Page 7 of 8
Re: Lua script for controlling humidity in the bathroom
Posted: Sunday 10 November 2019 19:44
by Dekereluitherel
Hi Guys,
frequent reader of the forum, but first post.
I'm having the same problems as BarryT since updating to latest beta:
the script does not work anymore because of the decimal in data from the humidity sensor (xiaomi sensor)
changing the integer to string does not work with me because the targetFanOffHumidity stays 0.
anyone knows how to fix this?
Posted: Sunday 10 November 2019 20:46
by waaren
Dekereluitherel wrote: Sunday 10 November 2019 19:44
There are many different versions of this script flying around on this forum. If you share the version you use (or a link to it) I will have a look.
Posted: Monday 11 November 2019 20:39
by Dekereluitherel
Hi waaren,
This is my script.
This script controls the humidity in a typical bathroom setting by detecting
relative rises in humidity in a short period.
Of course it requires a humidity sensor and a binary switch controlling a fan/ventilator.
(there is no provision for variable speed ventilators here!)
How it works (assuming the default constants as defined below):
Every 5 minutes a reading is done. Every reading is stored together
with the previous reading and is stored in two user variables (humidityTmin5 and humidityTmin10).
So it has two reading over the past 10 minutes.
It then takes the lowest of the two and compares it with the latest reading and
calculates a delta.
If the delta is 3 or higher (see constants) then the fan will be turned
on, it calculates the target humidity and the 'humidity-decrease program' is started (fanFollowsProgram=1).
From then on, every 5 minutes the current humidity is compared to the
stored target humidity. Basically if that target is reached, the fan is turned off
and the 'program' is ended.
Of course, it is possible that the target is never reached (might start raining outside
or whatever). Then there is a failsafe (FAN_MAX_TIME) after which the ventilator
will be turned off.
Also, it will detect if the ventilator is manually switched off during a program
or when it is switched on before the program starts.
Along the lines it prints to the log and sends notifications
but of course you can turn that off by removing those lines.
-- declare some constants
-- adjust to your specific situation
SAMPLE_INTERVAL = 5 -- time in minutes when a the script logic will happen
FAN_DELTA_TRIGGER = 3 -- rise in humidity that will trigger the fan
FAN_MAX_TIME = 15 -- maximum amount of sample cycles the fan can be on,
-- in case we never reach the target humidity
TARGET_OFFSET = 5 -- ventilator goes off if target+offset is reached
-- (maybe it takes too long to reach the true target due to wet towels etc)
FAN_NAME = 'ventilatie percentage' -- exact device name of the switch turning on/off the ventilator
SENSOR_NAME = 'luchtvochtigheid badkamer' -- exact device name of the humidity sensor
TEST_MODE = false -- when true TEST_MODE_HUMVAR is used instead of the real sensor
TEST_MODE_HUMVAR = 'testHumidity' -- fake humidity value, give it a test value in domoticz/uservars
PRINT_MODE = true -- when true wil print output to log and send notifications
if PRINT_MODE == true then
print('Fan control')
-- get the global variables:
-- this script runs every minute, humCounter is used to create SAMPLE_INTERVAL periods
humCounter = tonumber(uservariables['humCounter'])
humidityTmin5 = tonumber(uservariables['humidityTmin5']) -- youngest reading
humidityTmin10 = tonumber(uservariables['humidityTmin10']) -- oldest reading
targetFanOffHumidity = tonumber(uservariables['targetFanOffHumidity']) -- target humidity
fanMaxTimer = tonumber(uservariables['fanMaxTimer'])
fanFollowsProgram = tonumber(uservariables['fanFollowsProgram']) -- marker indicating that the
-- decrease program is started
target = 0 -- will hold the target humidity when the program starts
-- get the current humidity value
if (TEST_MODE) then
current = tonumber(uservariables[TEST_MODE_HUMVAR])
current = otherdevices_humidity[SENSOR_NAME]
-- check if the sensor is on or has some weird reading
if (current == 0 or current == nil) then
print('current is 0 or nil. Skipping this reading')
print('Current humidity:' .. current)
print('targetFanOffHumidity:' .. targetFanOffHumidity)
print('humidityTmin5: ' .. humidityTmin5)
print('humidityTmin10: ' .. humidityTmin10)
print('fanMaxTimer: ' .. fanMaxTimer)
print('humCounter:' .. humCounter)
print('fanFollowsProgram:' .. fanFollowsProgram)
-- increase cycle counter
humCounter = humCounter + 1
if (humCounter >= SAMPLE_INTERVAL) then
if (humidityTmin5 == 0) then
-- initialization, assume this is the first time
humidityTmin5 = current
humidityTmin10 = current
humCounter = 0 -- reset the cycle counter
-- pick the lowest history value to calculate the delta
-- this also makes sure that two relative small deltas in the past 2*interval minutes are treated as one larger rise
-- and therefore will still trigger the ventilator
-- I don't want to use a longer interval instead because I want the ventilator to start as soon as possible
-- (so rather after 5 minutes instead of after 15 minutes because the mirrors in the bathroom become kinda useless ;-)
delta = current - math.min(humidityTmin10, humidityTmin5)
print('Delta: ' .. delta)
target = math.min(humidityTmin10, humidityTmin5) + TARGET_OFFSET
-- shift the previous measurements
humidityTmin10 = humidityTmin5
-- and store the current
if (otherdevices[FAN_NAME]=='Off' or (otherdevices[FAN_NAME]=='On' and fanFollowsProgram==0)) then
-- either the fan is off or it is on but the decrease program has not started
-- in that latter case we start the program anyway. This could happen if someone turns on the ventilator
-- manually because he/she is about to take a shower and doesn't like damp mirrors.
-- I don't do this because the ventilator removes heat from the bathroom and I want this to happen
-- as late as possible ;-)
if (fanFollowsProgram == 1 and otherdevices[FAN_NAME]=='Off') then
-- likely someone turned off the ventilator while the program was running
fanFollowsProgram = 1
-- see if we have to turn it on
if (delta >= FAN_DELTA_TRIGGER) then
-- time to start the fan
commandArray[FAN_NAME] = 'Set Level 99'
targetFanOffHumidity = target
if (fanFollowsProgram == 1) then
print('Ventilator was already on but we start the de-humidifying program')
-- set the safety stop
fanMaxTimer = FAN_MAX_TIME
print('Rise in humidity. Turning on the vents. Delta: ' .. delta)
print('Target humidity for turning the ventilator: ' ..targetFanOffHumidity)
commandArray['SendNotification'] = 'Ventilator is on#The ventilator was activated at humidity level ' .. current .. '#0'
if (fanMaxTimer > 0) then
-- possible that someone started the ventialator manually
fanMaxTimer = fanMaxTimer - 1
if (fanFollowsProgram == 1) then -- not manually started
-- ok, there is another FAN_DELTA_TRIGGER rise in humidity
-- when this happen we reset the fanMaxTimer to a new count down
-- because we have to ventilate a bit longer due to the extra humidity
print('Another large increase detected, resetting max timer. Delta: ' .. delta)
-- first see if it can be turned off
if (current <= targetFanOffHumidity or fanMaxTimer==0) then
commandArray[FAN_NAME] = 'Off'
msg = ''
if (fanMaxTimer == 0 and current > targetFanOffHumidity) then
msg = 'Target not reached but safety time-out is triggered.'
print(msg)
msg = 'Target humidity reached'
print(msg)
print('Turning off the ventilator')
msg = msg .. '\nTurning off the ventilator'
targetFanOffHumidity = 0
fanMaxTimer = 0
fanFollowsProgram = 0
-- reset history in this case.. we start all over
-- Tmin10 is still in the 'ventilator=On'-zone
commandArray['SendNotification'] = 'Ventilator is off#' .. msg .. '#0'
-- we haven't reached the target yet
print('Humidity delta: ' .. delta)
print('New values >>>>>>>>>>>')
print('------ target: ' .. targetFanOffHumidity)
-- save the globals
commandArray['Variable:humCounter'] = tostring(humCounter)
commandArray['Variable:humidityTmin10'] = tostring(humidityTmin10)
commandArray['Variable:humidityTmin5'] = tostring(humidityTmin5)
commandArray['Variable:targetFanOffHumidity'] = tostring(targetFanOffHumidity)
commandArray['Variable:fanMaxTimer'] = tostring(fanMaxTimer)
commandArray['Variable:fanFollowsProgram'] = tostring(fanFollowsProgram)
edit: removing and re-adding the variable targetFanOffHumitiy seems to fix te working of the script!
Posted: Tuesday 12 November 2019 0:24
by waaren
waaren wrote: Tuesday 12 November 2019 0:18
tonumber('12.0') in Lua <= 5.2 returns 12
tonumber('12.0') in Lua >= 5.3 returns 12.0
can you try with this.
calculates a delta.
will be turned off.
local function toInteger(str)
return math.floor(str)
humCounter = toInteger(uservariables['humCounter'])
humidityTmin5 = toInteger(uservariables['humidityTmin5']) -- youngest reading
humidityTmin10 = toInteger(uservariables['humidityTmin10']) -- oldest reading
targetFanOffHumidity = toInteger(uservariables['targetFanOffHumidity']) -- target humidity
fanMaxTimer = toInteger(uservariables['fanMaxTimer'])
fanFollowsProgram = toInteger(uservariables['fanFollowsProgram']) -- marker indicating that the
if (TEST_MODE) then
current = toInteger(uservariables[TEST_MODE_HUMVAR])
current = toInteger(otherdevices_humidity[SENSOR_NAME])
-- possible that someone started the ventilator manually
msg = ''
print(msg)
print(msg)
fanMaxTimer = 0
-- save the globals
Posted: Wednesday 13 November 2019 21:17
by Dekereluitherel
Waaren, thanx for your time. but see edit in my previous post.
i fixed the problem bij re-adding the variable in domoticz. (and making it a string)
the scrips works like a charm again!
Posted: Wednesday 13 November 2019 21:28
by waaren
Dekereluitherel wrote: Wednesday 13 November 2019 21:17
I fixed the problem bij re-adding the variable in domoticz. (and making it a string)
Good to read it is solved.
Reason why I replied anyway is that this type of problem might well affect other Lua scripts comparing integers with floats.
Posted: Tuesday 17 December 2019 20:02
by RikkerdNL
I have searched this topic, but could the script also use FAN_NAME = for a ifttt trigger? I have unflashed sonoff using IFTTT as power switch.
I think I solved it with the solution from post:
https://www.domoticz.com/forum/viewtopi ... 87#p175921 it created a dummy switch that will function with ifttt
Posted: Sunday 30 August 2020 19:07
by Jasper79
I tried to control the bathroom fan with Blockly and it just doesn't work. This script works though the fan is turning off way too soon.
I just took a shower and after 2 minutes the fan came on. Then little over 2 minutes later it turned off.
After me my wife went to the shower and the same thing happened, on and 2 minutes later off.
I checked the humidity sensor and it was 92%, is the script not working, did I do something wrong or can I add a backup somewhere that when humidity is above 80% it stays on?
Thanks,
Posted: Wednesday 02 September 2020 16:01
by Jasper79
Turned on logging and the target is set ot 0 when on.
2020-09-02 16:00:32.568 Status: LUA: humidityTmin10: 82.0
2020-09-02 16:00:32.568 Status: LUA: fanMaxTimer: 11
2020-09-02 16:00:32.568 Status: LUA: humCounter:4
2020-09-02 16:00:32.568 Status: LUA: fanFollowsProgram:1
2020-09-02 16:00:32.568 Status: LUA: Delta: 0.0
2020-09-02 16:00:32.568 Status: LUA: Humidity delta: 0.0
2020-09-02 16:00:32.568 Status: LUA: New values >>>>>>>>>>>
2020-09-02 16:00:32.568 Status: LUA: humidityTmin5: 82.0
2020-09-02 16:00:32.568 Status: LUA: fanMaxTimer: 10
2020-09-02 16:00:32.568 Status: LUA: humCounter:0
2020-09-02 16:00:32.568 Status: LUA: ------ target: 0
2020-09-02 16:00:32.572 Status: EventSystem: Script event triggered: script_time_humidity
2020-09-02 16:00:32.796 Status: LUA: Fan control
2020-09-02 16:00:32.796 Status: LUA: Current humidity:82.0
2020-09-02 16:00:32.797 Status: LUA: targetFanOffHumidity:0
2020-09-02 16:00:32.797 Status: LUA: humidityTmin5: 82.0
2020-09-02 16:00:32.797 Status: LUA: humidityTmin10: 82.0
2020-09-02 16:00:32.797 Status: LUA: fanMaxTimer: 10
2020-09-02 16:00:32.797 Status: LUA: humCounter:0
2020-09-02 16:00:32.797 Status: LUA: fanFollowsProgram:1
2020-09-02 16:00:32.800 Status: EventSystem: Script event triggered: script_time_humidity
2020-09-02 16:00:32.814 Status: LUA: Fan control
2020-09-02 16:00:32.814 Status: LUA: Current humidity:82.0
2020-09-02 16:00:32.814 Status: LUA: targetFanOffHumidity:0
2020-09-02 16:00:32.814 Status: LUA: humidityTmin5: 82.0
2020-09-02 16:00:32.814 Status: LUA: humidityTmin10: 82.0
2020-09-02 16:00:32.814 Status: LUA: fanMaxTimer: 10
2020-09-02 16:00:32.814 Status: LUA: humCounter:1
2020-09-02 16:00:32.814 Status: LUA: fanFollowsProgram:1
2020-09-02 16:00:32.817 Status: EventSystem: Script event triggered: script_time_humidity
Also the counter thats set to 24 goes down very fast, I thought that are minutes??
Posted: Wednesday 02 September 2020 18:01
by waaren
Did you save the script as time triggered?
Posted: Wednesday 02 September 2020 18:15
by Jasper79
Thanks, that's the part I missed I think.
Posted: Thursday 08 October 2020 11:08
by robgeisink
I'm getting these errors (first time use)...what is the problem? or should i let the script be active for some time to retrieve different data?
2020-10-08 11:05:00.234 Error: EventSystem: Error updating variable humidityTmin10: Not a valid integer
2020-10-08 11:05:00.235 Error: EventSystem: Error updating variable humidityTmin5: Not a valid integer
Posted: Thursday 08 October 2020 11:30
by Jasper79
Manual is old.
Posted: Thursday 08 October 2020 12:05
by waaren
Jasper79 wrote: Thursday 08 October 2020 11:30
Manual is old.
Updated the wiki page with a last known working version.
Posted: Thursday 08 October 2020 12:10
by robgeisink
No more errors,
But my fan won't go on...i thought i had the correct vallues
Counter keeps resetting
Status: LUA: Automatisch Keukenspotjes Aan
2020-10-08 12:09:00.593 Status: LUA: Fan control
2020-10-08 12:09:00.593 Status: LUA: Current humidity:74.0
2020-10-08 12:09:00.593 Status: LUA: targetFanOffHumidity:67
2020-10-08 12:09:00.593 Status: LUA: humidityTmin5: 74.0
2020-10-08 12:09:00.593 Status: LUA: humidityTmin10: 74.0
2020-10-08 12:09:00.593 Status: LUA: fanMaxTimer: 0
2020-10-08 12:09:00.593 Status: LUA: humCounter:0
2020-10-08 12:09:00.593 Status: LUA: fanFollowsProgram:0
So it stays op program 0 and counter keeps going round and reset. so it never switches on, not even when humidity is way above target (67)
And another log writing:
2020-10-08 12:20:00.523 Status: LUA: Current humidity:74.0
2020-10-08 12:20:00.523 Status: LUA: targetFanOffHumidity:67
2020-10-08 12:20:00.523 Status: LUA: humidityTmin5: 74.0
2020-10-08 12:20:00.523 Status: LUA: humidityTmin10: 74.0
2020-10-08 12:20:00.524 Status: LUA: fanMaxTimer: 0
2020-10-08 12:20:00.524 Status: LUA: humCounter:3
2020-10-08 12:20:00.524 Status: LUA: fanFollowsProgram:0
2020-10-08 12:20:00.524 Status: LUA: Delta: 0.0
2020-10-08 12:20:00.524 Status: LUA: New values >>>>>>>>>>>
2020-10-08 12:20:00.524 Status: LUA: humidityTmin5: 74.0
2020-10-08 12:20:00.524 Status: LUA: humidityTmin10: 74.0
2020-10-08 12:20:00.524 Status: LUA: humCounter:0
2020-10-08 12:20:00.524 Status: LUA: ------ target: 67
Posted: Thursday 08 October 2020 12:28
by waaren
robgeisink wrote: Thursday 08 October 2020 12:10
No more errors,
From the commentLines:
If the delta is 3 or higher (see constants) then the fan will be turned on
The start of the Fan is not controlled by the humidity as such but by looking at the delta humidity. Your delta is 0 so Fan will not start.
Posted: Thursday 08 October 2020 12:30
by Jasper79
waaren wrote: Thursday 08 October 2020 12:05
Manual is old.
Was looking at a other online version. Thought that was wat he followed according to the error message given.
Posted: Saturday 03 April 2021 14:52
by Hcroij
This thing is killing me
Used the latest script from wiki
https://www.domoticz.com/wiki/Humidity_control
But this time getting the error
script_time_humidity.lua:61: bad argument #1 to 'floor' (number expected, got nil)
Line 61 represents the line in the script
59 -- Function added to overcome compatibility problem between Lua version 5.2 an 5.3
60 local function toInteger(str)
61 return math.floor(str)
62 end
Anyone can offer some help with this ?
Posted: Saturday 03 April 2021 16:20
by Jasper79
I think you changed something to "floor" because I don't remember that being in the script?
Posted: Saturday 03 April 2021 20:40
by Hcroij
@Jasper
Its in the script.
The Wiki script on line 61 on the waaren script (few posts above) its around line 52 or so.
On wiki it says
