[Resolved] PR: BV (Bad Value)

Post by CaptainSlow »

Hello gents,

Im running the OTGW using an ai thinker ESP-12 wifi to serial module together with a Remeha Tzerra plus (includes the return water temp) and an Isense Thermostat.
All is working pretty fine I would say but once in a while (2 times a day) I sudden see a whole list is PR: BV in the log. the problem resolves itself but Im wandering what causes this.

The OTGW website of Schelte Bron says: BV - Bad Value. The command contained a data value that is not allowed.

But what does it mean really. Who is sending a data value not allowed? The thermostat, the CH (CV) or the OTGW is mizing things itself.
Knipsel.PNG
Knipsel.PNG (21.02 KiB) Viewed 1633 times
Last edited by CaptainSlow on Tuesday 27 October 2020 18:51, edited 1 time in total.
____________________________________________________________________
Raspberry PI 3 Model B with USB stick, Domoticz Stable, OTGW LAN with ESP wifi-bridge and Isense Thermostat using the Outside Temp from Buienradar via Domoticz, Milight Ibox-2(V6)
CaptainSlow
Posts: 60
Joined: Thursday 08 December 2016 21:07
Target OS: Raspberry Pi / ODroid
Domoticz version: Beta
Location: Bussum
Contact:

[Resolved]:Re: PR: BV (Bad Value)

Post by CaptainSlow »

by accident I loaded the wrong firmware on the OTGW. Now running 4.2.5. No PR: BV anymore.