device.name .. ' a un seuil % bas défini à  ' .. settings.low_threshold_percent..'%', domoticz.LOG_INFO)
                        --sensorType
                        if device.sensorType ~= nil and settings.high_threshold_custom ~= nil then  -- seuil haut sensorType
                            domoticz.log(device.name .. ' a un seuil haut défini à  ' .. settings.high_threshold_custom..' '..device.sensorUnit, domoticz.LOG_INFO)
                        if device.sensorType ~= nil and settings.low_threshold_custom ~= nil then  -- seuil bas sensorType
                            domoticz.log(device.name .. ' a un seuil bas défini à  ' .. settings.low_threshold_custom..' '..device.sensorUnit, domoticz.LOG_INFO)
                        --low_watt_usage
                        if device.WhActual ~= nil and settings.low_watt_usage ~= nil then  -- seuil bas sensorType
                            domoticz.log(device.name .. ' a un seuil bas défini à  ' .. settings.low_watt_usage..' Wh', domoticz.LOG_INFO)
                        if device.WhActual ~= nil and settings.high_watt_usage ~= nil then  -- seuil bas sensorType
                            domoticz.log(device.name .. ' a un seuil haut défini à  ' .. settings.high_watt_usage..' Wh', domoticz.LOG_INFO)
                        if device.current ~= nil and settings.low_current_usage ~= nil then  -- seuil bas sensorType
                            domoticz.log(device.name .. ' a un seuil bas défini à  ' .. settings.low_current_usage..' A', domoticz.LOG_INFO)
                        if device.current ~= nil and settings.high_current_usage ~= nil then  -- seuil bas sensorType
                            domoticz.log(device.name .. ' a un seuil haut défini à  ' .. settings.high_current_usage..' A', domoticz.LOG_INFO)
                        if device.state == 'Off' or device.state == 'Close' then    -- Alarme dispositif inactif
                            if settings.time_active_notification ~= nil then
                                domoticz.log('Le délai est fixé à '.. settings.time_active_notification.. ' minutes.', domoticz.LOG_INFO)
                        elseif device.state == 'On' or device.state == 'Open' then   -- Alarme dispositif actif
                            if settings.time_inactive_notification ~= nil then
                                domoticz.log('Le délai est fixé à '.. settings.time_inactive_notification.. ' minutes.', domoticz.LOG_INFO)
                        -- Alarme dispositif injoignable
                        if settings.timeout_notification and device.timedOut then
                            domoticz.log(device.name .. ' est injoignable. Sa dernière activité remonte à ' .. device.lastUpdate.minutesAgo .. ' minutes.', domoticz.LOG_INFO)
                            message = device.name .. ' est injoignable depuis '.. tostring(settings.timeout_notification) ..' minutes'
                            domoticz.helpers.managedNotify(domoticz, subject, message, notificationTable(subSystems), frequency_notifications , quiet_hours)
                        --batterie
                        if device.batteryLevel ~= nil and device.batteryLevel ~= 255 and settings.low_battery_level ~= nil then
                            domoticz.log('Le niveau de batterie de '.. device.name .. ' est de  ' .. device.batteryLevel .. '%', domoticz.LOG_INFO)
                            if settings.low_battery_level ~= nil and device.batteryLevel < settings.low_battery_level then  -- seuil bas batterie
                                domoticz.log(device.name .. ' a un niveau de batterie de ' .. device.batteryLevel..'%', domoticz.LOG_INFO)
                                message = 'Le niveau de batterie '.. device.name .. ' est inférieur au seuil défini ('..settings.low_battery_level..'%). Valeur : '..tostring(domoticz.utils.round(device.batteryLevel, 1)) ..'%'
                                --domoticz.log(message, domoticz.LOG_INFO)
                        --low_signal_level
                        if device.signalLevel ~= nil and settings.low_signal_level ~= nil then
                            domoticz.log('Le niveau de signal de '.. device.name .. ' est de  ' .. device.signalLevel, domoticz.LOG_INFO)
                            if settings.low_signal_level ~= nil and device.signalLevel < settings.low_signal_level then  -- seuil bas signal
                                domoticz.log(device.name .. ' a un niveau de signal de ' .. device.signalLevel, domoticz.LOG_INFO)
                                message = 'Le niveau de signal '.. device.name .. ' est inférieur au seuil défini ('..settings.low_signal_level..'). Valeur : '..device.signalLevel
                        --low_watt_usage
                            domoticz.log('Le niveau de puissance de '.. device.name .. ' est de  ' .. device.WhActual..' Wh', domoticz.LOG_INFO)
                            if settings.low_watt_usage ~= nil and device.WhActual < settings.low_watt_usage then  -- seuil bas puissance
                                domoticz.log(device.name .. ' a un niveau de puissance de ' .. device.WhActual..' Wh', domoticz.LOG_INFO)
                                message = 'Le niveau de puissance '.. device.name .. ' est inférieur au seuil défini ('..settings.low_watt_usage..'). Valeur : '..device.WhActual..' Wh'
                            if settings.high_watt_usage ~= nil and device.WhActual > settings.high_watt_usage then  -- seuil haut puissance
                                message = 'Le niveau de puissance '.. device.name .. ' est superieur au seuil défini ('..settings.high_watt_usage..'). Valeur : '..device.WhActual..' Wh'
                        --low_current_usage
                            domoticz.log('Le niveau de '.. device.name .. ' est de  ' .. tostring(domoticz.utils.round(device.current, 0))..' A', domoticz.LOG_INFO)
                            if settings.low_current_usage ~= nil and device.current < settings.low_current_usage then  -- seuil bas intensite
                                domoticz.log(device.name .. ' a un niveau de ' .. tostring(domoticz.utils.round(device.current, 0)), domoticz.LOG_INFO)
                                message = 'Le niveau de '.. device.name .. ' est inférieur au seuil défini ('..settings.low_current_usage..'). Valeur : '..tostring(domoticz.utils.round(device.current, 0))..' A'
                        --current
                            if settings.high_current_usage ~= nil and device.current > settings.high_current_usage then  -- seuil haut intensite
                                message = 'Le niveau '.. device.name .. ' est superieur au seuil défini ('..settings.high_current_usage..'). Valeur : '..tostring(domoticz.utils.round(device.current, 0))..' A'
                            domoticz.log(device.name .. ' est à l\'état ' .. device.state, domoticz.LOG_INFO)
                            if settings.time_inactive_notification ~= nil and device.lastUpdate.minutesAgo >= settings.time_inactive_notification then
                                domoticz.log(device.name .. ' est inactif depuis ' .. device.lastUpdate.minutesAgo .. ' minutes. Le délai est fixé à '.. settings.time_inactive_notification.. ' minutes.', domoticz.LOG_INFO)
                                message = 'Le délai d\'inactivité fixé à '.. settings.time_inactive_notification .. ' minutes pour '.. device.name .. ' est dépassé'
                        elseif device.temperature ~= nil or device.humidity ~= nil then
                        -- Alarme température
                            if device.temperature ~= nil and (settings.low_threshold_temp ~= nil or settings.high_threshold_temp ~= nil)  then
                                --test settings.duration_exceeded_temp
                                if settings.duration_exceeded_temp ~= nil then
                                    domoticz.data.managedValue.add(domoticz.utils.round(device.temperature, 2))
                                    domoticz.data.managedId.add(device.id)
                                    if settings.high_threshold_temp ~= nil then high_threshold_temp = settings.high_threshold_temp else high_threshold_temp = nil end
                                    if settings.low_threshold_temp ~= nil then low_threshold_temp = settings.low_threshold_temp else low_threshold_temp = nil end
                                    --test_high_threshold, test_low_threshold = managed(dz, id, duration_exceeded, high_threshold, low_threshold)
                                    test_high_threshold, test_low_threshold = managed(domoticz, device.id, settings.duration_exceeded_temp, high_threshold_temp, low_threshold_temp)
                                domoticz.log('La température mesurée par '.. device.name .. ' est de  ' .. tostring(domoticz.utils.round(device.temperature, 1)) ..'°C', domoticz.LOG_INFO)
                                if settings.low_threshold_temp ~= nil and device.temperature < settings.low_threshold_temp and test_low_threshold == true then  -- seuil bas température
                                    message = 'La température mesurée par '.. device.name .. ' est inférieure au seuil défini ('..settings.low_threshold_temp..'°C). Valeur : '..tostring(domoticz.utils.round(device.temperature, 1)) ..'°C'
                                        domoticz.data.managedValue.add(settings.low_threshold_temp)
                                if settings.high_threshold_temp ~= nil and device.temperature > settings.high_threshold_temp and test_high_threshold == true then  -- seuil haut température
                                    message = 'La température mesurée par '.. device.name ..' est supérieure au seuil défini ('..settings.high_threshold_temp..'°C). Valeur : '..tostring(domoticz.utils.round(device.temperature, 1)) ..'°C'
                                        domoticz.data.managedValue.add(settings.high_threshold_temp)
                        -- alarme hygrométrie
                            if device.humidity ~= nil and (settings.low_threshold_hr ~= nil or settings.high_threshold_hr ~= nil)  then
                                --test settings.duration_exceeded_hr
                                if settings.duration_exceeded_hr ~= nil then
                                    domoticz.data.managedValue.add(device.humidity)
                                    if settings.high_threshold_hr ~= nil then high_threshold_hr = settings.high_threshold_hr else high_threshold_hr = nil end
                                    if settings.low_threshold_hr ~= nil then low_threshold_hr = settings.low_threshold_hr else low_threshold_hr = nil end
                                    test_high_threshold, test_low_threshold = managed(domoticz, device.id, settings.duration_exceeded_hr, high_threshold_hr, low_threshold_hr)
                                domoticz.log('L\'hygrometrie mesurée par '.. device.name .. ' est de  ' .. tostring(device.humidity)..'%hr', domoticz.LOG_INFO)
                                if settings.low_threshold_hr ~= nil and device.humidity < settings.low_threshold_hr and test_low_threshold == true then -- seuil bas hygrométrie
                                    domoticz.log(device.name .. ' a un seuil hygrometrie bassse défini à  ' .. settings.low_threshold_hr..'%hr', domoticz.LOG_INFO)
                                    message = 'L\'humidité mesurée par '.. device.name .. ' est inférieure au seuil défini ('..settings.low_threshold_hr..'%hr). Valeur : '..tostring(device.humidity)..'%hr'
                                        domoticz.data.managedValue.add(settings.low_threshold_hr)
                                if settings.high_threshold_hr and device.humidity > settings.high_threshold_hr and test_high_threshold == true then -- seuil haut hygrométrie
                                    domoticz.log(device.name .. ' a un seuil hygrometrie haute défini à  ' .. settings.high_threshold_hr..'%hr', domoticz.LOG_INFO)
                                    message = 'L\'humidité mesurée par '.. device.name .. ' est supérieure au seuil défini ('..settings.high_threshold_hr..'%hr). Valeur : '..tostring(device.humidity)..'%hr'
                                        domoticz.data.managedValue.add(settings.high_threshold_hr)
                            if settings.time_active_notification ~= nil and device.lastUpdate.minutesAgo >= settings.time_active_notification then
                                domoticz.log(device.name .. ' est actif depuis ' .. device.lastUpdate.minutesAgo .. ' minutes. Le délai est fixé à '.. settings.time_active_notification.. ' minutes.', domoticz.LOG_INFO)
                                message = 'Le délai fixé à '.. settings.time_active_notification .. ' minutes pour '.. device.name .. ' est dépassé'
                        -- auto on
                            if settings.auto_on_minutes ~= nil and device.lastUpdate.minutesAgo >= settings.auto_on_minutes then
                                if settings.state == 'Off' then
                                    domoticz.log('Allumage de '..device.name .. ' car inactif depuis ' .. settings.auto_on_minutes .. ' minutes.', domoticz.LOG_INFO)
                                    device.switchOn()
                            --auto off
                                    domoticz.log('Extinction de '..device.name .. ' car actif depuis ' .. settings.auto_off_minutes .. ' minutes.', domoticz.LOG_INFO)
                                    device.switchOff()
                                        domoticz.log('Extinction de '.. device.name .. ' car aucune détection de mouvement dans la piece depuis ' .. settings.auto_off_minutes .. ' minutes.', domoticz.LOG_INFO)
                                        device.switchOff()
                                    local off = true
                                            off = false
                                    if off then
                                        device.switchOff()
                       elseif device.sensorType ~= nil and (settings.high_threshold_custom ~= nil or settings.low_threshold_custom ~= nil)  then
                        --alarme custom sensor
                            domoticz.log('La valeur mesurée par '.. device.name .. ' est de  ' .. tostring(domoticz.utils.round(device.state, 1)) .. device.sensorUnit, domoticz.LOG_INFO)
                            if settings.low_threshold_custom ~= nil and tonumber(device.state) < settings.low_threshold_custom then -- seuil bas %
                                domoticz.log(device.name .. ' a un seuil bas défini à  ' .. settings.low_threshold_custom..device.sensorUnit, domoticz.LOG_INFO)
                                message = 'La valeur mesurée par '.. device.name .. ' est inférieure au seuil défini ('..settings.low_threshold_custom..device.sensorUnit..'). Valeur : '..tostring(domoticz.utils.round(device.state, 1))..device.sensorUnit
                            if settings.high_threshold_custom ~= nil and tonumber(device.state) > settings.high_threshold_custom then -- seuil haut %
                                domoticz.log(device.name .. ' a un seuil haut défini à  ' .. settings.high_threshold_custom..device.sensorUnit, domoticz.LOG_INFO)
                                message = 'La valeur mesurée par '.. device.name ..' est supérieure au seuil défini ('..settings.high_threshold_custom..device.sensorUnit..'). Valeur : '..tostring(domoticz.utils.round(device.state, 1))..device.sensorUnit
                        elseif device.percentage ~= nil and (settings.high_threshold_percent ~= nil or settings.low_threshold_percent ~= nil)  then
                            -- test settings.duration_exceeded_hr
                            if settings.duration_exceeded_percent ~= nil then
                                domoticz.data.managedValue.add(device.percentage)
                                if settings.high_threshold_percent ~= nil then high_threshold_percent = settings.high_threshold_percent else high_threshold_percent = nil end
                                if settings.low_threshold_percent ~= nil then low_threshold_percent = settings.low_threshold_percent else low_threshold_percent = nil end
                                test_high_threshold, test_low_threshold = managed(domoticz, device.id, settings.duration_exceeded_percent, high_threshold_percent, low_threshold_percent)
                            -- alarme pourcentage
                            domoticz.log('La valeur mesurée par '.. device.name .. ' est de  ' .. tostring(domoticz.utils.round(device.percentage, 1)) ..'%', domoticz.LOG_INFO)
                            if settings.low_threshold_percent ~= nil and device.percentage < settings.low_threshold_percent and test_low_threshold == true then  -- seuil bas %
                                message = 'La valeur mesurée par '.. device.name .. ' est inférieure au seuil défini ('..settings.low_threshold_percent..'%). Valeur : '.. tostring(domoticz.utils.round(device.percentage, 1)) ..'%'
                                    domoticz.data.managedValue.add(settings.low_threshold_percent)
                            if settings.high_threshold_percent ~= nil and device.percentage > settings.high_threshold_percent and test_high_threshold == true then  -- seuil haut %
                                message = 'La valeur mesurée par '.. device.name ..' est supérieure au seuil défini ('..settings.high_threshold_percent..'%). Valeur : '.. tostring(domoticz.utils.round(device.percentage, 1)) ..'%'
                                    domoticz.data.managedValue.add(settings.high_threshold_percent)
                        elseif device.color ~= nil and settings.high_threshold_color ~= nil and device.color > settings.high_threshold_color then
                            -- notification alerte
                            domoticz.log('Le seuil d\'alerte de '.. device.name .. ' est de  ' .. tostring(device.color), domoticz.LOG_INFO)
                            message = 'Le seuil d\'alerte de  '.. device.name ..' est supérieur au seuil défini ('..settings.high_threshold_color..'). Valeur : '.. tostring(device.color) ..' alerte : '.. tostring(device.text)
                            domoticz.log( 'la description de '.. device.name ..' n\'est pas au format json. Ignorer cet appareil.', domoticz.LOG_ERROR)
                            domoticz.log('--------------------------------------------------------------------------------------------------', domoticz.LOG_INFO)
        domoticz.log(tostring(cnt) .. ' devices scannés.', domoticz.LOG_INFO)
Posted: Monday 06 May 2019 22:31
by papoo
script update (in previous post)
already in v0.9:
- low and high threshold temp notifications
- low and high threshold Hr notifications
- low and high threshold percent notifications
- low and high threshold custom device notifications
- high threshold alert device notifications
- duration exceeded temp and Hr notifications
- frequency notifications
- quiet Hours notifications
- time active and inactive notifications
- timeout notifications
adding in v1.01:
- low battery level
- low signal level
- low and high watt usage
- low and high current usage
- auto on device
- personalized notification system(s) for each device
Posted: Monday 23 December 2019 23:28
by rinyheuvelman
I knew I am not the most talented person when it comes to scripting, but...
Would someone please be so kind to explain it is done in case of multiple motion sensors?
Followed the gives examples which resulted in errors:
2019-12-23 23:12:00.199 Error: dzVents: Error: (2.5.3) Error parsing json to LUA table: /home/pi/domoticz/scripts/dzVents/../lua/JSON.lua:1009: /home/pi/domoticz/scripts/dzVents/../lua/JSON.lua:660: expected colon at char 66 of: {
2019-12-23 23:12:00.199 "auto_off_minutes": 5,
2019-12-23 23:12:00.199 "auto_off_motion_device": {"PIRBadkamer", "XiaomiBadPIR"}
2019-12-23 23:12:00.199 }
2019-12-23 23:12:00.199 Error: dzVents: Error: (2.5.3) Device description for Bad ambiance spot 1 is not in json format. Ignoring this device.
I can't figure out te correct way (most probably quit obvious to others) to list multiple sensors...
Posted: Tuesday 24 December 2019 7:28
by waaren
rinyheuvelman wrote: Monday 23 December 2019 23:28 Would someone please be so kind to explain it is done in case of multiple motion sensors?
Not sure what your question is.
Which version of the script do you use ? Can you post the script you are using now and also what you entered in the description field of your devices controlled by the script ?
Maybe that will help finding what is causing your error(s)
Posted: Tuesday 24 December 2019 9:09
by rrozema
rinyheuvelman wrote: Monday 23 December 2019 23:28 I knew I am not the most talented person when it comes to scripting, but...
Given that you have 2 motion sensors "Overloop: Motion 1" and "Overloop: Motion 2" and want your light to go off 5 minutes after the last motion was detected on either sensor, this would be the text you would need to put in your light's description field:
   "auto_off_motion_device": ["Overloop: Motion 1","Overloop: Motion 2"]
Posted: Tuesday 24 December 2019 9:41
by waaren
rrozema wrote: Tuesday 24 December 2019 9:09 Given that you have 2 motion sensors "Overloop: Motion 1" and "Overloop: Motion 2" and want your light to go off 5 minutes after the last motion was detected on either sensor, this would be the text you would need to put in your light's description field:
   "auto_off_motion_device": "Overloop: Motion 1",
   "auto_off_motion_device": "Overloop: Motion 2"
Are you sure ? Tested with this
        timer = { 'every minute' }},
    execute = function(dz)
        dz.log('-------- first auto_off_motion_device will be overwritten by 2nd')
        description = '{ "auto_off_minutes": 5,   "auto_off_motion_device": "Overloop: Motion 1",   "auto_off_motion_device": "Overloop: Motion 2"}'
        dz.utils.dumpTable(dz.utils.fromJSON(description))
        dz.log('------ should it not be this ?')
        description = '{"auto_off_minutes":5,"auto_off_motion_device":["Overloop: Motion 1","Overloop: Motion 2"]}'
I get this
2019-12-24 09:37:00.312 Status: dzVents: Info: -------- first auto_off_motion_device will be overwritten by 2nd
2019-12-24 09:37:00.314 Status: dzVents: > auto_off_minutes: 5
2019-12-24 09:37:00.314 Status: dzVents: > auto_off_motion_device: Overloop: Motion 2
2019-12-24 09:37:00.314 Status: dzVents: Info: ------ should it not be this ?
2019-12-24 09:37:00.315 Status: dzVents: > auto_off_minutes: 5
2019-12-24 09:37:00.315 Status: dzVents: > auto_off_motion_device:
2019-12-24 09:37:00.315 Status: dzVents: > 1: Overloop: Motion 1
2019-12-24 09:37:00.315 Status: dzVents: > 2: Overloop: Motion 2
2019-12-24 09:37:00.315 Status: dzVents: Info: ------ Finished Script #1
Posted: Tuesday 24 December 2019 9:55
by rrozema
:oops: You're right. I t has been a long time since I last did anything with the scripts (they work, so why fix it ;) ) I will correct my post accordingly.
Also added the example to the opening post.
Posted: Friday 03 January 2020 4:18
by rinyheuvelman
Thanks rrozema and Waarren.
The .rext fin the description field can be read in the errors I copied from the log-file.
I made a copied from the script above, replaced the names with my sensor names.
Only this type of description kept returning errors
My original (as still in the 2nd script rrozema posted aswell in the bi-lingual script papoo posted.
Rrozema's original post, the one he updates,a tiny detail is changed:
{ went to the gym and became [
"auto_off_motion_device": ["PIRBadkamer", "XiaomiBadPIR"]
No errors this time.
[20200103 EDIT] (waaren) also corrected in earlier examples
Posted: Sunday 26 January 2020 22:07
by Vondee
The script runs perfectly. Is it possible instead of turning devices off, set a certain level. I have dimmable lights in the kitchen, and want to turn them to 20% after a certain time when no motion is detected. I tried to do this in lua but I cannot make it work.
Posted: Monday 27 January 2020 0:24
by waaren
Vondee wrote: Sunday 26 January 2020 22:07 The script runs perfectly. Is it possible instead of turning devices off, set a certain level. I have dimmable lights in the kitchen, and want to turn them to 20% after a certain time when no motion is detected. I tried to do this in lua but I cannot make it work.
Warning: [Quick and Dirty way]
If you do not need to control other lights with this script, you could try to change device.switchOff() to device.dimTo(20) on the three lines in the script where you see this command. You also need to change line with
to
if device.level and device.level ~= 20 then