Hey guys!
Have this weird problem with my Fibaro FGS-223 Double relay that I just installed.
Switch 1 (S1/Q1) is working as expected. I can turn it on/off via Domoticz, and if I turn the wall-switch on/off Domoticz get updated with the correct value (light bulb icon on/off).
The problem is with Switch 2 (S2/Q2). I can turn it on/off via Domoticz and the status is usually correct (light bulb icon on/off), but not always.
For example I can turn off the light via Domoticz, but the icon (light-bulb) still shows as ON.
If I switch the wall-switch the light turns on and off as expected but the status in Domoticz is never updated here.
Any clues? Can I debug this in some way?
I have just compiled Domoticz and OZW (2021-07-19), so I guess I'm running the latest version.
Best regards
/S
Fibaro FGS-223 Double relay - Status not updated
Moderator: leecollings
-
- Posts: 15
- Joined: Monday 02 November 2015 14:04
- Target OS: Linux
- Domoticz version:
- Contact:
Re: Fibaro FGS-223 Double relay - Status not updated
I became a bit impatient and bought a Qubino Flush 2 Relay and installed. This one works great (switching on/off) via Domoticz interface, but when I flip the wall switch the status does not get updated in Domoticz.
I did a little more reading and realized that maybe it didn't get included correctly regarding "Groups". This is how it looked after inclusion (and not working):
After I configured Group 3 and 6 like below, it works! When I flip the Wall-switch Domoticz get the status update (light bulb icon on/off)
Qubino Flush 2 Relay manual:
Root device:
• Group 1: Lifeline group (reserved for communication with the primary gateway (hub)), 1 node
allowed.
• Group 2: Basic on/off (status change report for Q1 load), up to 16 nodes.
• Group 3: Switch binary report (status change report for Q1 load), up to 16 nodes.
• Group 4: Power meter report (power consumption report of Q1 load at status change), up to 16
nodes.
• Group 5: Basic on/off (status change report for Q2 load), up to 16 nodes.
• Group 6: Switch binary report (status change report for Q2 load), up to 16 nodes.
• Group 7: Power meter report (power consumption report of Q2 load at status change), up to 16
nodes.
• Group 8: Multilevel sensor report (external temperature sensor report – sensor sold separately),
up to 16 nodes.
BRs
/S
I did a little more reading and realized that maybe it didn't get included correctly regarding "Groups". This is how it looked after inclusion (and not working):
After I configured Group 3 and 6 like below, it works! When I flip the Wall-switch Domoticz get the status update (light bulb icon on/off)
Qubino Flush 2 Relay manual:
Root device:
• Group 1: Lifeline group (reserved for communication with the primary gateway (hub)), 1 node
allowed.
• Group 2: Basic on/off (status change report for Q1 load), up to 16 nodes.
• Group 3: Switch binary report (status change report for Q1 load), up to 16 nodes.
• Group 4: Power meter report (power consumption report of Q1 load at status change), up to 16
nodes.
• Group 5: Basic on/off (status change report for Q2 load), up to 16 nodes.
• Group 6: Switch binary report (status change report for Q2 load), up to 16 nodes.
• Group 7: Power meter report (power consumption report of Q2 load at status change), up to 16
nodes.
• Group 8: Multilevel sensor report (external temperature sensor report – sensor sold separately),
up to 16 nodes.
BRs
/S
-