Search found 4 matches
- Thursday 05 January 2017 7:55
- Forum: Heating/cooling
- Topic: Setpoint POPP thermostat
- Replies: 9
- Views: 3166
Re: Setpoint POPP thermostat
Since this topic was kinda dead, I was in doubt of posting the solution I finally found but here goes. First I tried all kind of things, for example altering the manufacturer_specific.xml file, excluding/reincluding the valve, setting the valve to factory settings, updating all kinds of libraries ...
- Monday 05 December 2016 9:31
- Forum: Heating/cooling
- Topic: Setpoint POPP thermostat
- Replies: 9
- Views: 3166
Re: Setpoint POPP thermostat
Unfortunately it doesn't update its setpoint. Didn't know if the time-out had something to do with it. I haven't checked in OZWCP if they are awake when I push the button, though the thermostat needs to be awake when I change the wakeup interval. SInce this works fine, I guess the wake up part works ...
- Sunday 04 December 2016 18:53
- Forum: Heating/cooling
- Topic: Setpoint POPP thermostat
- Replies: 9
- Views: 3166
Re: Setpoint POPP thermostat
300 sec, although I lowered this to 60 sec for testing purposes.
Since that didn't do the trick, I put both back to 300
Since that didn't do the trick, I put both back to 300
- Sunday 04 December 2016 17:48
- Forum: Heating/cooling
- Topic: Setpoint POPP thermostat
- Replies: 9
- Views: 3166
Setpoint POPP thermostat
Hi All, Recently I purchased 2 POPP thermostats (kinda the same as the Danfoss LC-13, but with different firmware). I included both thermostats and they are available in domoticz. However when I try to alter the setpoint, domoticz gets a time-out http://i66.tinypic.com/2af0epe.png This happens to ...