Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Monday 31 December 2018 11:40
by dzaq
Hi,
I have an issue with using modbus plugin. Right now I have PLC for controlling lights and heating. I would like to use Domoticz for visualisation.
I have found plugin for Modbus TCP. I tried to install like it is showed in manual, but there is an issue with (i thnink) python version.
2018-12-31 10:19:20.889 Error: (Modbus) failed to load 'plugin.py', Python Path used was '/home/jacek/domoticz/plugins/modbus-read/:/usr/lib/python36.zip:/usr/lib/python3.6:/usr/lib/python3.6:/usr/lib/python3.6/lib-dynload'.
2018-12-31 10:19:20.889 Error: (testowy) Module Import failed, exception: 'ModuleNotFoundError'
2018-12-31 10:19:20.889 Error: (testowy) Module Import failed: ' Name: pymodbus'
2018-12-31 10:19:20.889 Error: (testowy) Error Line details not available.
(Python 3.6.7, Ubuntu 18.04.1 server, Domoticz 4.9701)
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Saturday 05 January 2019 1:24
by raymonvdm
I`m trying to setup the READ plugin to pull an output from a WAGO PLC. I still learning the basics of the PLC but i got a working Node-RED setup using this youtube video
https://www.youtube.com/watch?v=fV78MQks6BI
But when i want to read the value using the plugin it is not working yet. I have 3 input cards four ports so it should be registere 0 - 15 if is stand correct. Seems to be verified by fiddling around with node-red.
But no go so far using READ plugin.
I`m recieving the following error
2019-01-05 01:26:01.380 (DI_01) Modbus error decoding or recieved no data (TCP/IP)!, check your settings!
Code: Select all
Version: 4.10311
Build Hash: e588266e
Compile Date: 2019-01-01 16:54:11
dzVents Version: 2.4.9
Python Version: 3.6.7 (default, Oct 22 2018, 11:32:17) [GCC 8.2.0]
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Tuesday 29 January 2019 13:56
by tomlb
Hi!
Ive downloaded and install Modbus Plugin but I get error:
Error: PluginList: Parsing '/home/pi/domoticz/plugins/modbus-write/', 'Error document empty.' at line 0 column 0 in XML
does anybody know what is wrong?
domoticz Version: 4.9700
python Version: 3.5.3
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Saturday 20 April 2019 14:56
by eSbek
I corrected a little the script for Modbus RTU TCP and Modbus TCP that was giving decoding errors, you can find test version here:
https://github.com/DomoticX/domoticz-modbus/issues/12
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Wednesday 22 May 2019 8:38
by gogofram
Has anybody got the PZEM-016 energy measure device working?
The PZEM-014/016 can measure Ac voltage V, current A, active power W, frequency Hz, power factor pf and used energy Wh. You can read all these values from the PZEM with the help of a Rs-485 Half duplex bus. The protocol they used is the well known modbus protocol.
I tried different settings but I cannot read any data, in the log no errors except check you settings.
I'm using the latest version 1.2 of the read plugin on a raspberry pi with latest stable Domoticz build
Here is a link to the manual
http://kimgrity.com/ac-communication-mo ... OTsA6T-uUk
How can I activated more advanced logging, or try to see more debug information?
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Sunday 02 June 2019 14:15
by eSbek
Try to verify if modbus on the device side is set correcty using PC (eg. Modbus Poll). Once you know it's ok then you can troubleshoot the python.
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Friday 05 July 2019 21:01
by hanskie
@Domoticx, or anyone else
could you help me to read my energy meter with RTU Modbus produced in Poland?
https://www.fif.com.pl/en/index.php?con ... hment=1334
How should i configure Modbus Plugin to read "Active energy" in kWh ? I have added Modbus read and write plugins.
Unfortunately, I do not have experience in this kind of communication and devices but I would like to be able to read the parameters of this power meter in my domoticz.
I would be very grateful for your help.
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Monday 15 July 2019 22:30
by grasuoare
Hi,
Thank you for this plugin! It works like a charm. I have now 2 boards with relays with lights on.
My questions. It is possible to read the state of the relays from the board? The board is the exact model that you used. If yes could you please tell me the settings? I tried all
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Tuesday 16 July 2019 19:45
by ahjwinth
I could use some help. I have an Domoticz running on RPI3B without issues.
I have installed solar panels with an Solar edge inverter which I try to read data from using modbus TCP. I have tested the modbus read option using an simulator on the PC and I can read the requested addresses.
On domoticz installed the modbus option including the dependancies. I have configured the modbus read but whatever I do I get the same error message: "Can't convert 'int' object to str implicitly"
Can someone help me with what I'm doing wrong.
See below:
Code: Select all
2019-07-16 19:39:52.330 Status: (Solaredge) Stopped.
2019-07-16 19:39:56.887 (Solaredge) onStart called
2019-07-16 19:39:56.887 (Solaredge) Debug logging mask set to: NONE
2019-07-16 19:39:56.887 (Solaredge) Sensor Type: Custom
2019-07-16 19:39:56.888 (Solaredge) Modbus RTU/ASCII/TCP - Universal READ loaded.
2019-07-16 19:39:56.525 Status: (Solaredge) Started.
2019-07-16 19:39:56.883 Status: (Solaredge) Entering work loop.
2019-07-16 19:39:56.885 Status: (Solaredge) Initialized version 1.2.0, author 'S. Ebeltjes / domoticx.nl'
2019-07-16 19:40:06.906 Error: (Solaredge) 'onHeartbeat' failed 'TypeError':'Can't convert 'int' object to str implicitly'.
2019-07-16 19:40:06.906 Error: (Solaredge) ----> Line 489 in '/home/pi/domoticz/plugins/modbus-read/plugin.py', function onHeartbeat
2019-07-16 19:40:06.906 Error: (Solaredge) ----> Line 297 in '/home/pi/domoticz/plugins/modbus-read/plugin.py', function onHeartbeat
Configuration:
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Sunday 21 July 2019 20:39
by grasuoare
grasuoare wrote: ↑Monday 15 July 2019 22:30
Hi,
Thank you for this plugin! It works like a charm. I have now 2 boards with relays with lights on.
My questions. It is possible to read the state of the relays from the board? The board is the exact model that you used. If yes could you please tell me the settings? I tried all
Anyone?
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Tuesday 23 July 2019 0:14
by michaelz
hi guys,
i have excactly the same problem :
2019-07-23 00:08:57.565 Error: (lecture modbus) 'onHeartbeat' failed 'TypeError':'Can't convert 'int' object to str implicitly'.
2019-07-23 00:08:57.565 Error: (lecture modbus) ----> Line 489 in /home/pi/domoticz/plugins/modbus-read/plugin.py, function onHeartbeat
i have raspberry pi3b+
installed dependencies
i have tested it with modbus simulator and always the same message
domoticz v4.97000
modbus read v1.2
i use modbus tcp-ip
i have made a lot of test and nothing is working is the v1.2 has a bug ? is the version 4.97 is not working fine?
thank you so mush for your helping
michael
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Tuesday 23 July 2019 0:19
by michaelz
ahjwinth wrote: ↑Tuesday 16 July 2019 19:45
hi same problem is that working when you use modbus slave simulator instead of your solar system ? it is not clear for me?
I could use some help. I have an Domoticz running on RPI3B without issues.
I have installed solar panels with an Solar edge inverter which I try to read data from using modbus TCP. I have tested the modbus read option using an simulator on the PC and I can read the requested addresses.
On domoticz installed the modbus option including the dependancies. I have configured the modbus read but whatever I do I get the same error message: "Can't convert 'int' object to str implicitly"
Can someone help me with what I'm doing wrong.
See below:
Code: Select all
2019-07-16 19:39:52.330 Status: (Solaredge) Stopped.
2019-07-16 19:39:56.887 (Solaredge) onStart called
2019-07-16 19:39:56.887 (Solaredge) Debug logging mask set to: NONE
2019-07-16 19:39:56.887 (Solaredge) Sensor Type: Custom
2019-07-16 19:39:56.888 (Solaredge) Modbus RTU/ASCII/TCP - Universal READ loaded.
2019-07-16 19:39:56.525 Status: (Solaredge) Started.
2019-07-16 19:39:56.883 Status: (Solaredge) Entering work loop.
2019-07-16 19:39:56.885 Status: (Solaredge) Initialized version 1.2.0, author 'S. Ebeltjes / domoticx.nl'
2019-07-16 19:40:06.906 Error: (Solaredge) 'onHeartbeat' failed 'TypeError':'Can't convert 'int' object to str implicitly'.
2019-07-16 19:40:06.906 Error: (Solaredge) ----> Line 489 in '/home/pi/domoticz/plugins/modbus-read/plugin.py', function onHeartbeat
2019-07-16 19:40:06.906 Error: (Solaredge) ----> Line 297 in '/home/pi/domoticz/plugins/modbus-read/plugin.py', function onHeartbeat
Configuration:
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Tuesday 23 July 2019 13:10
by ahjwinth
Hi Michael,
Good to hear I’m not the only one. I still have not found the answer to the issue and trying different things without results. For my work I often deal with modbus in industrial control systems. But I don’t have knowledge about python code to troubleshoot the script.
Regards, Alex
michaelz wrote: ↑Tuesday 23 July 2019 0:14
hi guys,
i have excactly the same problem :
2019-07-23 00:08:57.565 Error: (lecture modbus) 'onHeartbeat' failed 'TypeError':'Can't convert 'int' object to str implicitly'.
2019-07-23 00:08:57.565 Error: (lecture modbus) ----> Line 489 in /home/pi/domoticz/plugins/modbus-read/plugin.py, function onHeartbeat
i have raspberry pi3b+
installed dependencies
i have tested it with modbus simulator and always the same message
domoticz v4.97000
modbus read v1.2
i use modbus tcp-ip
i have made a lot of test and nothing is working is the v1.2 has a bug ? is the version 4.97 is not working fine?
thank you so mush for your helping
michael
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Tuesday 23 July 2019 16:40
by michaelz
hi,
ok i have find the problem
on tcp-ip you need to put the ID
example : 192.168.3.10/1
i can read value in a schneider m241 data settings int16 is working fine
next step writing value
thanks a lot to the author of this plugin
good day
michael z
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Tuesday 23 July 2019 21:11
by ahjwinth
Thanks Michael,
I also now got the modbus connection working. The trick with the ID did it.
I didn't notice this since in the example screenshot on Github this was not implemented yet.
Thanks for your tip and many thanks for the developer putting all the efforts in to make the program.
michaelz wrote: ↑Tuesday 23 July 2019 16:40
hi,
ok i have find the problem
on tcp-ip you need to put the ID
example : 192.168.3.10/1
i can read value in a schneider m241 data settings int16 is working fine
next step writing value
thanks a lot to the author of this plugin
good day
michael z
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Wednesday 24 July 2019 19:04
by Antikillerbm
Hi
Im trying modbus first time. I use domoticz v4.11024@Python 3.5.3
I just upload an example to my arduino and try to read something trough modbus RTU
Code: Select all
#include <ModbusRtu.h>
// assign the Arduino pin that must be connected to RE-DE RS485 transceiver
#define TXEN 2
// data array for modbus network sharing
uint16_t au16data[16] = {
3, 1415, 9265, 4, 2, 7182, 28182, 8, 0, 0, 0, 0, 0, 0, 1, -1 };
/**
* Modbus object declaration
* u8id : node id = 0 for master, = 1..247 for slave
* u8serno : serial port (use 0 for Serial)
* u8txenpin : 0 for RS-232 and USB-FTDI
* or any pin number > 1 for RS-485
*/
Modbus slave(1,0,TXEN); // this is slave @1 and RS-485
void setup() {
slave.begin( 9600 );
}
void loop() {
slave.poll( au16data, 16 );
}
Unfortunately I always get the error that ot depend of payload or register number.
Code: Select all
2019-07-24 19:53:25.632 (test_device) Modbus error decoding or received no data (RTU/ASCII/RTU over TCP)!, check your settings!
On the other side I can read data with modbus poll simulator
What am I doing wrong? Thx.
PS there is no any information what should be a payload for common purpose in domoticz (sensors, buttons etc).
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Wednesday 24 July 2019 22:49
by ahjwinth
Try to use function 3, read holding register in combination with data type int16
Antikillerbm wrote: ↑Wednesday 24 July 2019 19:04
Hi
Im trying modbus first time. I use domoticz v4.11024@Python 3.5.3
I just upload an example to my arduino and try to read something trough modbus RTU
Code: Select all
#include <ModbusRtu.h>
// assign the Arduino pin that must be connected to RE-DE RS485 transceiver
#define TXEN 2
// data array for modbus network sharing
uint16_t au16data[16] = {
3, 1415, 9265, 4, 2, 7182, 28182, 8, 0, 0, 0, 0, 0, 0, 1, -1 };
/**
* Modbus object declaration
* u8id : node id = 0 for master, = 1..247 for slave
* u8serno : serial port (use 0 for Serial)
* u8txenpin : 0 for RS-232 and USB-FTDI
* or any pin number > 1 for RS-485
*/
Modbus slave(1,0,TXEN); // this is slave @1 and RS-485
void setup() {
slave.begin( 9600 );
}
void loop() {
slave.poll( au16data, 16 );
}
Unfortunately I always get the error that ot depend of payload or register number.
Code: Select all
2019-07-24 19:53:25.632 (test_device) Modbus error decoding or received no data (RTU/ASCII/RTU over TCP)!, check your settings!
On the other side I can read data with modbus poll simulator
What am I doing wrong? Thx.
PS there is no any information what should be a payload for common purpose in domoticz (sensors, buttons etc).
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Thursday 25 July 2019 7:44
by Antikillerbm
Every functions gives same error
I even tried to use discrete output slave, but error still the same
Have nothing here
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Thursday 25 July 2019 22:40
by Antikillerbm
I tried example script as well
Code: Select all
#!/usr/bin/env python
from pymodbus.client.sync import ModbusSerialClient
client = ModbusSerialClient(method="rtu", port="/dev/ttyUSB0", stopbits=1, bytesize=8, parity="N", baudrate=9600, timeout=1, retries=2)
data = client.read_input_registers(0, 4, unit=12) # FUNCTIE 04 - Lees register (start=0, lengte=4, unitid=12)
client.close()
print data
print "waarde_0:", data.registers[0]
print "waarde_1:", data.registers[1]
print "waarde_2:", data.registers[2]
print "waarde_3:", data.registers[3]
But the error looks like same with domoticz plugin
Code: Select all
root@orangepipcplus:/home/anti# python3 mbtest.py
Modbus Error: [Input/Output] Modbus Error: [Invalid Message] Incomplete message received, expected at least 2 bytes (0 received)
Traceback (most recent call last):
File "mbtest.py", line 8, in <module>
print("waarde_0:", data.registers[0])
AttributeError: 'ModbusIOException' object has no attribute 'registers'
Slave device answering nothing to any read requests
Re: [RELEASED] Python plugin: Modbus RTU / ASCII / TCP/IP
Posted: Sunday 28 July 2019 10:17
by ahjwinth
Hi I see in the below script you use unit ID 12. Were in the previous screenshots from the windows tool you use function 3 and unit ID 1.
Antikillerbm wrote: ↑Thursday 25 July 2019 22:40
I tried example script as well
Code: Select all
#!/usr/bin/env python
from pymodbus.client.sync import ModbusSerialClient
client = ModbusSerialClient(method="rtu", port="/dev/ttyUSB0", stopbits=1, bytesize=8, parity="N", baudrate=9600, timeout=1, retries=2)
data = client.read_input_registers(0, 4, unit=12) #[b] FUNCTIE 04[/b] - Lees register (start=0, lengte=4,[b] unitid=12)[/b]
client.close()
print data
print "waarde_0:", data.registers[0]
print "waarde_1:", data.registers[1]
print "waarde_2:", data.registers[2]
print "waarde_3:", data.registers[3]
But the error looks like same with domoticz plugin
Code: Select all
root@orangepipcplus:/home/anti# python3 mbtest.py
Modbus Error: [Input/Output] Modbus Error: [Invalid Message] Incomplete message received, expected at least 2 bytes (0 received)
Traceback (most recent call last):
File "mbtest.py", line 8, in <module>
print("waarde_0:", data.registers[0])
AttributeError: 'ModbusIOException' object has no attribute 'registers'
Slave device answering nothing to any read requests