Get sensor values with MQTT into Domoticz [Solved]
FireWizard
Re: Get sensor values with MQTT into Domoticz [Solved]
Post by FireWizard »
Hi @Stiv32
OK, you answered a small part of the question.
1. Have you installed Node Red?
2. Which of the values do you want to use in Domoticz or all?
3. What are the values for pvstatus? (Solar inverter state) Is it a boolean (only 0 or 1)?
4. What are pv1watt and pv2watt? Expressed in W. Does it need a divider??
Same question for pvpowerin (Solar inverter input power) and pvpowerout (Solar inverter output power)
Probably all expressed in W. Does it need a divider?
5. pvfrequentie is in Hz (divided by 100)
6. pvgridvoltage, expressed in V (divided by 10)
7. pvenergytoday (Solar inverter total energy today) in kWh. Does it need a divider?
8. pvenergytotal (Solar inverter total energy) in kWh. Does it need a divider?
9. pv1voltage and pv2voltage in V (divided by 10)
10 pv1current and pv2current in A. Does it need a divider?
11. pvtemperature in degrees Celsius (divided by 10) Is this the outdoor (solar panel) temperature
12, pvipmtemerature in degrees Celsius (divided by 10) Is this the inverter temperature? It looks indoor
If you can answer this, I can support you.
Stiv32
Post by Stiv32 »
Yes
Not all - pvenergytoday(divide by 10),pvgridvoltage(divide by 10),
yes - only 0 ant 1 (on/off)
the power of pv strings - divide by 10
- yes by 10 - only pvpowerout
yes
yes
yes - need by 10
yes by 10
yes
yes - need - by 10
inverter temp - need divide by 10
not needed - internal circut temp.
Stiv32
Post by Stiv32 »
FireWizard
Hello @Stiv32
Thank you for the link, this one is very useful.
As you have already Node Red installed and up and running, I ask you to go to the worksheet (http://IP address:1880) and drag and drop a MQTT input node on the worksheet. Do the same with a "Debug" node and connect these two nodes together.
Configure the "MQTT In " node as follows:
If you have installed the MQTT broker (Mosquitto) on the same device as Node Red you can configure the MQTT node as follows:
Screenshot_MQTT-localhost config.png (30.04 KiB) Viewed 9220 times
For the server, you may insert your local IP address, localhost or 127.0.0.1. The port, you should leave, as default, 1883.
If you have not secured your MQTT broker, with a user name and password, you can leave all other settings as default, otherwise you should fill in your username/password under the "Security" tab.
You can give the server a name, in this case I called it 'localhost'.
The topic should be energy/growatt. Do not use a leading forward slash before 'energy'.
QoS, you can leave for the moment to 0
The output should be 'a parsed JSON object' and the name is up to you.
If you go to the "Debug"pane (CTRL-g d), you should see the same (except the values) as shown in the picture of my post October 13, 19:52h.
Can you confirm this?
Stiv32
Post by Stiv32 »
Yes - i try write funcion:
var msg1 ={};
var msg2 ={};
var msg3 ={};
var msg4 ={};
var msg5 ={};
var msg6 ={};
var msg7 ={};
var msg8 ={};
var msg9 ={};
var msg10 ={};
var msg11 ={};
var msg12 ={};
var msg13 ={};
var msg14 ={};
var msg15 ={};
msg1.payload = {"command":"udevice","idx":1004,"nvalue":0,"svalue": msg.payload.pvstatus};
msg2.payload = {"command":"udevice","idx":1005,"nvalue":0,"svalue": msg.payload.pv1watt};
msg3.payload = {"command":"udevice","idx":1006,"nvalue":0,"svalue": msg.payload.pv2watt};
msg4.payload = {"command":"udevice","idx":1004,"nvalue":0,"svalue": msg.payload.pvpowerin};
msg5.payload = {"command":"udevice","idx":1005,"nvalue":0,"svalue": msg.payload.pvpowerout};
msg6.payload = {"command":"udevice","idx":1006,"nvalue":0,"svalue": msg.payload.pvfrequentie};
msg7.payload = {"command":"udevice","idx":1007,"nvalue":0,"svalue": msg.payload.pvgridvoltage};
msg8.payload = {"command":"udevice","idx":1008,"nvalue":0,"svalue": msg.payload.pvenergytoday};
msg9.payload = {"command":"udevice","idx":1009,"nvalue":0,"svalue": msg.payload.pvenergytotal};
msg10.payload = {"command":"udevice","idx":1010,"nvalue":0,"svalue": msg.payload.pv1voltage};
msg11.payload = {"command":"udevice","idx":1011,"nvalue":0,"svalue": msg.payload.pv2voltage};
msg12.payload = {"command":"udevice","idx":1012,"nvalue":0,"svalue": msg.payload.pv1current};
msg13.payload = {"command":"udevice","idx":1013,"nvalue":0,"svalue": msg.payload.pv2current};
msg14.payload = {"command":"udevice","idx":1014,"nvalue":0,"svalue": msg.payload.pvtemperature};
msg15.payload = {"command":"udevice","idx":1014,"nvalue":0,"svalue": msg.payload.pvipmtemperature};
return [[msg1,msg2,msg3,msg4,msg5,msg6,msg7,msg8,msg9,msg10,msg11,msg12,msg13,msg14,msg15]];
Stiv32
Post by Stiv32 »
Domoticz idx numbers are only for testing
Here output debug - no values
Node-RED
Deploy
14.10.2020, 15:36:10node: 84a689fc.d03c7energy/growatt : msg.payload : Object
{ device: "6FZI9080D7", time: "2020-10-14T15:36:06", buffered: "no", values: object }
14.10.2020, 15:36:10node: a113198c.ab3a5msg.payload : Object
{ command: "udevice", idx: 1004, nvalue: 0 }
{ command: "udevice", idx: 1005, nvalue: 0 }
{ command: "udevice", idx: 1006, nvalue: 0 }
{ command: "udevice", idx: 1007, nvalue: 0 }
{ command: "udevice", idx: 1008, nvalue: 0 }
{ command: "udevice", idx: 1009, nvalue: 0 }
{ command: "udevice", idx: 1010, nvalue: 0 }
{ command: "udevice", idx: 1011, nvalue: 0 }
{ command: "udevice", idx: 1012, nvalue: 0 }
{ command: "udevice", idx: 1013, nvalue: 0 }
{ command: "udevice", idx: 1014, nvalue: 0 }
FireWizard
Hi @Stiv32,,
Hi, you are on track, but not completely there.
I suggest, you create the following virtual hardware: Dummy (does nothing, use for virtual switches only) and create 15 virtual sensors under it as follows:
Give the sensors the name you like and note down their IDX numbers. You will need that later.
1. For pvstatus: 1 "Alert" Sensor
2. For pv1watt, pv2watt, pvpowerin and pvpowerout: 4 "Usage" Sensors
3. For pvfrequentie: "Custom" Sensor (on the x-axis fill in Hz).
4. For pvgridvoltage, pv1voltage and pv2voltage: 3 "Voltage" Sensors
5. For pvenergytoday and pvenergytotal: 2 "Custom" Sensors (on the x-axis fill in kWh).
6. For pv1current and pv2current: 2 "Ampere" Sensors
7. For pvtemperature and pvipmtemperature: 2 "Temperature" Sensors.
That makes 15 virtual Sensors. You can omit the ones, you don't want to use.
This will be the flow.
You will have to replace the IDX numbers 1001 - 1015 for the IDX numbers, you wrote down, when created the virtual sensors.
The flow is included below:
[{"id":"1f6fae81.f09fe1","type":"debug","z":"79ac4ad4.26563c","name":"","active":true,"tosidebar":true,"console":false,"tostatus":false,"complete":"false","statusVal":"","statusType":"auto","x":370,"y":220,"wires":[]},{"id":"a0aec7c7.7eb038","type":"mqtt in","z":"79ac4ad4.26563c","name":"MQTT In","topic":"energy/growatt","qos":"0","datatype":"json","broker":"f9f13036.e28b58","x":180,"y":280,"wires":[["1f6fae81.f09fe1","4f7c10a1.d16a5"]]},{"id":"4f7c10a1.d16a5","type":"function","z":"79ac4ad4.26563c","name":"","func":"var msg1 = {}; // pvstatus, Inverter run state\nvar msg2 = {}; // pv1watt, PV1 input watt (0.1W)\nvar msg3 = {}; // pv2watt, PV2 input watt (0.1W)\nvar msg4 = {}; // pvpowerin, Actual input power (0.1W)\nvar msg5 = {}; // pvpowerout, Actual output power (0.1W)\nvar msg6 = {}; // pvfrequentie, Grid frequency (0.01Hz)\nvar msg7 = {}; // pvgridvoltage, Three/single phase grid voltage (0.1V)\nvar msg8 = {}; // pvenergytoday, Today generated energy (0.1KWH)\nvar msg9 = {}; // pvenergytotal, Total generated energy (0.1KWH)\nvar msg10 = {}; // pv1voltage, PV1 voltage (0.1V)\nvar msg11 = {}; // pv2voltage, PV2 voltage (0.1V)\nvar msg12 = {}; // pv1current, PV1 input current (0.1A)\nvar msg13 = {}; // pv2current, PV2 input current (0.1A)\nvar msg14 = {}; // pvtemperature, Inverter temperature (0.1C)\nvar msg15 = {}; // pvipmtemperature, The inside IPM in inverter temperature (0.1C), be aware not available in all inverters!\n\nswitch (msg.payload.values.pvstatus) {\n    case 0 :\n        msg1.payload = {\"command\":\"udevice\",\"idx\":1001,\"nvalue\":0,\"svalue\": \"Waiting\"};\n    break\n\n    case 1 :\n        msg1.payload = {\"command\":\"udevice\",\"idx\":1001,\"nvalue\":1,\"svalue\": \"Normal\"};\n    break\n\n    case 2 :\n        msg1.payload = {\"command\":\"udevice\",\"idx\":1001,\"nvalue\":2,\"svalue\": \"Fault\"};\n    break\n}\n\nmsg2.payload = {\"command\":\"udevice\",\"idx\":1002,\"nvalue\":0,\"svalue\":((msg.payload.values.pv1watt) / 10).toString()};\nmsg3.payload = {\"command\":\"udevice\",\"idx\":1003,\"nvalue\":0,\"svalue\":((msg.payload.values.pv2watt) / 10).toString()};\nmsg4.payload = {\"command\":\"udevice\",\"idx\":1004,\"nvalue\":0,\"svalue\":((msg.payload.values.pvpowerin) / 10).toString()};\nmsg5.payload = {\"command\":\"udevice\",\"idx\":1005,\"nvalue\":0,\"svalue\":((msg.payload.values.pvpowerout) / 10).toString()};\nmsg6.payload = {\"command\":\"udevice\",\"idx\":1006,\"nvalue\":0,\"svalue\":((msg.payload.values.pvfrequentie) / 100).toString()};\nmsg7.payload = {\"command\":\"udevice\",\"idx\":1007,\"nvalue\":0,\"svalue\":((msg.payload.values.pvgridvoltage) / 10).toString()};\nmsg8.payload = {\"command\":\"udevice\",\"idx\":1008,\"nvalue\":0,\"svalue\":((msg.payload.values.pvenergytoday) / 10).toString()};\nmsg9.payload = {\"command\":\"udevice\",\"idx\":1009,\"nvalue\":0,\"svalue\":((msg.payload.values.pvenergytotal) / 10).toString()};\nmsg10.payload = {\"command\":\"udevice\",\"idx\":1010,\"nvalue\":0,\"svalue\":((msg.payload.values.pv1voltage) / 10).toString()};\nmsg11.payload = {\"command\":\"udevice\",\"idx\":1011,\"nvalue\":0,\"svalue\":((msg.payload.values.pv2voltage) / 10).toString()};\nmsg12.payload = {\"command\":\"udevice\",\"idx\":1012,\"nvalue\":0,\"svalue\":((msg.payload.values.pv1current) / 10).toString()};\nmsg13.payload = {\"command\":\"udevice\",\"idx\":1013,\"nvalue\":0,\"svalue\":((msg.payload.values.pv2current) / 10).toString()};\nmsg14.payload = {\"command\":\"udevice\",\"idx\":1014,\"nvalue\":0,\"svalue\":((msg.payload.values.pvtemperature) / 10).toString()};\nmsg15.payload = {\"command\":\"udevice\",\"idx\":1015,\"nvalue\":0,\"svalue\":((msg.payload.values.pvipmtemperature) / 10).toString()};\n\nreturn [[msg1,msg2,msg3,msg4,msg5,msg6,msg7,msg8,msg9,msg10,msg11,msg12,msg13,msg14,msg15]];\n","outputs":1,"noerr":0,"initialize":"","finalize":"","x":360,"y":280,"wires":[["b2f06144.0b9f5","440bf20b.c27ab4"]]},{"id":"b2f06144.0b9f5","type":"debug","z":"79ac4ad4.26563c","name":"","active":true,"tosidebar":true,"console":false,"tostatus":false,"complete":"false","statusVal":"","statusType":"auto","x":550,"y":340,"wires":[]},{"id":"440bf20b.c27ab4","type":"mqtt out","z":"79ac4ad4.26563c","name":"MQTT to Domoticz","topic":"domoticz/in","qos":"0","retain":"","broker":"f9f13036.e28b58","x":570,"y":280,"wires":[]},{"id":"f9f13036.e28b58","type":"mqtt-broker","z":"","name":"localhost","broker":"127.0.0.1","port":"1883","clientid":"","usetls":false,"compatmode":true,"keepalive":"60","cleansession":true,"birthTopic":"","birthQos":"0","birthRetain":"false","birthPayload":"","closeTopic":"","closeQos":"0","closePayload":"","willTopic":"","willQos":"0","willPayload":""}]
Any sensor, you do not want to use, you can comment out the corresponding message (2 places) and omit it from the return.
Actually the only thing that caused that no result has been presented was the path to the data.
You used msg.payload.pvstatus and that should be msg.payload.values.pv1watt, etc.
Looking forward for the result
Stiv32
Post by Stiv32 »
Thank you very much, one question, is it possible to use the pvpowerout and pvenergytoday values in one counter - Electic (instant + counter).
Today I have to complete the test (inverter finished work) - but everything looks very good already and many thanks in advance for your help
FireWizard
Hi, @Stiv32,
You asked:
Yes, that is possible.
You can find the following at: https://piandmore.wordpress.com/2019/02 ... -domoticz/
Electric
The electric sensor will show the current usage of electricity in Watt and the cumulative usage in kWh. You can add digits after the decimal if needed.
{"command":"udevice", "idx":1234, "svalue":"us;cu"}
where us is usage in Watt and cu is cumulative usage in Wh (even though it is displayed in kWh)
To do so: Create a virtual Sensor of type Electric (Instant + Counter)
Do the configuration as below:
To send the data to Domoticz, you have to change the command to:
msg16.payload = {"command":"udevice","idx":13,"nvalue":0,"svalue":((msg.payload.values.pvpowerout) / 10).toString() + ";" + ((msg.payload.values.pvenergytoday) * 100).toString()};
return msg16
You can replace two of the lines by this one, e.g comment out msg5 and msg8. Remove these two from the "return" line.
Declare a new msg, e.g. msg16 and add the line below. Add it also in the "return" line.
Last edited by FireWizard on Thursday 15 October 2020 21:04, edited 1 time in total.
Stiv32
Post by Stiv32 »
Hello, one more big thank you to FireWizard - with his great help, we managed to run a thorough monitoring of the PV Growatt Inverter - all possible parameters. Software used: https://github.com/johanmeijer/grott and the above translation to Domoticz by Node Red
FireWizard
Hi, @Stiv
That looks good. The only thing is that you have several sensors with a red bar.
This is caused by a sensor time-out.You can solve that by increasing this time-out.
Go to: Setup > Settings > Other > Sensor Timeout
E.g for 1 day ( = 24h) you have to insert 24 x 60 (minutes) = 1440
Stiv32
Post by Stiv32 »
After changing the timeout it looks better, thanks again.
johanm
Post by johanm »
Nice! Well done.
Is it oke when I link to this topic from my Grott Github pages (wiki)?
Regards,
Johan
FireWizard
Hi @johanm,
I don't think, that there is any legal objection to link to this topic.
However, this topic started with a post of @McMellow about the iSpindle, followed by requests for a Wiki, and ended with the Growatt inverter..
For clearity you should mention that.
But I suggest you contact the board administrator about this.
joostnl
Post by joostnl »
I don't wanna steal the topic but i have a simular issue.
I have an ESP32 with OPENMQQTgateway with read out the xiaomi flower sensor with bluetooth.
topic mqtt in: home/OpenMQTTGateway_ESP32_BLE/BTtoMQTT/C47C8D66476D
With debug i get:
{"id":"C4:7C:8D:66:47:6D","name":"Flower care","rssi":-87,"distance":18.07764,"model":"HHCCJCY01HHCC","moi":40}
moi is the moisture level i need
sometimes i get more info, {"id":"C4:7C:8D:66:47:6D","name":"Flower care","rssi":-91,"distance":25.51913,"model":"HHCCJCY01HHCC","tem":20.3,"tempc":20.3,"tempf":68.54}
With the function:
var msg1 ={};
var msg2 ={};
msg1.payload = {"command":"udevice","idx":230,"nvalue":0,"svalue": msg.payload.moi};
msg2.payload = {"command":"udevice","idx":229,"nvalue":0,"svalue": msg.payload.tempc};
return [[msg1,msg2]];
i get the folowing debug from nodered:
{"command":"udevice","idx":229,"nvalue":0,"svalue":20.4}
and sometimes:
{"command":"udevice","idx":230,"nvalue":0,"svalue":40}
i made a dummy hardware and tried temperature/percentage/custom sensor but the sensors don't get updated.
Domoticz log:
2020-10-25 15:45:58.054 Error: MQTT: unknown idx received! (idx 0)
2020-10-25 15:47:03.797 Error: MQTT: Invalid data received!
2020-10-25 15:51:29.060 Error: MQTT: Invalid data received!
2020-10-25 15:52:40.796 Error: MQTT: Invalid data received!
2020-10-25 15:53:44.105 Error: MQTT: Invalid data received!
2020-10-25 15:54:49.966 Error: MQTT: Invalid data received!
2020-10-25 15:55:50.062 Error: MQTT: Invalid data received!
i looked at https://piandmore.wordpress.com/2019/02 ... -domoticz/ but my knowdledge i too low.
I can see that when no sensor value is detected it sends, nvalue:0, so its updated to 0, its just not updating svalue
Can someone explain how to get the sensor values in domoticz?
THanks!!!
FireWizard
Hello,@joostnl
I see 2 issues in your application.
1,
You said:
With debug i get:
The first stream gives you the "moi" (moisture level).
This is indicated in the upper picture.
Sometimes (but not always!!!!) you get more info. You get extra temperature information.
The temperature, temperature in Celsius (is the same as temperature) and the temperature in Fahrenheit.
This is reflected in the lower picture.
As you can see the "moi" and the "tem" are in different messages. So, if you want to send these to Domoticz in a single message, you will have to merge these first. That is complicated, because the first message has to wait on the second. When will the second arrive?
So the best solution is not to merge and to send the messages independent.
2
Both temperature, percentage and also the custom sensor require a format, like {"command":"udevice", "idx":1234, "svalue":"3.45"}.
See: https://piandmore.wordpress.com/tag/domoticz/
As you also can see, the value after "svalue" : is between " " ("3.45"), which means that it is a string.
Remember that all values after svalue should be strings, like all values after nvalue should be numerical values.
In the upper picture you see the value as a numerical value (blue, without " ") and the lower picture you see it as a string value ( red, with " ").
So, in order to create a message, that Domoticz understands, you have to convert the number to a string.
The function to do this is toString().
So the message in the function node will become:
msg.payload = {"command":"udevice","idx":229,"nvalue":0,"svalue": msg.payload.tempc.toString()};
return msg;
and similar:
msg.payload = {"command":"udevice","idx":230,"nvalue":0,"svalue": msg.payload.moi.toString()};
return msg;
As the above is for a single solution, we have to solve also issue one.
Have a look to the flow below:
The two Inject nodes act as your input from the Plant sensor via MQTT.
Only payloads with "moi" and "temp" will pass to the output, with the correct IDX. Everything else is blocked.
[{"id":"80f399dc.fc0558","type":"tab","label":"Test","disabled":false,"info":""},{"id":"bb960a7a.6f0308","type":"inject","z":"80f399dc.fc0558","name":"Inject  Temperature","props":[{"p":"payload"},{"p":"topic","vt":"str"}],"repeat":"","crontab":"","once":false,"onceDelay":0.1,"topic":"","payload":" {\"id\":\"C4:7C:8D:66:47:6D\",\"name\":\"Flower care\",\"rssi\":-91,\"distance\":25.51913,\"model\":\"HHCCJCY01HHCC\",\"tem\":20.3,\"tempc\":20.3,\"tempf\":68.54}","payloadType":"json","x":170,"y":160,"wires":[["baec393.44fb8c8"]]},{"id":"b89c69be.dd2cb8","type":"inject","z":"80f399dc.fc0558","name":"Inject Moi","props":[{"p":"payload"},{"p":"topic","vt":"str"}],"repeat":"","crontab":"","once":false,"onceDelay":0.1,"topic":"","payload":" {\"id\":\"C4:7C:8D:66:47:6D\",\"name\":\"Flower care\",\"rssi\":-87,\"distance\":18.07764,\"model\":\"HHCCJCY01HHCC\",\"moi\":40}","payloadType":"json","x":140,"y":240,"wires":[["baec393.44fb8c8"]]},{"id":"3f5e8c5b.a61d5c","type":"debug","z":"80f399dc.fc0558","name":"","active":true,"tosidebar":true,"console":false,"tostatus":false,"complete":"false","statusVal":"","statusType":"auto","x":570,"y":220,"wires":[]},{"id":"baec393.44fb8c8","type":"function","z":"80f399dc.fc0558","name":"","func":"if (msg.payload.hasOwnProperty(\"moi\")){\n    msg.payload = {\"command\":\"udevice\",\"idx\":230,\"nvalue\":0,\"svalue\": msg.payload.moi.toString()};\n    return msg;\n} else if (msg.payload.hasOwnProperty(\"tem\")){\n    msg.payload = {\"command\":\"udevice\",\"idx\":229,\"nvalue\":0,\"svalue\": msg.payload.tempc.toString()};\n    return msg;\n} else {\n    return;\n}","outputs":1,"noerr":0,"initialize":"","finalize":"","x":380,"y":220,"wires":[["3f5e8c5b.a61d5c"]]}]
Play with it and implement it.
joostnl
Post by joostnl »
@Firewizard Your help is appreciated!
Your flow works great the domoticz sensors are being updated.
I finalized it, the injectors are only for test purpose (im new :lol: )
I expanded your function:
tem = temperature
moi = moisture
lux = lux :mrgreen:
fer = fertility
Final function:
if (msg.payload.hasOwnProperty("moi")){
    msg.payload = {"command":"udevice","idx":44,"nvalue":0,"svalue": msg.payload.moi.toString()};
    return msg;
} else if (msg.payload.hasOwnProperty("tem")){
    msg.payload = {"command":"udevice","idx":45,"nvalue":0,"svalue": msg.payload.tempc.toString()};
    return msg;
} else if (msg.payload.hasOwnProperty("lux")){
    msg.payload = {"command":"udevice","idx":46,"nvalue":0,"svalue": msg.payload.lux.toString()};
    return msg;
} else if (msg.payload.hasOwnProperty("fer")){
    msg.payload = {"command":"udevice","idx":47,"nvalue":0,"svalue": msg.payload.fer.toString()};
    return msg;
} else {
    return;
Thank you!
FireWizard
Hi @joostnl
Indeed, they injected the same JSON object as you receive by MQTT.
If you want, you can also remove the (green) Debug nodes.
I let them in, in order to show you the different results.
Lipa
Domoticz version: 2024.4
Post by Lipa »
Hello to all.
I also have a problem that I can't solve because I don't know much about Node Red. So I ask you for help.
I have a Solar weather station https://github.com/3KUdelta/Solar_WiFi_Weather_Station
Every 10 minutes a MQTT message is send to the MQTT-broker.
With MQTT-Explorer, I can see the messages on the MQTT-broker.
home
weather
solarweatherstation
tempc = 10.1
humi = 63
abshpa = 992
relhpa = 1027
battv = 4.01
dewpointc = 3.3
heatindexc = 10.1
accuracy = 94
spreadc = 6.7
zambrettisays = Lepo vreme
trendinwords = stabilen
trend = -0.05
In Node Red MQTT input node I get the following values:
12. 11. 2020 13:41:38node: e7f6fdd4.4080d
home/weather/solarweatherstation/tempc : msg.payload : string[3]
"9.9"
home/weather/solarweatherstation/humi : msg.payload : string[3]
" 64"
home/weather/solarweatherstation/abshpa : msg.payload : string[3]
"992"
home/weather/solarweatherstation/relhpa : msg.payload : string[4]
"1027"
home/weather/solarweatherstation/battv : msg.payload : string[4]
"4.01"
home/weather/solarweatherstation/dewpointc : msg.payload : string[3]
"3.3"
home/weather/solarweatherstation/heatindexc : msg.payload : string[3]
"9.9"
home/weather/solarweatherstation/accuracy : msg.payload : string[3]
" 94"
12. 11. 2020 13:41:39node: e7f6fdd4.4080d
home/weather/solarweatherstation/spreadc : msg.payload : string[3]
"6.6"
home/weather/solarweatherstation/zambrettisays : msg.payload : string[10]
"Fine Weather"
home/weather/solarweatherstation/trendinwords : msg.payload : string[8]
"steady"
home/weather/solarweatherstation/trend : msg.payload : string[5]
"-0.05"
How can I get these values into Domoticz Virtual Sensor Type: »temp+hum+baro«
{"command":"udevice", "idx":121, "svalue":"10.1;63;1;1027;2"}
{"command":"udevice", "idx":121, "svalue":"tm;hu;lv;ba;pr"}
where tm is the temperature, hu is the humidity and lv is the environment level, ba is the pressure and pr is the prediction.
Roman
FireWizard
Hello @Lipa
I see that you have already Node Red and a MQTT server running.
Can you connect a "Debug" node, directly after your MQTT Input node and publish a screenshot of the Debug node output, with the tree openen as much as possible. Click on all triangle , so that as much information is visible. There are a number of examples in this thread.
If you open de MQTT input node, insert the following in the "Topic" field: home/weather/solarweatherstation.
Are the temperature, humidity environment level, pressure and prediction the only values, you should like to see send to Domoticz?
I see, also the dewpoint, heatindex, something like trend (also in words).
The list of published MQTT is:
Source: https://github.com/3KUdelta/Solar_WiFi_ ... Settings.h
It is important that the sensors for temperature, humidity and pressure are published at the same moment.
Where should environment level and prediction come from?
"Lepo vreme" means "Nice weather", but that is relative for each person :), but it is not in the Domoticz list.
